Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 26-08-2014, 02:45   #166
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Inverter Dying?

Quote:
Originally Posted by sparrowhawk1 View Post
It's connected together through a breaker. I describe it in a previous post. My main is three Breakers controlled by one switch. And it does not look like the breaker panel has been modified in any way
A triple breaker does not connect neutral and ground but switches them to their respective buses. These buses should not have any interconnection.

A house is static after initial construction, no changes are regularly made to the wiring. If it is correct when built it will stay that way.

A boat that goes anywhere is plugged into the source in any number of marinas, any of which can be badly wired, This can include no ground connection to shore and the possibility of reverse polarity. In North America ABYC calls for the AC ground to be connected to the DC negative bus for safety reasons. While this is debatable it is done this way on virtually every boat in North America by the builder. If you were to plug into a reverse polarity shorepower connection and had the ground and neutral connected on the boat the neutral would become hot as would the DC system. That is why it is dangerous.
mitiempo is offline   Reply With Quote
Old 26-08-2014, 02:50   #167
Registered User
 
sparrowhawk1's Avatar

Join Date: Jan 2014
Location: Miami Beach Fl
Boat: Colombia Cc 11.8
Posts: 1,758
Damn one more thing to add to my to do list. luckily I'm at anchor so I can push it off for a while. Edit: I don't think it's possible for me to write post without editing it. but did you read my previous post? the ground goes directly from shore to the bus bar from the bus bar to the top the circuit breaker. from the bottom of the circuit breaker to the top of the neutral circuit breaker. so I would think if neutral was hot the breaker would blow. And maybe that's its whole point
sparrowhawk1 is offline   Reply With Quote
Old 26-08-2014, 02:54   #168
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Inverter Dying?

I watched one of the videos and it doesn't relate to a boat's proper wiring.
mitiempo is offline   Reply With Quote
Old 26-08-2014, 02:58   #169
Registered User
 
sparrowhawk1's Avatar

Join Date: Jan 2014
Location: Miami Beach Fl
Boat: Colombia Cc 11.8
Posts: 1,758
Nope not about boat wiring it all. Just ways an inverter can be dangerous
sparrowhawk1 is offline   Reply With Quote
Old 26-08-2014, 03:00   #170
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Inverter Dying?

All wiring can be dangerous if done incorrectly.

If one is not sure they should hire a professional.
mitiempo is offline   Reply With Quote
Old 26-08-2014, 03:12   #171
Registered User
 
sparrowhawk1's Avatar

Join Date: Jan 2014
Location: Miami Beach Fl
Boat: Colombia Cc 11.8
Posts: 1,758
I know a professional that burned down a church: whistling
sparrowhawk1 is offline   Reply With Quote
Old 26-08-2014, 04:35   #172
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Inverter Dying?

Quote:
Originally Posted by transmitterdan View Post
I like your idea of asking others about this. Here are a couple of test question for the EEs
I won't do that. It would be rude. "Would you do me a favor and review this? Oh, take this test first."

Quote:
Originally Posted by rwidman View Post
Well I'm not an engineer, only a technician, so my decision would be to replace the bulb with one with a smaller wattage rating.

What do you think of that solution?
Very practical. The scenario transmitterdan proposes is the basis for many light dimmer circuits, especially those that use LEDs.

Quote:
Originally Posted by transmitterdan View Post
Fluke make high quality true RMS clamp-on meters as do other test equipment manufacturers. They will be disappointed to learn here on the internet that they are selling expensive equipment that provides misleading results to those poor unsuspecting "scientists" who don't understand their tools.
Companies like Fluke and Agilent and others will be the first to tell you that RMS meters will read wrong for non-sinusoidal waveforms. If I recall correctly a square wave with 50% duty cycle (not the PWM we have been discussing for an inverter) will measure almost 50% low due to the waveform crest factor.

Quote:
Originally Posted by transmitterdan View Post
You mean the scope with the "AC/DC" switch on the front? If you switch an oscilloscope to the "AC" coupling position what you see is exactly what it says.
The choice of AC or DC coupling is simply to determine what portions of the signal you see. With AC coupling you will only see the AC component and time variant DC as long as the variation is fast enough to pass through the capacitive coupling. With DC coupling you will see both the AC and DC components.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 26-08-2014, 05:52   #173
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Inverter Dying?

Quote:
Originally Posted by Auspicious View Post
I won't do that. It would be rude. "Would you do me a favor and review this? Oh, take this test first."
It's a really easy question for the however many EEs here that all disagree with me.

