Re: Water heater works on generator, but not on shore power

Just keep in mind, any voltage checks are no good unless under load.
Cadence is offline   Reply With Quote
Old 05-07-2017, 13:25   #17
Registered User
 
Dave_S's Avatar

Join Date: Jun 2016
Location: Brisbane Australia
Boat: Schionning Waterline 1480
Posts: 1,987
Re: Water heater works on generator, but not on shore power

Another vote for dodgy water heater.

Because....
On shore power the breaker can blow at the dock or on the boat so the over draw is beyond the boats breaker. It is possible the generator can not produce the power to trip the breakers so even though the heater is drawing enough to trip the breaker the generator can't produce the current so it pulls the voltage down. You would hear the generator struggle more.
__________________
Regards
Dave
Dave_S is offline   Reply With Quote
Old 05-07-2017, 13:56   #18
Registered User

Join Date: May 2016
Posts: 13
Re: Water heater works on generator, but not on shore power

Thanks for your leads!

The voltage seems fine, always around 230V (it's an EU boat). We've checked the shore power cord (which is high amperage, so shouldn't be a wire gauge issue), but will now check the connector on the boat for corrosion, and look at the water heater element. Given that the air conditioning, microwave and stick blender all work, and we've now been in a dry climate for months, perhaps it is an issue with the water heater's element. And we'll see where the gen set is grounded, out of curiosity.

Thanks again, and we'll let you know.
RedHeather is offline   Reply With Quote
Old 05-07-2017, 14:00   #19
Registered User

Join Date: May 2016
Posts: 13
Re: Water heater works on generator, but not on shore power

It could also be calcium build-up on the element, but the difference in behavior between shore power and generator is what puzzled us so thanks for the many angles on that.
RedHeather is offline   Reply With Quote
Old 05-07-2017, 14:09   #20
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Water heater works on generator, but not on shore power

Quote:
Originally Posted by RedHeather View Post
Thanks for your leads!

The voltage seems fine, always around 230V (it's an EU boat). We've checked the shore power cord (which is high amperage, so shouldn't be a wire gauge issue), but will now check the connector on the boat for corrosion, and look at the water heater element..
Have you checked it with just the water heater on with shore power. Does it still trip or would it continue to run.

As it runs with the genny but trips on shore power with the same element and wire, it has to be a difference (drop) in voltage on shore power causing the breaker to trip.

However a water heater element is fairly inexpensive in the typical boat kw range. So I would replace that first. If the breaker still trips replace the breaker (it's cheap too). Breakers can go bad). It could trip on shore as the voltage may be slightly lower which causes a higher amp draw, possible anyway. Lastly if all else fails replace the shore cable. Though check that the dock power is adequate.

I had to cut 10 feet off my cable to get to good wire. I need to replace my 10 year old shore cable this winter.
sailorchic34 is offline   Reply With Quote
Old 05-07-2017, 16:19   #21
Registered User
 
Alan Mighty's Avatar

Join Date: Mar 2014
Location: Moreton Bay
Boat: US$4,550 of lead under a GRP hull with cutter rig
Posts: 2,141
Re: Water heater works on generator, but not on shore power

Quote:
Originally Posted by RedHeather View Post
The voltage seems fine, always around 230V (it's an EU boat).
Given that your boat was wired to EU standards, you may find that the metal case of the water heater is earthed with a wire that connects eventually to the earth wire of your AC shore power cord. The metal case of the water heater will likely be covered by some non-metallic insulation (which will probably also be an electrical insulator).

If the metal case of water heater is earthed in that way, and if you have access to that earthing wire somewhere near the water heater, you could put a clamp-on ammeter on that earthing wire.

If AC is leaking into the water from a crack in the heater element, that earth wire will be carrying some AC. Note the potential for personal danger if you place yourself in the circuit to earth. Enuff said.

Note that the metal case of the water heater may not be earthed. Even more reason for not putting yourself in a circuit to earth.

The dockside circuit breaker more likely just meters the difference between AC Active and AC Neutral.

Please post a photo of the element of the water heater, if it proves to be the culprit.
__________________
“Fools say that you can only gain experience at your own expense, but I have always contrived to gain my experience at the expense of others.” - Otto von Bismarck
Alan Mighty is offline   Reply With Quote
Old 05-07-2017, 16:27   #22
Registered User
 
Alan Mighty's Avatar

Join Date: Mar 2014
Location: Moreton Bay
Boat: US$4,550 of lead under a GRP hull with cutter rig
Posts: 2,141
Re: Water heater works on generator, but not on shore power

Note also that what trips an Earth Leakage Circuit Breaker can be cumulative.

Meaning that there is a remote chance that more than one AC appliance, when added together, might be faulting and result in a trip of the ELCB.

Inspection of the element of the water heater will eliminate the biggest risk.

