Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 19-06-2020, 06:54   #1
Registered User
 
NorthernMac's Avatar

Join Date: Mar 2019
Boat: A185F, Mystic 30’ Cutter
Posts: 705
Reverse Polarity on AC all of a sudden

Hey

My boat has been on the hard for a few days, I’ve had it plugged in to shore power to run the portable air conditioner, I come out to the boat and the A/C systems are not working battery charger as well as the portable air con.

I turn all the breakers off, unplug shore power, check everything, plug it back in, turn everything back on, but the second I turn the master AC breaker on, alls fine, turn any other breakers on and nothing plus I get a rev pol indicator.

On further examination two of the wires going (B & W) going into the AC panel got toasted right at the terminal, with the white one completely separated

Any thoughts?
NorthernMac is offline   Reply With Quote
Old 19-06-2020, 07:03   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Rev Pol on AC all of a sudden

Neutral / ground fault is my guess, after verifying correct polarity at the pedestal. Unlikely but they may have done some work on the Marina’s side.
a64pilot is offline   Reply With Quote
Old 19-06-2020, 07:59   #3
Registered User
 
NorthernMac's Avatar

Join Date: Mar 2019
Boat: A185F, Mystic 30’ Cutter
Posts: 705
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by a64pilot View Post
Neutral / ground fault is my guess, after verifying correct polarity at the pedestal. Unlikely but they may have done some work on the Marina’s side.

Nothing has been changed on the boat over the last week, as in the boats just been getting painted, nothing has been plugged into or out of the boat, just sitting with the trickle charger and air con on
NorthernMac is offline   Reply With Quote
Old 19-06-2020, 08:09   #4
Registered User

Join Date: Apr 2020
Boat: Amel 53, Super Maramu
Posts: 428
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by NorthernMac View Post
Hey

My boat has been on the hard for a few days, I’ve had it plugged in to shore power to run the portable air conditioner, I come out to the boat and the A/C systems are not working battery charger as well as the portable air con.

I turn all the breakers off, unplug shore power, check everything, plug it back in, turn everything back on, but the second I turn the master AC breaker on, alls fine, turn any other breakers on and nothing plus I get a rev pol indicator.

On further examination two of the wires going (B & W) going into the AC panel got toasted right at the terminal, with the white one completely separated

Any thoughts?
Based on your description, there is absolutely no way to tell if the damaged wires you see are a CAUSE or and EFFECT of the base problem. Heck, we don’t even know what wires they are!

The most likely cause is a bad connection at the point you see the damage that resulted in a high resistance connection and heat that then “toasted” the wires. But that’s just a SWAG based on almost no information.

If you can’t figure this out, it’s time to call a marine electrician. Seriously, “toasted wires” are just inches away from “fire” and fire is the scariest thing to happen on a boat.
SVHarmonie is offline   Reply With Quote
Old 19-06-2020, 08:53   #5
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by NorthernMac View Post
On further examination two of the wires going (B & W) going into the AC panel got toasted right at the terminal, with the white one completely separated

Any thoughts?
I didn’t notice this until now, but that’s your problem, the white wire is Neutral, and with it being disconnected a there is now a fault in the neutral to ground bond, the fault is of course the neutral is unbounded.

There should be three wires, black is hot, green ground and white is neutral.

This is on the boat side? If so and please don’t be offended, but you should call an electrician, because there may be a fault that caused the wires to overheat and not throw the breaker, likely was just loose, but just hooking them back up without checking everything else out may burn the boat down.

If on the pedestal, then of course don’t touch it, call the marina.
a64pilot is offline   Reply With Quote
Old 19-06-2020, 09:15   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Rev Pol on AC all of a sudden

A bad netreal connection will cause a rev pol light. My guess is wires were already bad.
smac999 is offline   Reply With Quote
Old 19-06-2020, 09:39   #7
Registered User
 
NorthernMac's Avatar

Join Date: Mar 2019
Boat: A185F, Mystic 30’ Cutter
Posts: 705
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by smac999 View Post
A bad netreal connection will cause a rev pol light. My guess is wires were already bad.
Just got a new run of 10g, terminals and a shore power outlet.
NorthernMac is offline   Reply With Quote
Old 20-06-2020, 04:34   #8
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Rev Pol on AC all of a sudden

Smac999: A bad N connection will not illuminate a reverse polarity light.

The reverse polarity light is connected to the N and G via a >25kohm resistor. If L and N are reversed, the definition of reversed polarity, then the white conductor becomes hot and will light the reverse polarity light.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 20-06-2020, 13:38   #9
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by CharlieJ View Post
Smac999: A bad N connection will not illuminate a reverse polarity light.

The reverse polarity light is connected to the N and G via a >25kohm resistor. If L and N are reversed, the definition of reversed polarity, then the white conductor becomes hot and will light the reverse polarity light.


voltage drop in the neutral wire will cause a voltage difference between N and G. the light only needs a few volts to start lighting up. it may only be dim and not fully on.

IE you might measure 110v hot to N, 120v hot to ground, 10v N to ground.

the rev pol light will likely be on with 10v across it

it would only light if loads on the boat were on. otherwise the voltage drop would not exist.
smac999 is offline   Reply With Quote
Old 20-06-2020, 17:02   #10
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Rev Pol on AC all of a sudden

smac999:
Don't loose the main point of my post: A bad N connection will not illuminate a reverse polarity light.

