Old 30-07-2019, 15:40   #16
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

Quote:
Originally Posted by a64pilot View Post
Unless I’m mistaken my AC ground bus and DC ground bus are connected? Have to open the panel to be sure.
That should only be true if you have no shore power. When you have shore power the AC and DC grounds must not be connected inside the boat anywhere. Only when using generator or inverter should they be connected and then only directly at the generator or inverter. No where else on board should the AC and DC grounds be connected. For sure not inside your electrical panel.
transmitterdan is offline   Reply With Quote
Old 30-07-2019, 16:00   #17
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,135
Re: Burned ground wire on inverter

Quote:
Originally Posted by transmitterdan View Post
That should only be true if you have no shore power. When you have shore power the AC and DC grounds must not be connected inside the boat anywhere. Only when using generator or inverter should they be connected and then only directly at the generator or inverter. No where else on board should the AC and DC grounds be connected. For sure not inside your electrical panel.
The DC negative and AC ground should always be bonded on the vessel
(as per ABYC).

I believe you may be thinking of the AC ground and AC neutral which should only be bonded at the power source whether generator, inverter or shore power.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is online now   Reply With Quote
Old 30-07-2019, 16:00   #18
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Burned ground wire on inverter

I believe your talking about the neutral and ground.
I just looked boat was wired 32 yrs ago with both grounds bonded to each other.
a64pilot is offline   Reply With Quote
Old 30-07-2019, 16:05   #19
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,135
Re: Burned ground wire on inverter

Quote:
Originally Posted by sailingunity View Post
No it is not a marine inverter, it is a "motomaster" 1000W pure sine wave. It says "mobile inverter" on the casing. If the cheapo inverter was the issue, it won't be for much longer as it is going to be replaced with a victron inverter / charger soon.
The Canadian Tire "Motomaster" inverter is not a marine inverter and should never be used on a boat. Like automotive type battery chargers the AC and DC sides are not isolated. AC and DC leaks are common and can cause significant corrosion through the DC side and are potentially lethal through the AC side particularly in fresh water. (read up on ESD-Electric Shock drowing).
__________________
If you're not laughing, you're not doin' it right.
boatpoker is online now   Reply With Quote
Old 30-07-2019, 17:16   #20
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

Quote:
Originally Posted by boatpoker View Post
The DC negative and AC ground should always be bonded on the vessel

(as per ABYC).



I believe you may be thinking of the AC ground and AC neutral which should only be bonded at the power source whether generator, inverter or shore power.
Ok, ABYC says connect boat AC shore ground to DC negative. Personally I think that is bad advice but I agree it is the ABYC recommendation. However, it should be done at one and only one point else there is risk of DC current in the AC ground wire. And when shore power is switched off so too should the shore ground be disconnected. Just connecting all the green wires together inside the boat is a poor practice IMO.
transmitterdan is offline   Reply With Quote
Old 30-07-2019, 17:17   #21
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

Quote:
Originally Posted by a64pilot View Post
I believe your talking about the neutral and ground.
I just looked boat was wired 32 yrs ago with both grounds bonded to each other.
It’s a pet peeve I have. When the boat is on internal power it should not be connected to shore at all.
transmitterdan is offline   Reply With Quote
Old 30-07-2019, 17:40   #22
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Burned ground wire on inverter

In earlier days the connection between the AC ground (green conductor) and the 12 Volt negative (black or yellow conductor) was where the galvanic isolator was inserted. Recent thinking has inserted the galvanic isolator in the shore power AC ground circuit and connected the AC ground to the 12 Volt negative with a conductor with the same ampacity as that feeding the 12 VDC to the inverter. Apparently with some inverter designs/ topology there are failures that can put large currents into this ground / return conductor.

Frankly
Frankly is offline   Reply With Quote
Old 30-07-2019, 20:58   #23
Registered User

Join Date: Jun 2016
Posts: 850
Re: Burned ground wire on inverter

Quote:
Originally Posted by transmitterdan View Post
Ok, ABYC says connect boat AC shore ground to DC negative. Personally I think that is bad advice but I agree it is the ABYC recommendation. However, it should be done at one and only one point else there is risk of DC current in the AC ground wire. And when shore power is switched off so too should the shore ground be disconnected. Just connecting all the green wires together inside the boat is a poor practice IMO.

Ok so I just went and traced all my green wires and it looks like one of them does bond my DC ground to the AC. So I guess I'm good there.

I'm sure the cheapo inverter had something to do with the issue.

I don't have a galvonic isolator, are you saying I need one?
sailingunity is offline   Reply With Quote
Old 30-07-2019, 21:22   #24
Registered User

Join Date: Oct 2012
Location: Gulf Harbour, New Zealand
Boat: Farr Phase 4, 12.8m
Posts: 1,160
Re: Burned ground wire on inverter

Yes. It's a safety device that should, IMO be mandatory. Either a galvanic isolator or an isolating transformer.

And be careful! if there was sufficient current to burn the ground wire, it could be dangerous - we don't know if it was AC or DC....

