Suck or Blow ? Compressor Venting

Hi Folks.

My Frigiboat fridge compressor is inside and at the back of a cupboard.

The compressor goes a bit weird when (i think) when it gets hot... Its sort of goes HoooooooErrrrrrrrrHoooooooooooErrrrrrrrrrrrrrrrrrr rrrrrr. Not the same sort of switching on and off sound as it makes when the batteries are too low.

Anyway, some time ago I put in a computer fan to SUCK the warm air out of the compartment.
The fan position does not align to the compressor at all. So sucking or blowing wont be right towards the compressor.

I have wondered what is better? A sucker or a blower?
If you were installing a fan what would you normall do?


Thanks My cold beer appreciates your thoughts


Mark
__________________
Notes on a Circumnavigation.
OurLifeAtSea.com

Somalia Pirates and our Convoy
MarkJ is offline   Reply With Quote
Old 26-05-2011, 08:49   #2
Registered User

Join Date: Dec 2009
Posts: 2,959
Images: 4
Re: Suck or Blow? Compressor venting.

If cool air can be directed into the condenser then blowing may be better. If the fan can only generally circulate air in the compressor area then sucking, exhaust, may be better as the hot air can be blown far from the area of the compressor. In either case make sure there are easy ways for cool air to enter and the hot air to leave in some other direction. Little holes are not effective.
daddle is offline   Reply With Quote
Old 26-05-2011, 09:11   #3
Registered User
 
lorenzo123's Avatar

Join Date: Dec 2010
Location: San Francisco
Boat: O'Day 37 Center Cockpit "Namaste"
Posts: 85
Re: Suck or Blow? Compressor venting.

Or you could drink beer like an Englishman.
lorenzo123 is offline   Reply With Quote
Old 26-05-2011, 09:43   #4
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by lorenzo123 View Post
Or you could drink beer like an Englishman.
Never in the presence of an Aussie, compare them to the British. I learned that while visiting Oz. I would imagine it might work the other way as well.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 26-05-2011, 10:31   #5
Long Range Cruiser
 
MarkJ's Avatar

Join Date: Dec 2007
Location: Australian living on "Sea Life" currently in England.
Boat: Beneteau 393 "Sea Life"
Posts: 12,822
Images: 25
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by David M View Post
Never in the presence of an Aussie, compare them to the British. I learned that while visiting Oz. I would imagine it might work the other way as well.
I don't know if the English own any of their brewries anymore. Haven't they all be bought out by the Aussies, Kiwis and Irish?

But it would make sailing easier: Bung the beer in a hot bath and place in the sun till ripe.



Thanks for the advice
__________________
Notes on a Circumnavigation.
OurLifeAtSea.com

Somalia Pirates and our Convoy
MarkJ is offline   Reply With Quote
Old 08-06-2011, 18:29   #6
CF Adviser
 
Bash's Avatar

Join Date: Dec 2008
Location: sausalito
Boat: 14 meter sloop
Posts: 7,260
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by lorenzo123 View Post
Or you could drink beer like an Englishman.
Wow. That's some of the worst advice I've ever seen on this forum.
__________________
cruising is entirely about showing up--in boat shoes.
Bash is offline   Reply With Quote
Old 26-05-2011, 09:38   #7
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Suck or Blow? Compressor venting.

If it is in an enclosure, it makes no difference. You either want an exhaust fan towards the top or an inlet fan towards the bottom. You want some sort of powered way of removing the heat.

The 12 volt computer fan is a great idea. I installed some in two places where I have electronics generating heat. You can even buy thermostatically controlled computer fans which run faster when more heat is being generated, saving you the noise and wasted energy of having a computer fan running at full speed all the time.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 07-06-2011, 12:38   #8
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by David M View Post
If it is in an enclosure, it makes no difference. You either want an exhaust fan towards the top or an inlet fan towards the bottom. You want some sort of powered way of removing the heat.

