Old 24-03-2024, 21:45   #1
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Victron battery monitor weirdness.

So my faithful old Votronic battery monitor died last week. Better part of ten years faithful service. RIP Votronic monitor.

Anyway, as luck would have it, I had the Victron BMV-712 Smart battery monitor ready to install in the new boat. So I pinched it.

But it’s acting a bit weird.

This boat has 675 AH @ 12 volts of Trojan T105s. (6 batteries) They are all happy as Larry after about five years of service. They have a nice life, being connected to 760 Watts of solar via a pair of Victron 100/30 MPPT controllers and a Victron smart battery monitor. The chargers are programmed exactly as Trojan specify for float, absorption and temperature compensation etc. And for the last five years the Votronic battery monitor has registered 100% about half an hour before the solar controllers start absorption. All great.

But the Victron BMS has the biggest case of charge optimism I’ve ever seen. Wake up in the morning with the battery bank at 80% or so… check. About right.

Sun comes up, next time I check the monitor and it’s telling me the batteries are at 100%. In less than an hour.

No way. Not even close, and the solar controllers sure don’t think so, the last few days we’ve barely made it to absorption by late afternoon.

So I’ve had a look at the trend screen and it shows a practically impossible rate of charge. (See picture attached.)

I must have some setting wrong, but which one?
Attached Thumbnails
Click image for larger version

Name:	IMG_0520.jpg
Views:	53
Size:	219.5 KB
ID:	288045  
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 24-03-2024, 22:30   #2
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 2,936
Re: Victron battery monitor weirdness.

There are three parameters that need to be set correctly in the BMV. I forget the exact names but they are:
Charged Voltage
Charged time
Tail Current

Charged voltage is your Absorption Voltage, or about one tenth of a volt less.
Charged time is how long that voltage must be maintained before resetting to 100% Somewhere in the neighborhood of 10 minutes is normal.
Tail Current is the charge current at which the bmv will reset to 100%.Typically 2-5% of capacity. Older batteries would require a higher tail current as they age.

An issue that some people experience is that when solar production drops off and charge current drops, the BMV interprets that as the battery not accepting any more charge because it is full, and resets to 100% early. It takes careful adjustment of those parameters to prevent that, or set the charged voltage higher than your absorption voltage (effectively preventing the meter from every resetting) and sync it yourself every couple days.

I would start be checking the tail current. Perhaps it needs to be lowered. And/or the charged voltage raised. IIRC Trojan has some aggressive charge voltages and the defaults in the BMV might be too low.

FWIW, if your old meter read 100% half an hour before your solar controller hit absorption, it was reading wrong also. Your batteries aren't fully charged until they are in absorption for 4-5 hours in most cases. Never before absorption even starts. (perhaps you meant float?)
__________________
-Warren
wholybee is offline   Reply With Quote
Old 24-03-2024, 23:38   #3
Marine Service Provider

Join Date: Jun 2015
Location: Croatia
Boat: Elan 45 impression
Posts: 1,212
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by GILow View Post
So my faithful old Votronic battery monitor died last week. Better part of ten years faithful service. RIP Votronic monitor.

Anyway, as luck would have it, I had the Victron BMV-712 Smart battery monitor ready to install in the new boat. So I pinched it.

But it’s acting a bit weird.

This boat has 675 AH @ 12 volts of Trojan T105s. (6 batteries) They are all happy as Larry after about five years of service. They have a nice life, being connected to 760 Watts of solar via a pair of Victron 100/30 MPPT controllers and a Victron smart battery monitor. The chargers are programmed exactly as Trojan specify for float, absorption and temperature compensation etc. And for the last five years the Votronic battery monitor has registered 100% about half an hour before the solar controllers start absorption. All great.

But the Victron BMS has the biggest case of charge optimism I’ve ever seen. Wake up in the morning with the battery bank at 80% or so… check. About right.

Sun comes up, next time I check the monitor and it’s telling me the batteries are at 100%. In less than an hour.

No way. Not even close, and the solar controllers sure don’t think so, the last few days we’ve barely made it to absorption by late afternoon.

So I’ve had a look at the trend screen and it shows a practically impossible rate of charge. (See picture attached.)

