Hi folks,

I'm adding a Victron MultiPlus inverter between shore power and the main breaker of my 120VAC panel. My current AC panel has a single throw main breaker, and there's no ELCI on the boat.

I want to add an ELCI with double pole breaker in the circuit, and I'd want it to be effective when the boat is powered with the inverter only. Basically, I consider the inverter as the main AC source. Which makes me think that I should put the ELCI after the inverter, replacing the main panel's AC single pole breaker. Then I'd add a regular double pole breaker to the shore -> inverter cabling.

Is this okay? Or must I put the ELCI breaker on the shore input line, before the inverter?
__________________
--
Antoine
aybabtme is offline   Reply With Quote
Old 19-01-2020, 09:18   #2
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,084
Re: ELCI breaker before or after inverter?

How much unfused AC cable are you comfortable having in your boat? General rule is put the breaker as soon as possible, because any unfused (or unknown unfused somewhere at the marina) wire can give you a nasty and dangerous AC fire. As in, run like hell.
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 19-01-2020, 09:29   #3
Registered User
 
aybabtme's Avatar

Join Date: Oct 2015
Location: California
Boat: Seawind 1000 XL2
Posts: 189
Re: ELCI breaker before or after inverter?

There's going to be a breaker before and after the inverter, so nothing unfused, but I'd like to buy only 1 ELCI one if possible. I feel that putting it after the inverter will actually provide more effective protection given that the inverter is the primary source of AC.
aybabtme is offline   Reply With Quote
Old 19-01-2020, 09:39   #4
Registered User
 
Dsanduril's Avatar

Join Date: Aug 2011
Location: Petersburg, AK
Boat: Outremer 50S
Posts: 4,229
Re: ELCI breaker before or after inverter?

An ELCI on the output of the inverter will protect in both invert and shore modes, so provides the most protection for the money. However, it will do nothing to protect for faults in the wiring between the shore power inlet and the inverter or inside the inverter itself. Whether to put a second ELCI on the shore side is a risk tolerance question. Personally, we have a similar setup and have a second ELCI mounted on the back side of the shore power connector on the boat. There’s about 150mm of unprotected wire between the shore power terminals and the shore side ELCI. That was our decision, YMMV.
Dsanduril is offline   Reply With Quote
Old 19-01-2020, 09:46   #5
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,084
Re: ELCI breaker before or after inverter?

Hmmm. GFCIs are cheap to install in every outlet, saving your going back to the panel, and supplying better protection because they respond to a smaller imbalance in current than do ELCIs. You have some reason to prefer ELCIs, so at their cost you probably want a central unit at the panel. I went with GFCis, and my only complaint is very occasionally needing to reset one of the on-deck outlets before I use it. They are in gasketed boxes, so it doesn't happen often. I've never felt a shock from a GFCI circuit.
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 19-01-2020, 20:37   #6
Marine Service Provider

Join Date: May 2011
Location: Cruising Mexico Currently
Boat: Gulfstar 50
Posts: 1,979
Re: ELCI breaker before or after inverter?

I use an ELCI before my victron inverter/charger and also GFCI on individual AC circuits in the boat.

It should be noted that the ELCI has a 30 mA leakage current trip and the GFCI have 5 mA trips.

Thus the ELCI is there primarily to protect people in the water near your boat should there be a fault in your boats wiring causing leakage current intot he water. (30 mA)

And GFCI are there to protect the people in your boat in the event they coming in contact with a hot conductor. (5 mA)

You need both.
evm1024 is offline   Reply With Quote
Old 19-01-2020, 21:21   #7
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: ELCI breaker before or after inverter?

@evm1024 post#6: +1
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 20-01-2020, 17:07   #8
Registered User
 
CarinaPDX's Avatar

Join Date: Jan 2010
Location: Portland, Oregon, USA
Boat: 31' Cape George Cutter
Posts: 3,283
Re: ELCI breaker before or after inverter?

FWIW as of 2010 the ABYC standards require an ELCI on the power inlet, with the over-current protection on both conductors (which is usually integral with the ELCI). This protects against any problems with the wiring to the inverter/charger, as well as the inverter/charger itself, and all downstream AC devices when on shore power. Just do it that way. It is the right thing to do.

The AC output of the invert/charger will also need a 2-pole circuit breaker for disconnect/overcurrent protection. Considering that you will have installed weather-resistant GFCI outlets, a second ELCI at the inverter output will only add leakage protection for the downstream AC devices that are hard-wired and for inverter output only - a much smaller set of potential problems. If you currently have a 2-pole breaker then it may not be worth buying a second ELCI; if you need to buy a new 2-pole breaker then it might be worth paying for the second ELCI instead.

Greg
CarinaPDX is online now   Reply With Quote
Old 21-01-2020, 06:49   #9
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: ELCI breaker before or after inverter?

Ideally, you will have a shore power inlet, and within 10ft an AC source panel equipped with ELCI main breaker, source control switch if you have a generator, shore power only load breakers , such as water heater, A/C, and any chargers (including one for the multiplus) etc.

