Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 24-04-2020, 18:29   #1
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
ITR Marine Heater Review and Installation

I have been researching Diesel fueled heaters to identify which one will be suitable for our steel boat so as to winter as liveaboards above Lat 49° N.

(Next year, we will travel from Philippines to Kodiak via Hokkaido, Aleutian Islands, clearing in at Dutch Hbr)

Deciding Issues for me on what system to retrofit are:

Ease of Installation: This steered me towards a Hydronic system running ¾” piping for Heating Fluid in Series though to 5 Zones, rather than Forced Air. I could not afford to lose all the storage space of fitting a forced air ducted system

Ease of Maintenance: I wanted a system that I can trouble shoot and maintain myself and to fit boiler inside my engine room where it is dry and spacious

Reliability: This is where I am dependent on the experience and advice of others

Energy Efficiency: Initially I was very much attracted to the quiet Passive system of Radiators. Then I found out that Radiators use a 3/4" copper fin and tube.

To compare 1 foot of Copper fin and tube is only 500 BTU whereas a small Cabin Heater fan provides 8700 BTU. So, I would need 17 feet equivalent tube to compare. Also, more plumbing is involved as you need to branch off to radiators and then come back in the main loop.
That means more challenges with Noise and Vibration

Comfortable Interior at -6°C?: The coldest month on record at Vancouver International Airport was January 1950 when an arctic air inflow moved in from the Fraser Valley and remained locked over the city, with an average low of −9.7 °C (15 °F) and an average high of only −2.9 °C (27 °F), making for a daily average of −6.3 °C (20.7 °F), 10 °C (18 °F) ...

So, does that mean I should size heater for the worst at -6C or take an
average of say 8°C from Nov to March?

If I oversize, the Heater may cycle on and off too many times, which could cause fuel nozzle problems and premature failures. If undersize, then slow to heat up and be comfortable after a day’s sail.

What would those living aboard in those conditions advise from their experience?

Calculating Cabin Heater Size:
One Manufacturer uses the formula of Cubic Feet of Zone x 0.80 adjustment for furniture,
Then Multiply by
x8 For small spaces like heads
x10 For sleeping spaces for all other
x12 For all other spaces generally below 48 North and Non Liveaboard
x15 For High Use Spaces and Liveaboard.
I asked the sales person which factor I should apply, his reply 15 is for a colder climate but that is fine you can be really safe with that. The heater will cycle off more. Usually between 40 to 60%.

So, for those liveaboards in cold climates like Vancouver would you advise using Factor 15 for ALL sizing Cabin Heaters?

Noise and Vibration Levels: I think it is important as a liveaboard to have a system you can live with instead of listening to a Truck Heater all evening…. Any thoughts and advice on that is really appreciated.

From my shortlist of Hydronic suppliers, this Canadian one ticked most of the boxes.

https://itrheat.com/products/marin-heating-systems/


I do remember reading negatives about them from one user on another CF Thread, but no details.
Appreciate reviews and advice from those who have used and installed them

Thanks for reading
Pelagic is offline   Reply With Quote
Old 24-04-2020, 20:20   #2
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: ITR Marine Heater Review and Installation

We've had an ITR Zephyr for 4 or 5 years. It has been a really good system. We use it everyday to get on-demand hotwater. I removed our old hotwater tank and installed the ITR in its place.
__________________
Paul
Paul L is offline   Reply With Quote
Old 24-04-2020, 21:11   #3
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by Paul L View Post
We've had an ITR Zephyr for 4 or 5 years. It has been a really good system. We use it everyday to get on-demand hotwater. I removed our old hotwater tank and installed the ITR in its place.
Hi Paul,
Do you liveaboard year round?
What was the coldest temperature you designed the 33,000Btu Zepher for?
Did you use that multiplier 15 for cabin heater sizing?
How noisy are their cabin heaters?
Thanks
Pelagic is offline   Reply With Quote
Old 24-04-2020, 21:46   #4
Registered User
 
wefleenor's Avatar

Join Date: Nov 2010
Location: Pittsburg, CA
Boat: 49ft custom power catamaran
Posts: 126
Re: ITR Marine Heater Review and Installation

