Adding 50a service to existing 30a boat

Sorry for the naïveté here.
We want to upgrade to a smart plug shore power cable. I know we need a new addition inlet on board to receive the smart connection, but Instead of just replacing the 30a cable, I’m wondering why the cable and inlet couldn’t be 50a and tied into our existing 30a panel without major work: while the initial line in would have to be upgraded to a thicker wire, aren’t there fuses and breakers on all existing circuits to prevent too much amperage from flowing into each circuit? And open up the potential for more circuits on the panel?
If there are shore pedestals that don’t really provide the listed 30a from shore, wouldn’t this be more likely to provide at least the 30a, and allow the addition of more outlets or ability to draw more current?
In addition, I was thinking of occasionally still using the 30a cable with our pigtail (30a-to-15a) to run one more appliance separately or even creating another inlet connected to a new 30a panel to supply a few outlets just off it.
All observations welcome.
wgerstmyer is offline   Reply With Quote
Old 05-11-2019, 06:38   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Adding 50a service to existing 30a boat

You’ll also need to replace the cable between the shore inlet and the panel.....unless you’ve got a 30 amp breaker directly behind the shore inlet on the boat.

Otherwise, no real problem other than the huge cable.
Sailmonkey is offline   Reply With Quote
Old 05-11-2019, 17:13   #3
Registered User

Join Date: Oct 2015
Posts: 2,007
Re: Adding 50a service to existing 30a boat

Have you price a 50AMP cable yet? That might be all it take to change your mind....
billknny is offline   Reply With Quote
Old 05-11-2019, 18:42   #4
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,687
Re: Adding 50a service to existing 30a boat

Wgerstmyer,

Assuming your boat is currently wired for N American 115V AC, you will more than tripple your available AC wattage by rewiring for 50A 115/230V AC. [The 50A service provides you with two 115V AC hot legs to distribute instead of the one you now have with your 30A panel.]

That is how our boat is wired. [With two Smart Plug 50Amp inlets for convenience, not simultaneous use... they have a lock-out selector breakers so only one at a time can be hot...]

As we travel in summer, I still typically use the 30A shorepower cord [since it is much easier to handle] and we are only using it for water heater and battery charger... Our 10 AWG 3 conductor 30A cord has a 50A Smart Plug fitted to it to eliminate troublesome adapters...

In winter [think electric heat] and other times as needed, we use the 6 AWG, 4 conductor 50A cord. It is a beast to handle and stow. [Not an issue if you don't move around a lot...]

This can all be accomplished, but you will be doing quite a bit of rewiring on the infeed and distribution side of things if you wish to tripple your available wattage; and you will be optimized only for N American shorepower... [Which may not be an issue...?]

As Bill K mentioned, sit down when you start researching the costs of this upgrade.

Best wishes with your project.

Cheers! Bill
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is offline   Reply With Quote
Old 06-11-2019, 03:31   #5
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,439
Re: Adding 50a service to existing 30a boat

Quote:
Originally Posted by billknny View Post
Have you price a 50AMP cable yet? That might be all it take to change your mind....

50A cable is really heavy, too.

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 06-11-2019, 05:27   #6
Registered User
 
Bill O's Avatar

Join Date: Jul 2015
Boat: Bruce Bingham Christina 49
Posts: 3,328
Re: Adding 50a service to existing 30a boat

Instead of a 50A service, could possibly go w/2-30A inlets. The separate 30A cords are easier to handle. Depending on how your boat is set up electrically you may not always need the full 50A service (30A may do).

What equipment do you have or are planning to add to the boat to run off shore power? In our last boat, the big shore power users were the water heater, A/C unit and battery charger. Only when we wanted to run all of them at once did we need the 2-30A, otherwise a single 30A service would do 90% of the time.


Bill O.
__________________
Bill O.
KB3YMH
https://phoenixketch.blogspot.com/
Bill O is offline   Reply With Quote
Old 06-11-2019, 08:59   #7
Registered User
 
Lancerbye's Avatar

Join Date: Mar 2007
Location: Cormorant Island, BC, Canada
Boat: Lancer 44 Motorsailer
Posts: 1,877
Images: 38
Re: Adding 50a service to existing 30a boat

I have both 50/125 and 30/125 . The 30 is just wired parallel to the 50 with 10 ga. , but the 50 is wired to the 50 amp panel breaker with 6 ga. I haven't used the 50 amp cord in 10 years.
__________________
The basis of accomplishment is in never quitting
Mengzi Meng-tse
Lancerbye is offline   Reply With Quote
Old 06-11-2019, 09:33   #8
Moderator

Join Date: Jun 2015
Posts: 6,222
Re: Adding 50a service to existing 30a boat

wgerstmyer:

You haven't said what sort of boat you have. It is a BIG boat that requires 50A. A shoreside 2-bedroom apartment in Vancouver gets by handsomely on 100A and that includes electric baseboard heating in the winter.

