Old 30-01-2021, 13:53   #61
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: wires burned up with 4 100 watt panels

Agree, but...there is always a but...I prefer the breaker between the panel and the controller, near the controller, as well as an output breaker between the controller and the battery. I then follow the ABYC 7" rule at the battery. With this scheme:
1. I can easily isolate the panels from the controller.
2. I can easily isolate the bank from the controller and have an easy method for bring DC back to the controller from the bank after controller programming.
3. The fuse at the bank keeps surveyors content that the installation is in compliance with ABYC Standards, voluntary as they are.

And since UL 489 DIN CB are relatively cheap ($30 for a DPCB; 125VDC/63A) it seems reasonable.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 30-01-2021, 13:55   #62
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: wires burned up with 4 100 watt panels

I get a kick out of the positioning of the fuse in the length of wire. It is amperage that blows it and it doesn't really care where in the wire it is located.
Maybe if you expect the wire to be shorted to ground.
Cadence is offline   Reply With Quote
Old 30-01-2021, 13:59   #63
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: wires burned up with 4 100 watt panels

Quote:
Originally Posted by Cadence View Post
I get a kick out of the positioning of the fuse in the length of wire. It is amperage that blows it and it doesn't really care where in the wire it is located.

ok do this test. hook up a 20' long wire to you battery. put a fuse 18' away from the battery. now 10' from the battery strip away the cable sheath and thouch the inner wires to your engine block.

let me know if the fuse blows and what happens.
smac999 is offline   Reply With Quote
Old 30-01-2021, 14:07   #64
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: wires burned up with 4 100 watt panels

Quote:
Originally Posted by smac999 View Post
ok do this test. hook up a 20' long wire to you battery. put a fuse 18' away from the battery. now 10' from the battery strip away the cable sheath and thouch the inner wires to your engine block.

let me know if the fuse blows and what happens.
I love partial quotes. And if that's the case the dressing of wiring runs would be suspect.
Cadence is offline   Reply With Quote
Old 31-01-2021, 02:29   #65
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: wires burned up with 4 100 watt panels

Quote:
Originally Posted by smac999 View Post
it's a self limited power source. the controller does not need a fuse on the controller side. nor do alternators, battery chargers. and solar panels. they are self limiting sources of power. the power will never exceed the amp rating of the cable.
The maximum current that can be generated by the solar panels is self limited, but with multiple panels the combined limit may be higher than the rating.

Where this applies, fusing on the solar panel side (in adittition to a fuse between the controller and the batteries) is needed to avoid the problem of a fault condition melting the internal wires and starting a fire.
noelex 77 is offline   Reply With Quote
Old 31-01-2021, 07:10   #66
Registered User

Join Date: Nov 2016
Location: Sarnia ON
Boat: S2 9.1
Posts: 267
Re: wires burned up with 4 100 watt panels

Quote:
Originally Posted by Cadence View Post
I get a kick out of the positioning of the fuse in the length of wire. It is amperage that blows it and it doesn't really care where in the wire it is located.
Maybe if you expect the wire to be shorted to ground.

The over current device is sized and installed to protect the conductor, not the load, so to do that it needs to be installed next to the source.


I agree with what has been suggested here, that the high resistant connections at the fuse block, is the likely source of the smoke!
Gary Mc is offline   Reply With Quote
Old 01-02-2021, 00:20   #67
Registered User
 
hzcruiser's Avatar

Join Date: Aug 2008
Location: Sydney, Australia
Boat: Roberts 45
Posts: 1,037
Re: wires burned up with 4 100 watt panels

Quote:
Originally Posted by Gary Mc View Post
The over current device is sized and installed to protect the conductor, not the load, so to do that it needs to be installed next to the source.

