Switch or Breaker?

I've been looking at a fair number of lithium system designs and a fair number have a switch or breaker right at the battery. This makes sense to me as it means you can shut everything down (BMS included).

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?

I really would like to use one of these:
https://www.bluesea.com/products/cat...ers/187-Series

It's a much nicer size that the standard switch I can find:
https://www.bluesea.com/products/cat...tches/e-Series

(In either case I'll have a fuse (ANL or T-Class) as well...)
geoffr is offline   Reply With Quote
Old 07-12-2023, 10:57   #2
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 2,946
Re: Switch or Breaker?

Switches and breakers are for different purposes. A fuse and a switch is what you should use.

There is a more convenient size:
https://www.bluesea.com/products/cat...tches/m-Series
__________________
-Warren
wholybee is offline   Reply With Quote
Old 07-12-2023, 12:45   #3
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,508
Images: 241
Re: Switch or Breaker?

Many circuit breakers are rated foe “Switch Duty”.
For Instance: Blue Sea Systems ‘285-Series’ [up to 150A, 48V] & ‘187-Series’ [up to 200A] Surface [or Flush] Mount Circuit Breakers combine switching and circuit protection into a single device.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 07-12-2023, 14:49   #4
Registered User

Join Date: Nov 2008
Location: Ottawa,Canada
Boat: Prout Snowgoose 37' Catamaran
Posts: 570
Re: Switch or Breaker?

Thanks, but my actual question is:

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?
geoffr is offline   Reply With Quote
Old 07-12-2023, 15:16   #5
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,503
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
Thanks, but my actual question is:

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?
polarity of I not an issue. It makes the same magnitude of magnetic flux to pull in the latch...

just like a magnet N pole will stick to iron same as a S pole....
team karst is offline   Reply With Quote
Old 07-12-2023, 16:44   #6
Registered User

Join Date: Feb 2011
Location: Pecan Grove, Oriental, NC
Boat: Hunter 27
Posts: 70
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
I've been looking at a fair number of lithium system designs and a fair number have a switch or breaker right at the battery. This makes sense to me as it means you can shut everything down (BMS included).

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?

I really would like to use one of these:
https://www.bluesea.com/products/cat...ers/187-Series

It's a much nicer size that the standard switch I can find:
https://www.bluesea.com/products/cat...tches/e-Series

(In either case I'll have a fuse (ANL or T-Class) as well...)

The switch or breaker will not turn off the BMS. It is powered by the small sense wires inside the battery. It is always on, unless the battery cells fall outside the set safety limits.
misssherry is offline   Reply With Quote
Old 07-12-2023, 19:26   #7
Registered User

Join Date: Dec 2019
Location: on our boat cruising the Bahamas and east coast
Boat: 2000 Catalina 470 #058
Posts: 1,309
Re: Switch or Breaker?

Yeh you cant turn off a battery. A switch is the best option as close as possible to the output(s) of the batteries.
__________________
Sailing a Catalina 470; now retired
GreenWave is offline   Reply With Quote
Old 08-12-2023, 21:01   #8
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,037
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
Thanks, but my actual question is:

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?
You are wrong, a DCbreaker can accept current both ways.
What cannot accept current both ways are SSR, maybe you saw a switch that actually uses an SSR to cut off the big load.
CaptainRivet is offline   Reply With Quote
Old 09-12-2023, 23:42   #9
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,476
Images: 22
Re: Switch or Breaker?

Quote:
Originally Posted by CaptainRivet View Post
You are wrong, a DC breaker can accept current both ways.
What cannot accept current both ways are SSR, maybe you saw a switch that actually uses an SSR to cut off the big load.
You have used the abbreviation "SSR" without explaining it first. The result is I am at a loss to know what you mean by SSR. Is it another name for a voltage sense relay (VSR)?

If so, are you aware that some are dual sensed and can connect power to flow either way.

