Flat Roll Bond Evaporator Source

Well the old BD-2.5 finally died its final death. Time to rebuild.

I'm looking for a source for Roll Bond Evaps. I would like two - 8" wide by 36-42" in length that can be bent at 12 & 20" from line set.

I've found some on RPart.com but they're 11.38" wide. I've thought about sheering the edges to desired dimensions but have no experience with this small of equipment. (Commercial/Industrial Refrig.Tech by trade)

Any info you be most helpful.

Cheers with warm rum
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 06-11-2012, 10:30   #2
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Flat Roll Bond Evaporator Source

A BD 2.5 compressor failure would be extremely rare if it was on an air-cooled condensing unit. Finding an eight inch wide evaporator is going to be hard to find. Have you tried Dometic and Frigoboat.

Have you considered using 25 feet of ¼ inch OD refrigerant dehydrated copper tubing for an evaporator? I built these at one time clamped in back of a stainless steel 18 gauge sheet. I believe Frigoboat has this simple inexpensive type evaporator although it is wider than 8 inches. SeaFrost will make you an evaporator plate any size but it is not aluminum roll bond. On more than one boat where evaporator coil was behind box liner and failed I clamped 25 to 35 feet of ¼ aluminum tubing to box walls as a good solution.
Richard Kollmann is offline   Reply With Quote
Old 09-11-2012, 05:45   #3
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Re: Flat Roll Bond Evaporator Source

Thanks Richard...I went to Frigoboat and found an evaporator that would do the job. Then I checked the price crazy...Then I referred back to your comment about making my own evap.....why not.
Any suggestions on captube size & length? I'm just being lazy and didn't want to go dig out my school books.

Thanks again for the redirection
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 09-11-2012, 06:30   #4
Registered User

Join Date: May 2009
Location: Massachusetts
Boat: 40' Silverton Aftcabin with twin Crusaders
Posts: 1,791
Re: Flat Roll Bond Evaporator Source

Richard's suggestion for copper tubing makes sense. I thought about that technique for a future project. My earlier ideas included sandwiching the tubing in the box's fiberglass walls. That idea has risks because fiberglass and copper have different expansion rates that would ultimately break their bond.

Richard mentions clamping the tubing to a SS plate (also consider aluminum 6061 or 5052) but it might be easier to sandwich the tubing between two plates but either way, it will work. You might find more on this using Google.
foggysail is offline   Reply With Quote
Old 23-12-2012, 12:28   #5
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Thumbs up Thank You Richard!!

I took your advice Richard and built my own evap. and rebuilt the entire refrigeration system. I really am quite ashamed of myself that I didn't just do it in the first place. Refrigeration mechanic is my second trade.
Here are some pics
Attached Thumbnails
Click image for larger version

Name:	1.jpg
Views:	256
Size:	335.2 KB
ID:	51618   Click image for larger version

Name:	3.jpg
Views:	206
Size:	409.9 KB
ID:	51619  

Click image for larger version

Name:	4.jpg
Views:	229
Size:	432.5 KB
ID:	51620   Click image for larger version

Name:	10.JPG
Views:	301
Size:	153.5 KB
ID:	51621  

Click image for larger version

Name:	14.JPG
Views:	219
Size:	335.5 KB
ID:	51622   Click image for larger version

Name:	15.JPG
Views:	261
Size:	182.6 KB
ID:	51623  

__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 23-12-2012, 12:36   #6
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Something I've never seen onboard before!!



80F ambient

I have a data logger in the box now. Will report back
Attached Thumbnails
Click image for larger version

Name:	18.jpg
Views:	225
Size:	425.0 KB
ID:	51617  
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 23-12-2012, 17:33   #7
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Flat Roll Bond Evaporator Source

Looks good but two comments:
1. With an expansion valve expansion device it needs a small receiver to handle changes of refrigerant flow as evaporator plate freezes.
2. I hope you used the smallest valve orifice 00, 1300 btu or lower . If valve orifice is too large pressure differential will not occur on a warm 80 degree F temperature start up.
Richard Kollmann is offline   Reply With Quote
Old 25-12-2012, 07:01   #8
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Re: Flat Roll Bond Evaporator Source

Thank you.

I did make a small receiver out of inch & 1 and it seems to be doing its job as site glass is clear.
I currently have orifice 01 installed for testing, but can roll back to a 00 if need be. I also went for an MOP valve in hopes of getting some assistance during start up.
I did have one start up issue on initial start, but that was because I was over charged. I have also added a 2" scrubber fan in the box that runs when refrigeration is running as an experiment.
Attached Thumbnails
Click image for larger version

Name:	SCAN0034.jpg
Views:	218
Size:	251.8 KB
ID:	51673  
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 26-12-2012, 04:34   #9
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Flat Roll Bond Evaporator Source

The location of Data Logger is only relative to box temperature and thermostat setting but it appears thermostat is set at 40 degrees F. Most logger soft wear permit one area to be expanded to measure a complete compressor cycle time between one compressor start and the next start. From the number of cycles on graph it would seem that there is higher than necessary compressor speed.

This is the first time I have seen box Dew point and Humidity reaction to compressor cycles. I would have guessed they would both decrease as moisture collected and froze on evaporator.