If, as you reported, the fault has been around for some time, I would expect that you will find obvious cracks and a clearly enlarged and expanded region of the element.
__________________
“Fools say that you can only gain experience at your own expense, but I have always contrived to gain my experience at the expense of others.” - Otto von Bismarck
Alan Mighty is offline   Reply With Quote
Old 05-07-2017, 17:01   #23
Registered User

Join Date: Dec 2015
Posts: 523
Images: 1
Re: Water heater works on generator, but not on shore power

Maybe buy yourself a nice length of Cab-Tire #8 AWG extension cord cable and buy the proper ends ( high quality ) and put them together real good, then never have to worry about the problem being caused by your equipment again. It'll be such a nice cord you might need to lock it to the dock.
Rorzech is offline   Reply With Quote
Old 05-07-2017, 17:09   #24
Registered User

Join Date: Jun 2006
Location: Dayton, WA
Posts: 140
Re: Water heater works on generator, but not on shore power

Quote:
Originally Posted by capt jgw View Post
Another cause could voltage from the dock supply. If you're out near the end of the line you may not be getting full 110-120 volts. As volts go down, amps go up and that can trip a breaker. Easy to check, if a volt meter shows like 90 volts that would be your problem. Good luck getting the marina to fix it.
The heating element in the WH is a (nearly) purely resistive load.

Current draw: I=V/R

Resistance is constant. If voltage drops then so does current. On inductive loads (motors) things play a little differently.
mohave_steve is offline   Reply With Quote
Old 05-07-2017, 20:02   #25
Registered User
 
J Clark H356's Avatar

Join Date: Jun 2010
Location: Grand Rivers, KY
Boat: Hunter 2003 356 - Persistence
Posts: 609
Re: Water heater works on generator, but not on shore power

I have a 5 kW generator and use 1 30 Amp power cord at the dock (have 2 but just parallel the 1 30amp and manage power by not running HVAC heat pump, microwave and hot water heater at the same time on shore power or I trip my boat mainbreaker. On genset I have 41.6 amps at 5kw 120 volts so can run all three with no tripped breaker. Could you possibly have a similar situation? Might be your shore power just doesn't provide as many amps as your genset?
J Clark H356 is offline   Reply With Quote
Old 18-07-2017, 06:55   #26
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Water heater works on generator, but not on shore power

Commenting on Post #15:

Quote:
Unfortunately, many boats have their 120v AC green ground wire connected inadvertently to their battery - terminal. This happens because many boats have their AC green ground wire connected to the ships ground/ engine block... as is the negative wire from the starter batteries/ ship's battery bank.
This is not an unfortunate situation; it is required by the American Boat and Yacht Council Standards.

Quote:
... it also could cause a serious electrolysis issue anything the gen is running and waterhearer breaker on.
Possible but extremely unlikely as it takes very high AC (> 100A/m^2) to induce stray current corrosion.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 18-07-2017, 07:59   #27
Registered User

Join Date: May 2015
Location: Muskegon, Mi
Boat: Columbia 36
Posts: 1,212
Re: Water heater works on generator, but not on shore power

One of my commercial boats does the same thing. 30A shore connection, with the water heater and cabin heater on the dock breaker trips. 50A genset runs everything just fine
capt jgw is offline   Reply With Quote
Old 20-07-2017, 19:35   #28
Registered User

Join Date: Jan 2008
Location: SF Bay Area (Boat Sold)
Boat: Former owner of a Valiant V40
Posts: 1,158
Re: Water heater works on generator, but not on shore power

Quote:
Originally Posted by mohave_steve View Post
The heating element in the WH is a (nearly) purely resistive load.

Current draw: I=V/R

Resistance is constant. If voltage drops then so does current. On inductive loads (motors) things play a little differently.
This is correct. ... but theres more to the story...

Reason breakers sometimes trip on low AC voltage is when an AC motor is trying to start. It draws high current on startup, but can't get up to speed on the low voltage. This causes the breaker to blow. It's not a high current draw due to low voltage per se, rather the extended duration on the high current trying to start.
jamhass is offline   Reply With Quote
Old 28-07-2017, 07:22   #29
Registered User

Join Date: May 2016
Posts: 13
Re: Water heater works on generator, but not on shore power

Thanks, Alan and others! The boiler works again with a new element. Now to investigate why it didn't trip on the generator... Thanks for the insights!
RedHeather is offline   Reply With Quote
Old 28-07-2017, 17:27   #30
Registered User

Join Date: Aug 2015
Posts: 474
Re: Water heater works on generator, but not on shore power

Quote:
Originally Posted by RedHeather View Post
Thanks, Alan and others! The boiler works again with a new element. Now to investigate why it didn't trip on the generator... Thanks for the insights!
I'd recommend checking your generator wiring to make sure you have (a) green ground wire connected to generator case (b) strap between neutral and ground connected at the generator wiring box.

If you're missing either one, the breaker would not trip when the failed heating element exposed line voltage to the grounded water heater.
boatbod is offline   Reply With Quote
Reply

Tags
generator, shore power, water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replaced Water Heater, Only Seems To Work From Shore Power Not Engine bstowers Plumbing Systems and Fixtures 7 25-04-2013 12:21
Can you Damage a Water Heater by Leaving it on Shore Power ? Hugh Walker Plumbing Systems and Fixtures 7 16-02-2012 02:33
Open CPN Works Initially But Then Will Not Open GrahamW OpenCPN 4 25-01-2012 04:57
Anchor Alarm Works, but Not with Recorder Messages s51ta OpenCPN 5 01-11-2010 22:42
Bizzare Problem: Autopilot Only Works when Shore Power Is Plugged In sgtPluck Electrical: Batteries, Generators & Solar 22 29-12-2009 12:14

Advertise Here


All times are GMT -7. The time now is 21:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.