There are a few things you should understand about Frigoboat
keel cooler refrigeration as it is not a conventional design. These
keel cooler systems suffer from three design deviations not present on conventional boat
refrigeration, lack of compressor
cooling, location of filter/ moisture dryer, and improper O ring design line connector
seals. Boaters with this
keel cooler system who operate their
boats in moderate seawater temperatures that limit compressor to a duty cycle of less than thirty minutes per hour should not need to worry about
reliability.
Compressor cooling: of any
water cooled only hermetically sealed compressor can expose it to high temperatures unless temperature of its return line is supplying cool enough refrigerant. Conventional system generally supplement compressor cooling with large amounts of ambient air, this is especially important when return cool gas is reduced at low evaporator temperatures. Prolonged high temperature operation on Danfoss BD compressors has resulted in
oil flow contamination destroying complete system. Running refrigeration when boat is out of the water with only a keel cooler condenser will quickly shorten the life of your Frigoboat system.
Filter dryer and its location: Filter dryers come in many sizes and shapes. The system manufacture hopefully selects a filter dryer capable of collecting any small amount of contaminants and moisture left in a new system. On conventional refrigeration the filter dry is located in the liquid high pressure line after condenser and prior to refrigerant flow control device where its temperature is only slightly warm. Frigoboat keel cooler systems have the filter dryer in the return line next to the hot compressor iwhere it can not protect material blockage of orifice cap tube expansion device. Frigoboat reports point out another mistake with dryer too close to hot compressor discharged stored moisture into gas vapor circulating it again when it is heated.
Refrigerant final leak sealing, actual flow O ring, line
seals: are not permanent seals. Conventional quick disconnects use only actual flow O rings to prevent loss of refrigerant during line connecting and final seal is when metal to metal seal is compressed.
My recommendation to a void future problems with solder brazing and its flux migration restrictions is to cut out present line connectors and replace with refrigerant quality heavy cast brass flare nuts and flared unions. As far as the filter dryer I would leave present filter as is and install a small 32 or 50 flared filter dryer some where in line from keel cooler to evaporator. The
parts for this upgrade will cost around $ 25. I
sold over 100 small compressor complete kits where these proper flare nuts were used.
Following this procedure I would pressurize system and leek test all new connection carefully before super dehydration, holding vacuum at 200 micron for at least 4 hours.
Super dehydration today with ester
oil in system must include keeping complete system at around 100 degrees F, this includes evaporator temperature.