Old 11-08-2015, 19:45   #1
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Wire Ampacity - NEC or ABYC?

Explain this one to me please.

Per widely published data, ABYC states that 12/3 wire, for example, has an ampacity of 45 amps outside of an engine room, 38.3 amp inside an engine room.

NEC however, to the best of my knowledge, allows a maximum of 20 amp breaker for this size wire.

Am I to believe that boats are less demanding than commercial and residential construction? What gives?

Personally, I follow the NEC for all AC circuits on board, but use the 3% tables for all 12V wiring.

I find this perplexing and potentially dangerous. For our foreign friends, the NEC is the National Electric Code and is the mandatory governing standard for all US electrical construction (other than some military and other applications). The ABYC is the American Boat and Yacht Council and is a voluntary non-governmental organization for boat builders.

Any answers?
redsky49 is offline   Reply With Quote
Old 11-08-2015, 21:21   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Wire Ampacity - NEC or ABYC?

are you comparing DC to AC values? the DC vaule is 45/38 single conductor, no bundle. which never happens. a 12/3 carrying DC drops to 32/27 vs single open strand. but I'm pretty sure AC has it's own table.

I don't think I've looked at an ABYC AC table for years. I just use 15/20/30 for 14awg / 12awg / 10awg.


also most house stuff is 75degree rated and boat wire is 105 which adds a lot to the tables.



in DC once you start using the voltage drop tables the max current one becomes pointless anyways.
smac999 is offline   Reply With Quote
Old 11-08-2015, 21:25   #3
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Wire Ampacity - NEC or ABYC?

The ABYC ratings depend on the temperature rating of the insulation, number of conductors and ambient temperature. In the case you mention the current ampacity is based on 105C insulation rated wire for a single conductor in free air of not more than 30C ambient temperature (table VI-A). Therefore it is definitely not the correct table for 12-3 wire.

You have to be sure each installation meets the specified conditions. For higher ambient you have to derate and for multiple wires in a bundle further derating is required. So for your example of 12-3 the ABYC table VI-B specifies allowed ampacity for 105C insulation wire in 30C maximum ambient would be 32A outside the engine room and 27A inside. If you have more than one such group of wires there is further derating.

Using the correct table and following all the derating factors for a specific situation I think you will find the ABYC ratings are fairly similar or even more conservative than NEC.
transmitterdan is offline   Reply With Quote
Old 11-08-2015, 21:54   #4
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wire Ampacity - NEC or ABYC?

Taken directly from one major US source of marine wire:

"12/3 AWG marine grade wire is a flat triplex 3 conductor wire features flexible, tinned copper stranding which is ideal for your boat wiring needs. Our boat wire is made in the USA and meets ABYC and US Coast Guard specifications while UL listed as UL1426 Boat Cable. The maximum allowable amperage of 12/3 AWG marine grade primary wire is 45 amps outside of engine spaces and 38.3 amps inside the engine space."

How would you interpret this?
redsky49 is offline   Reply With Quote
Old 11-08-2015, 22:06   #5
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by redsky49 View Post
Taken directly from one major US source of marine wire:

"12/3 AWG marine grade wire is a flat triplex 3 conductor wire features flexible, tinned copper stranding which is ideal for your boat wiring needs. Our boat wire is made in the USA and meets ABYC and US Coast Guard specifications while UL listed as UL1426 Boat Cable. The maximum allowable amperage of 12/3 AWG marine grade primary wire is 45 amps outside of engine spaces and 38.3 amps inside the engine space."

How would you interpret this?
Based on my reading of the ABYC tables they are wrong. The tables specifically says those ampacities are for a single conductor in free air. And last time I checked 12-3 was not a single conductor cable.
transmitterdan is offline   Reply With Quote
Old 11-08-2015, 22:23   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Wire Ampacity - NEC or ABYC?

http://assets.bluesea.com/files/reso...ence/21731.pdf


2nd table
"Up to three conductors in a sheath, conduit or bundle)"


12/3 would be sheathed cable. I would only count it as 2 conducter in AC but same table as 3 anyways


but I still think there is an AC table. but I don't have my E11 handy
smac999 is offline   Reply With Quote
Old 11-08-2015, 22:26   #7
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wire Ampacity - NEC or ABYC?

Per the 2007 draft requirements from ABYC committee, under alternating current:

Sec. E-11, Table VII A, For No More Than Two Circuits Bundled:

Chart shows again 45/38A for 12/3 105C cabling.

I have a secured document and haven't found a way yet to copy and post.

It's on page 84 of my copy.
redsky49 is offline   Reply With Quote
Old 11-08-2015, 23:28   #8
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by redsky49 View Post
Per the 2007 draft requirements from ABYC committee, under alternating current:

Sec. E-11, Table VII A, For No More Than Two Circuits Bundled:

Chart shows again 45/38A for 12/3 105C cabling.

