Old 13-06-2013, 09:17   #16
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

From an engineering standpoint an accumulator is called an expansion tank. The design and function is the same. If an "accumulator" is installed on a pressure water system that includes a water heater/ clorifier, the "accumulator" also works as an expansion tank and will accept the expanding water from the heater.

In engineering speak there is no such thing as a accumulator, its always called an expansion tank. I call it a accumulator here as that is what many here call it.

By expansion tank, I mean a bladder style expansion tank. In olden days expansion tanks were just tanks with an air bubble in the top 1/2. But as Oliver L. indicated quite correctly the air is over time absorbed back into the water and the tank would get water logged and need to be drained.

While the manufacturers of VSD pumps are correct that you don't need a accumulator/expansion tank after the pump, the typical 6 gallon water heater will expand roughly 1/4 gallon (~.8 liter) of water. This is with engine heating. That water needs somewhere to go.

Using the T&P relief for thermal expansion has been banned by the US plumbing codes for about 15 years. Reason being is that sometimes the T&P relief becomes defective and then the expanding water will find the weakest spot in the system and cause a leak.

Prudent design requires a small expansion tank somewhere in all pressurized water systems to allow for thermal expansion at the water heater / clorifier.

If you have an accumulator /expansion tank in your system because of the on/off style pump, then it also functions as a thermal expansion tank for the water heater.

Though the jabsco accumulator is not quite larger enough to handle the thermal expansion caused by engine heating. That is why I, with my 30+ years designing plumbing systems among many other things, recommend the small thermal expansion tanks at the big box stores. They are larger the smallest being about a gallon (4 liter) size and meet the plumbing code at least in the US. Because it does not have marine in the name it is also less expensive.

When adding an expansion tank to a system using a VSD pump, it is best to install a check valve after the pump. This will keep the VSD pump from hunting quite so much. I've done this on 1200 GPM booster pumps.

Myself I'm not quite a fan of the small VSD pumps now available for use on boats. They generally will use a bit more power then a standard on/off pump. This as the impeller is less efficient at lower speeds and due to parasitic electric use in the control circuit. On land side buildings it was quite common to use on/off pump on systems under 300 GPM as the power usage was overall lower.

I don't think the energy used in the small VSD pumps are that much more but it is more. Just a bit. Probably not enough to worry about unless your an engineer.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 09:51   #17
Registered User

Join Date: Sep 2011
Location: Germany
Boat: secondarily boatless
Posts: 184
Re: Is an expansion tank necessary on a fresh hotwater system?

Sailorchick,

thank god, a voice of reason! The only thing you've got to look up is the thermal expansion coefficient: If I heat water from 20 C (mid 60F) to 60 C (150 F), I am looking at just over 1% of expansion. Therefore 6 gal (25 l) should expand by about 0.25 l. I believe the thermostat in the Diesel won't let it get much hotter than that.

For any pump, the check valve needs to be between the pump and the tank, i.e. on the suction side - otherwise the pump would not stop cycling; typically they all have the pressure sensor built into the pump.

Smooth sailing, and warm showers...

Oliver
Oliver L. is offline   Reply With Quote
Old 13-06-2013, 11:43   #18
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,450
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by sailorchic34 View Post

If you have an accumulator /expansion tank in your system because of the on/off style pump, then it also functions as a thermal expansion tank for the water heater.

Though the jabsco accumulator is not quite larger enough to handle the thermal expansion caused by engine heating.
...
Hmmm... interesting point.

I didn't realize hot water could back-flow out of the HWH tank to effect pressure at the "accumulator" tank (so called, here, simply 'cause that's what Jabsco names it)... and I assume that in turn would effect operation of the pressure switch on the pump itself.

BTW, I simply quoted Atwood's manual (above) -- with no intention of defending their comments

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 13-06-2013, 11:44   #19
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by Oliver L. View Post
Sailorchick,

thank god, a voice of reason! The only thing you've got to look up is the thermal expansion coefficient: If I heat water from 20 C (mid 60F) to 60 C (150 F), I am looking at just over 1% of expansion. Therefore 6 gal (25 l) should expand by about 0.25 l. I believe the thermostat in the Diesel won't let it get much hotter than that.

For any pump, the check valve needs to be between the pump and the tank, i.e. on the suction side - otherwise the pump would not stop cycling; typically they all have the pressure sensor built into the pump.

Smooth sailing, and warm showers...

Oliver
Most of the diesels I've seen are 180 degree F. Though 170-175 with heat exchanger approach temp is probably about right. I'm just conservative.

I was going off the top of my head as I didn't have the coefficients handy at that time, and was using 45 degree F (7C) to 180F(82C) or roughly 75c rise. I get about 2.5% (.15 gallon) expansion or a bit more then a pint. So I was a bit high before.

While some heaters have a safety to prevent overheating from engine water, some don't have them. Plus some, possibly engineers and possibly blonde, tend to remove them, going for more thermal energy storage.

The small DC pumps have a build in check valve so no check valve is required before the pump.

