Danfoss BD35F Cooling System

Hi all,

I have a top loading fridge with the above cooling system (air cooled).

Looking for some experience with these systems.

We are seeing two issues:

1) What we are seeing is that at times, when the battery voltage drops below 12V, the fridge fails to run yet our separate freezer is running ok. Is this a low voltage issue or something else? The result is that overnight as our batteries are in use, the fridge stops running. However, everything else is running ok.

2) When the fridge is running well, frost will collect on the internal condensation unit. Is this just the effects of us living in the Caribbean and the warm air condensing to frost on the condensation unit or does it indicate something else?

Many thanks in advanced.
lawrence_craig is offline   Reply With Quote
Old 09-03-2019, 09:01   #2
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Danfoss BD35F Cooling System

Condensation, then frost is normal. Keep it defrosted and you will use less battery juice.
Shutdown of fridge, but not a separate freezer sounds like you're diving to deep in battery, and possibly supply wiring to fridge is inadequate, or bad connection(s).
What matters is battery voltage at startup surge right at fridge compressor electronics input, not just at battery terminals.
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is online now   Reply With Quote
Old 12-03-2019, 23:50   #3
Registered User

Join Date: Oct 2017
Posts: 67
Re: Danfoss BD35F Cooling System

We have the same problem
medsailor1 is offline   Reply With Quote
Old 13-03-2019, 05:54   #4
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Danfoss BD35F Cooling System

The number one problem causing longer out of service trouble for Danfoss BD compressors is failure to understand the importance of clean electrical power.

In the low voltage range from 11 to 12.7 volts amperage surges created by the Danfoss compressor starting will increase any potential point of resistance in wiring or old circuit breakers and switches to drop voltage. Danfoss control monitors incoming voltage and amperage that generally will alert you by flashes of Trouble LED, one flash code for low voltage every 4 seconds. The problem with Danfoss module’s low safety protection voltage trip that prevents compressor from starting is the module recognizes a few nanosecond of low voltage as a problem. This short spike can not be seen with a volt meter that prevents compressor from running. Yes basic electrical training tells us low voltage drops can be detected with a good volt meter but the short duration nanoseconds of low voltage can not be seen with the human eye.

Correct action for voltage drop do to amperage surge is to by passing each and every possible resistance area until you find the problem. A voltmeter reading without current flow is never the solution.
Richard Kollmann is offline   Reply With Quote
Old 13-03-2019, 12:48   #5
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Danfoss BD35F Cooling System

Try this, take a 10Ga wire or larger directly to the battery from the controller when it shuts down, if it runs then your problem is too small a wiring, dirty connectors or anything else that may add resistance.
If the wire is old, that is a possibility.
a64pilot is offline   Reply With Quote
Old 13-03-2019, 13:48   #6
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Danfoss BD35F Cooling System

Quote:
Originally Posted by a64pilot View Post
Try this, take a 10Ga wife or larger directly to the battery from the controller when it shuts down, if it runs then your problem is too small a wiring, dirty connectors or anything else that may add resistance.
If the wire is old, that is a possibility.
It takes two wires to Tango and make sure there is a fuse in positive wire. Then for a final fix original problem still needs to be located and corrected.
Richard Kollmann is offline   Reply With Quote
Reply

Tags
cooling


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fridge Failure - Danfoss BD35F motor start failure Anjin Plumbing Systems and Fixtures 67 22-03-2018 05:21
Problem with danfoss bd35f compressor LJScott Europe & Mediterranean 7 06-06-2016 06:52
Norcold BD35F Danfoss running but not cooling properly actionpaintball Plumbing Systems and Fixtures 47 16-09-2015 06:43
Danfoss BD35F 5 blink led flash issue Matt Johnson Plumbing Systems and Fixtures 3 10-11-2013 16:09
240vac Danfoss Compressor to 12vdc Danfoss cat man do Plumbing Systems and Fixtures 15 30-05-2013 13:13

Advertise Here


All times are GMT -7. The time now is 09:32.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.