Since you brought it up, the voltage drop for a feeder on a pier will cause a small potential on the N. The NEC spec is for <2VAC (I rarely see close >2VAC in Florida in the summer) which may dimly light an incandescent reverse polarity light but probably not an LED. If there is 10VAC across the reverse polarity light, there are probably some serious issues with the dock wiring.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 20-06-2020, 17:36   #11
Registered User
 
NorthernMac's Avatar

Join Date: Mar 2019
Boat: A185F, Mystic 30’ Cutter
Posts: 705
Re: Rev Pol on AC all of a sudden

Alls back up to running fine after I replaced that run of wire and I tossed a new shore power connector on too.

I think the root of the issue was someone I hired to install a dripless as I had my shaft out, I found my NEW bilge pump wires were torn too, I think he pushed up some stuff on the back of the exposed power panel and arched it too. Dude is kinda a don’t give a F’ type, older and north of 200lbs, I think in my boat it was like a hog rooting for a truffle and some wiring got the worst of it.
NorthernMac is offline   Reply With Quote
Old 20-06-2020, 21:56   #12
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by CharlieJ View Post
smac999:
Don't loose the main point of my post: A bad N connection will not illuminate a reverse polarity light.

Since you brought it up, the voltage drop for a feeder on a pier will cause a small potential on the N. The NEC spec is for <2VAC (I rarely see close >2VAC in Florida in the summer) which may dimly light an incandescent reverse polarity light but probably not an LED. If there is 10VAC across the reverse polarity light, there are probably some serious issues with the dock wiring.
not if the n-g is 0v at the pedestal and 10v at the ac panel. that is a bad n wire causing 10v drop on the wire at load. shut off AC main and load drops and light turns off and n-g voltage goes back to 0

no different then having 12v at a battery and 6v at a device. bad wire / connection
smac999 is offline   Reply With Quote
Old 20-06-2020, 22:15   #13
Registered User
 
Uncle Bob's Avatar

Join Date: May 2010
Location: Sydney Australia
Boat: Fisher pilothouse sloop 32'
Posts: 3,428
Re: Rev Pol on AC all of a sudden

Quote:
Originally Posted by NorthernMac View Post
Alls back up to running fine after I replaced that run of wire and I tossed a new shore power connector on too.

I think the root of the issue was someone I hired to install a dripless as I had my shaft out, I found my NEW bilge pump wires were torn too, I think he pushed up some stuff on the back of the exposed power panel and arched it too. Dude is kinda a don’t give a F’ type, older and north of 200lbs, I think in my boat it was like a hog rooting for a truffle and some wiring got the worst of it.

Priceless.
__________________
Rob aka Uncle Bob Sydney Australia.

Life is 10% the cards you are dealt, 90% how you play em
Uncle Bob is offline   Reply With Quote
Old 21-06-2020, 04:21   #14
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Reverse Polarity on AC all of a sudden

smac999 #12
Quote:
not if the n-g is 0v at the pedestal and 10v at the ac panel. that is a bad n wire causing 10v drop on the wire at load. shut off AC main and load drops and light turns off and n-g voltage goes back to 0
Look, I am really trying to understand what you are saying but, even after sketching it out, there is no way that a "bad" N conductor is going to cause the RP light to illuminate. And by "bad" I go back to the OP:
Quote:
On further examination two of the wires going (B & W) going into the AC panel got toasted right at the terminal, with the white one completely separated
and I consider "completely separated" as "bad". In the OP's case, there was no N. That is really bad.

The function of the RP light is to protect a boat from receiving RP shore power when the boat initially plugs in. The RP light is on the line side of the main panelboard shore power breaker.

I just do not understand
Quote:
not if the n-g is 0v at the pedestal and 10v at the ac panel.
as the most common arrangement is a shore power cable > inlet > inboard cable > panelboard main breaker so we are at opposite ends fo the same conductive paths. How can there be 0VAC N > G at the pedestal and 10VAC N > G at the panel??

I am honestly trying to understand your position but so far I can't see it.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 21-06-2020, 05:38   #15
Registered User
 
Boatwright's Avatar

Join Date: Jul 2016
Location: Traverse City, Michigan
Boat: Hinterhoeller Niagara 35
Posts: 289
Re: Reverse Polarity on AC all of a sudden

Good advice from Charlie.

I note that you were trying to power a portable AC, which can draw heavy amps, especially when starting. High load, bad /loose connections, toasted wires are the known facts. 200# mechanic is a maybe.

I'd be looking at every connection and device between your shore power plug and the AC unit for heat damage and incorrectly installed wiring. I'd also look at the AC unit itself. The cheap compressors can stall when starting and a stalled AC motor can draw very high amps. Repeated hard start, wires get hot, etc......

Before settling on the 200# theory you really need to eliminate all other possible problems. Someone, best a qualified marine electrician like Charlie, who knows how to use a VOM and an amp-clamp needs to do the proper detective work before you start a fire.
Boatwright is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rev counter Marauder Engines and Propulsion Systems 10 09-08-2020 07:53
Baffled - battery charge rate all of a sudden cut in half?? CookiesnTequila Electrical: Batteries, Generators & Solar 20 03-11-2016 14:40
Autohelm ST 7000 all of sudden wont hold course... Jbingham Marine Electronics 29 27-04-2015 14:50
Engine Won't Rev in Gear n8cal@hotmail.c Engines and Propulsion Systems 15 16-06-2009 09:44
REV counter pickup Alan Wheeler Electrical: Batteries, Generators & Solar 25 12-11-2006 13:27

Advertise Here


All times are GMT -7. The time now is 19:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.