Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 06-02-2018, 15:07   #16
Registered User
 
boom23's Avatar

Join Date: Oct 2012
Location: Med.
Boat: Amel 50
Posts: 1,016
Re: Isolation Transformer

The Victron Isolation transformer converts 110V to 230V or 230V to 110V. It does not change the frequency.

Here is the brochure: https://www.victronenergy.com/upload...formers-EN.pdf
boom23 is offline   Reply With Quote
Old 06-02-2018, 16:14   #17
Elvish meaning 'Far-Wanderer'
 
Palarran's Avatar

Join Date: Jan 2008
Location: Boat - Greece - Me - Michigan
Boat: 56' Fountaine Pajot Marquises
Posts: 3,489
Re: Isolation Transformer

I don't think so. If you put 230v in, you get 230v out. So if your in Europe and have 230 single phase, and want to get 115v, you have to use the auto transformer to create the neutral between the 230v. The Charles had a center tap on the transformer that allowed this easily.
__________________
Our course is set for an uncharted sea
Dante
Palarran is offline   Reply With Quote
Old 06-02-2018, 16:19   #18
Registered User
 
boom23's Avatar

Join Date: Oct 2012
Location: Med.
Boat: Amel 50
Posts: 1,016
Re: Isolation Transformer

Quote:
Originally Posted by Palarran View Post
I don't think so. If you put 230v in, you get 230v out. So if your in Europe and have 230 single phase, and want to get 115v, you have to use the auto transformer to create the neutral between the 230v. The Charles had a center tap on the transformer that allowed this easily.
My boat was 110V 60Hz. I connected to S. Pacific 230V 50Hz shore power and I had 110V 50Hz on board. I had the non-auto 3600W Victron Isolation transformer... If you had a different experience with the same equipment, you were doing something wrong.

Read the manual: https://www.victronenergy.com/upload...L-FR-DE-ES.pdf
boom23 is offline   Reply With Quote
Old 06-02-2018, 21:07   #19
Registered User
 
boom23's Avatar

Join Date: Oct 2012
Location: Med.
Boat: Amel 50
Posts: 1,016
Re: Isolation Transformer

I did not mean to sound harsh in my last post. It's been a long day...

The non-auto Victron isolation transformer does the same thing as the auto version. On the non-auto version, you just have to change a couple of jumpers and you can up-convert or down-convert the incoming voltage. It does work. I chose the non-auto version because I wanted to reduce complexity (electronics) and future problems.
boom23 is offline   Reply With Quote
Old 06-02-2018, 22:10   #20
Registered User
 
SailRedemption's Avatar

Join Date: Feb 2014
Location: New Orleans
Boat: Kaufman 47
Posts: 1,184
Re: Isolation Transformer

We decided not to go with a transformer on our boat. We have a basic Victron Phoenix battery charger that can do power supply and take 110-230v 50-60hz and charge our batteries. From there we are 90% 12v on board and will have an inverter soon. We can connect to shore power and just turn on the battery charger in any country. Or I can pigtail just the battery charger if need be. We do have a 50a ELCI main breaker and a DEI galvanic isolator before our main distribution panel. There will be a switch for the shore/inverter connection when the inverter gets connected.

Being a mostly 12v boat we didn't see the reason for the expense of a transformer. But I figured I would share another way.
SailRedemption is offline   Reply With Quote
Old 07-02-2018, 04:31   #21
Elvish meaning 'Far-Wanderer'
 
Palarran's Avatar

Join Date: Jan 2008
Location: Boat - Greece - Me - Michigan
Boat: 56' Fountaine Pajot Marquises
Posts: 3,489
Re: Isolation Transformer

Quote:
Originally Posted by boom23 View Post
I did not mean to sound harsh in my last post. It's been a long day...

The non-auto Victron isolation transformer does the same thing as the auto version. On the non-auto version, you just have to change a couple of jumpers and you can up-convert or down-convert the incoming voltage. It does work. I chose the non-auto version because I wanted to reduce complexity (electronics) and future problems.
That's all right, you are right. I didn't know that but am glad to now.
__________________
Our course is set for an uncharted sea
Dante
Palarran is offline   Reply With Quote
Old 05-05-2018, 17:31   #22
Registered User

Join Date: Apr 2017
Location: Guam
Boat: Kings Legend 41
Posts: 9
Re: Isolation Transformer

Any concerns for heat? I have been considering a Charles G2 but I'm concerned about the amount of heat it will give off. If I install it in the aft stateroom I have concern for the amount of heat in a sleeping quarter. If I position it in my alternate location it will be near a 500Ah battery bank, I'd prefer not to expose the battery bank to excessive heat when plugged in. Any comments on how much heat a Charles Marine G2 3.8Kv transformer produces? I was told to expect output similar to a portable quartz halogen workshop light.
__________________
Austin & Belinda
SV Flying Spirit
Kings Legend 41
SV FlyingSpirit is offline   Reply With Quote
Old 05-05-2018, 18:34   #23
Registered User

