When you do ground your
inverter make sure the ground conductor and lugs are sized correctly.
Inverter Grounding
I am sure most of us know the high voltage of the AC system presents a shock hazard and can certainly be lethal. The DC system is not normally an electrocution hazard but can provide a lot of
current, and so is potentially a source of fire. A suitable ground must be installed between the AC and DC system. During my inverter fitment I noticed in the operating instructions the requirement for grounding connections on both the AC side and DC side of the unit’s case. This grounding can prevent shocks from AC, and fire hazard from DC.
My previous unit only had the smaller AC grounding connection made. A fault in the DC side of the system could provide enough
current to overheat the AC grounding conductor (think enough heat to melt
insulation and start a fire) without blowing the large DC fuse. Keep in mind the fact that the AC ground is not fused and current will flow through the conductor until it burns out. A high amperage capacity DC grounding path back to the DC system should be made. The conductor size for the ground needs to be of sufficient cross sectional area (bigger is better) to be able to sustain enough current to blow the supply fuse.
The
installation instructions for older inverters (as I had previously) typically do not include this precaution, but most newly designed units do. Though looking into some different manufactures install instructions this connection is not addressed in any
depth, most only state or draw the connection in on the
installation schematic. Due to the fuse size in my inverter we needed a 70 mm2 ground wire for the DC ground.
When using an inverter in the
marine environment onboard, tests should be carried out after instalation to make sure the inverters
electrical noise isn't enough to compromise
reception on
VHF frequencies used for radiotelephone, Digital Select Calling,(DSC) and Automatic Identification System (AIS)