I have a secured document and haven't found a way yet to copy and post.

It's on page 84 of my copy.
Does your copy differ in any significant way to this?

http://www.paneltronics.com/atimo_s/...11Excerpts.pdf
transmitterdan is offline   Reply With Quote
Old 12-08-2015, 07:00   #9
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wire Ampacity - NEC or ABYC?

I have found a later edition of the standard here:

http://www.paneltronics.com/atimo_s/...11Excerpts.pdf

In this version, conductors are grouped together DC and AC. It shows 12/3 105C being good for 31.5A outside engine room, 26.8A inside. This is Table VI-B.

?????

This later version is different than the draft form I have.
redsky49 is offline   Reply With Quote
Old 12-08-2015, 07:27   #10
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by redsky49 View Post
I have found a later edition of the standard here:

http://www.paneltronics.com/atimo_s/...11Excerpts.pdf

In this version, conductors are grouped together DC and AC. It shows 12/3 105C being good for 31.5A outside engine room, 26.8A inside. This is Table VI-B.

?????

This later version is different than the draft form I have.
The data posted by redsky49 (31.5 and 26.8A for 12/3 with 105°C insulation matches exactly my copy of the current ABYC E-11 standard (table VI-B).
svlamorocha is offline   Reply With Quote
Old 12-08-2015, 08:23   #11
Registered User

Join Date: Nov 2013
Location: Homeport: Fair Haven, NY
Boat: 1993 Sabre 362 #113
Posts: 609
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by redsky49 View Post
Explain this one to me please.

Per widely published data, ABYC states that 12/3 wire, for example, has an ampacity of 45 amps outside of an engine room, 38.3 amp inside an engine room.

NEC however, to the best of my knowledge, allows a maximum of 20 amp breaker for this size wire.

Am I to believe that boats are less demanding than commercial and residential construction? What gives?

Personally, I follow the NEC for all AC circuits on board, but use the 3% tables for all 12V wiring.

I find this perplexing and potentially dangerous. For our foreign friends, the NEC is the National Electric Code and is the mandatory governing standard for all US electrical construction (other than some military and other applications). The ABYC is the American Boat and Yacht Council and is a voluntary non-governmental organization for boat builders.

Any answers?
All amps are not the same. 40 amps at 12 volts is equal to about 4 amps at 120 volts. (see Volts/Amps/Watts Converter)

Voltage and amperage are inversely related. For the same amount of electrical power the higher the voltage the lower the amperage. Also, AC and DC are not entirely equivalent in these calculations. AC travels through wires much more efficiently than DC which tends to heat up wires more quickly than AC causing more resistance in the wire and subsequently more heat and power loss.

Without getting into all the nitty gritty, this is why larger boats are moving towards 24 volt DC systems (fewer amps and less current loss) and Power grids use extremely high voltage (Hundreds of Kilovolts) to deliver AC to your home.

Since shore power is essentially an extension of the power grid to your boat, using NEC sizes for the AC system is OK. But, do not use household wire or automotive wire on the boat. Stick with marine grade wire.

For DC wiring use the ABYC guidelines and marine grade wire.
Dave Lochner is offline   Reply With Quote
Old 12-08-2015, 08:52   #12
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Wire Ampacity - NEC or ABYC?

I believe they did change the tables sometime in the last 10 years. As noted the E11 I have seems to be the same as the last post from redsky. The insulation is important the 105c rated does change things quite a bit.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 12-08-2015, 08:55   #13
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wire Ampacity - NEC or ABYC?

Dave Lochner - I don't dispute this. My concern is for alternating current and what maximum ampacity is allowed under ABYC versus NEC.

From all I can see, ABYC permits much higher current than NEC. This applies to all wire gauges and insulation types. 31.5A per ABYC is way higher than 20A per NEC, for 12/3 for example.
redsky49 is offline   Reply With Quote
Old 12-08-2015, 09:00   #14
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Wire Ampacity - NEC or ABYC?

On the ABYC table 60C wire bundled up to 3 conductors is rated at 17.5 amps. I believe NEC ratings are for 60c or 75c wire insulation. This would put them inline with NEC 20 amp rating (actually a bit more conservative).
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 12-08-2015, 09:03   #15
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Wire Ampacity - NEC or ABYC?

I found a link to an NEC table here which seems to put the ABYC as more conservative.
Houston Wire & Cable Company - NEC Table 310.16
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
wire rigging dyform, compact wire, rod RDW Deck hardware: Rigging, Sails & Hoisting 4 12-11-2014 02:51
What's the Best Way to Connect a 4mm Wire to the Middle of a 6mm Wire? mischief Electrical: Batteries, Generators & Solar 11 07-11-2013 09:31
New wire being made 5 foot battery wire to terminal strip sdowney717 Electrical: Batteries, Generators & Solar 3 20-08-2012 08:27
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47

Advertise Here


All times are GMT -7. The time now is 18:39.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.