Mystery propane sensor alarm

My Trident propane alarm has been going off recently. Today was 18 minutes after starting cooking. The sensor is mounted just below the oven, at the level of the sole.

I have an analog pressure gauge mounted near the tank. I regularly check for leakage by opening the propane solenoid, closing the manual valve on the propane tank, and checking to see if the pressure in the line drops. I have NO pressure drop, even after two hours. This tells me the propane line to the stove burner valves is leak tight. Also, the alarm does not go off during this two hour period.

It is a Tasco stove, about seven years old.

Any thoughts on what may be causing the alarm to go off? We are in a marina with the AC on, so hatches are closed and we don’t have the ventilation we do when at anchor. Could it be combustion products from the stove? Seems unlikely, since the sensor is located beneath the oven.

Cheers!

Steve
steve77 is offline   Reply With Quote
Old 22-09-2022, 16:22   #2
Registered User

Join Date: Dec 2009
Location: Australia
Boat: BUILT!!! Roberts Mauritius 43ft
Posts: 3,670
Re: Mystery propane sensor alarm

These alarms are very trigger happy apparently.

https://www.practical-sailor.com/saf...d-false-alarms
coopec43 is offline   Reply With Quote
Old 22-09-2022, 17:38   #3
Senior Cruiser
 
michaeld's Avatar

Cruisers Forum Supporter

Join Date: Sep 2010
Location: Pompano Beach, FL
Boat: Kaufman 47, Cutter
Posts: 366
Re: Mystery propane sensor alarm

Our Trident propane alarm goes off when making breakfast Bloody Marys or just about anytime we spill liquor in the galley area. It's super sensitive. Same is true if someone sprays bug repellent nearby.
michaeld is offline   Reply With Quote
Old 22-09-2022, 17:45   #4
Registered User

Join Date: Jul 2009
Location: 2023 - Colombia
Boat: Amazon 49 cutter, custom steel boat built in Surrey, Canada
Posts: 841
Images: 1
Re: Mystery propane sensor alarm

Quote:
Originally Posted by michaeld View Post
Our Trident propane alarm goes off when making breakfast Bloody Marys or just about anytime we spill liquor in the galley area. It's super sensitive. Same is true if someone sprays bug repellent nearby.
I agree, the unit is sensitive. My wife and I are very careful not to spill any rum, so we can’t speak to the sensitivity of the sensor to alcohol.

Thanks!

Steve
steve77 is offline   Reply With Quote
Old 22-09-2022, 21:21   #5
Registered User

Join Date: Dec 2009
Location: Australia
Boat: BUILT!!! Roberts Mauritius 43ft
Posts: 3,670
Re: Mystery propane sensor alarm

QUOTE"We are in a marina with the AC on, so hatches are closed and we don’t have the ventilation we do when at anchor"UNQUOTE

Obviously that is the cause.

https://www.airforums.com/forums/f16...rm-223586.html
coopec43 is offline   Reply With Quote
Old 23-09-2022, 13:15   #6
Registered User

Join Date: Jul 2013
Location: Australia East coast
Boat: EuroCat 2000 71 ft
Posts: 282
Re: Mystery propane sensor alarm

I comment for what it may be worth- you say sensor is below stove , I would consider that a further sensor should be in each lower bilge. Even a mouse hole can allow gas to flow. Permanent ventilation , regular bilge pumping and blowers especially when engine is using a lot of air , are highly recommended.
BobFord is online now   Reply With Quote
Old 23-09-2022, 19:08   #7
Senior Cruiser
 
michaeld's Avatar

Cruisers Forum Supporter

Join Date: Sep 2010
Location: Pompano Beach, FL
Boat: Kaufman 47, Cutter
Posts: 366
Re: Mystery propane sensor alarm

Just to mention that our Trident system and sensor is energized around the clock. We are rarely at marinas. Not just rum but vodka as well.
michaeld is offline   Reply With Quote
Old 24-09-2022, 13:40   #8
Registered User

Join Date: Jul 2009
Location: 2023 - Colombia
Boat: Amazon 49 cutter, custom steel boat built in Surrey, Canada
Posts: 841
Images: 1
Re: Mystery propane sensor alarm

Quote:
Originally Posted by coopec43 View Post
QUOTE"We are in a marina with the AC on, so hatches are closed and we don’t have the ventilation we do when at anchor"UNQUOTE

Obviously that is the cause.

https://www.airforums.com/forums/f16...rm-223586.html
Australian humor! Cheers!

Steve
steve77 is offline   Reply With Quote
Old 25-09-2022, 04:37   #9
Registered User

Join Date: Oct 2018
Location: St Thomas USVI
Boat: CSY 44
Posts: 23
Re: Mystery propane sensor alarm

I was told the sensor couldn't smell vodka
floydmiami1 is offline   Reply With Quote
Old 25-09-2022, 11:09   #10
Registered User

Join Date: Sep 2021
Posts: 108
Re: Mystery propane sensor alarm

Carbon monoxide can be generated from the propane burning in some cases. Your alarm may be detecting that. This page has a good explanation: https://www.elgas.com.au/blog/2107-d...o-natural-gas/
silvercreek is offline   Reply With Quote
Old 26-09-2022, 00:11   #11
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Mystery propane sensor alarm

Quote:
Originally Posted by steve77 View Post
My Trident propane alarm has been going off recently. Today was 18 minutes after starting cooking. The sensor is mounted just below the oven, at the level of the sole.



