Re: Wire too big for Victron charge controller

Quote:
Originally Posted by Senojev View Post
Response to Wotname

I don’t want to extend the debate on to ferrule or not to ferrule but only to post my source of information on Victron recommendation which is as follows. Guy is the Victron Community Manager and Produces a number of the Victron Training videos...............”
Thanks Senojev for providing Guy's point of view. It interesting to note how different it is to that of Margreet Leeftink, the author of Victron's Wiring Unlimited document.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 30-05-2023, 17:45   #122
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,447
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by Emmalina View Post
Wow reminds me of the 70's when we used to strip ww2 stuff. Whipping wires is an old art...
Not only an art but one that has different disciples -

I note Jedi used half hitches around the loom whereas we (in Coms trade school over a half century ago) had to use overhand knots. Half hitches were certainly quicker and I was never convinced the overhand (thumb) knot was better even if the instructors were certain they were.

Moving into aviation, lacing went out the window and single ties using a clove hitch topped with a reef knot was considered normal. Again I never liked them and replaced the clove hitch/reef knot with a modified constrictor knot topped with a thumb knot. When using waxed twine, a quick pass of a hot air gun allowed the wax to melt enough to add a level security to each tie.

Cable zip ties be gone...

The existential question remains - white or black twine? Me - I use both but never mixed; clean areas get white, potential dirty areas get black.
Attached Thumbnails
Click image for larger version

Name:	IMG_4814.jpg
Views:	54
Size:	406.3 KB
ID:	276047  
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 31-05-2023, 00:49   #123
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by Statistical View Post
I never said Victron requires it. In many land jurisdictions a DC disconnect on the PV side is require for code compliance regardless of what Victron says or doesn't say. I thought it was clear but I updated it for clarity.

I fully admit there is no such requirement on a boat. That doesn't mean it is a good thing just it isn't required. Until recently ELCI/GFCI weren't required on boats either despite being used on land for 30+ years. They didn't only become a good thing when ABYC finally belatedly added those requirements they were always a good thing the ABYC requirements were just lacking.

"You can always just disconnect the panel connector."
Panel connectors should not be disconnected under load. This is why a PV side DC disconnect is standard mandatory equipment in most land jurisdictions.


Look I am not saying there is any legal requirement for you to put a PV side disconnect on your boat. I am saying the exact opposite that no such requirement exists (to my knowledge). The question is if that lack of a requirement is a good thing. If you were putting solar power on your off-grid cabin in most parts of the world it would require a PV side DC disconnect. Moving that cabin to be floating on water certainly doesn't reduce risk.
I only asked you to provide us with some citations that support your statements. You come with this response like if I state that you claim it is mandatory on boats etc. but I didn’t, those are all your words, I never wrote that.

But no citations to support your claims?

Also, hiding behind some code in some country without making a case as to why this would be good or not isn’t how I roll. You have to explain why the disconnect “should be” required. Technical insight, critical thinking.

I actually have disconnects because they are convenient. Not because they are needed.

I never wrote that the panel connectors should be disconnected under load; I wrote you can simply turn the solar charge function off with the Bluetooth app or a remote switch. That is the best way to take the load of the PV and Battery circuits. After that, you can unplug, take a wire out of a terminal etc. A disconnect is a convenience, not a necessity.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 31-05-2023, 04:21   #124
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by s/v Jedi View Post
I only asked you to provide us with some citations that support your statements. You come with this response like if I state that you claim it is mandatory on boats etc. but I didn’t, those are all your words, I never wrote that.

But no citations to support your claims?
NEC 690.13

Quote:
690.13Photovoltaic System Disconnecting Means.
Means shall be provided to disconnect the PV system from all wiring systems including power systems, energy storage systems, and utilization equipment and its associated premises wiring.

(A)Location. The PV system disconnecting means shall be installed at a readily accessible location. Where disconnecting means of systems above 30 V are readily accessible to unqualified persons, any enclosure door or hinged cover that exposes live parts when open shall be locked or require a tool to open.

Informational Note: PV systems installed in accordance with 690.12 address the concerns related to energized conductors entering a building.

(B)Marking. Each PV system disconnecting means shall plainly indicate whether in the open (off) or closed (on) position and be permanently marked “PV SYSTEM DISCONNECT” or equivalent. Additional markings shall be permitted based upon the specific system configuration. For PV system disconnecting means where the line and load terminals may be energized in the open position, the device shall be marked with the following words or equivalent:

WARNING
ELECTRIC SHOCK HAZARD
TERMINALS ON THE LINE AND LOAD SIDES
MAY BE ENERGIZED IN THE OPEN POSITION

The warning sign(s) or label(s) shall comply with 110.21(B).

(C)Maximum Number of Disconnects. Each PV system disconnecting means shall consist of not more than six switches or six sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, or in a group of separate enclosures. A single PV system disconnecting means shall be permitted for the combined ac output of one or more inverters or ac modules in an interactive system.