Join Date: Dec 2017
Posts: 49
Re: Isolation Transformer

The more you draw out of the transformer the more heat you will get from it. According to the Charles tech support web site the range of temperature is from 0 to 50C. If the space the transformer is installed in is enclosed space even a warm transformer will become hot over time if no ventilation.
windcastle1 is offline   Reply With Quote
Old 05-05-2018, 20:08   #24
Registered User

Join Date: Apr 2012
Location: Currently in the Caribbean
Boat: Cheoy Lee 47 CC
Posts: 1,037
Re: Isolation Transformer

Quote:
Originally Posted by Jammer View Post
You will have to answer two questions:

1. How much time will you spend in marinas, rather than on the hook?

2. To what extent does your boat and your boating lifestyle depend upon 120v?

I personally would opt for other solutions unless I had specific plans to stay in marinas and run the air conditioning.
We are planning a 3-5 year trip with many ports of call and varying standards, I like to have options.
I'm, already rewiring the boat so putting in an isolation transformer would not be that much more work, if I could get one for $275.00 it would be well worth the price. We won't be staying in marinas much but when you need to you usually really need to.
The boat already has a 5kw generator and a pretty up to date charging system but for those days when we need to stay in a marina I'd like to protect my internal systems. It won't be often, but even with the limited periods I've stayed in marinas I've run into issues with the marina electrical systems.
lifeofreilly57 is offline   Reply With Quote
Old 05-05-2018, 21:09   #25
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,072
Re: Isolation Transformer

We have a US 120/240V 60Hz boat and installed a Victron Isolation transformer. We configure it to output 240V regardless of input (120 or 240V). This 240V output is fed into a Victron Quattro 3kW 230V/50Hz unit. You can reprogram it to 240V/60Hz which we did. It also has a genset input that is 240V/60Hz so there is no 120V involved and no balancing issues.

The output of the Quattro is connected to a Victron Autotransformer which creates a new Neutral so that you get the familiar 120-0-120 again. Any unbalance is taken care of by the Autotransformer.

These transformers are 9 years old and still work perfectly
s/v Jedi is offline   Reply With Quote
Old 06-05-2018, 02:53   #26
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,595
Images: 241
Re: Isolation Transformer

Greetings and welcome aboard the CF, Windcastle.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 06-05-2018, 14:22   #27
Registered User

Join Date: Dec 2017
Posts: 49
Re: Isolation Transformer

An often overlooked feature of these transformers is complete electrical isolation between your boat and shore power. In addition to saving your zincs it also prevents a ground fault interuption in marinas that have GFI breakers.
If any of your green ground wires touch any of your white neutral wires in your boat you will trip the GFI breaker on the dock.
windcastle1 is offline   Reply With Quote
Old 06-05-2018, 17:52   #28
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,671
Re: Isolation Transformer

Quote:
Originally Posted by windcastle1 View Post
An often overlooked feature of these transformers is complete electrical isolation between your boat and shore power. In addition to saving your zincs it also prevents a ground fault interuption in marinas that have GFI breakers.
If any of your green ground wires touch any of your white neutral wires in your boat you will trip the GFI breaker on the dock.

the transformer then becomes a band aid for other problems... no properly wired boat should trip a GFI. if it does, find and fix your issues first.

the safty issue is does add is if a dock ground has no ground or a bad dock ground, the iso transformer will still trip a shorted to ground issue on the boat. IE stove hot wire shorts out to metal frame of appliance. in a house that would trip the breaker, in a good wired marina it will trip the breaker, if the dock ground is poor and can't handle 15+ amps it will no trip anything.
the iso transformer creating new ground on the boat, will trip breakers no mater how bad the dock ground is.
smac999 is offline   Reply With Quote
Old 06-05-2018, 19:24   #29
Registered User

Join Date: Dec 2017
Posts: 49
Re: Isolation Transformer

It is a band aid and it should be corrected but until it is fixed it solves an immediate problem until resolved as well with all of the previously described benefits.
windcastle1 is offline   Reply With Quote
Old 07-05-2018, 07:17   #30
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,540
Re: Isolation Transformer

Post #28: Spot on.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Isolation Transformer for Europe Charlie Electrical: Batteries, Generators & Solar 22 27-06-2011 06:55
Victron Isolation Transformer Voltage Increase Ultimarv Electrical: Batteries, Generators & Solar 5 06-09-2010 09:42
ELCI and Isolation Transformer Microship Electrical: Batteries, Generators & Solar 20 19-08-2010 15:54
Isolation Transformer and SSB Sailabel Marine Electronics 3 02-04-2010 16:30
Isolation transformer Pa La O La Construction, Maintenance & Refit 11 12-08-2008 13:14

Advertise Here


All times are GMT -7. The time now is 18:57.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.