[..]
That's correct. The person "getting a kick out of it" did not grasp the basic reasoning behind the concept. Time for him/her to kick himself ?
__________________
Fair winds,
heinz

https://www.timantra.net
hzcruiser is offline   Reply With Quote
Old 01-02-2021, 06:29   #68
Registered User

Join Date: Sep 2013
Location: Montreal
Boat: Dufour 39 Frers
Posts: 404
Re: wires burned up with 4 100 watt panels

What is the brand of the fuse and fuse holder ? Is it a cheap made in china fuse box ?
Emouchet is offline   Reply With Quote
Old 01-02-2021, 06:37   #69
Registered User

Join Date: Nov 2018
Location: NJ
Boat: Mariner 38 Pilot House
Posts: 186
Re: wires burned up with 4 100 watt panels

Ok there is so much bad information on this thread that I suggest not reading it.

I’m an ABYC certified marine electrician and you need to either hire a pro immediately or replace your system with a professionally designed one. You need an audit of what you have by someone with experience and training it will be the best money you’ve ever spent.

The amount of bad advice on this thread if horrifying.
mcon12000 is offline   Reply With Quote
Old 01-02-2021, 06:51   #70
Registered User
 
djdeakyne's Avatar

Join Date: Apr 2006
Location: Malaysia
Boat: Privilege 45 - Tortuguita
Posts: 36
Re: wires burned up with 4 100 watt panels

Put your panels in series, or at least 2S2P. That will 1/2 or 1/4 your current and your 10ga wire will be fine.
djdeakyne is offline   Reply With Quote
Old 01-02-2021, 07:35   #71
Registered User

Join Date: Mar 2012
Location: USVI
Boat: Lagoon 450S
Posts: 87
Re: wires burned up with 4 100 watt panels

The amperage capacity of 10 awg is 30 amps - doing a quick Google and seeing several concurring sources. If you can find your wire's manufacture and wire type, you can find the actual value. All my comments below are predicated that your 10AWG wire can handle the 30 amps.

Your solar panels are 100W each and will output at best 8 Amps each. "At best" because output voltage of the panels will be greater than 12 V, so current will be 8 Amps or less from each panel. In reality the panels will output more than 12 Volts, and current goes down as voltage goes up with constant watt output.

So the 10AWG wire coming from each panel is more than adequate to handle the panel's output current.

The cables from the panels feed into a solar charge controller. Right?

The output of the solar charge controller is 12 to 14 V, depending on the charge controller, the batteries being charged and their charge state. Worse case for amperage calculation at 12 Volts. So your charge controller will output 400W / 12 volts or 33.3 Amps. This will occur when your solar panels are outputting at 400W, which will not be often. But, can happen.

The maximum current output of the solar controller dictates that the wire going from your solar controller to your batteries should be 8 AWG or 6 AWG, carrying 40 and 55 Amps respectively. 10 AWG will not handle the expected loads when your getting 400W of solar power. You got away with this (sort of) because you do not often get 400W and the output voltage is above 12 V, probably 13, so current output is 300W / 13 V = 23 Amps.

Using 6AWG with a 50Amp fuse is how I would install the after controller to my batteries. The 6 AWG wire goes for both positive and negative branches. Fuse goes on the positive side, nearest the charge controller.

A reason your fuse block melted might be because the contacts were in bad shape. Bad contacts generate heat at the connection (even if the current is only 10 Amp and fuse does not blow) the block will heat up. Ensure the connections are good (i.e. clean and tight) and ensure that the block is designed for that size fuse.

While you are sorting all this out, you may be able to limit the output of the solar charger to 25 Amps and install a 30 amp fuse to the output cable. My Victron controller can limit current output, you'll need to see if your controller has this capability. Else, there is a chance the wires from the controller to the battery will melt and ruin your day. This will limit your solar generation, but it will help keep your boat afloat.

Another alternative for short term fix, after cleaning up all the connections and replacing the fuse with a 25 Amp fuse, is simply disconnect one solar panel. With only 300 W maximum output, your are in the capacity range of the 10 AWG wire after the controller. 300W / 12 V = 25 Amps, and your 10 AWG wire from the controller should handle this.

