Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Question is if the selector switch is turned to OFF how can any power flow into the boat to trip the GFI?

if the N and G wires were swapped in the dock wiring. nothing normally would be noticed. (unless you clamped the green wire in the panel) but then current can flow from the N of the dock panel into the boat ground and into the water. even with his double pole main breaker off.

if everything is wired correctly. when his double pole breaker is off. no current can flow on either the N or H and you can't blow a GFI if there is no current. there is obvisouly an issue. with a clamp meter, volt meter, and knowledge it wouldn't take long to find.
smac999 is offline   Reply With Quote
Old 16-09-2016, 14:20   #17
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Problem solved!
The inverter has a relay that switches the neutral wire when the inverter is switched on,
When there is no power to the inverter I.E.: no shore power, it defaults to "inverter mode" which connects ground and neutral (as it should) the problem occurs when the shore power is first connected the transfer relay is in inverter mode which immediately blows ground fault.
We isolated all the inverter load neutrals to a separate bus and no more problems.
Thanks for all the in put.
Panacea2183 is offline   Reply With Quote
Old 16-09-2016, 22:36   #18
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Ground fault on shore power trips

is your inverter before or after the main switch and breaker which you said was off?

I have seen this happen but an inverter / charger should be after these. and therefore shouldn't have happened when off.
smac999 is offline   Reply With Quote
Old 17-09-2016, 05:09   #19
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Quote:
Originally Posted by smac999 View Post
is your inverter before or after the main switch and breaker which you said was off?

I have seen this happen but an inverter / charger should be after these. and therefore shouldn't have happened when off.
Inverter is after main but neutrals were tie together so when no power to inverter the inverter grounds the neutral as it should
Panacea2183 is offline   Reply With Quote
Old 17-09-2016, 05:15   #20
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Inverter is after main but neutrals were tie together so when no power to inverter the inverter grounds the neutral as it should
This implies your main is a single pole breaker, might want to look at a double pole.
DotDun is offline   Reply With Quote
Old 17-09-2016, 05:22   #21
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Inverter is after main but neutrals were tie together so when no power to inverter the inverter grounds the neutral as it should

Inverter should only Earth the neutral when it is in operation and inverting. When passing shore power, not inverting, neutral and ground should be unbonded by the transfer switch.
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 17-09-2016, 06:56   #22
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Inverter is after main but neutrals were tie together so when no power to inverter the inverter grounds the neutral as it should
Which neutrals are tied together?

The neutral going to the inverter should not join with the neutral leaving the inverter.
mitiempo is offline   Reply With Quote
Old 17-09-2016, 08:33   #23
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Correct!
That was the problem
Fixed now.
Panacea2183 is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore Power Problem - Ground Fault or Other Issue ? SailFastTri Electrical: Batteries, Generators & Solar 29 19-03-2017 20:51
GFCI - Ground Fault Breaker Rex Delay Electrical: Batteries, Generators & Solar 26 17-03-2016 13:45
Prosine 2 Ground Fault so34chi Electrical: Batteries, Generators & Solar 0 26-02-2015 19:40
For Sale: Fall Cleaning Sale Marinco Shore Power and Ground Plate velero Classifieds Archive 2 17-10-2013 19:44
Ground fault protector problems tsl Electrical: Batteries, Generators & Solar 6 12-04-2013 15:51

Advertise Here


All times are GMT -7. The time now is 07:03.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.