Old 28-12-2017, 18:57   #31
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Shunt wiring

Wotname,

It's not the volt meter that causes the problem. Take your example of a 1 milliohm shunt. It's impossible to get the big bolt connections to be anywhere close to 1 milliohm. So this creates a higher resistance than 1 milliohm and thus higher voltage than designed across the bolt connections. So the current reading will be too high. But the small kelvin screws don't see this higher voltage drop because they carry no significant current. That's why shunts are made the way they are. Read an explanation here: https://en.m.wikipedia.org/wiki/Four-terminal_sensing
transmitterdan is offline   Reply With Quote
Old 28-12-2017, 20:51   #32
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 4,862
Re: Shunt wiring

Quote:
Originally Posted by transmitterdan View Post
This will not work. There are 4 connections to a shunt. 2 are high current connections. 2 are just for measuring the voltage which is related to current. The big connections can never give the right voltage and the current measured will always be wrong and and it will vary too much with temperature.

Either fix the small broken connections or get a new shunt.
Quote:
Originally Posted by Paul L View Post
Why would the voltage drop between the two large connectors be any different than between the two small ones? They are only a few cm further apart in the solid shunt, if that.
Quote:
Originally Posted by transmitterdan View Post
Wotname,

It's not the volt meter that causes the problem. Take your example of a 1 milliohm shunt. It's impossible to get the big bolt connections to be anywhere close to 1 milliohm. So this creates a higher resistance than 1 milliohm and thus higher voltage than designed across the bolt connections. So the current reading will be too high. But the small kelvin screws don't see this higher voltage drop because they carry no significant current. That's why shunts are made the way they are. Read an explanation here: https://en.m.wikipedia.org/wiki/Four-terminal_sensing

Heh. You're both right.

The meter is, of course, always wrong, insofar as there is always some error and uncertainty in the measurement. The questions are: How much error is acceptable? Does using the large terminals contribute to the error in a way that makes it unacceptable when it otherwise would not be?

#12 copper wire is roughly one milliohm per foot. The brass posts on a shunt are much larger than #12 and much shorter than a foot in length. How much resistance is added by the extra distance? Not much, far less than a milliohm, perhaps a few microohms. There is some resistance in the pressure connection itself, and it is difficult to get a good, stable, reliable electrical connection when the large battery cables and the small instrument wires share the same terminal.

Will it work? Sure. Will there be a measurement error? Yes. Enough to matter? It depends, probably not if everything is clean and tight and if you can live with an 0.1A difference or so.

Quote:
Originally Posted by fritzdfk View Post
I have a little bit unrelated question. Is a shunt generic other than amp rating? Can a various amp meters be connected to a shunt? Only one connected at a time of course.
Quote:
Originally Posted by Wotname View Post
No, there is no generic shunt. There are some industry standards but no requirements to be a set standard.

Some common numbers are 50, 75 and 100 mV.

Thus for a certain amp rating, say 100 amps, the shunt might be designed to drop (develop) 75 mV when 100 amps is flowing though the shunt. Another 100 Amp shunt might drop 100 mV and so on. You can do the maths to find the resistance of the shunt (by using ohms law).
In the immortal words of Andy Tannenbaum, the good thing about standards is that there are so many to choose from.
Jammer is online now   Reply With Quote
Old 28-12-2017, 20:56   #33
Registered User
 
daletournier's Avatar

Join Date: Jan 2012
Location: Australia
Boat: Catalina 470
Posts: 4,578
Re: Shunt wiring

Quote:
Originally Posted by Jammer View Post
Heh. You're both right.

The meter is, of course, always wrong, insofar as there is always some error and uncertainty in the measurement. The questions are: How much error is acceptable? Does using the large terminals contribute to the error in a way that makes it unacceptable when it otherwise would not be?

#12 copper wire is roughly one milliohm per foot. The brass posts on a shunt are much larger than #12 and much shorter than a foot in length. How much resistance is added by the extra distance? Not much, far less than a milliohm, perhaps a few microohms. There is some resistance in the pressure connection itself, and it is difficult to get a good, stable, reliable electrical connection when the large battery cables and the small instrument wires share the same terminal.

Will it work? Sure. Will there be a measurement error? Yes. Enough to matter? It depends, probably not if everything is clean and tight and if you can live with an 0.1A difference or so.