Informational Note: This requirement does not limit the number of PV systems connected to a service as permitted in 690.4(D). This requirement allows up to six disconnecting means to disconnect a single PV system. For PV systems where all power is converted through interactive inverters, a dedicated circuit breaker, in 705.12(B)(1), is an example of a single PV system disconnecting means.

(D)Ratings. The PV system disconnecting means shall have ratings sufficient for the maximum circuit current, available fault current, and voltage that is available at the terminals of the PV system disconnect.

(E)Type of Disconnect. The PV system disconnecting means shall simultaneously disconnect the PV system conductors that are not solidly grounded from all conductors of other wiring systems. The PV system disconnecting means or its remote operating device or the enclosure providing access to the disconnecting means shall be capable of being locked in accordance with 110.25. The PV system disconnecting means shall be one of the following:

(1)A manually operable switch or circuit breaker

(2)A connector meeting the requirements of 690.33(D)(1) or (D)(3)

(3)A pull-out switch with the required interrupting rating

(4)A remote‐controlled switch or circuit breaker that is operable locally and opens automatically when control power is interrupted

(5)A device listed or approved for the intended application

Informational Note: Circuit breakers marked “line” and “load” may not be suitable for backfeed or reverse current.
Statistical is offline   Reply With Quote
Old 31-05-2023, 04:42   #125
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by Statistical View Post
NEC 690.13
Yes, clear.

This pertains to wiring entering a building that must be able to be de-energized. Reasons for this is that it can be de-energized during emergencies like a fire.

If you want to implement this on a boat, you need to construct a weatherproof housing with disconnect above deck, between the solar array and the cable gland where wiring enters the boat.

This is the reason that this requirement doesn’t exist for boats: the fire brigade will not enter the boat anyway
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-04-2024, 05:02   #126
Registered User

Join Date: Jul 2022
Posts: 16
Re: Wire too big for Victron charge controller

I just checked this post again as I am once again confronted with the same issue - wiring 1 awg wire to a victron DC/DC charger that accepts a maximum of 6 gauge. Makes me wonder why the previous owners chose this battery placement…

Anyways - thank you all for your input, didn’t realize this was such a polarizing topic! I solved the problem by using a step-down connector for the negative wire, and stepping down the positive via the isolator switch. I attached a photo for posterity. And yes, the charger to battery run is fused - everything works great!
Attached Thumbnails
Click image for larger version

Name:	IMG_8486.jpg
Views:	15
Size:	445.5 KB
ID:	288792  
nash_sailing is offline   Reply With Quote
Old 13-04-2024, 12:36   #127
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by nash_sailing View Post
I just checked this post again as I am once again confronted with the same issue - wiring 1 awg wire to a victron DC/DC charger that accepts a maximum of 6 gauge. Makes me wonder why the previous owners chose this battery placement…

Anyways - thank you all for your input, didn’t realize this was such a polarizing topic! I solved the problem by using a step-down connector for the negative wire, and stepping down the positive via the isolator switch. I attached a photo for posterity. And yes, the charger to battery run is fused - everything works great!
So here the positive conductor was wired okay, but the step down in the negative conductor creates two unnecessary crimp connections. Here’s my critique on this install:

1. Mounted on flammable surface isn’t allowed.
2. No crimped ferrules used at the Victron terminals.
3. Step down terminal shouldn’t have been used. It is now a candidate for high resistance. Simply remove strands from the 1 AWG cable until it fits the Victron terminal and crimp those in a ferrule.

Also, the screw terminals at the Victron must be very tight (can’t tell from picture)
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-04-2024, 12:45   #128
Registered User

Join Date: Oct 2010
Location: Southeastern Alaska and Guatemala, Rio Dulce
Boat: 40 foot Schucker motorsailer and 46 foot Ted Brewer custom
Posts: 254
Images: 7
Re: Wire too big for Victron charge controller

Someone probably already said this I ran into the same thing and have to say a poor design on Victron part. I’ve also Victron connections on their other products like battery monitor very poor. Come on Victron you can do better than that I know it.
freshalaska is offline   Reply With Quote
Old 13-04-2024, 12:48   #129
Registered User
 
Zanshin's Avatar

Join Date: Feb 2007
Location: Caribbean
Boat: Jeanneau 57
Posts: 2,284
Images: 2
Re: Wire too big for Victron charge controller

I have to admit that I cut sufficient strands from the AWG oversize cable to fit into my Victron controller then solder the end. I figure that <1mm of smaller gauge isn't going to make any difference at all.

Here's my current (live) setup: https://vrm.victronenergy.com/instal...share/00b72ff4
__________________
Zanshin sailing
Zanshin is offline   Reply With Quote
Old 13-04-2024, 13:05   #130
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by freshalaska View Post
Someone probably already said this I ran into the same thing and have to say a poor design on Victron part. I’ve also Victron connections on their other products like battery monitor very poor. Come on Victron you can do better than that I know it.
Yeah it is just poor form by Victron. Even if cutting a few strands doesn't matter if it janky for that to the 'solution'. The connection point should be sized to handle any reasonable AWG wire.

