Quote:
Originally Posted by CaptainRivet View Post
Just saw this.
You are sure thats the issue?
Active or passive balancing?
At voltage level did you stop charging daily, 3,55V?
It depends how and when balancing starts with the REC, if done from 3,45 volt on and you go to 3,55 then it might not be enough time but if it done from 3,30V or continous then it should be.
There is a ongoing discussion if a active balance can work properly and eg Dacian, the developer of the electrodacus BMS states it cannot and thats why he implemented a passive one.
If thats right I have not enough experience about that to judge, still learning here....

Interesting article from Eric Bertscher from Nordkyn design when terminating the charge:
https://nordkyndesign.com/charging-m...battery-banks/


I see no argument that active balancing can’t be used.

Firstly cell Imbalance is it the end of the world. If you implement cell level monitoring ( and every lithium system should be cell monitored then all that happens is the charge terminates on the first cell to reach the designated charge cutoff parameters.

Now in most cases cell imbalance where fractional C usage is deployed ( typical of boats ) you will see imbalances of 5-10 % all this means is you have slightly less energy available then the theocratical Ah number suggests. So your 500Ah system might now be a 475Ah. Given you should have built in some capacity headroom anyway , big deal , so what.

In my experience cell imbalance tends to remain fairly static over time. So it’s not rust things get progressively worse.

Balancing is sometimes presented as somehow “ drawing off charge “ to reduce the voltage to a balance , this is not right. What ( top) balancing is in fact is diverting charge current away from the cell that has reached charge stop so as to allow the other cells to continue to charge to their charge stop points.

With active or passive top balancing , therefore you need to have two conditions , (a) the charge current at the start of balance must be within the allowable range of the balance load. And (b) there has to be enough time to achieve the balance.

So if we have say 25aH imbalance and a 1A balance load , then it will take 25 hours at 1A charging so the charging process must have this time available. This can be problematic on boats.

Secondly most top balancing is made nonsense of by the battery continuing to supply loads while charging , because in many cases ( low capacity mains chargers or falling sunlight ) the load currents exceed the available charge currents and a discharge cycle begins , top balancing is useless here

Active and passive balancers ( in terms of terminology , these terms are used in the electronics industry to simply mean the load type ) do the same thing they provide a load which diverts charge current away from the out of balance cell either lost as heat for passive balancers or converted into charge current for active balancers.

The other issue is of course that the battery charging current at the time of a cell reaching its charge stop point may be to high to engage the balance load. If your charge current is 2A and you balance load can only handle 1A , and you reach a cell charge stop point , you are now forced to stop charging the whole bank irrespective of whether you can balance it or not.


I’m coming to the conclusion that cell based charging is actually the best way to handle lithium recharging. Ie a dedicated isolated boost converter dedicated to each cell. All 12v nominal charges sources are paralleled into the cell charger and the BMS has one charger per cell to control and NO balancing is every necessary as each cell is dealt with individually

I really think the issues we have are largely brought about by trying to shoehorn lithium into a overall charging system designed for a different battery technology entirely.

In my opinion in process passive balancing , ie diverting current from cells charging slower is a travesty of engineering
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-05-2022, 11:08   #797
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,214
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

My question is why does almost everyone want to complicate a simple job ?
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 14-05-2022, 12:21   #798
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by newhaul View Post
My question is why does almost everyone want to complicate a simple job ?


How is it simple !
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-05-2022, 12:36   #799
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,214
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by goboatingnow View Post
How is it simple !
My system is 250ah calb cells 4p1s 12 v nom . 200 amp DALY BMS passive top balance at 3.6v .
300 amp shunt battery monitor. Tracer 30 amp Mppt solar controller. ( fully programmable via Bluetooth)
On my vessel all normal loads go through the load circuit on the controller except the inverter charger. ( trace 2512 ) fully programmable charging )
3 years liveaboard. With no (0) issues. It does its job so I don't have to think about it .
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 14-05-2022, 19:27   #800
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by Catapulte View Post
CatNewBee....


Would it be possible to show the integration of the Mastervolt inverter on the original Cerbo GX Touchscreen when running your software ?
Or asked the other way ... Could your software be run in the original Cerbo GX instead of the original software from Victron Energy or is this only possible when it runs on the Raspberry Pi ?


BTW: Thank you for the great work you are doing here and all the inspiration.
It is the modified Victron software, so yes, it would run on Victron hardware too (most of it, the part that uses USB Interfaces). The temperature sensors not sure. Cerbos have GPIO ports, maybe configurable for 1Wire or I2C, maybe not. But in general it is just python / qml script software.

Well, the changes I made were not meant to be used on other systems, some are hard coded based on my setup.
__________________
Lagoon 400S2 refit for cruising: LiFeYPO4, solar and electric galley...
CatNewBee is offline   Reply With Quote
Old 15-05-2022, 02:02   #801
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by newhaul View Post
My system is 250ah calb cells 4p1s 12 v nom . 200 amp DALY BMS passive top balance at 3.6v .

300 amp shunt battery monitor. Tracer 30 amp Mppt solar controller. ( fully programmable via Bluetooth)

On my vessel all normal loads go through the load circuit on the controller except the inverter charger. ( trace 2512 ) fully programmable charging )

3 years liveaboard. With no (0) issues. It does its job so I don't have to think about it .