I must have some setting wrong, but which one?
Peukert exponent in setings set it at
1.25 for lead-acid batteries.
read manual
https://www.victronenergy.com/upload...unt-pdf-en.pdf
more is online now   Reply With Quote
Old 25-03-2024, 00:31   #4
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by more View Post
Peukert exponent in setings set it at
1.25 for lead-acid batteries.
read manual
https://www.victronenergy.com/upload...unt-pdf-en.pdf
Yeah, thanks for that. Of course I’ve RTFM.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 25-03-2024, 00:34   #5
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by wholybee View Post
There are three parameters that need to be set correctly in the BMV. I forget the exact names but they are:
Charged Voltage
Charged time
Tail Current

Charged voltage is your Absorption Voltage, or about one tenth of a volt less.
Charged time is how long that voltage must be maintained before resetting to 100% Somewhere in the neighborhood of 10 minutes is normal.
Tail Current is the charge current at which the bmv will reset to 100%.Typically 2-5% of capacity. Older batteries would require a higher tail current as they age.

An issue that some people experience is that when solar production drops off and charge current drops, the BMV interprets that as the battery not accepting any more charge because it is full, and resets to 100% early. It takes careful adjustment of those parameters to prevent that, or set the charged voltage higher than your absorption voltage (effectively preventing the meter from every resetting) and sync it yourself every couple days.

I would start be checking the tail current. Perhaps it needs to be lowered. And/or the charged voltage raised. IIRC Trojan has some aggressive charge voltages and the defaults in the BMV might be too low.

FWIW, if your old meter read 100% half an hour before your solar controller hit absorption, it was reading wrong also. Your batteries aren't fully charged until they are in absorption for 4-5 hours in most cases. Never before absorption even starts. (perhaps you meant float?)
I wondered about those defaults. Victron seemed adamant about them so I left well alone, but yes, now that you mention it, Trojan does like to charge hard.

Regarding the old meter, yes, technically 100% BEFORE absorption is not fully charged, but it was a one of those situations where I knew it well enough to know where I stood. It didn’t have an ability to handle Mr Peukert so I just did that in my head.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 25-03-2024, 00:41   #6
Registered User

Join Date: Jan 2023
Posts: 1,516
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by GILow View Post
So my faithful old Votronic battery monitor died last week. Better part of ten years faithful service. RIP Votronic monitor.

Anyway, as luck would have it, I had the Victron BMV-712 Smart battery monitor ready to install in the new boat. So I pinched it.

But it’s acting a bit weird.

This boat has 675 AH @ 12 volts of Trojan T105s. (6 batteries) They are all happy as Larry after about five years of service. They have a nice life, being connected to 760 Watts of solar via a pair of Victron 100/30 MPPT controllers and a Victron smart battery monitor. The chargers are programmed exactly as Trojan specify for float, absorption and temperature compensation etc. And for the last five years the Votronic battery monitor has registered 100% about half an hour before the solar controllers start absorption. All great.

But the Victron BMS has the biggest case of charge optimism I’ve ever seen. Wake up in the morning with the battery bank at 80% or so… check. About right.

Sun comes up, next time I check the monitor and it’s telling me the batteries are at 100%. In less than an hour.

No way. Not even close, and the solar controllers sure don’t think so, the last few days we’ve barely made it to absorption by late afternoon.

So I’ve had a look at the trend screen and it shows a practically impossible rate of charge. (See picture attached.)

I must have some setting wrong, but which one?
It would be most helpful sorting this out if you could post the graph and include current flow. It certain looks like the monitor is resetting to 100% as part of the synch process. Now the next step is to figure out if the issue is you batteries/charging set up, or the monitor settings.
SailingHarmonie is offline   Reply With Quote
Old 25-03-2024, 01:00   #7
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by SailingHarmonie View Post
It would be most helpful sorting this out if you could post the graph and include current flow. It certain looks like the monitor is resetting to 100% as part of the synch process. Now the next step is to figure out if the issue is you batteries/charging set up, or the monitor settings.
Yeah, current is no good because, as I implied the controllers are not even in absorption when this happens, and being solar the charge current is all over the place. Meaningless at that time of morning really. Also, this charge system has been perfect for years, sure the controller MAY have chosen to die in sympathy with the old battery monitor, but it’s unlikely.

This feels like the Victron recommended voltage threshold is just too low as wholybee is suggesting. I’m going to make those changes and see how it behaves tomorrow,
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 25-03-2024, 01:20   #8
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Victron battery monitor weirdness.

The default charged voltage setting (13.2v) does not work with solar. It should be set to ~0.5v below absorb for lead batt. So around 14.2v. Otherwise as soon as the battery hits 13.2v (on the way up). It triggers a reset because the solar amps is so small in the morning. Or if a cloud goes by. (Charging drops Under tail current setting so it think s battery is full). Where as a battery charger would be a solid ~100a on the whole charge up. Abd not be under tail current till near full.