Are you coming at this "problem" from the "wrong end", maybe? As others have also pointed out, it is not necessarily the case that "bigger is better", Have you done a power budget so you know what your boat REQUIRES?

Remember that what goes through the "umbilical" is what the boat "sucks up" when all your wizard devices are working at the same time. It is not what get's "pushed" from the shore end. There is rarely, if ever, a need for all your juice consumers to be working at the same time. In fact you have to work at it to make them do that, so it's unlikely that you'd ever need to suck more than 30A through the umbilical.

So my recommendation is to do a power budget. It's quite simple really, and if it is new to you, we'll be glad to help you.

Cheers

TrentePieds
TrentePieds is offline   Reply With Quote
Old 06-11-2019, 10:20   #9
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,512
Re: Adding 50a service to existing 30a boat

Quote:
Originally Posted by wgerstmyer View Post
Sorry for the naïveté here.
If there are shore pedestals that don’t really provide the listed 30a from shore, wouldn’t this be more likely to provide at least the 30a, and allow the addition of more outlets or ability to draw more current?

All observations welcome.
What TrentePieds said is right. You are looking at this backwards. A fifty amp cordset can carry 50 amps safely. If the shore power source cannot supply 30 amps going to a fifty amp cordset will not provide additional current.

And Bill O also has a good point - the cost of two 30's is far less than a single 50 and they are much easier to handle.

You need to asses your power demands. I have lived aboard a 44 foot boat in the winter with reverse cycle A/C for heat with two 30 amp cords - one being dedicated to the reverse cycle A/C. But I have also lived aboard on a single 30 amp source using space heaters, again in winter - a little more challenging but doable.

Tell us more about your power needs.
stormalong is offline   Reply With Quote
Old 07-11-2019, 06:08   #10
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Adding 50a service to existing 30a boat

Quote:
Originally Posted by wgerstmyer View Post
Sorry for the naïveté here.
We want to upgrade to a smart plug shore power cable. I know we need a new addition inlet on board to receive the smart connection, but Instead of just replacing the 30a cable, I’m wondering why the cable and inlet couldn’t be 50a and tied into our existing 30a panel without major work: while the initial line in would have to be upgraded to a thicker wire, aren’t there fuses and breakers on all existing circuits to prevent too much amperage from flowing into each circuit? And open up the potential for more circuits on the panel?
If there are shore pedestals that don’t really provide the listed 30a from shore, wouldn’t this be more likely to provide at least the 30a, and allow the addition of more outlets or ability to draw more current?
In addition, I was thinking of occasionally still using the 30a cable with our pigtail (30a-to-15a) to run one more appliance separately or even creating another inlet connected to a new 30a panel to supply a few outlets just off it.
All observations welcome.
If your goal is a belt and suspended solution (move up to a 50 A cordset, so that it is more robust and more capable, of safely carrying 30A than a 30A cord set, then go for it.

Your idea of using two cord sets is more complicated. To pass survey, two shore power inlets cannot be connected to the same AC circuits. (There must be an “exclusive or” switch or they must be connected to separate, isolated circuits.)

To add breakers is also more complicated. You have to ensure the connected loads due not exceed the panel and feeder cable ratings.

If you are not well versed in marine electrical standards and highly skilled in marine electrical wiring, for the latter two scenarios I recommend hiring a “certified” and “insured” (insist on seeing both certs with your own eyes) marine electrical tech.
ramblinrod is offline   Reply With Quote
Reply

Tags
boat, service


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combining 50A and 30A Galvanic Isolator HBWT Electrical: Batteries, Generators & Solar 11 21-03-2016 07:34
Marinco 50A to 30A converter Blues_Harp Classifieds Archive 0 29-03-2014 12:43
For Sale: Marinco Y- 50a male-two 30a female- lightly used. islandsailing Classifieds Archive 0 13-09-2013 09:13
30a service to 50a.... read the post. s/v 'Faith' Electrical: Batteries, Generators & Solar 15 04-10-2012 14:18
For Sale: Shorepower Pigtail - Marinco 121A Adapter 30A Female to 50A Male Critical Classifieds Archive 2 11-11-2010 22:25

Advertise Here


All times are GMT -7. The time now is 05:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.