The 12 volt computer fan is a great idea. I installed some in two places where I have electronics generating heat. You can even buy thermostatically controlled computer fans which run faster when more heat is being generated, saving you the noise and wasted energy of having a computer fan running at full speed all the time.
In high humidity environment water tend to condense on the fan blade. If blowing into an enclosure, that water will be thrown at the equipment in the enclosure.
chala is offline   Reply With Quote
Old 07-06-2011, 15:59   #9
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,171
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by chala View Post
In high humidity environment water tend to condense on the fan blade. If blowing into an enclosure, that water will be thrown at the equipment in the enclosure.
Look on the bright side The water might then evaporate from the heated equipment, thus further cooling it... <sarcasm>
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 08-06-2011, 18:13   #10
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by senormechanico View Post
Look on the bright side The water might then evaporate from the heated equipment, thus further cooling it... <sarcasm>
Evaporative cooling does not work that well in high humidity.
chala is offline   Reply With Quote
Old 08-06-2011, 21:30   #11
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,171
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by chala View Post
Evaporative cooling does not work that well in high humidity.
That's why I added the <sarcasm>
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 26-05-2011, 10:18   #12
Registered User
 
Astrid's Avatar

Join Date: Oct 2008
Location: Northern British Columbia, part of the time in Prince Rupert and part of the time on Moresby Island.
Boat: 50-ft steel Ketch
Posts: 1,884
Send a message via MSN to Astrid Send a message via Yahoo to Astrid
Re: Suck or Blow? Compressor venting.

Indeed. A former RAF officer of my acquaintance was detailed in the summer 0f 1940 to pick up a group of Australian RAAF pilots who had arrived in Portsmouth by troopship and bring them back to the air base. He found them at the dock gazing around the harbour looking at the numerous barrage balloons. As he was about to introduce himself, one of the pilots quipped, "Why don't the Germans just cut the balloon cables and let the bloody island sink."
__________________
'Tis evening on the moorland free,The starlit wave is still: Home is the sailor from the sea, The hunter from the hill.
Astrid is offline   Reply With Quote
Old 26-05-2011, 11:01   #13
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,793
Re: Suck or Blow? Compressor venting.

I would cut a hole in the bottom of the cupboard and have the fan suck air from the bilge area--its cooler.
donradcliffe is offline   Reply With Quote
Old 26-05-2011, 11:55   #14
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,171
Re: Suck or Blow? Compressor venting.

Cool air is denser and therefore you will achieve better fan efficiency by "blowing".
I also agree about the bilge air.
I did that on my boat and in doing so, significantly cut the power usage.
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 26-05-2011, 12:59   #15
Long Range Cruiser
 
MarkJ's Avatar

Join Date: Dec 2007
Location: Australian living on "Sea Life" currently in England.
Boat: Beneteau 393 "Sea Life"
Posts: 12,822
Images: 25
Re: Suck or Blow? Compressor venting.

Quote:
Originally Posted by senormechanico View Post
I also agree about the bilge air.
I did that on my boat and in doing so, significantly cut the power usage.
Thanks Steve. I was wondering is Don was cmopletely off his rocker... so nice to have confirmation about the bilge air, I mean

It certasinly is getting warmer in grenada than I've had it probably since Malaysia and Thailand.

And it will get even warmer come September.
__________________
Notes on a Circumnavigation.
OurLifeAtSea.com

Somalia Pirates and our Convoy
MarkJ is offline   Reply With Quote
Reply

Tags
compressor


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Macerator Pump Blow Up ! CS33H Construction, Maintenance & Refit 6 15-11-2010 20:50
Blow Up at Sidney hummingway Pacific & South China Sea 16 09-04-2010 21:23
I Suck at Woodwork unbusted67 Construction, Maintenance & Refit 31 29-08-2009 22:25
Leaking Intake Gasket Caused by Too Much Blow-By? Killick Engines and Propulsion Systems 4 18-08-2009 21:08
Battery venting sailor.mo Electrical: Batteries, Generators & Solar 0 09-09-2008 07:29

Advertise Here


All times are GMT -7. The time now is 23:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.