Quote:
Originally Posted by Auspicious View Post
Companies like Fluke and Agilent and others will be the first to tell you that RMS meters will read wrong for non-sinusoidal waveforms. If I recall correctly a square wave with 50% duty cycle (not the PWM we have been discussing for an inverter) will measure almost 50% low due to the waveform crest factor.
These company's marketing teams will be disappointed to hear this as they will have to now rewrite all their sales literature. The current we are discussing is not square wave as no inverter draws square wave current from the battery. Fluke and Agilent claim exactly the opposite as you believe. They put RMS circuitry into their meters precisely so they can measure true RMS with high crest factors. I suspect you are thinking of older meters that measure AC by rectification (like Simpson 260) and these meters do not give accurate results for high crest factor currents. The crest factor of the battery current is within the limits of any good Fluke handheld clamp-on meter.
transmitterdan is offline   Reply With Quote
Old 26-08-2014, 06:21   #174
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Inverter Dying?

Quote:
Originally Posted by sparrowhawk1 View Post
............ Edit: and just curious why is it mandatory for houses to connect the ground and the neutral where electricity enters the home but on boats it's dangerous. ........
When a boat is connected to shore power the ground is at the service entrance to the marina or home where the shore power originates. This is the "source" The ground and neutral are connected together at that point. Connecting them together at the boat creates two neutral to ground connections.

Once you disconnect the boat from shore power, you need to connect the ground and neutral together at the inverter or genset. One of these now becomes the "source".
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 26-08-2014, 06:49   #175
Registered User
 
sparrowhawk1's Avatar

Join Date: Jan 2014
Location: Miami Beach Fl
Boat: Colombia Cc 11.8
Posts: 1,758
Great explanation. So I guess my main breaker is wired the way it is, is to" break" If the neutral is hot
sparrowhawk1 is offline   Reply With Quote
Old 26-08-2014, 09:00   #176
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Inverter Dying?

Rwidman is right about connecting neutral and ground at source. But this is a US thing and many boats in other countries don't connect neutral to ground for onboard generated AC power. I don't wish to debate this since it was covered extensively in another thread. I just wanted to point out that there are different recommendations in the world so don't go nuts when you find a boat with isolated neutral. There are lots of them in the world.
transmitterdan is offline   Reply With Quote
Old 26-08-2014, 10:04   #177
Registered User

Join Date: Apr 2006
Posts: 4,413
Re: Inverter Dying?

Thanks for these comments. I may relocate the 1000 watt inverter to about 3 feet from fuse although I use pretty small loads. This would reduce the length of the wire from 8' to 3'. Would #1 wire or #2 wire be OK for 3'?
Sandero is offline   Reply With Quote
Old 26-08-2014, 10:23   #178
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Inverter Dying?

Quote:
Originally Posted by Sandero View Post
Thanks for these comments. I may relocate the 1000 watt inverter to about 3 feet from fuse although I use pretty small loads. This would reduce the length of the wire from 8' to 3'. Would #1 wire or #2 wire be OK for 3'?
You must count the length of the cable from the battery to the fuse in your calculations. Also, the negative cable.

Your best advice is the manufacturer's instructions as to cable size and length.

In general, the DC cables should be as short as possible. The AC cables can be any reasonable length just like they are in your house.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 26-08-2014, 10:26   #179
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Inverter Dying?

Quote:
Originally Posted by Sandero View Post
...I may relocate the 1000 watt inverter to about 3 feet from fuse...
3' from the batteries is what I would shoot for.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 26-08-2014, 10:38   #180
Registered User

Join Date: Apr 2006
Posts: 4,413
Re: Inverter Dying?

The actual distance is not what counts... it's the length of the wire... so...new location is maybe 25" from batts... but the wire distance (guessing from memory here) would be 30" from

12v -
24" to neg disconnect switch
4" to neg buss
38" to inverter
66" +/-

12v +
22" to pos buss
12" to fuse
36" to inverter
80" +/-

Best I can do!
Sandero is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
420: 420 inverter issues. Our inverter is not working and we are not able to find a manual EW-WE Lagoon Catamarans 5 15-04-2020 07:04
Inverter Draw is it relative to the appliance using it or the wattage of the inverter felixqld66 Electrical: Batteries, Generators & Solar 5 06-06-2011 05:50
True (Pure) Sine Inverter vs Modified Sine Inverter Alecadi Electrical: Batteries, Generators & Solar 19 05-05-2011 06:19
Separate Charger and Inverter or Charger-Inverter ? SvenG Electrical: Batteries, Generators & Solar 14 15-10-2010 17:14
Calculating Amps Drawn Before Inverter and After Inverter ? impi Electrical: Batteries, Generators & Solar 23 26-09-2010 22:24

Advertise Here


All times are GMT -7. The time now is 06:38.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.