I have an ITR Hurricane, 50K BTU and it can turn the boat into a sauna. Great system. Assists the hot water heater, takes heat from one of the engines, and has electric for minimal support at the dock. I could look up my volume later if it would help, but I doubt I have anything close to a factor of 15.
wefleenor is offline   Reply With Quote
Old 24-04-2020, 22:55   #5
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by wefleenor View Post
I have an ITR Hurricane, 50K BTU and it can turn the boat into a sauna. Great system. Assists the hot water heater, takes heat from one of the engines, and has electric for minimal support at the dock. I could look up my volume later if it would help, but I doubt I have anything close to a factor of 15.
Thanks wefleenor. Note you have a big cat in Oregon.
How cold did you factor for there in wintertime?
Do you liveaboard full time?
Pelagic is offline   Reply With Quote
Old 24-04-2020, 23:40   #6
Registered User
 
nwdiver's Avatar

Join Date: Aug 2011
Location: Vancouver, BC
Boat: C&C Landfall 38
Posts: 823
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by Paul L View Post
We've had an ITR Zephyr for 4 or 5 years. It has been a really good system. We use it everyday to get on-demand hotwater. I removed our old hotwater tank and installed the ITR in its place.
I replaced my hot water tank with an ITR 4 zone system, works great now in its 7th year.......I only use 3 zones and the 4th loop goes to preheating my engine....
nwdiver is offline   Reply With Quote
Old 25-04-2020, 00:54   #7
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by nwdiver View Post
I replaced my hot water tank with an ITR 4 zone system, works great now in its 7th year.......I only use 3 zones and the 4th loop goes to preheating my engine....
Hi Nw Diver,
Note that you are from Vancouver, which was my home town. Since we will winter there as liveaboard, how did you calculate your cabin heater sizes and are you happy with it during a cold snap?
Pelagic is offline   Reply With Quote
Old 25-04-2020, 01:23   #8
Registered User
 
SteelEagle's Avatar

Join Date: Apr 2020
Location: Alaska
Boat: Kristen 465 Pilothouse
Posts: 18
Re: ITR Marine Heater Review and Installation

Hey Pelagic

We live aboard in Alaska on a 47’ steel pilothouse and have an ITR hurricane 2, we love it and couldn’t imagine using something else. It kept our boat toasty all winter, even during the cold snaps down to 0F we could have made a sauna.

It was installed when we bought the boat, but it doesn’t seem difficult, as long as you have access to run heater hose and wire for the fan. Previous owner did the install himself.

Maintenance is straight forward, we just did the 3 year service on it, took maybe an hour. Fuel nozzles are affordable and easy to clean so no big deal if you coke one up, you will notice it start to run rougher if you do.

Our heater is pretty quiet but our engine room is well insulated, ymmv. Fans are quiet too, I can barely hear them. It runs maybe 4-6 hours on a cold (5F) winter day and burns about 2 gallons per day, and maybe runs for an hour on a 40F day burning about 0.5 gallons per day. We also use it for hot water.

No idea what the cabin fan sizing is but will look into it.

Give the exhaust port some consideration. Ours is the one which also has an air intake and they are sensitive to saltwater intrusion. Ours is mounted on the side and I wish it wasn’t, we have to turn our heater off and plug the exhaust sailing in any heavy seas.

Cheers
SteelEagle is offline   Reply With Quote
Old 25-04-2020, 05:01   #9
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 51,311
Images: 241
Re: ITR Marine Heater Review and Installation

Greetings and welcome aboard the CF, SteelEagle.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 25-04-2020, 11:59   #10
Registered User

Join Date: Dec 2019
Location: Chehalis WA
Boat: Bayliner 2655
Posts: 77
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by Paul L View Post
We've had an ITR Zephyr for 4 or 5 years. It has been a really good system. We use it everyday to get on-demand hotwater. I removed our old hotwater tank and installed the ITR in its place.
Wow between 4 and 6k spendy
tekdiver is offline   Reply With Quote
Old 25-04-2020, 12:07   #11
Registered User
 
wefleenor's Avatar

Join Date: Nov 2010
Location: Pittsburg, CA
Boat: 49ft custom power catamaran
Posts: 126
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by Pelagic View Post
Thanks wefleenor. Note you have a big cat in Oregon.
How cold did you factor for there in wintertime?
Do you liveaboard full time?
Pelagic,

I simply told the builder that my wife can stand anything but cold. When I calculate the internal volume of the boat that I want to heat, or cool, it comes out between 3200-3500 sq ft. That would provide a factor of about 13-15. I have only been farther north in the summer months, but boat is currently in Portland and for the barely freezing temperatures there the heater does not work very hard to keep it toasty. I do not live on board, but since I live 600 miles away, I do spend a week there almost once a month (except now).