Pete
Pete7 is offline   Reply With Quote
Old 09-12-2023, 23:54   #10
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,476
Images: 22
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
I've been looking at a fair number of lithium system designs and a fair number have a switch or breaker right at the battery. This makes sense to me as it means you can shut everything down (BMS included).

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?

I really would like to use one of these:
https://www.bluesea.com/products/cat...ers/187-Series

(In either case I'll have a fuse (ANL or T-Class) as well...)
Geoff we have both, a 120A Blue Sea 187 panel mount, which is about to be upgraded to 150A version. Pricey, but this is one item I want to work properly and not have to replace or have cause problems as a single point of failure. The panel mount version bolts directly to a Victron Lynx or Power In box which is handy and saves a couple of connections in a high current cable.

Note, they don't "pop" straight away, they allow a degree of over current before disconnecting. Higher current earlier pop. I only know because whilst cooking breakfast one morning on the all electric galley, I turned the electric kettle on whilst the toaster was running and the induction hobs. Way more than the inverter or Blue Sea was rated for. Anyway it managed 3 minutes before popping so cutting the power to the inverter.

This was the point I realised what I had done A simple reset and we were back to cooking breakfast.

We have a NH00 fuse as well. These are the European equivalent to a class T fuse, just a quarter of the price in the EU. Sadly more expensive than class T in the US.

Pete
Attached Thumbnails
Click image for larger version

Name:	Blue Sea and inverter.jpg
Views:	71
Size:	195.2 KB
ID:	284237  
Pete7 is offline   Reply With Quote
Old 10-12-2023, 00:18   #11
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,461
Re: Switch or Breaker?

SSR = Solid State Relay
https://en.wikipedia.org/wiki/Solid-state_relay
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Old 10-12-2023, 05:41   #12
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,037
Re: Switch or Breaker?

Quote:
Originally Posted by Wotname View Post
Thanks.
A DC breaker is generally both ways but yes you can buy special models that only work one way on purpose. As with fuses they are so many specs and use cases out there, so be careful what you buy. And there are one way DC breaker out there that effectly using a SSR inside the dc breaker enclosure to switch the high load side but also have a protection diode to protect the SSR from current the wrong way.

With NH fuses 5 tips and facts:
1) there are printed on DC only fuses available specially speced for solar parc installs which you can also get in superfast like class T fuses are only available. They are expensive, even more then class T.
2) the standard NH AC fuses (only uses GS or GG spec type!!!) from top notch Eaton, Bussmann... are also all DC rated but not printed on and hard to find in the specs. But they are DC approved and only the short circuit current rating is 80kA for DC and 100kA for AC. That's also part of the corresponding ISO Norms and certification for grid station, which is the main use case and what they are developed for originally. They are all fast fuses in GS and GG spec.
3) there is nothing wrong with buying NH fuses used, you get a lot eg on Ebay from factories that are demolished. These factories have often a huge stock of replacement fuses never used and even if they are used they have no real wear and aging. As long as the indicator shows they are intact and the ceramic body is undamaged they are good to use. If they are black and ugly the reason is they are silver coated and oxidized (that's 95% optical as oxidizedsilver is not effecting electric conductivity), take a polish for silver cutlery and 10min later they look like new and work like new out of the box. I bought a box with around 50 fuses and 30 fuse holder for 80Euro from ebay, most where unused. A NH3 fuse holder for 250 till 630A fuses costs 300Euro new, used between 30 and 50. Its just ceramic and highest grad cooper coated in silver made to last very long.
4) in 12-48DC spec the NH GG AND gS for the constant power draws you have in your system and or constant current delivery of your bank NOT peak!
they are fast fuses and made for 24/7/365 running at 100% rating (my NH3 500A fuses is 8-10 degrees above ambient temp when pulling 500A). The superfast Class T you need to spec for peak current, they are developed for electronics to protect them from spikes like lighting. Not really the best main battery fuse. The bigger the fuse, the bigger the voltage drop=losses...NH are metricously designed to have the smallest voltage drop possible as eg losses here can cost a company 1000s of dolars a year more on their eletricity bill.
5) their are no fakes and copies out there of NH as thats a) highly controlled and b) its simply massive material used where no much space for savings, just a big chunk of ceramic and silverplated cooper...use tin or cheaper cooper and fuse will immediately heat up significantly showing you its a fake and a) will then take care of this manufacturer. Megafuse as well as ANL are a lot fakes and low quality out there that are nearly impossible to dedect as fake but when its melting down and introducing massive heat into the install its already too late.
CaptainRivet is offline   Reply With Quote
Old 11-12-2023, 01:34   #13
Marine Service Provider
 
