... thanks CarlF... forgive my ignorance, but wouldn't it trip the breakers on the circuits the of the devices that are causing the amperage spikes if that were the case? For example, the Watermaker is almost always on when the genset breaker trips, but the breaker for the WM pump isn't tripped.
|
Yes, a lower rated, downstream circuit breaker
should trip, prior to any higher rated upstream breaker. This is called Selective Coordination.
However, two circuit breakers,
with instantaneous trips, can not be selectively coordinated, for fault currents, above a certain level. That level is
the fault
current at which the upstream circuit breaker operates in its
instantaneous trip region.
When a fault above the instantaneous trip level occurs, the lower
circuit breaker (Device/Equipment) unlatches. However, before it clears the circuit, the upstream circuit breaker(s) [Generator] also unlatches.
Once a circuit breaker unlatches, it will open, thereby disconnecting the circuit from the
power source.
For any fault
current, greater than where the two circuit breaker curves intersect, the upstream circuit breaker does not necessarily coordinate with the down stream circuit breaker.
Circuit breaker coordination is a very technical subject, and I don't remember much detail, from 30+ years ago.