From the multiplus AC out, you connect your load panel, equipped with a main breaker, and all “inverter load” branch circuit breakers. From these any receptacle in a head, galley, machinery space (no gasoline engine compartment or battery compartment) and space possibly exposed to weather, needs to be GFCI protected.

(ABYC Electrical and Marine Systems certified technician).

Make sure the water heater is protected by the ELCI.
ramblinrod is offline   Reply With Quote
Old 21-01-2020, 07:05   #10
Registered User

Join Date: Jun 2011
Location: Texas
Boat: Baba 35
Posts: 385
Re: ELCI breaker before or after inverter?

Have had to put an ELCI in swimming pool equipment breaker boxes for a while now as well.

People keep thinking im making stuff up when I say the replacement breaker is 100 dollars.
ttex is offline   Reply With Quote
Old 21-01-2020, 09:18   #11
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 667
Images: 5
Re: ELCI breaker before or after inverter?

In researching my issue with my marine air and an ELCI, I read that inverters and ELCI breakers do NOT play well together. The AYBC rules require the neutral and safety ground to be bonded when the inverter is the power source, but not when the shore power is the source. The switch over takes enough time that the ELCI will see the current 'leak' to the safety ground and trip. You will need to research how to deal with this issue.
OS2Dude is offline   Reply With Quote
Old 11-03-2024, 14:07   #12
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

Hi All,
I am just about to install ELCI and the agony where to put it drags on.

I have a simple 120V 30A shore power with a galvanic isolator already installed. I also have a Victron 2000W inverter/charger with a 120V input that is not hard wired. I connect it manually via an extension cord when I want a quick charge on anchor from my generator or shore power. When on shore power, I use only Xyntrex 40A charger. I want people to swim safely around my boat when on shore power, generator, or on anchor making morning esspresso (inverter ON with no external 120V source).

My plan was to place the ELCI upstream to my main (and only) 120V panel, downstream my shore/inverter transfer switch and this approach was initially blessed by my friendly electrical guru.
But I read numerous warnings NOT to place ELCI downstream the inverter as the inverter has apparently a nasty habit to connect grounding and neutral for a short period after being turned on. This brief interconnection is apparently enough to trip the ELCI and render the inverter useless. I guess, I could test this approach, but it is a lot of work, so I rather get someone advise.

Upon carefull consideration I am now planning to install ELCI right at the inlet of shore power as per ABYC guidelines and live with the risk of no ELCI protection of inverter's 120V. This risk is, to my understanding, neglibeable as the main source of current leakeage (electrical water heater) will be switched off when inverter is on. My inverter runs the entire 120V panel and I have to manually switch off the water heater and battery charger before running inverter. When I forget (and yes, I do occassionally and will install some automation here soon), the inverter shuts off on overload or reverse polarity, so I assume my crew will be safe swimming when I am making esspresso on anchor. As another precaution I was advised to connect the inverter casing ground with the boat grounding bus. I do not understand the logic behind it and if it is OK with the inverter wellbeing, but I will try and see.
All outlets are protected by GFPI so I cannot think of any swimmers safety issues.

Anyone went through this exercise?
Any comments?

Best regards
mroc is offline   Reply With Quote
Old 11-03-2024, 15:22   #13
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: ELCI breaker before or after inverter?

under ABYC you need a main elci before anything. within 10' of the shore inlet.

if you wanted one after the inverter you'd need 2. you can't have stray current leaving the boat from an inverter. so it's less usefull there.


the battery charger and hot water heater should be run from ac2 output of the multiplus. this will save you from having to switch all the time.
smac999 is offline   Reply With Quote
Old 11-03-2024, 19:17   #14
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

Thanks smac999. Sounds like a decisive and competent suggestion. As I mentioned, I am planning to do just as you suggested. I would appreciate a bit of explanation why I can’t have strait current leaving the boat from the inverter.
Big thanks
mroc is offline   Reply With Quote
Old 11-03-2024, 19:38   #15
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,003
Re: ELCI breaker before or after inverter?

Quote:
Originally Posted by mroc View Post
Thanks smac999. Sounds like a decisive and competent suggestion. As I mentioned, I am planning to do just as you suggested. I would appreciate a bit of explanation why I can’t have strait current leaving the boat from the inverter.
Big thanks
The inverter output is galvanically isolated from shore power so the only return path for a circuit is back to the inverter. It is a new AC power source.

You can get the same safety from shore power by using an isolation transformer.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Shore Power Pedestals - Will They Ever Be ELCI Breakered ? sdowney717 Electrical: Batteries, Generators & Solar 31 15-07-2011 12:39
Calculating Amps Drawn Before Inverter and After Inverter ? impi Electrical: Batteries, Generators & Solar 23 26-09-2010 22:24
ELCI and Isolation Transformer Microship Electrical: Batteries, Generators & Solar 20 19-08-2010 15:54

Advertise Here


All times are GMT -7. The time now is 13:36.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.