Bill
Double-Wide
wefleenor is offline   Reply With Quote
Old 25-04-2020, 12:10   #12
Registered User
 
SV__Grace's Avatar

Join Date: Dec 2019
Location: Puget Sound, WA
Boat: Nauticat 43 ketch
Posts: 794
Images: 5
Re: ITR Marine Heater Review and Installation

We just completed our first winter in PNW with our ITR Hurricane Combi 2.

First, to be clear, it is a hydronic heater such as Espar and Webasto, which means that it uses a diesel burner to heat up fluid (coolant) which gets circulated through hoses to heat exchangers that have 12v fans to blow warm air into the cabin, so to me it is a forced air heater, not a radiant heater because it has a fan that forces air over the heating element. If you review the video you provided you will see that clearly. The difference is that you use hoses (2 hoses per register) rather than ducts, which might save some space, but not by much.

We've lived aboard our boat for 3 years now, spending the first two in CA refitting her for full time high latitude cruising. In CA we used the Combi mostly for hot water. It's a great on-demand hot water system (no hot water tank needed). Gets up to full temp within 5 minutes.

During our refit we expanded the heating system of the Combi to 5 registers throughout the boat. This past winter we experienced temps in the low 20's, which our heater easily handled. Other owners tell me that this system can handle temps far lower.

Using the "Summer/Winter" valve on the Combi you can switch between hot water only (5 minutes to cycle up) and hot water + heat (15-20 minutes to cycle up and comes on @50% of the time to keep temp up).

It is a pretty easy unit to service, and the customer service of ITR is great. I have their tech support on speed dial and between texting and phone calls they have been very generous in spending as much time needed to help me figure out and fix any problems.
SV__Grace is offline   Reply With Quote
Old 25-04-2020, 13:22   #13
Registered User

Join Date: Aug 2017
Posts: 40
Re: ITR Marine Heater Review and Installation

Check out Sure Marine Seattle's website. Lots of info on how to size a system and they have some kits priced out with suggested equipment needed to fully install a system. Note that a $3500 heater can easily become close to $10000 with all the fan heaters, circ pump, valves, hose, thermostats, etc. Then figure 40-60 hours for a professional installation.
rphdiego is offline   Reply With Quote
Old 25-04-2020, 13:22   #14
Registered User
 
wefleenor's Avatar

Join Date: Nov 2010
Location: Pittsburg, CA
Boat: 49ft custom power catamaran
Posts: 126
Re: ITR Marine Heater Review and Installation

Obviously, that is 3200-3500 cu ft and not sq ft. I have to hope none of those students I chastised over units all those years see this error.
wefleenor is offline   Reply With Quote
Old 26-04-2020, 00:12   #15
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: ITR Marine Heater Review and Installation

Quote:
Originally Posted by SteelEagle View Post
Hey Pelagic

We live aboard in Alaska on a 47’ steel pilothouse and have an ITR hurricane 2, we love it and couldn’t imagine using something else. It kept our boat toasty all winter, even during the cold snaps down to 0F we could have made a sauna.

It was installed when we bought the boat, but it doesn’t seem difficult, as long as you have access to run heater hose and wire for the fan. Previous owner did the install himself.

Maintenance is straight forward, we just did the 3 year service on it, took maybe an hour. Fuel nozzles are affordable and easy to clean so no big deal if you coke one up, you will notice it start to run rougher if you do.

Our heater is pretty quiet but our engine room is well insulated, ymmv. Fans are quiet too, I can barely hear them. It runs maybe 4-6 hours on a cold (5F) winter day and burns about 2 gallons per day, and maybe runs for an hour on a 40F day burning about 0.5 gallons per day. We also use it for hot water.

No idea what the cabin fan sizing is but will look into it.

