I am intending to install Victron Pheonix Inverter to be the exclusive provider of AC power on my boat with a seperate charger for charging the house bank from AC shore power. I am assuming negates the need for a isolation transformer as the AC power is only connected to the battery charger not the inverter.

However it has been suggested to use a Multiplus Inverter instead of the Pheonix. The Multiplus has a battery charger built into it. The problem I am considering is when the AC shore power connects to the Multiplus inverter, the boats ground plates will be connted to the shore based earth and thus could paralise someone in the water within the vicinity of my boat.

Where as with the Pheonix Inverter there is no connection to the AC shore based power, instead the AC power is connected only to the seperate battery charger.
ArranP is offline   Reply With Quote
Old 27-10-2023, 21:23   #2
Registered User
 
fxykty's Avatar

Join Date: Apr 2016
Location: Indonesia
Boat: Outremer 55L
Posts: 3,851
Re: Safety Shore based power

You want to isolate the shore earth from the boat ground. If you want to avoid using an isolation transformer then why not a galvanic isolator like this: https://www.victronenergy.com/isolat...anic-isolator?
fxykty is offline   Reply With Quote
Old 31-10-2023, 13:16   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Safety Shore based power

The separate charger and inverter is the way to go of you want to travel the world. As a good charger will take 120 - 230v and 50-60hz. So you can charge in any country and the inverter will make correct power for your plugs no mater where you are. The multiplus does not. The charger needs to be big enough to handle all the loads plus charge though. So you might need 200a of chargers.

If you are not traveling. The multi is fine and has some advantages. They are on 1000’s of boats. You’d want a galvanic isolator or iso transformer.
smac999 is offline   Reply With Quote
Old 31-10-2023, 15:22   #4
Registered User

Join Date: Jan 2023
Posts: 1,518
Re: Safety Shore based power

Your strategy of charger separate from inverter is a valid one, but you need to be sure that the charger is galvanically isolated from the boat’s electrical system. Not all are.

Also, the charger does not need to be sized for peak load, only the average load, letting the batteries buffer the peaks out of the inverter.
SailingHarmonie is offline   Reply With Quote
Old 31-10-2023, 15:26   #5
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,119
Re: Safety Shore based power

Quote:
Originally Posted by ArranP View Post
when the AC shore power connects to the Multiplus inverter, the boats ground plates will be connted to the shore based earth and thus could paralise someone in the water within the vicinity of my boat.
I'm assuming you are in salt water ... There are no recorded incidents of electrocution in salt water from vessel AC current. It is a fresh water phenomena.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 31-10-2023, 23:30   #6
Registered User

Join Date: May 2006
Posts: 1,150
Re: Safety Shore based power

that’s right, the simple reason is that in fresh water a salty person provides a better path… however an iso transformer is a good idea.
Fuss is offline   Reply With Quote
Old 01-11-2023, 03:40   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,482
Images: 241
Re: Safety Shore based power

Quote:
Originally Posted by boatpoker View Post
I'm assuming you are in salt water ... There are no recorded incidents of electrocution in salt water from vessel AC current. It is a fresh water phenomena.
Quote:
Originally Posted by Fuss View Post
that’s right, the simple reason is that in fresh water a salty person provides a better path… however an iso transformer is a good idea.
In fact, electrical conductivity* [measured in microsiemens per centimeter (uS/cm)] is how we measure of the salinity [or purity] of water.

Freshwater is usually between 0 and 1,500 uS/cm [depending upon TDS - Distilled Water ≈0.5-3 uS/cm], and typical sea water has a conductivity value of about 50,000 uS/cm.
Hence sea water is as much as a million times more conductive than [pure] fresh water.
Ironically, the more polluted the water, the less likely is electrocution.


Conductivity of human tissue [S/m] https://www.researchgate.net/figure/..._tbl1_43148155
1 S/m = 1,000 uS/m

The electrical conductivity, of the human body, varies for different organs, like muscle, liver, and blood. The skin is the least conductive part, at about 10,000 uS/cm.
Hence the human body is over six times more conductive than fresh water, but only one fifth as conductive as sea water.

* Conductivity is formally defined as the reciprocal of resistivity, measured in Ohms [Ω]. Water can conduct electricity, because of the ion concentration within the water, which comes from dissolved solids and inorganic materials, like carbonate compounds, chlorides, and sulfides like sodium [salt]. The conductivity range also depends on the ion’s potential to bind with water.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 01-11-2023, 14:43   #8
Registered User

Join Date: Mar 2019
Location: Live aboard in Simonstown (Cape Town) - now Grenada having crossed the Atlantic.
Boat: 1986 Bruce Roberts 45 raised saloon
Posts: 374
Re: Safety Shore based power

Very interesting read, thanks for that info.

What would be the risk of shock due to nearby lightning strike in salt water? If I am swimming and see a storm approaching I get out of the water - is that maybe unnecessary?
markcouz is offline   Reply With Quote
Old 01-11-2023, 21:23   #9
Registered User
 
fxykty's Avatar

Join Date: Apr 2016
Location: Indonesia
Boat: Outremer 55L
Posts: 3,851
Re: Safety Shore based power

Quote:
Originally Posted by markcouz View Post
Very interesting read, thanks for that info.

What would be the risk of shock due to nearby lightning strike in salt water? If I am swimming and see a storm approaching I get out of the water - is that maybe unnecessary?

Unless you get a direct hit or extremely near miss I would assume the shock is minimal. However, even your head above water raises your risk of getting struck by lightning, so the short answer is leave the water when a lightning storm approaches.
fxykty is offline   Reply With Quote
Reply

Tags
power, safety


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore based accommodations near Nice Glenn.Brooks Europe & Mediterranean 6 05-02-2023 01:24
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
Using OpenCPN as a shore based Coastwatch Station Yachtbits OpenCPN 10 29-09-2018 06:57
Shore-Based Installation of Marine SSB colo.sail Marine Electronics 2 29-11-2010 08:48
Florida Base for Shore-Based Classes? lottie Training, Licensing & Certification 4 03-09-2009 15:07

Advertise Here


All times are GMT -7. The time now is 09:43.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.