I have an analog pressure gauge mounted near the tank. I regularly check for leakage by opening the propane solenoid, closing the manual valve on the propane tank, and checking to see if the pressure in the line drops. I have NO pressure drop, even after two hours. This tells me the propane line to the stove burner valves is leak tight. Also, the alarm does not go off during this two hour period.



It is a Tasco stove, about seven years old.



Any thoughts on what may be causing the alarm to go off? We are in a marina with the AC on, so hatches are closed and we don’t have the ventilation we do when at anchor. Could it be combustion products from the stove? Seems unlikely, since the sensor is located beneath the oven.



Cheers!



Steve
Almost certainly your stove is not burning all of the gas it is consuming.

Very common with ovens that use a pilot light. There is a significant delay between the gas starting to flow again and the pilot light igniting the gas.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 26-09-2022, 05:39   #12
Registered User
 
pcmm's Avatar

Join Date: May 2014
Location: Whitby, Canada
Boat: Morgan Out Island 41
Posts: 2,267
Images: 2
Re: Mystery propane sensor alarm

Quote:
Originally Posted by steve77 View Post
My Trident propane alarm has been going off recently. Today was 18 minutes after starting cooking. The sensor is mounted just below the oven, at the level of the sole.

I have an analog pressure gauge mounted near the tank. I regularly check for leakage by opening the propane solenoid, closing the manual valve on the propane tank, and checking to see if the pressure in the line drops. I have NO pressure drop, even after two hours. This tells me the propane line to the stove burner valves is leak tight. Also, the alarm does not go off during this two hour period.

It is a Tasco stove, about seven years old.

Any thoughts on what may be causing the alarm to go off? We are in a marina with the AC on, so hatches are closed and we don’t have the ventilation we do when at anchor. Could it be combustion products from the stove? Seems unlikely, since the sensor is located beneath the oven.

Cheers!

Steve

your "test" only covers you from the tank to the solenoid (which is normally within the fist 12 inches from the tank). What about the rest of the line?

I would soap test the joint at the stove and any other joints in the system in the vicinity of the stove.

Their sensors are normally pretty good. I've been using them on different boats for 20+ years, never an issue. Their Solenoids... are almost annual disposables!
pcmm is offline   Reply With Quote
Old 26-09-2022, 06:22   #13
Registered User

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40 (sold). Still have a Hobie 20
Posts: 2,945
Images: 7
Re: Mystery propane sensor alarm

Quote:
Originally Posted by pcmm View Post
your "test" only covers you from the tank to the solenoid (which is normally within the fist 12 inches from the tank). What about the rest of the line?

I would soap test the joint at the stove and any other joints in the system in the vicinity of the stove.

Their sensors are normally pretty good. I've been using them on different boats for 20+ years, never an issue. Their Solenoids... are almost annual disposables!
l"eakage by opening the propane solenoid, closing the manual valve on the propane tank,"

He's doing it right. After pressurizing the entire system, he closes the tank valve, leaving the solenoid on. Now everything from the tank valve to the stove valves are pressurized.
cal40john is offline   Reply With Quote
Old 26-09-2022, 06:31   #14
Registered User
 
pcmm's Avatar

Join Date: May 2014
Location: Whitby, Canada
Boat: Morgan Out Island 41
Posts: 2,267
Images: 2
Re: Mystery propane sensor alarm

Quote:
Originally Posted by cal40john View Post
l"eakage by opening the propane solenoid, closing the manual valve on the propane tank,"

He's doing it right. After pressurizing the entire system, he closes the tank valve, leaving the solenoid on. Now everything from the tank valve to the stove valves are pressurized.
Good point I guess I didn't see the "opening the propane solenoid" comment
pcmm is offline   Reply With Quote
Old 26-09-2022, 14:02   #15
Registered User

Join Date: Jul 2009
Location: 2023 - Colombia
Boat: Amazon 49 cutter, custom steel boat built in Surrey, Canada
Posts: 841
Images: 1
Re: Mystery propane sensor alarm

Quote:
Originally Posted by cal40john View Post
l"eakage by opening the propane solenoid, closing the manual valve on the propane tank,"

He's doing it right. After pressurizing the entire system, he closes the tank valve, leaving the solenoid on. Now everything from the tank valve to the stove valves are pressurized.
Thanks for clarifying for me.

I’ve about decided that there must be a leak between one of the valves on the stove and one of the burners. I’m checking to see if I get the alarm when I use any of the three burners, or only one of them. It’s just a time consuming troubleshooting job.

Appreciate the input, gentlemen.

Steve
steve77 is offline   Reply With Quote
Reply

Tags
alarm, propane, sensor


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Navico 508 Wind Sensor - Mystery !!! timohara Product or Service Reviews & Evaluations 10 09-06-2021 11:37
Mystery md2030 volvo alarm vtsailguy Engines and Propulsion Systems 14 02-03-2015 05:16
Inexpensive High Water Alarm (and boat alarm) kiltym Marine Electronics 2 04-11-2012 09:22

Advertise Here


All times are GMT -7. The time now is 12:24.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.