Great System.
Richard Kollmann is offline   Reply With Quote
Old 26-12-2012, 18:27   #10
Registered User

Join Date: May 2009
Location: Massachusetts
Boat: 40' Silverton Aftcabin with twin Crusaders
Posts: 1,791
Re: Flat Roll Bond Evaporator Source

Quote:
Originally Posted by Richard Kollmann View Post
Looks good but two comments:
1. With an expansion valve expansion device it needs a small receiver to handle changes of refrigerant flow as evaporator plate freezes.
2. I hope you used the smallest valve orifice 00, 1300 btu or lower . If valve orifice is too large pressure differential will not occur on a warm 80 degree F temperature start up.
Richard-- I am a novice here so most likely my question will make that obvious. You state the refrigerant flow will change as the evaporator plate freezes. I got lost on that. Does not the refrigerant flow independently of the evaporator plate condition? Even the cycling is determined by a temperature sensor someplace but does not control the flow.

Now if the system utilizes a variable pump rate governed by some type of external sensor, that is another matter especially if it monitors the plate.

Just trying to understand this stuff--

Thanks

Foggy
foggysail is offline   Reply With Quote
Old 26-12-2012, 18:33   #11
Registered User

Join Date: May 2009
Location: Massachusetts
Boat: 40' Silverton Aftcabin with twin Crusaders
Posts: 1,791
Re: Flat Roll Bond Evaporator Source

Caribsailors--

Impressive evaporator! What material is your mounting plate and how did you secure the tubing to it?

Thanks--

Foggy
foggysail is offline   Reply With Quote
Old 27-12-2012, 14:53   #12
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Flat Roll Bond Evaporator Source

Quote:
Originally Posted by foggysail View Post
Richard-- I am a novice here so most likely my question will make that obvious. You state the refrigerant flow will change as the evaporator plate freezes. I got lost on that. Does not the refrigerant flow independently of the evaporator plate condition? Even the cycling is determined by a temperature sensor someplace but does not control the flow.

Now if the system utilizes a variable pump rate governed by some type of external sensor, that is another matter especially if it monitors the plate.

Just trying to understand this stuff--

Thanks

Foggy

Refrigerant flow determines Btu of work accomplished while refrigerant’s boiling point controls heat absorption temperatures within evaporator. Both refrigerant Flow and refrigerant boiling point when condenser and evaporator are in balance are controlled by a refrigerant expansion device. When evaporator is warm refrigerant flow is highest. As evaporator temp decreases flow control device reduces refrigerant flow lowering boiling point of refrigerant and lowering evaporator temperature.

There are three different flow control devices used in small refrigeration systems, Long fixed orifice capillary tubes, Low fixed pressure control valves and Thermo Expansion Valves. Purpose of refrigerant flow control device is to insure that refrigerant’s liquid phase change to a gas occurs only inside evaporator where heat can be most efficiently absorbed. This temperature range change inside evaporator is defined as superheat range. Although capillary tubes on small Danfoss compressors are fixed orifice they have an evaporator temperature range that depends on evaporator/capillary size. Low pressure control valves maintain a fixed low pressure and limit refrigerant flow reducing Btu work done at warm evaporator temperatures. Thermo expansion valves provide an automatic evaporator temperature range from -40 to +50 degrees F. Because of thermo expansion valve’s wide temperature and refrigerant flow range a receiver is required to store excess refrigerant at low evaporator temperatures.
Richard Kollmann is offline   Reply With Quote
Old 27-12-2012, 15:56   #13
Registered User

Join Date: May 2009
Location: Massachusetts
Boat: 40' Silverton Aftcabin with twin Crusaders
Posts: 1,791
Re: Flat Roll Bond Evaporator Source

WOW! I need to look this stuff up. Richard--- my printer is down now while I wait for my new desktop to arrive. But I am going to print out your post. It is technical but I believe there are some gold nuggets in it.

I was thinking back to my old thermodynamics class in college where the principles of refrigeration were covered. Great stuff although limited practical use. For example, a nozzle was just a nozzle. Most likely I will have other simple questions but I need to review what you just provided.

Thanks Rich--

Foggy
foggysail is offline   Reply With Quote
Old 27-12-2012, 18:27   #14
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Re: Flat Roll Bond Evaporator Source

Foggy

Thanks
The backing plate is 18 awg copper. I'm lucky enough on the little island I'm on presently, to have a friend who is an international award winning metal sculptor. So I was able to access sheet copper in the 2nd world.
I attached the perimeter tubing using 15% silfos, but got to much metal distortion moving inward because of the heat required for silfos, and moved to soft solder. I think if I had used a sand bed while welding it may have help, but I need to talk with my sculptor for his thoughts
I'm not really happy with it, but it seems to be doing the job. I did consider epoxy resin, but moisture and refrigeration can make some dramatic results, has been my experience. That said I still haven't given up on the thought of epoxy, maybe placed in a vacuum while curing? Just a thought.

Cheers.
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 27-12-2012, 18:55   #15
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
Re: Flat Roll Bond Evaporator Source

[QUOTE=foggysail;1116116]WOW! I need to look this stuff up. Richard-

I'd buy his book....Kollmann Marine

I'm seriously considering it. I'm a commercial/industrial refrigeration mechanic by trade. Refrigerant phase change is refrigerant phase change, but what I LOVE of the trade, is the different nuances in each genre, if I can use that. I've worked on ice machines that drop 250 Lbs of ice every 45 minutes, supermarkets, grow opp air filtration to morgue cooling and commercial fishing. What is currently stirring the brain of need to know, is the algorithm of the AEO controller. I love the LED diagnostics but need to see the parameters that determine its output. That's why refrigeration is COOL!
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 09:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.