The 4% tail current default is probably ok for flooded batts. So is the 1.25 perkurt.
smac999 is offline   Reply With Quote
Old 25-03-2024, 02:13   #9
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by smac999 View Post
The default charged voltage setting (13.2v) does not work with solar. It should be set to ~0.5v below absorb for lead batt. So around 14.2v. Otherwise as soon as the battery hits 13.2v (on the way up). It triggers a reset because the solar amps is so small in the morning. Or if a cloud goes by. (Charging drops Under tail current setting so it think s battery is full). Where as a battery charger would be a solid ~100a on the whole charge up. Abd not be under tail current till near full.

The 4% tail current default is probably ok for flooded batts. So is the 1.25 perkurt.
Thank you, you’ve made me feel good because an hour ago I slapped myself and told myself to just go with my gut feel and use 14.2.

And you’ve articulated something that was bothering me about the Victron algorithm, which was that it seemed more appropriate to mains chargers than solar.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 25-03-2024, 19:06   #10
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

So far, so good…

Voltage and current over the same time period for clarity. Solar input is being hampered by the current swinging the bow into the sun and throwing a shadow over both panel banks.
Attached Thumbnails
Click image for larger version

Name:	IMG_0522.jpg
Views:	18
Size:	201.8 KB
ID:	288072   Click image for larger version

Name:	IMG_0523.jpg
Views:	18
Size:	211.2 KB
ID:	288073  

__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 25-03-2024, 23:09   #11
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Yep, 14.2 for Charged Voltage and kept the 4% tail current. Looks about right now. Thanks to all for the useful contributions.
Attached Thumbnails
Click image for larger version

Name:	IMG_0525.jpg
Views:	14
Size:	210.2 KB
ID:	288075   Click image for larger version

Name:	IMG_0524.jpg
Views:	14
Size:	212.5 KB
ID:	288076  

__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 26-03-2024, 07:23   #12
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,004
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by GILow View Post
Yep, 14.2 for Charged Voltage and kept the 4% tail current. Looks about right now. Thanks to all for the useful contributions.
What is the absorption voltage in the mppt configuration?
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 26-03-2024, 07:36   #13
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,317
Re: Victron battery monitor weirdness.

With my AGMs, I have the Victron "full charge" settings set for 13.3v and 0.5% tail current for at least 10 minutes. It never syncs to 100% prematurely, only after completing absorb, dropping to float and then being in float for a bit. Basically, 0.5% won't happen for any sustained period at or above 13.3 volts unless the batteries are pretty much full.
rslifkin is offline   Reply With Quote
Old 26-03-2024, 15:19   #14
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by s/v Jedi View Post
What is the absorption voltage in the mppt configuration?
A picture is worth a thousand words. Well, a couple of dozen in this case.
Attached Thumbnails
Click image for larger version

Name:	IMG_0526.jpg
Views:	36
Size:	197.2 KB
ID:	288108  
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 26-03-2024, 15:22   #15
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,155
Re: Victron battery monitor weirdness.

Quote:
Originally Posted by rslifkin View Post
With my AGMs, I have the Victron "full charge" settings set for 13.3v and 0.5% tail current for at least 10 minutes. It never syncs to 100% prematurely, only after completing absorb, dropping to float and then being in float for a bit. Basically, 0.5% won't happen for any sustained period at or above 13.3 volts unless the batteries are pretty much full.
I’ve not had much to do with AGMs yet but it is my understanding that they are less “resistive” to charge than FLA?

Also, are you charging with solar or some other source? As smac999 notes, solar fluctuations can really muddy the picture.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Reply

Tags
battery, monitor, Victron


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dinghy prop 4 blade super weirdness nfbr Propellers & Drive Systems 21 24-07-2022 20:56
Weirdness With Jabsco Sensor Max 14 pump Jd1 Marine Electronics 12 26-09-2016 18:31
voltage mismatch weirdness xeon_tsd Electrical: Batteries, Generators & Solar 4 29-02-2016 16:38
Bullet On-Board Wifi Weirdness ThatSailorDude Marine Electronics 0 16-11-2014 07:53
Victron battery monitor auto synch question Downeaster Electrical: Batteries, Generators & Solar 16 15-07-2013 17:25

Advertise Here


All times are GMT -7. The time now is 10:50.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.