Again, look up the amperage capacity of the 10 AWG cable you have installed. Some people have done some pretty poor installs and used crappy wire.
geekoman is offline   Reply With Quote
Old 01-02-2021, 07:37   #72
Registered User

Join Date: Dec 2016
Posts: 142
Re: wires burned up with 4 100 watt panels

As suggested, fuse probably too small
Sidney777 is offline   Reply With Quote
Old 01-02-2021, 08:01   #73
Registered User

Join Date: Mar 2012
Location: USVI
Boat: Lagoon 450S
Posts: 87
Re: wires burned up with 4 100 watt panels

Yes. Probably didn't blow because the current peaked above 20 Amps, and fuse is slow blow and rode through the peaks.
geekoman is offline   Reply With Quote
Old 01-02-2021, 08:14   #74
Registered User

Join Date: Feb 2014
Location: Pennsylvania
Boat: 43' Albin Sundeck
Posts: 116
Re: wires burned up with 4 100 watt panels

Last July we installed 3-220W Xantrex Flex panels in series. A Victron MPPT 150/60 Smart charge controller is between the panels & the batts, as well as some circuit breakers. IF I could figure out how to post a picture I'd be able to show the setup.

If I remember correctly our wiring from the panel wiring (that had a dual wire and special connectors already attached) to the MPPT and then to the batts is 10g or a little smaller.

The panels are located on a Hard to Top over the bridge and wiring drops straight down to the engine room and then to the batts. A less than 20' run.

BTW, we are a trawler, if that makes any difference.

I'd add, if you aren't sure, bring in a technician who knows what they are doing. You've seen what can occur if you don't know.

Good luck.
__________________
Charles
m/v Nepidae
MTOA-3927 AGLCA-12114 (Ret)
Nepidae is offline   Reply With Quote
Old 01-02-2021, 08:16   #75
Registered User
 
capnorv's Avatar

Join Date: Sep 2010
Location: Bainbridge Island Washington on the Salish Sea
Boat: Hardin 45 Voyager Alice B., Gig Harbor 10, Orca 7 1/2 sloop, 16' sea kayak
Posts: 439
Images: 1
Re: wires burned up with 4 100 watt panels

If you don't want to change the fuse and wiring, why don't you wire the panels in series and install a mppt charge controller? Your maximum output would be more like seventy five volts, about twelve amps, end of overload, and the higher voltage will carry the available current much more efficiently through your wires. More important, in less than ideal conditions you will be wringing all the charging current you can out of your system. I've used solar panels since the eighties in both houses and boats, and the change to mppt charge controllers was a true godsend. Try it you'll like it. On another subject, don't expect your panels to put out what they say very often. They are rated on maximum efficiency. A cold day, perfect sun angle, short term exposure. Anything else will be less so having the ability to milk all the available power out of the charging circuit is the way to go. Midday on a minty degree day, you'll be lucky to see seven amps a panel. I usually figure I'll be fortunate to get fifty percent of rated current through the six hours of midday. On another subject, fusing the output of a charge controller is a good way to buy a new charge controller. Always disconnect the panel side before disconnecting the sponge (batteries). I've seen too many sad stories by people doing this the wrong way. Good luck.
capnorv is offline   Reply With Quote
Reply

Tags
panels


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aquair 100 Watt, 12 Volt Generator - r sailor bum 2020 Electrical: Batteries, Generators & Solar 0 20-12-2017 05:26
Connecting LED dome lights small wires to big wires... Rowglide Electrical: Batteries, Generators & Solar 59 13-11-2017 15:32
Pactor with 100 Watt radio? GWB Marine Electronics 22 07-11-2013 09:51
if you were looking at smaller, 100-watt panels? foojin Electrical: Batteries, Generators & Solar 2 24-10-2013 16:06
Will a 100 Watt Solar Panel Cover the Following? LBW399 Electrical: Batteries, Generators & Solar 29 29-10-2012 08:41

Advertise Here


All times are GMT -7. The time now is 13:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.