Give the exhaust port some consideration. Ours is the one which also has an air intake and they are sensitive to saltwater intrusion. Ours is mounted on the side and I wish it wasn’t, we have to turn our heater off and plug the exhaust sailing in any heavy seas.

Cheers
Hi SteelEagle,
Welcome to CF and great first post on a beautiful boat that is similar to mine, which helps me a lot!
Really encouraging to hear your use figures for a cold snap and typical chill temps

Took a look at the Kristen 465 Pilothouse… really beautiful and purposely built for colder climates, whereas mine, (16 years older) was built in Holland for the Med, then did a circumnavigation but after 1995 with new Owners stayed in Tropics until now with their focus on lots of Aircon and a Marina/ generator boat!

Changes I’ve made since buying in 2004 in Phuket has been to make her more off grid and cruising ready. ...Now to take her to high latitudes

The Hurricane is a big-ticket item for me @ over $10k +shipping and I will self-install in the Philippines so appreciate any tips from all, on various things to consider.

Your note about Exhaust Shutoff in rough seas being a weakness is right on and I’ve already brought this up with ITR.

They don’t have a solution for an internal shutoff valve that can handle the heat, so I’m still looking for one. Maybe our detail guru, GordMay or others have ideas. (My first thought was a “Steam Valve”)
On the leg trip from Japan to Bering Sea, it would be nice to have a useable heater if conditions allow!

It would be nice to know more about the Cabin Heater choices and where the previous owner installed the cabin heaters for your similar layout

Note, your H2 is rated at 35,000 BTU/h I am specing out the Chinook which is at 50.000 BTU/h because it can be maintained from the front. But I am working on these decisions sight unseen. It replaced The Hurricane Combi 2 that SV Grace has on board

My Boat is a bit longer at 55ft on deck (not counting Bowspirit) but skinner for that length, and I doubt if she has as good a temperature insulation as your boat.
So I just don't know yet if that 50,000BTU/h is overkill??

Boiler Location: ….My Midship Engine room would be better place as the aft locker is a wet locker storing storm sails, towing warps and fenders etc…. ER is dry, well insulated for sound and I have dedicated spaces . So to exhaust out the stern is too long a run

Sketch shows Blue Exhaust so no issues with back pressure Green Fresh Air Intake from side vent or maybe a 2nd hull penetration above and Fwd. of exhaust. (Need to think about best location for loop to diffuse salt water mist? )

Photo shows the location where an overkill Aircon compressor will be relocated beside so that Chinook front facing inboard, with left side Aft.

I am presently going thru a design and installation checklist with ITR Sales and Marketing VP Marcelleo in Richmond, who has been very responsive to my questions?

So will document on this thread to help others and hopefully get advice for my installation and design....

Cheers! Nick
Attached Thumbnails
Click image for larger version

Name:	1 Profile lay out.jpg
Views:	164
Size:	401.7 KB
ID:	213722   Click image for larger version

Name:	2 Star-Layout.jpg
Views:	210
Size:	93.7 KB
ID:	213723  

Click image for larger version

Name:	1 Chinook Location ER .jpg
Views:	554
Size:	322.9 KB
ID:	213724   Click image for larger version

Name:	1a remove compresor.jpg
Views:	258
Size:	426.0 KB
ID:	213725  

Click image for larger version

Name:	1 Chinook Dimensions Tray.jpg
Views:	153
Size:	194.8 KB
ID:	213726   Click image for larger version

Name:	1 Chinook waterline  Exhausr .jpg
Views:	239
Size:	425.1 KB
ID:	213727  

Pelagic is offline   Reply With Quote
Reply

Tags
installation, marine, heater

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ITR Hurricane Heater TBW Plumbing Systems and Fixtures 3 18-01-2020 17:31
Diesel heater installation and ducting Tenedos Plumbing Systems and Fixtures 1 08-12-2019 05:50
Planar heater purchase and installation (later) starcruiser Plumbing Systems and Fixtures 32 13-08-2018 08:48
Wallas 30DT review (includes review of ScanMarine Equipment) basssears Product or Service Reviews & Evaluations 0 21-06-2016 12:59
380: Lagoon 380 User Review (15,500 Mile Review) 3Eagles Lagoon Catamarans 23 28-02-2013 18:25

Advertise Here


All times are GMT -7. The time now is 11:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.