I didn’t think Daly did balancing ?
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 15-05-2022, 06:38   #802
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,214
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by goboatingnow View Post
I didn’t think Daly did balancing ?
Yes they actually do top balance. Here is a shot of the spec sheet
Attached Thumbnails
Click image for larger version

Name:	Screenshot_20220514-102501_Photos.jpg
Views:	100
Size:	238.1 KB
ID:	257770  
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 15-05-2022, 07:14   #803
Marine Service Provider

Join Date: Jun 2015
Location: Croatia
Boat: Elan 45 impression
Posts: 1,278
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by BetterDays 2020 View Post
I have been searching for a 500 amp Marine Rated Circuit Breaker, and can't find one. Who makes them and where can I find one?

Thanks,
https://www.eti.hr/proizvodi-i-uslug...mounting-plate

https://www.megashop.hr/product/1859...DC-690-VAC-1-S
more is offline   Reply With Quote
Old 18-05-2022, 20:11   #804
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,222
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Ok the first 500A breaker that’s up to the spec, like NH fuses high amp public grid equipment that’s also DC rated. Can‘t find the resistance though as with primarily AC fuse this is not a critical parameter,especially in the 690 and 1000V range.
The 1000V one will have a very high resistance for sure, same with NH3 1000V spec which is too much drop for 12 or 24V. 690V can or cannot work well.
Best is 400V spec equipment for low voltage dc use as here resistance is a critical parameter for purchase decisions and therefor resistance is as low as possible.
CaptainRivet is offline   Reply With Quote
Old 18-05-2022, 23:24   #805
Marine Service Provider

Join Date: Jun 2015
Location: Croatia
Boat: Elan 45 impression
Posts: 1,278
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by CaptainRivet View Post
Ok the first 500A breaker that’s up to the spec, like NH fuses high amp public grid equipment that’s also DC rated. Can‘t find the resistance though as with primarily AC fuse this is not a critical parameter,especially in the 690 and 1000V range.
The 1000V one will have a very high resistance for sure, same with NH3 1000V spec which is too much drop for 12 or 24V. 690V can or cannot work well.
Best is 400V spec equipment for low voltage dc use as here resistance is a critical parameter for purchase decisions and therefor resistance is as low as possible.
pick Size 3 / 630A Resistance (R) = 8.4E-5 ohm (Ω)
more is offline   Reply With Quote
Old 19-05-2022, 01:55   #806
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,222
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by more View Post
pick Size 3 / 630A Resistance (R) = 8.4E-5 ohm (Ω)
Good
Thank you, learned something new
CaptainRivet is offline   Reply With Quote
Old 19-05-2022, 04:49   #807
Registered User

Join Date: Jan 2015
Boat: Lagoon 450 F
Posts: 159
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

The problem with balancing not only on top is that each cell has its own individual charging curve. The one that bottoms out (without balancing) at around 3.4V may be the same one that tops out at around 3.55V (without balancing). If this cell has already been topped up at 3.4V, it will end up much further above the others at 3.55. Therefore balancing below the top range is counterproductive. It forces debalancing at the end of charge.

The charge curves of the individual cells can be very irregular with LiFePO4, sometimes in the range of 3.3V even at higher state of charge the voltage drops by mV to rise again later. If this is then rebalanced, the result is debalancing.
Ulstue is offline   Reply With Quote
Old 19-05-2022, 13:10   #808
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,222
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Quote:
Originally Posted by Ulstue View Post
The problem with balancing not only on top is that each cell has its own individual charging curve. The one that bottoms out (without balancing) at around 3.4V may be the same one that tops out at around 3.55V (without balancing). If this cell has already been topped up at 3.4V, it will end up much further above the others at 3.55. Therefore balancing below the top range is counterproductive. It forces debalancing at the end of charge.

The charge curves of the individual cells can be very irregular with LiFePO4, sometimes in the range of 3.3V even at higher state of charge the voltage drops by mV to rise again later. If this is then rebalanced, the result is debalancing.
Thats why your BMS rhould also track charge current, nos only Volt. Then it can balance earlier without getting into debalancing.
If you are 4S =12V and charge or load stays under 50%of its max cont C-Rate then no till little balancing needed which also takes a small amount of time to do so.
CaptainRivet is offline   Reply With Quote
Old 20-05-2022, 14:05   #809
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

It doesnt work like this, cells change their resistance when being charged or discharged, sometimes lower cells during bulk outrun the higher cell when hitting absorption and may even cause disconnects. You can only judge imbalances when the cells are near full.
__________________
Lagoon 400S2 refit for cruising: LiFeYPO4, solar and electric galley...
CatNewBee is offline   Reply With Quote
Old 20-05-2022, 14:24   #810
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,214
Re: Merged LiFeYPO4 1000Ah Winston prismatic cells and all electric galley...

Actually did capacity test on Tuesday at full charge 3.6v on 3 cells 3.42v on cell #2 drew down to 12v to test and on full recharge got 265.8ah out of the cells that were sold to me as 240ah units . Now all 4 cells are within .1v of each Other at 14.4v cells were as follows 3.6v, 3.59v, 3.6v , and 3.61v
Reset my meter to read as a 250ah bank all is good. It was reading at 265.1ah 3 years ago at start of service life
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Reply

Tags
electric, galley


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Winston 700Ah lithium cells Drelen General Classifieds (no boats) 16 23-09-2019 17:04
Has the all-electric galley come of age? Jammer Cooking and Provisioning: Food & Drink 166 06-12-2018 09:26
Specific Question about Voltage of LiFeYPO4 Cells JoeFish Electrical: Batteries, Generators & Solar 11 18-06-2014 17:08

Advertise Here


All times are GMT -7. The time now is 14:42.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.