Putting a check valve after the pump discharge, which is after the pressure sensor on a VSD pump, will help a little to prevent hunting by the speed controller built into the pump. It will work ok without the extra check valve, btw.

The VSD pump marketing guys were getting rid of the expansion tank/ accumulator to partly justify the more expensive VSD pump. Which is true. But that same tank also handled thermal expansion, and that part is still needed. Properly sized a standard on off pump with a tank works just about as well, costs less and also does double duty handling thermal expansion.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 12:02   #20
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by ranger42c View Post
Hmmm... interesting point.

I didn't realize hot water could back-flow out of the HWH tank to effect pressure at the "accumulator" tank (so called, here, simply 'cause that's what Jabsco names it)... and I assume that in turn would effect operation of the pressure switch on the pump itself.

BTW, I simply quoted Atwood's manual (above) -- with no intention of defending their comments

-Chris
Yes there is a check valve in the water pump so everything downstream is one pressure zone. So when the water expands in the heater, it pressurizes the entire system. It does delay the pump switch, but only till the system pressure drops to the normal cut in point of the pressure switch.

If you added a pressure gauge you would see the pressure rise a bit as water fills the expansion tank(assuming no flow conditions).

What happens is the expanded water backs up into the accumulator / expansion tank. With the Jabsco that will just about fill the little tank and pressure will rise some from that.

Without an expansion tank the pressure will rise until the pressure relief setting on the water heater T&P relief is reached and then the T&P will pop off and burp some water out. Depending on the country the water heater was purchased in that pressure relief setting could be as high as 125-150 psig (in usa) before the relief pops.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 12:20   #21
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by JulianGullsway View Post
I thought that it was essential to have an expansion tank if you required a reasonable pressure , I have just installed our hot/ cold pressurised system aboard, however I think I need a larger expansion tank on the hot water side and I am thinking of adding one to the cold water side as well. On the Hot water side I have a 35ltr Calorifier and a 5ltr expansion tank but the pressure drops off quickly, the cold pressure is good but only for a short period, any ideas!!!!
Unless there is a check valve at the water heater inlet, and normally there isn't, then you only need one expansion tank, located on the cold water side. If the pressure drops off quickly it could be that the expansion tank is water logged. Even bladder expansion tanks fail. Once the expansion tank gets water logged then the pressure would drop off very quickly.

If there is a valve (Schrader type fill valve) at the top of the expansion tank, Turn off the water pump, open a cold water faucet, connect a bicycle pump to the fill valve and pump for a bit. If the tire pump has a gauge see if you can pressurize the expansion tank bladder to 1.5 bar (about 20 psig).If it does not come up to pressure then either you have a tear in the bladder or you have an older type expansion tank without a bladder.

In either case remove the pump, close the faucet and turn the pump on. Once the pump comes up to pressure and shuts off, see if you have more pressure before the pump kicks on.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 12:48   #22
Registered User
 
JulianGullsway's Avatar

Join Date: Jun 2010
Location: London
Boat: Endurance 35
Posts: 109
Thanks sailor chic I'll check that the weekend and report back 😊
JulianGullsway is offline   Reply With Quote
Old 13-06-2013, 14:24   #23
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,450
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by sailorchic34 View Post
If there is a valve (Schrader type fill valve) at the top of the expansion tank, Turn off the water pump, open a cold water faucet, connect a bicycle pump to the fill valve and pump for a bit. If the tire pump has a gauge see if you can pressurize the expansion tank bladder to 1.5 bar (about 20 psig).If it does not come up to pressure then either you have a tear in the bladder or you have an older type expansion tank without a bladder.

In either case remove the pump, close the faucet and turn the pump on. Once the pump comes up to pressure and shuts off, see if you have more pressure before the pump kicks on.

It happens I was just messing with our "accumulator tank" last weekend, since our pump was cycling faster than I thought it should. Your description is almost word for word like the Jabsco Manual... although it also says best results should happen at 10 psi. My tire pressure gauge didn't show much of any air pressure at first, and it won't measure below about 20 psi anyway, so after adding air I've now got somewhere between 10-20 psi in there. While overall water pressure didn't significantly increase, cycle times evened out a bit better, and that's actually what I was working toward.

I've been beginning to think that maybe air pressure in that tank could become a Spring maintenance issue, after winter temps have affected previous pressure levels. Or else maybe I'm beginning to see the effects of a slow leak in the bladder

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 13-06-2013, 14:38   #24
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by ranger42c View Post
It happens I was just messing with our "accumulator tank" last weekend, since our pump was cycling faster than I thought it should. Your description is almost word for word like the Jabsco Manual... although it also says best results should happen at 10 psi. My tire pressure gauge won't measure below about 20 psi, so I've got somewhere between 10-20 psi in there now, and while pressure didn't significantly increase, cycle times evened out a bit better, and that's actually what I was working toward.

I've been beginning to think that maybe air pressure in that tank could become a Spring maintenance issue, after winter temps have affected previous pressure levels. Or else maybe I'm beginning to see the effects of a slow leak in the bladder

-Chris
After you recharge the expansion tank, if it starts short cycling after a few weeks, there is a tear in the bladder. Happened to me, twice.