SOLAR SUPPORT's Avatar

Join Date: Aug 2010
Location: Turkiye
Boat: Bavaria Match35
Posts: 404
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
I've been looking at a fair number of lithium system designs and a fair number have a switch or breaker right at the battery. This makes sense to me as it means you can shut everything down (BMS included).

Where I get confused is when this is a breaker as I thought that DC circuit breakers could only accept current flowing in one direction - am I wrong?

I really would like to use one of these:
https://www.bluesea.com/products/cat...ers/187-Series

It's a much nicer size that the standard switch I can find:
https://www.bluesea.com/products/cat...tches/e-Series

(In either case I'll have a fuse (ANL or T-Class) as well...)
DC Switch, breaker, fuse can pass current in both directions. We can also add VS battery combiners to this. VS battery combiners allow bidirectional passage of current within a certain voltage range.

Imagine drawing energy from your battery above the charging current. Let's call the direction of this current polar "+". When the devices that consume energy are turned off, the direction of the current will be polar "-" and the energy current will begin to fill the battery.

It is a dc device battery isolator that allows unidirectional current flow. They are used in two types: Argodiode or Argofet. These are battery isolators that allow current to pass in one direction.
SOLAR SUPPORT is offline   Reply With Quote
Old 15-12-2023, 08:17   #14
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 667
Images: 5
Re: Switch or Breaker?

Quote:
Originally Posted by geoffr View Post
(In either case I'll have a fuse (ANL or T-Class) as well...)
For lithium you need a Class T fuse. Lithium batteries can produce a LOT of juice if they short. Class T can take over 20,000 amps and remain open when blown.

General Information: You can not use AC breakers on DC circuits.

If you are using the breaker as a combination fuse/switch, it needs to go at the battery end of the positive wire. If you use a separate fuse and switch, the fuse will go at the battery end of the wire and the switch can go anywhere before the distribution bus. Since you said you will have a Class T at the battery, why bother with a breaker instead of a switch?

A switch will not disconnect an internal BMS. The ABYC requirement for a switch is to have a means of shutting down the power to the system in case of an emergency such as an electrical fire. If you plan to also use it to turn off your DC devices when you leave, then you will have to bypass the disconnect for your bilge pumps, solar chargers and anything else that requires a current while you are gone, such as a radio memory.
OS2Dude is offline   Reply With Quote
Old 15-12-2023, 08:35   #15
Registered User
 
smacksman's Avatar

Join Date: Sep 2009
Posts: 192
Re: Switch or Breaker?

My surveyor told me that the coastguard require all positive supply leads off the battery to be fused within 6" of the terminal. When I was inspected by the Coastguard heading south they were suprised that I had complied to this rule. This inferred that many people don't.
smacksman is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker by shore power inlet serves as main breaker? gpsatsea Electrical: Batteries, Generators & Solar 19 13-11-2023 10:09
Windlass+engine to LFP hybrid starter/house:only breaker or breaker+disconnect relay? CaptainRivet Lithium Power Systems 11 26-05-2023 07:41
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Breaker / Switch Failure Wakadui Electrical: Batteries, Generators & Solar 8 10-08-2010 16:23
Switch in Off Position Causes Breaker to Trip Patrick_DeepPlaya Electrical: Batteries, Generators & Solar 6 03-08-2009 04:19

Advertise Here


All times are GMT -7. The time now is 02:44.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.