In the immortal words of Andy Tannenbaum, the good thing about standards is that there are so many to choose from.
Yep your right. I only know because it's working for me. The battery charger is saying 60a,the xantrex is showing 67a which is about right due to solar panel output. It's closer enough for me.
daletournier is offline   Reply With Quote
Old 29-12-2017, 06:31   #34
Senior Cruiser
 
BlackHeron's Avatar

Join Date: Jan 2016
Boat: Bathtub
Posts: 889
Images: 19
Re: Shunt wiring

If it is off a little bit how big of a deal is it? Just call them "metric amps" and be happy that you have something that tells you relatively how much you are drawing versus charging. If you are counting how many amps are charging and discharging from multiple meters as long as you are using the same equipment to measure in and out then it doesn't actually matter all that much the unit that is being measured. If not, then it can cause a little bit of a mismatch.

Our sailing club uses knotmeters on their boats that are "Calibrated for Fun." They tell you exactly how fast you are going in "Fun Knots" that are great for comparing how much faster or slower you are going compared to the last time you looked at the speed. It even is good to compare today versus yesterday, or last week.

Comparing speeds from boat to boat? ...not so much
BlackHeron is offline   Reply With Quote
Old 29-12-2017, 07:02   #35
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: Shunt wiring

Well, sometimes it might be important to know
if you are measuring metric Amps or Imperial.


CatNewBee is offline   Reply With Quote
Old 29-12-2017, 10:44   #36
Registered User
 
artisanmach's Avatar

Join Date: Aug 2013
Location: Anacortes, WA
Boat: Gulfstar 37 Sloop
Posts: 187
Re: Shunt wiring


Name:   sw shunt.jpg
Views: 279
Size:  4.2 KB
where's my small terminals?
artisanmach is offline   Reply With Quote
Old 29-12-2017, 12:36   #37
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,444
Re: Shunt wiring

Quote:
Originally Posted by artisanmach View Post
Attachment 161193
where's my small terminals?
On top of the big terminals.
.
.
.
.
.
.
.
But clearly this won't work and will give wildly erratic and unstable results
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 29-12-2017, 13:35   #38
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Shunt wiring

For that shunt (post # 36) I would install the big current carrying wires immediately above the lowest washer, then a big nut, then an insulating washer, another nut, the twisted wire pair and finally, another nut.
The nut just above the insulator would be tightened against the very top nut so the twisted pair sees only the shaft voltages across the shunt itself.
This would keep the twisted pair connected ONLY to the threads which would accurately represent the voltage drop across and proportionally, the current through the shunt.

So there !
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 29-12-2017, 15:01   #39
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,444
Re: Shunt wiring

Quote:
Originally Posted by senormechanico View Post
For that shunt (post # 36) I would install the big current carrying wires immediately above the lowest washer, then a big nut, then an insulating washer, another nut, the twisted wire pair and finally, another nut.
The nut just above the insulator would be tightened against the very top nut so the twisted pair sees only the shaft voltages across the shunt itself.
This would keep the twisted pair connected ONLY to the threads which would accurately represent the voltage drop across and proportionally, the current through the shunt.

So there !
No disagreement from me....but.... I would connect the small twisted pair of wires directly under the small bladed screws that are at the top of each post just as the manufacturer intended.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 29-12-2017, 16:24   #40
Registered User

Join Date: Dec 2010
Location: W Carib
Boat: Wildcat 35, Hobie 33
Posts: 13,486
Re: Shunt wiring

Timely thread, Im getting some inaccurate readings at my volt/amp meter...another maintenance task added to the long list. [emoji45]
belizesailor is offline   Reply With Quote
Old 29-12-2017, 16:28   #41
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Shunt wiring

Quote:
Originally Posted by artisanmach View Post
Attachment 161193
where's my small terminals?
The two small straight blade screws on top of the threaded posts.
transmitterdan is offline   Reply With Quote
Old 29-12-2017, 17:25   #42
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Shunt wiring

Quote:
Originally Posted by Wotname View Post
No disagreement from me....but.... I would connect the small twisted pair of wires directly under the small bladed screws that are at the top of each post just as the manufacturer intended.
Even better! I didn't inflate the pic, and mistakenly thought we were talking about the OP's shunt.
Your post amounts to the exact same connection as my detailed diatribe.

