Watch those amps champs!

Well after five years with electric propulsion I guess it was bound to happen. I was installing some new terminal connections for my helm mounted battery instrumentation project when a interconnect cable touched the terminal of the next battery. It was less than a second of contact but, lit up the space like a flashbulb. No major damage done except to the heavy duty cable lug which you can see here:
THE BIANKA LOG BLOG: MISTAKES OF AN ELECTRIC SAILOR
Got to respect what 200 DC amps can do!
__________________
Mike
mbianka is offline   Reply With Quote
Old 20-10-2012, 06:49   #2
Sponsoring Vendor
 
Tellie's Avatar

Community Sponsor

Join Date: Oct 2007
Location: Hollywood, Fl.
Boat: FP Athena 38' Poerava
Posts: 3,984
Re: Watch those amps champs!

Don't feel bad. Anyone that works on their electrical systems and says this hasn't happened to them are the same ones that tell you they've never run aground.
Tellie is offline   Reply With Quote
Old 20-10-2012, 06:57   #3
Marine Service Provider
 
Snore's Avatar

Join Date: Jan 2011
Location: St. Petersburg, FL
Boat: Retired Delivery Capt
Posts: 3,690
Send a message via Skype™ to Snore
Nice!! I still have a 30 year old ground connection from a meter can just to remind me of my mistake.

When I was much younger and working for an electric utility I was trained to physically isolate connections on different phases of a meter pan or bottom feed cabinet using rubber sheeting... By the book they wanted a physical barrier to prevent guys from what happened to you. A slip of the hand flash.

In reality, in the field, "some guys" were known to us a piece of cardboard to stop a slip of the hand cross-phase connection. Being an electric sailer, the rubberized mats fabric or a cardboard collection may be useful addition to your tool kit.

Bill
__________________
"Whenever...it requires a strong moral principle to prevent me from deliberately stepping into the street, and methodically knocking people's hats off- then, I account it high time to get to sea..." Ishmael
Snore is offline   Reply With Quote
Old 20-10-2012, 07:15   #4
Registered User
 
mbianka's Avatar

Join Date: Mar 2008
Posts: 2,147
Images: 1
Re: Watch those amps champs!

Quote:
Originally Posted by Snore View Post
Nice!! I still have a 30 year old ground connection from a meter can just to remind me of my mistake.

When I was much younger and working for an electric utility I was trained to physically isolate connections on different phases of a meter pan or bottom feed cabinet using rubber sheeting... By the book they wanted a physical barrier to prevent guys from what happened to you. A slip of the hand flash.

In reality, in the field, "some guys" were known to us a piece of cardboard to stop a slip of the hand cross-phase connection. Being an electric sailer, the rubberized mats fabric or a cardboard collection may be useful addition to your tool kit.

Bill
Bill:

Yeah, I do have rubber mats I put over the terminals when working from inside the cabin. I this case I had just gotten a little lazy as it was just a quick disconnect to put the additional terminal connector on and reconnect. That and the fact this battery interconnect cable was a little longer than it needed to be when I installed the electric propulsion system five years ago. It was on my list of things to change at some point. So this incident got me to get that done. I like the cardboard idea too or some type of insulating board in between the batteries when working around the lugs. I think I'll incorporate that in the future.
__________________
Mike
mbianka is offline   Reply With Quote
Old 20-10-2012, 08:19   #5
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Watch those amps champs!

Don't feel bad, it has happened to everyone who has spent enough time doing electrical work.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 21-10-2012, 06:13   #6
Registered User
 
mbianka's Avatar

Join Date: Mar 2008
Posts: 2,147
Images: 1
Re: Watch those amps champs!

Quote:
Originally Posted by David M View Post
Don't feel bad, it has happened to everyone who has spent enough time doing electrical work.
Dave:

Well, I don't feel bad because at least nothing blew up or caught fire. Just wanted to share what could happen when a wire goes someplace it should not. I've since replaced the lug and am now on a fall cruise.
__________________
Mike
mbianka is offline   Reply With Quote
Old 21-10-2012, 06:19   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,588
Images: 241
Re: Watch those amps champs!

Greetings and welcome aboard the CF, Richieg1g.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 21-10-2012, 10:13   #8
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,199
Re: Watch those amps champs!

Quote:
Originally Posted by mbianka View Post
Dave:

Well, I don't feel bad because at least nothing blew up or caught fire. Just wanted to share what could happen when a wire goes someplace it should not. I've since replaced the lug and am now on a fall cruise.
No over-current protection in that circuit? You might consider some fusing...

Keep in mind that the short circuit current available from even a group 27 deep cycle battery can exceed 1500A at 70F.. So a 200Ah bank or a battery with a CCA of 700 at 0F will pump a LOT more than 700A into a dead short at normal boating temps. Add a few batteries in parallel and the short circuit capability is then multiplied. It is not unusual to exceed 5000A of short circuit capability in a battery bank.

Some batteries throw a lot more than others into a short. For example the Odyssey TPPL AGM in group 31 size can supply 5000A of short circuit current per battery. A bank of four would be 20,000A of current into a dead short.... Ouch!!!!
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-10-2012, 09:25   #9
Registered User
 
mbianka's Avatar

Join Date: Mar 2008
Posts: 2,147
Images: 1
Re: Watch those amps champs!