I like to set the bladder tanks to about 40% of system pressure. So if static pressure is 40 psig then about 16-18 psig will work most of the time. If you have a 30 psig system then 10-15 psi might be good. 60 psig set it a little higher. Luckily it does not need to be exact and close is good enough.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 14:39   #25
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Is an expansion tank necessary on a fresh hotwater system?

In european marine hot water systems , I have yet to see a specific expansion tank , but accumalator tanks are common so they are providing both functions, Ive also seen as quite common , system where burping of teh pressure relief effectively provided the pressure relief.

I wasnt suggesting best practice, merely an observation

heres a good guide http://www.jabscoshop.com/itemimages...on%20Guide.pdf

including expansion tank computations

dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 13-06-2013, 16:00   #26
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by goboatingnow View Post
In european marine hot water systems , I have yet to see a specific expansion tank , but accumalator tanks are common so they are providing both functions, Ive also seen as quite common , system where burping of teh pressure relief effectively provided the pressure relief.

I wasnt suggesting best practice, merely an observation

heres a good guide http://www.jabscoshop.com/itemimages...on%20Guide.pdf

including expansion tank computations

dave
Oh, I love the copper tank of the C-warm heater. That should last a long time. There you have a separate expansion tank for the heater. This is because the heater is only rated a 44 psig and the relief pops at 44 psig (3 bar).

Where there is a pressure reducing valve or check valve on the inlet of the C-warm heater then you will of course need a separate expansion tank for the heater. If you only have a pump that generates 2.5 bar pressure then the check valve and pressure reducing valve (PRV) is not needed.

The check valve is there to prevent hot water from mixing with the cold side. But its not normally that big a problem on boats. Plus the check valves after some time tend to stick open a little.

BTW I'm aware that the EU and England have rather different standards then the US. Specially where water heaters/ clorifiers are concerned. A biggy is the tanks are designed to different pressure standards. If your cruising the US and need to repair a EU or English water heater / clorifier, be advised that the T&P relief valves available in North America, will most likely have a higher pressure rating then your tank is rated for. Just FYI.
sailorchic34 is offline   Reply With Quote
Old 13-06-2013, 16:23   #27
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Is an expansion tank necessary on a fresh hotwater system?

Primary because in Europe domestic system do not exceed 3 bar pressure, and has carried over to marine systems
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 13-06-2013, 16:33   #28
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Oh, I love the copper tank of the C-warm heater. That should last a long time.
Again a carry over from domestic practice. A 'copper cylinder' in every home

dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 13-06-2013, 16:47   #29
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: Is an expansion tank necessary on a fresh hotwater system?

SailorChic you rock.

If you have an "accumulator" tank, and no check valve between cold and hot systems, that tank acts as your expansion tank for hot water expansion. That's all I have in my system and works great.

Photo below might help in understanding expansion (aka accumulator) tank (cutaway tank on right). The little fitting on top is a Schrader valve where you set pressure with a tire pump.
Attached Thumbnails
Click image for larger version

Name:	water-heater-expansion-tank.jpg
Views:	1653
Size:	357.5 KB
ID:	62490  
Dennis.G is offline   Reply With Quote
Old 14-06-2013, 06:27   #30
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,450
Re: Is an expansion tank necessary on a fresh hotwater system?

Quote:
Originally Posted by sailorchic34 View Post
After you recharge the expansion tank, if it starts short cycling after a few weeks, there is a tear in the bladder. Happened to me, twice.

I like to set the bladder tanks to about 40% of system pressure. So if static pressure is 40 psig then about 16-18 psig will work most of the time. If you have a 30 psig system then 10-15 psi might be good. 60 psig set it a little higher. Luckily it does not need to be exact and close is good enough.

Thanks for the tip; I'll watch for that.

The water pump cut-on is 20 psi and cut-off is 40 psi, so I had thought setting the accumulator air pressure to about 35 psi would be nifty... NOT. The pump cycled very quickly! Once I reduced accumulator air pressure to something less -- enough to move the gauge, but less than 20 psi, so I'm guessing between 10-20 somewhere -- the pump cycle calmed down.

And in the meantime, the Jabso material says 10 psi is likely optimum... even though they make scant mention of pump cut-in/cut-off...

At that point, I guessed the accumulator air pressure should be lower than the pump cut-in pressure. If so, how much less, I haven't a clue.

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tank Monitor - SeeLevel ? alisewski Plumbing Systems and Fixtures 25 24-07-2014 06:23
Perkins 4.108 Overheating While Under Load Astral Blue Engines and Propulsion Systems 29 01-07-2013 13:30
Refilling Water Tanks ironhorserider2 Plumbing Systems and Fixtures 19 29-09-2011 06:01
Head Odors Sailagain Plumbing Systems and Fixtures 19 15-07-2011 10:06
Route Properties, Missing Functions James Baines OpenCPN 13 13-07-2011 04:31

Advertise Here


All times are GMT -7. The time now is 12:06.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.