I know, I know. PAY ATTENTION !!
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 29-12-2017, 20:29   #43
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,444
Re: Shunt wiring

Quote:
Originally Posted by Paul L View Post
......
Quote:
Originally Posted by transmitterdan View Post
Wotname,

It's not the volt meter that causes the problem. Take your example of a 1 milliohm shunt. It's impossible to get the big bolt connections to be anywhere close to 1 milliohm. So this creates a higher resistance than 1 milliohm and thus higher voltage than designed across the bolt connections. So the current reading will be too high. But the small kelvin screws don't see this higher voltage drop because they carry no significant current. That's why shunts are made the way they are. Read an explanation here: https://en.m.wikipedia.org/wiki/Four-terminal_sensing
Hmm... perhaps I'm not explaining myself very well or heaven forbid, perhaps I'm wrong.
First up, I understand all about four terminal measurements, especially low ohm meters etc. I've being doing this stuff for a long time now and have used all sorts of field and lab standard instrumentation as I am sure you have.

Second, the best way to use a shunt is of course the proper way, using the terminals exactly as the manufacturer intended.

However the OP had a problem and was looking for a "field" fix and after that we have got into a discussion about connecting the meter wiring directly to the "big" studs and the possible problems.

I maintain that it would be OK to connect the meter wires to the top of the big studs if that is the only fix available in the interim. There would not be large errors or inconsistent readings. If only one of the "kelvin" screws had failed, I would then use the other one as normal and field fix the failed side. If it was me, I would probably solder the meter wire directly to the brass block however fitting a large ring terminal to the meter wire and placing it on the very top of the big stud would get the amp meter functional again albeit with some error.

My reasoning is that surface of the brass block will have the near zero PD between any two points on it (maybe a some tens of micro volts). By extension, the PD between any side of the brass block and the top of the stud should only be in the order of hundreds microvolts to perhaps a few millivolts. Even if say it was 10 millivolts, there will only be a 10% error. It really boils down to the value of the current flowing though the stud and the resistance of the stud. I suggest this will not be a high number.

I understand the resistance between the large cable lug and the brass block can be high (i.e. > a few milliohms) but the degree of error will be determined by the value of the current flowing though the stud times the resistance of the stud. This will (in effect) give the PD between the existing small terminal and the top of the stud.

If I still had access to some of our old lab equipment and a micro voltmeter, I would run some tests but alas, this is no longer possible .
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 29-12-2017, 20:32   #44
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,444
Re: Shunt wiring

Quote:
Originally Posted by senormechanico View Post
Even better! I didn't inflate the pic, and mistakenly thought we were talking about the OP's shunt.
Your post amounts to the exact same connection as my detailed diatribe.

I know, I know. PAY ATTENTION !!
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 30-12-2017, 07:27   #45
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Shunt wiring

Guys,

Can you get a shunt like the OP had hooked up "wrong" to give some reading? Yes, and if that's a definition of "it works" then ok, it will work. But there is significant resistance in the studs and the brass block. So there is no good way to get an accurate reading using the big studs. For a small current shunt of 25-50A the error will be negligible. But for a big 250-500A shunt the error will be significant. That's my definition of "it won't work".

If the small screw holes are damaged the "best" field fix would be to drill out and tap to next larger screw size. Or drill and tap same size holes on opposite side of shunt. All cruisers ought to have a small set of drills and taps IMO.
transmitterdan is offline   Reply With Quote
Reply

Tags
wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Want To Buy: Link 2000 with Shunt - 84-2000-06 yacht_planb Classifieds Archive 2 21-02-2010 12:44
Location of Shunt bobelon Electrical: Batteries, Generators & Solar 9 27-03-2009 12:11
Battery Shunt ? ? ? S/V Mother Ocean Electrical: Batteries, Generators & Solar 5 22-10-2008 09:32
Battery Shunt ? ? ? S/V Mother Ocean Multihull Sailboats 3 21-10-2008 18:22
link 10 shunt on +? Ryan Electrical: Batteries, Generators & Solar 6 27-09-2005 14:17

Advertise Here


All times are GMT -7. The time now is 07:42.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.