Quote:
Originally Posted by Maine Sail View Post
No over-current protection in that circuit? You might consider some fusing...

Keep in mind that the short circuit current available from even a group 27 deep cycle battery can exceed 1500A at 70F.. So a 200Ah bank or a battery with a CCA of 700 at 0F will pump a LOT more than 700A into a dead short at normal boating temps. Add a few batteries in parallel and the short circuit capability is then multiplied. It is not unusual to exceed 5000A of short circuit capability in a battery bank.

Some batteries throw a lot more than others into a short. For example the Odyssey TPPL AGM in group 31 size can supply 5000A of short circuit current per battery. A bank of four would be 20,000A of current into a dead short.... Ouch!!!!
Well the lug did act as a fuse in this case. The bank is fused on the output which was disconnected at the time. Putting fuses in the battery interconnects would still require 100 amp fuses and add more connections and possible failure points into the circuitry. I do have the new helm battery monitor wiring fused at the battery connection ends though. I will certainly be more cautious should I have to do something with these connections in the future.
__________________
Mike
mbianka is offline   Reply With Quote
Old 20-10-2012, 08:38   #10
Registered User
 
rebel heart's Avatar

Join Date: Oct 2005
Posts: 6,185
Images: 3
Re: Watch those amps champs!

I just barely crossed a 1 gauge past a negative terminal one time, the spark was quite impressive, as was the heat that generated in the wire in a split second. I have the battery banks fused, and I think the house is fused to 100amp but since it was thermal it didn't trip. Kind of neat in a dangerous sort of way to learn all that.
rebel heart is offline   Reply With Quote
Old 20-10-2012, 08:38   #11
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,588
Images: 241
Re: Watch those amps champs!

I like to slide a short (±4") piece of clear hose over the positive cable lug(s); so that it normally sits over the cable insulation, but can be pulled down to protect the lug, when removed from the terminal post. This helps prevent a “loose” cable from shorting out on a negative post, or ground.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 20-10-2012, 08:46   #12
Registered User

Join Date: May 2008
Posts: 3,543
Re: Watch those amps champs!

I have a couple of old beach towels that I throw over everything and then peel just enough back to get at the spots I need. The towel also makes a good non-conductive place to rest tools.

Carl
CarlF is offline   Reply With Quote
Old 20-10-2012, 19:14   #13
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Watch those amps champs!

Quote:
Originally Posted by CarlF View Post
I have a couple of old beach towels that I throw over everything and then peel just enough back to get at the spots I need. The towel also makes a good non-conductive place to rest tools.

Carl
That may work for 12 volt single bats, but it is still a huge risk. First a beach towel made of cotton or some other fabric, isn't really an insulator.

Any moisture at all will conduct enough to cause a spark at the very least...now if the bats are at or recently were at gassing stage, then the spark causes an explosion, and the towel adds fuel to the fire. It may even be that the towel creates the environment for the explosion by containing the hydrogen gas cloud in a density that can explode. Now if we are talking 24,32,36, or 48 volt systems then a towel is of no value.

Boiling battery acid, is explosive at 4% by volume in open air. Battery acid starts boiling 12.3 volts at a 12 volt nominal, or 2.1 volts times the number of cells in the bat.

Before working on a live bank, make sure there has been no charge\discharge source to the bats for at least 2 hrs and the area is well ventilated for at least 2 hrs after charge\discharge.

Always disconnect the the ships neg to battery first, then disconnect each neg in the string, secure the cables from arc with a short piece of rubber hose, then secure each neg bat post, with a cap.

Now you can follow the same routine with the pos. cables/posts.

one marine average 12 volt battery has a potential of 1.3kw arc.


Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 21-10-2012, 06:17   #14
Registered User
 
mbianka's Avatar

Join Date: Mar 2008
Posts: 2,147
Images: 1
Re: Watch those amps champs!

Quote:
Originally Posted by GordMay View Post
I like to slide a short (±4") piece of clear hose over the positive cable lug(s); so that it normally sits over the cable insulation, but can be pulled down to protect the lug, when removed from the terminal post. This helps prevent a “loose” cable from shorting out on a negative post, or ground.
Good idea. I do have some Blue Sea battery covers over the battery terminals normally but, this could be additional protection when working on the interconnects.
__________________
Mike
mbianka is offline   Reply With Quote
Old 20-10-2012, 13:47   #15
Moderator
 
Jim Cate's Avatar

Join Date: May 2008
Location: cruising SW Pacific
Boat: Jon Sayer 1-off 46 ft fract rig sloop strip plank in W Red Cedar
Posts: 21,233
Re: Watch those amps champs!

And w hile on this subject, it's a good idea to not wear rings or metal watchbands whilst working around the electrics. Knew a chap who lost a finger when his gold wedding ring got shorted across a car battery. Pretty ugly...

Cheers,

Jim
__________________
Jim and Ann s/v Insatiable II, lying Port Cygnet Tasmania once again.
Jim Cate is online now   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 15:29.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.