BD50 Fan Replacement

The fan on our compressor has started making a rattling noise when it first starts. I can push on it and it will stop but I would like to replace it.

I have a Noctua NF-A12x25 PWM fan that I plan on using as the replacement but I want to make sure it is set up for the most efficient use in the tropics.

The current fan in mounted between the condenser and compressor and is pulling air through the condenser. Is this the best configuration? There is plenty of room to mount the fan on the outside of the condenser as well. Also pulling or pushing air is an option.

Thanks for the guidance.
crayiii is offline   Reply With Quote
Old 10-11-2022, 06:19   #2
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,084
Re: BD50 Fan Replacement

The rattle could be a worn out bearing or the tips hitting something. If it's the bearing, yeah, time to replace it since it will be a PITA to replace the bearing in a cheap fan.

Then. The job of the fan is to remove hot air from the compressor/motor/condenser. How can you best direct the air from some cool location (the bilge?) past those units and out of the boat? Don't waste air by having it bypass the hot units. If the cooling of your cooler was marginal before, consider a stronger fan and/or more ducting to make the air flow more effective in sucking hot air out.

Good luck with it.
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 10-11-2022, 07:44   #3
Registered User
 
Bill O's Avatar

Join Date: Jul 2015
Boat: Bruce Bingham Christina 49
Posts: 3,328
Re: BD50 Fan Replacement

For our frigoboat bd50 units, we changed out the fans because they we very noisy.

We bought these Noctua NF-P12 1700 rpm to replace the original fans that came w/the condensers. Compared to the original fans, they are of similar cfm, ~ half the noise and ~1/3 the power draw. The fan you selected looks like a good one and should work, but double the price of the one listed above.

The freezer compressor is in a cabinet and we added a duct to push the air out of the cabinet. The fan is mounted to pull air through the condenser and seems to work well.
__________________
Bill O.
KB3YMH
https://phoenixketch.blogspot.com/
Bill O is offline   Reply With Quote
Old 10-11-2022, 08:13   #4
Registered User

Join Date: Apr 2015
Posts: 191
Re: BD50 Fan Replacement

In my installation the fan pushes air over the condenser and compressor, so a fan with the ability to overcome the static pressure was needed (forgot the noctua part number).

In your case the static pressure is on the incoming side of the fan, and you'll need to consider that - which seems less common.

I think you know this, thus your question. Any way to mount the fan elsewhere? I was planning on making a new fan shroud for either dual fans or a larger fan. Power consumption is not a consideration for all practical purposes (big picture kind of thing).
two-rocks is offline   Reply With Quote
Old 10-11-2022, 08:18   #5
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,452
Re: BD50 Fan Replacement

Probably the biggest assortment of fans you'll find at one site.
More air flow is always better.

https://www.newark.com/c/cooling-the.../dc-axial-fans
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Reply

Tags
men


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Danfoss BD50 Compressor pulling way too many amps teneicm Plumbing Systems and Fixtures 38 10-06-2017 02:09
12v Danfoss BD50 stopping when heeled over chouliha Plumbing Systems and Fixtures 12 26-02-2015 16:51
Frigoboat K50/Danfoss BD50 fridge problem Sputnikus Plumbing Systems and Fixtures 16 13-07-2014 11:37
Using Danfoss BD50 as Vacuum Pump infinitysail Plumbing Systems and Fixtures 6 17-11-2013 09:53
Danfoss BD50 Morse Code Interference to SSB meridian@ Marine Electronics 0 09-02-2010 03:19

Advertise Here


All times are GMT -7. The time now is 16:00.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.