If you are not certain what you are doing, seek qualified assistance.
__________________
Matt Paulin
Neptune's Gear is offline   Reply With Quote
Old 31-07-2019, 03:19   #25
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

Quote:
Originally Posted by sailingunity View Post
Ok so I just went and traced all my green wires and it looks like one of them does bond my DC ground to the AC. So I guess I'm good there.



I'm sure the cheapo inverter had something to do with the issue.



I don't have a galvonic isolator, are you saying I need one?
Definitely I think these are a good thing. They are not a safety device in the sense they protect people. They protect the boat from corrosion caused when DC current flows from the boat to shore ground via the green safety ground wire. But I don’t think a galvanic isolator would help for the problem you had. You are doing the right thing by replacing with a proper marine rated inverter.

These truck stop inverters are a menace to boating.
transmitterdan is offline   Reply With Quote
Old 31-07-2019, 04:44   #26
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,530
Images: 241
Re: Burned ground wire on inverter

Quote:
Originally Posted by boatpoker View Post
The DC negative and AC ground should always be bonded on the vessel
(as per ABYC).

I believe you may be thinking of the AC ground and AC neutral which should only be bonded at the power source whether generator, inverter or shore power.
Indeed.
Which the transfer switch (should) accomplish.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 31-07-2019, 08:43   #27
Registered User

Join Date: Jan 2016
Location: Beaufort, NC, USA
Boat: Ta Chiao 56
Posts: 753
Re: Burned ground wire on inverter

Shouldn't the inverter AC ground wire also be sized to carry the fault current without burning?
Or is the concensus (i.e. group guess) that it was DC current, which shouldn't have been present on that conductor at all, that caused the charring?
Brewgyver is offline   Reply With Quote
Old 31-07-2019, 08:46   #28
Registered User

Join Date: Jun 2016
Posts: 850
Re: Burned ground wire on inverter

Quote:
Originally Posted by Brewgyver View Post
Shouldn't the inverter AC ground wire also be sized to carry the fault current without burning?
Or is the concensus (i.e. group guess) that it was DC current, which shouldn't have been present on that conductor at all, that caused the charring?
Yep I think the consensus is that the inverter was not isolated internally, thus allowing this fault to happen.
sailingunity is offline   Reply With Quote
Old 31-07-2019, 08:49   #29
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

Quote:
Originally Posted by Brewgyver View Post
Shouldn't the inverter AC ground wire also be sized to carry the fault current without burning?

Or is the concensus (i.e. group guess) that it was DC current, which shouldn't have been present on that conductor at all, that caused the charring?
In a proper installation there should be virtually zero current in the AC ground wire.

My guess is DC or a fault in the inverter. Since there are usually no fuses in the AC ground wire it’s important that the system design and installation follow all the standards.

But the root cause of this issue, in my opinion, was using a “trucker” type inverter. These have no place on a boat. Inverters are marine rated for a reason.
transmitterdan is offline   Reply With Quote
Old 31-07-2019, 09:25   #30
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Burned ground wire on inverter

Back in the early 1990's, Some offices where many personal computers were installed, were seeing ground wires burning up. The cause was the 208v/120v 3 phase service and 3rd order harmonic's in the PC's switching power supplies.

In layman terms the grounds were carrying several volts due to phase imbalance, where different groups of PC's were on a different 120 degree phase circuits in the 3 phase system. The fix at that time was to use a 240/120v transformer for switching power supply circuits as the 180 degree phase of a 240/120v transformer canceled out the 3rd order harmonics

On a boat, you don't have that, at least in theory. But many cheap inverters (I use one also) may have the ground connected to one leg of the inverter output. This to comply with the NEC. A residential 120v circuit uses a hot leg and neutral (center tap). The neutral always is at zero volt potential.

The typical single phase inverter does not have a neutral. That is there isn't a center tap. So while a inverter output looks like 120V 60hz, each leg alternates hot. Inverters on most boats don't have a neutral leg as shore power does. OK some inverters might have a neutral leg but I'm not aware of them.

When you connect the ground to the boats AC ground and your still plugged into shore power, it is quite possible for a phase imbalance to cause voltage potential on the ground to the inverter. This due to the switching nature of the inverter. This is exasperate as most marines are using 208v/120v transformers where leg to leg phase is 120 degrees apart.

One fix is to install a much thicker ground wire #6 or larger from inverter ground to AC ground. That to comply with ABYC. Assuming a 1000/2000 watt inverter.

I will note that I agree with TransmitterDan and I feel that connecting the AC ground to the boats DC ground can create problems. ABYC is a good code, but it assumes everything will always be perfect. On a boat that is almost never the case. So I do not have AC and DC ground connected on my boat. But that's just me.
sailorchic34 is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Negative Ground vs Positive Ground History Question. Wotname Electrical: Batteries, Generators & Solar 23 26-04-2021 04:22
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
9 V difference between ground and ground Arrandir Electrical: Batteries, Generators & Solar 12 19-07-2018 22:51
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
Smoking Hot Ground Wire Zydeco Electrical: Batteries, Generators & Solar 9 15-02-2011 04:52

Advertise Here


All times are GMT -7. The time now is 04:09.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.