Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 26-07-2016, 04:23   #16
Registered User

Join Date: Feb 2009
Posts: 69
Re: Northern Lights AC breaker tripping to much

Thanks for this. I'll need to check on my next trip to the boat.

A bit info From today. My electric panel has an AC amp meter. But only one of the air cons is hooked up to it. I am getting a reading of 5.8 amps when that air con is running but the air con label says full load amps is 4.5 amp (it's a Cruisair 16,000 btu 220 volt/50 Hz unit). Is this kind of discrepancy normal or does this indicate possible wiring problems with this air con? I will need to get a clamp meter to check the other AC items.


Sent from my iPad using Cruisers Sailing Forum
HKTim is offline   Reply With Quote
Old 26-07-2016, 05:05   #17
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Northern Lights AC breaker tripping to much

The current shown on the air con unit will not include the current drawn by the seawater cooling pump. So probably that current is responsible for the small extra you are measuring.

Strange that your AC amp meter does not measure all the AC current.
transmitterdan is offline   Reply With Quote
Old 26-07-2016, 05:08   #18
Registered User

Join Date: Feb 2009
Posts: 69
Re: Northern Lights AC breaker tripping to much

Just reconsidered my last post. Was not including the pump in the expected amps draw from running the air con. I'll need to check the exact amp draw but that might be difference.


Sent from my iPad using Cruisers Sailing Forum
HKTim is offline   Reply With Quote
Old 26-07-2016, 05:12   #19
Registered User

Join Date: Feb 2009
Posts: 69
Re: Northern Lights AC breaker tripping to much

Reason for the amp meter not measuring everything is due to some circuits being linked to the inverter which was only recently installed. All the inverter circuits are not being measured. Others only to the genset or shore power are captured by the amp meter. This process has made me realize that and will be rectifying it so all AC loads can be measured.

Thanks for your help.


Sent from my iPad using Cruisers Sailing Forum
HKTim is offline   Reply With Quote
Old 26-07-2016, 05:49   #20
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Northern Lights AC breaker tripping to much

If your air con is a "split" unit then the current for the evaporator fan will not be included on the nameplate either.
transmitterdan is offline   Reply With Quote
Old 26-07-2016, 06:16   #21
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Northern Lights AC breaker tripping to much

66C, that's 151F.
I still think you need to improve airflow through the sound enclosure, that is too hot in my opinion, especially since once you opened the enclosure the temp dropped, that should not happen, if anything it should get hotter as an enclosure should be designed to direct cooling air where it's needed. If it weren't a Northern Lights I may suspect enclosure design, but it is a Northern Lights, so I gotta think they got the design right, again in my opinion.

On edit how is your ducting run? What kind of hose? It exhausts out of the boat?
a64pilot is offline   Reply With Quote
Old 31-07-2016, 08:57   #22
Registered User
 
Wolfy's Avatar

Join Date: Aug 2010
Location: Morgan Shitty, Lousyana
Boat: Frers, Pilothouse, 72ft
Posts: 82
Re: Northern Lights AC breaker tripping to much

Sounds as if you need to stay at Home to enjoy the luxury of a fully Air Conditioned living environment, spending any time on a boat (any boat) is all a question of compromise.
Constantly expecting to run THREE A/C units and other electrical equipment simultaneously which incurs maximum loading on the Generator you can fully anticipate problems with breakers and other components in the associated Electrical System.
Also, If you're resetting the breaker under load, you will also trash the breaker really quickly by building up the layers of carbon on the breaker contacts every time the contacts are manually reset, this carbon layering is caused by the Arc or Spark at the contacts when the circuit is re-established while under load.
Please remember to isolate ALL circuits prior to resetting the breaker which has tripped, if you don't, then you're exposing your family and friends to a possible dangerous situation of fire or even explosion if any propane should be creeping around the lower areas of your vessel.
Change the breaker immediately and run your electrical system where it's comfortable and therefore reliable i.e. 70 - 80% of full load.
If you run anything at Max it will fail sooner than later....
__________________
"Common Sense is not so Common"
Wolfy is offline   Reply With Quote
Reply

Tags
Northern Lights


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fresh water pump hammering, tripping breaker Driftwoods Plumbing Systems and Fixtures 8 27-05-2014 14:00
microwave tripping breaker...what to look for? Jcolman Electrical: Batteries, Generators & Solar 53 24-03-2014 19:26
Why does my main AC breaker keep tripping? Toubab Electrical: Batteries, Generators & Solar 19 10-10-2013 13:31
My Refrigerator is Tripping its Breaker jonahmulski Plumbing Systems and Fixtures 15 17-04-2013 16:45
gas valve breaker tripping JusDreaming Plumbing Systems and Fixtures 4 25-10-2007 04:07

Advertise Here


All times are GMT -7. The time now is 06:08.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.