Icom recently refreshed their M510 as M510 "EVO" to no longer need a wireless bridge to use NMEA2000 (JFC what were they thinking) so if enough customers complain they might change it someday in a product refresh.
Statistical is offline   Reply With Quote
Old 13-04-2024, 13:06   #131
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by freshalaska View Post
Someone probably already said this I ran into the same thing and have to say a poor design on Victron part. I’ve also Victron connections on their other products like battery monitor very poor. Come on Victron you can do better than that I know it.
That’s a shunt with 3/8” bolts… what is so poor about that?

Quote:
Originally Posted by Zanshin View Post
I have to admit that I cut sufficient strands from the AWG oversize cable to fit into my Victron controller then solder the end. I figure that <1mm of smaller gauge isn't going to make any difference at all.

Here's my current (live) setup: https://vrm.victronenergy.com/instal...share/00b72ff4
The wire diameter is chosen for voltage drop over the distance of the circuit and it makes absolutely no difference to reduce diameter over the short distance of the terminal connection.
That said, a crimped ferrule would have been better than solder, which creates a hard spot and any vibration work-hardens the copper just beyond the solder which will lead to it cracking in the end. Of course securely fastening the wiring prevents that
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-04-2024, 13:52   #132
Registered User

Join Date: Oct 2010
Location: Southeastern Alaska and Guatemala, Rio Dulce
Boat: 40 foot Schucker motorsailer and 46 foot Ted Brewer custom
Posts: 254
Images: 7
Re: Wire too big for Victron charge controller

I’m not talking about the Victron battery shunt but comm connections ports that have frequently fallin out, dislodged when installing the gauges themselves. I forget what they call these type of ports, but it’s not a very positive secure connection if it falls out. There is almost nothing in all my many electronic connections as poor as theses are. If you feel different fine but it doesn’t change my feelings.
freshalaska is offline   Reply With Quote
Old 13-04-2024, 13:56   #133
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by freshalaska View Post
I’m not talking about the Victron battery shunt but comm connections ports that have frequently fallin out, dislodged when installing the gauges themselves. I forget what they call these type of ports, but it’s not a very positive secure connection if it falls out. There is almost nothing in all my many electronic connections as poor as theses are. If you feel different fine but it doesn’t change my feelings.
The display has an RJ-12 which does not fall out as it has a locking tab. Every old telephone had one of those.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-04-2024, 14:08   #134
Registered User

Join Date: Oct 2010
Location: Southeastern Alaska and Guatemala, Rio Dulce
Boat: 40 foot Schucker motorsailer and 46 foot Ted Brewer custom
Posts: 254
Images: 7
Re: Wire too big for Victron charge controller

I’m sorry to differ and yes it has fallen out a number of times, where you there to see it, I think not so don’t say it can’t happen. It’s happened on my color control and Victron battery monitor both. It’s seems solidly locked in but somehow falls out. I’m sure Victron can come up with something more positive then this even if it’s been used millions of times, time to improve like so many of Victron devices in general.
freshalaska is offline   Reply With Quote
Old 13-04-2024, 14:17   #135
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Wire too big for Victron charge controller

Quote:
Originally Posted by freshalaska View Post
I’m sorry to differ and yes it has fallen out a number of times, where you there to see it, I think not so don’t say it can’t happen. It’s happened on my color control and Victron battery monitor both. It’s seems solidly locked in but somehow falls out. I’m sure Victron can come up with something more positive then this even if it’s been used millions of times, time to improve like so many of Victron devices in general.
Well, no they won’t because RJ-12 is a proven connector type. If it falls out for you then it means it wasn’t fully inserted or somehow the connector is damaged so that the locking tab doesn’t function.

I have tested many to destruction: the cable will rip out the connector rather than the connector coming out. It is the same type of connector as for Ethernet and with the old telephones there were billions in use.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Victron BlueSolar charge controller mikedefieslife Electrical: Batteries, Generators & Solar 84 14-03-2021 04:46
Victron solar charge controller for LFP? tanglewood Lithium Power Systems 43 07-01-2019 16:26
Victron solar controller high charge voltage mikedefieslife Electrical: Batteries, Generators & Solar 28 23-12-2018 06:27
[SOLD] For Sale - Victron BlueSolar 100/50 solar charge controller with Bluetooth dongle Bleemus General Classifieds (no boats) 4 21-04-2018 20:27
Victron BlueSolar Charge Controller MPPT 75/115 "Load" Terminal Question PetePetePete Electrical: Batteries, Generators & Solar 5 30-04-2017 03:44

Advertise Here


All times are GMT -7. The time now is 12:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.