Old 12-04-2024, 20:25   #46
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,017
Re: ELCI breaker before or after inverter?

You have the GI between shore power and ELCI. There should be nothing in between the two.

Inlet - elci - gi - ac distribution

I agree that this shouldn’t cause the problems encountered so something is different or broken. The box requires ground for the test button I think.

(The breaker trips when current through hot is different than current through neutral. The test button does that by leaking some to ground)
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-04-2024, 05:42   #47
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

Thanks Jedi,
I will redo and test once I get to the boat again. But in this case, grounding from boat side cannot be hooked into the GI grounding terminal unless I want to cut my losses and sell the GI as useless (bypassed).
It’s still puzzles me why it trips upon flipping the “outlets” breaker even if there is nothing plugged in, so no current in theory. BTW the boat is still on hard, so no ground connections to write home about is present. Weird!
mroc is offline   Reply With Quote
Old 13-04-2024, 09:21   #48
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: ELCI breaker before or after inverter?

Quote:
Originally Posted by mroc View Post
Thanks Jedi,
I will redo and test once I get to the boat again. But in this case, grounding from boat side cannot be hooked into the GI grounding terminal unless I want to cut my losses and sell the GI as useless (bypassed).
It can. Speaking of ground wire only

Shorepower Inlet -> ELCI box* "source" connector -> ELCI box "load" connector -> shorepower side of GI

boat side of GI -> Rest of ground distribution. Everything "boat side" should eventually connect here and not to shorepower inlet, shorepower side of GI, or ELCI.

Or look at your diagram. Simply move the GI to be just below where it says "120V Load" on the ground wire.


* The ELCI itself (as in the actual physical breaker) has no ground connection but the box/housing is grounded since the rest of the wiring from shorepower inlet is going to be routed this way anyways might as well run the ground the same way. Currently you are creating a loop. Trace the wire on your diagram from the GI it branches out one part goes to the left and the other up through the ELCI box and meets back up at the branch which went left. This is pointless and confusion especially to someone in the future trying to figure out what you did and why.
Statistical is offline   Reply With Quote
Old 13-04-2024, 11:13   #49
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

Thanks Statistical,
It is very descriptive, helpfull and make sense.
I will redo and test. Do you believe this could have been the reason of tripping?
I am also puzzled that it trips without outlets being loaded. I also remembered now that the inverter/shore power selector switch disconnects both hot and neutral wires from either source, so it should not affect the ELCI.
mroc is offline   Reply With Quote
Old 13-04-2024, 11:53   #50
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: ELCI breaker before or after inverter?

Quote:
Originally Posted by mroc View Post
Thanks Statistical,
It is very descriptive, helpfull and make sense.
I will redo and test. Do you believe this could have been the reason of tripping?
I am also puzzled that it trips without outlets being loaded. I also remembered now that the inverter/shore power selector switch disconnects both hot and neutral wires from either source, so it should not affect the ELCI.

I think you should make this change for transparency and to avoid ground loops but I don't think this issue is causing the tripping.

Most likely somewhere on the boat there is either a hot & neutral reversed or a neutral and ground reversed. The best way to narrow that down is by process of elimination.

With AC master panel of does it trip? If no then the issue is "downstream" of the AC master panel.

With AC master panel ON but all branch circuits off does it trip? If no then it is one or more of the outlets.

Note if there are any "always on" branches (like charger) you may wish to temporarily disconnect them to avoid false positives.
Statistical is offline   Reply With Quote
Old 13-04-2024, 12:07   #51
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

Thanks again Statistical,
Panel ON- no trip
Outlets ON - trip
Charger on - trip
I can’t try water heater as it’s empty. But with these two clients tripping, it may be a tough chase. But I am sure, I will find the culprit.
Regards
mroc is offline   Reply With Quote
Old 13-04-2024, 12:26   #52
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,017
Re: ELCI breaker before or after inverter?

The whole shore power / inverter selector switch is wrong. This must be a transfer switch, which I think it is, so very different from your diagram.

I still recommend you hire an electrician to get this done right and I still don’t fully understand what you did and what is going on.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 14-04-2024, 07:58   #53
Registered User

Join Date: Jul 2008
Location: Penetanguishene
Boat: Hunter 380
Posts: 6
Re: ELCI breaker before or after inverter?

Just a thought: are the GFCI outlets the 'smart' ones that self-test every once in a while?
JanH is offline   Reply With Quote
Old 14-04-2024, 09:17   #54
Registered User

Join Date: May 2023
Posts: 23
Re: ELCI breaker before or after inverter?

No JanH, they are old fasion ones. Bad news is that ELCI trips upon any AC panel user turned on. Make trouble shooting a wild goose chase.
mroc is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Shore Power Pedestals - Will They Ever Be ELCI Breakered ? sdowney717 Electrical: Batteries, Generators & Solar 31 15-07-2011 12:39
Calculating Amps Drawn Before Inverter and After Inverter ? impi Electrical: Batteries, Generators & Solar 23 26-09-2010 22:24
ELCI and Isolation Transformer Microship Electrical: Batteries, Generators & Solar 20 19-08-2010 15:54

Advertise Here


All times are GMT -7. The time now is 10:02.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.