Re: Shore power inlet fuse/breaker

I wanted to come back and close the loop on this. It happens so very rarely! LOL

My solution may not be 100% ABYC compliant because my parts did not come from Blue Sea. I believe but I'm not certain that the only ELCI in the world comes from Blue Sea. But beyond that, I feel good.

The actual breaker is an RCD, which is mentioned in ABYC and is UL listed. The trip is 32 amps, not 30, but I am comfortable with that (the main breaker in the main panel is 30A). The residual current trip is 30 milliamps which is what is specified by ABYC. I believe the breaker is US manufactured and appears to be a credible brand. The install is about 18 in from my power inlet. The box is a sturdy unit and about a perfect size. I installed it with the breaker sideways because it works well in my installation, but it could also be installed with the breaker facing out.

This is the breaker I used:
ASI NDB1L-32C-32-120V DIN Rail... https://www.amazon.com/dp/B00NTVB6VY

And this is the box I used: https://www.amazon.com/dp/B077QM9VM9

I also ordered DIN rail, but could not use it in this application. It might have worked if the breaker was facing out.

I am really happy with the solution. And since the box replaced an existing junction box, total labor was less than 2 hours.Click image for larger version

Name:	PXL_20220101_010026842.jpg
Views:	52
Size:	105.0 KB
ID:	250645Click image for larger version

Name:	PXL_20220101_010055630.jpg
Views:	44
Size:	51.0 KB
ID:	250646Click image for larger version

Name:	PXL_20220101_211945968.MP.jpg
Views:	54
Size:	69.7 KB
ID:	250647
sailingharry is offline   Reply With Quote
Old 01-01-2022, 19:30   #32
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,503
Re: Shore power inlet fuse/breaker

Quote:
Originally Posted by Frankly View Post
If the pedestal breaker is functional (ELCI or regular) and rated to match the yacht service rating then the main breaker on the yacht serves no electrical purpose and is just a convenience to secure the electricity on the yacht..





Frankly


Thats a big IF. Many times, 30 to 50 adapters are used. And, the old 30 A twist lock system is far from robust.
team karst is offline   Reply With Quote
Old 02-01-2022, 10:15   #33
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Shore power inlet fuse/breaker

The 10' rule was adopted by the ABYC because of the lack of confidence in the condition of the pedestal circuit breaker. 10' of unprotected wire inside of the boat was thought to be a reasonable compromise.

To further protect this section of wiring that is considered vulnerable, the ABYC also requires supporting this wire run:
Quote:
11.15.4.1.9.2 by means of metal straps or clamps with smooth, rounded edges to hold the conductors firmly in place without damage to the conductors or insulation. That section of the conductor or cable directly under the strap or clamp shall be protected by means of a loom, tape, or another suitable wrapping to prevent injury to the conductor; or

11.15.4.1.9.3 by means of metal clamps lined with an insulating material resistant to the effects of oil, gasoline(petrol), and water

@sailingharry came up with an inexpensive and compliant solution. Congratulations!
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
shore power thermal fuse to prevent fires vpbarkley Electrical: Batteries, Generators & Solar 12 16-09-2021 12:37
Shore power off - circuit breaker hoppy Electrical: Batteries, Generators & Solar 2 14-03-2016 00:40
Battery switch with shore power breaker keelsidedown Electrical: Batteries, Generators & Solar 17 10-05-2015 20:46
Shore Power Breaker Amperage Aorta Electrical: Batteries, Generators & Solar 9 22-01-2015 09:40
Simple 15A Shore Power In Small Boat (Looking to install in-line 15A AC Breaker ) NS22Wren Electrical: Batteries, Generators & Solar 1 31-10-2012 05:51

Advertise Here


All times are GMT -7. The time now is 18:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.