Breaker tripping on Northern Lights generator

I have a Northern Lights M773LW3 7/9KW generator on our catamaran. This season, the 2-pole AC breaker on the generator is tripping regularly. The generator engine runs great and shows normal Temps. It continues to run after the breaker trips. I run the genset each evening to power our watermaker. After about an hour or two of normal operation, the breaker trips (usually right when a little extra load is added - but nowhere near what the generator used to easily handle). I do not see any wiring with obvious signs of overheating. I do notice a slight burning smell from the unit (no smoke and not the smell of burning oil, and again, temps all look normal).

So far, I have:
- Checked for loose electrical connections in the box that houses the AVR, breakers and wiring harness connections.

- Replaced the breaker itself (I originally thought perhaps it had gone bad)

- Removed the top from the insulating box the genset is in and opened the locker that houses it while running to improve airflow. I wondered if maybe an abnormally high ambient temperature might be contributing to the tripping.

What am I missing? Any suggestions would be greatly appreciated!
CWester is offline   Reply With Quote
Old 14-04-2024, 19:57   #2
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,367
Re: Breaker tripping on Northern Lights generator

Start with the easy stuff, take off the generator end plate and see if the brushes are ok. This can be harder than it sounds if the genset is installed with the live end close to a bulkhead or in a sound shell but if the hours are high, this is a wearing part, easy to replace. And yes , run it with the lid off the sound shell, if it makes a difference, pursue the cooling option and put a fan on the control box to cool it.
skipperpete is offline   Reply With Quote
Old 14-04-2024, 20:16   #3
Registered User

Join Date: May 2008
Posts: 3,540
Re: Breaker tripping on Northern Lights generator

The genset doesn’t cause a breaker to trip. A load causes the trip. Replacing the breaker was a good idea but you ruled that out.

So I think something in the boat is intermittently drawing high amperage for a few seconds. Perhaps a wire with frayed insulation shorting to a piece of metal. Or a seizing motor on your watermaker. These can (and should) trip the breaker quickly enough that there’s no smoke or hot wire.

I’d try to figure out which pieces of equipment are always running when this happens. Then turn things off one at a time until you isolate the culprit.
CarlF is offline   Reply With Quote
Old 15-04-2024, 06:21   #4
Registered User

Join Date: Dec 2021
Posts: 3
Re: Breaker tripping on Northern Lights generator

Quote:
Originally Posted by CarlF View Post
The genset doesn’t cause a breaker to trip. A load causes the trip. Replacing the breaker was a good idea but you ruled that out.

So I think something in the boat is intermittently drawing high amperage for a few seconds. Perhaps a wire with frayed insulation shorting to a piece of metal. Or a seizing motor on your watermaker. These can (and should) trip the breaker quickly enough that there’s no smoke or hot wire.

I’d try to figure out which pieces of equipment are always running when this happens. Then turn things off one at a time until you isolate the culprit.
... thanks CarlF... forgive my ignorance, but wouldn't it trip the breakers on the circuits the of the devices that are causing the amperage spikes if that were the case? For example, the Watermaker is almost always on when the genset breaker trips, but the breaker for the WM pump isn't tripped.
CWester is offline   Reply With Quote
Old 15-04-2024, 06:52   #5
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,493
Images: 241
Re: Breaker tripping on Northern Lights generator

Quote:
Originally Posted by CWester View Post
... thanks CarlF... forgive my ignorance, but wouldn't it trip the breakers on the circuits the of the devices that are causing the amperage spikes if that were the case? For example, the Watermaker is almost always on when the genset breaker trips, but the breaker for the WM pump isn't tripped.
Yes, a lower rated, downstream circuit breaker should trip, prior to any higher rated upstream breaker. This is called Selective Coordination.

However, two circuit breakers, with instantaneous trips, can not be selectively coordinated, for fault currents, above a certain level. That level is
the fault current at which the upstream circuit breaker operates in its
instantaneous trip region.
When a fault above the instantaneous trip level occurs, the lower
circuit breaker (Device/Equipment) unlatches. However, before it clears the circuit, the upstream circuit breaker(s) [Generator] also unlatches.
Once a circuit breaker unlatches, it will open, thereby disconnecting the circuit from the power source.
For any fault current, greater than where the two circuit breaker curves intersect, the upstream circuit breaker does not necessarily coordinate with the down stream circuit breaker.

Circuit breaker coordination is a very technical subject, and I don't remember much detail, from 30+ years ago.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
generator, Northern Lights


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Troubleshooting Running Lights Circuit Breaker Tripping DragonflyBob Electrical: Batteries, Generators & Solar 12 06-01-2024 21:38
AC Breaker tripping but not on Generator power Squanderbucks Electrical: Batteries, Generators & Solar 8 07-10-2023 03:54
Generator breaker tripping Snowandsail Electrical: Batteries, Generators & Solar 0 28-06-2022 05:13
DC circuit breaker tripping on Kohler generator JSurr Electrical: Batteries, Generators & Solar 6 15-06-2017 23:35
Northern Lights AC breaker tripping to much HKTim Electrical: Batteries, Generators & Solar 21 31-07-2016 08:57

Advertise Here


All times are GMT -7. The time now is 10:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.