Replacing ganged DC breakers

In the midst of a fairly aggressive electrical refit and I've been kind of stumped by the breaker set up. The original panel has 3 60amp breakers connected, in parallel, to a bus bar for the house DC circuit. And for the life of me, I'm not really sure what amperage breaker to replace them with to match the original sizing with a single breaker. The simple answer is a 60amp breaker, but a parallel circuit like that should be able to handle 180 amps, except there's no way the power would be distributed evenly so the actual rating would be far lower, but I'm not sure how much lower.

Any suggestions?
Corvidae is offline   Reply With Quote
Old 16-09-2018, 20:04   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,692
Re: Replacing ganged DC breakers

the problem is you won't find a 180a breaker that fits in a standard DC panel. that is why they put 3 in parallel.

IE the blueseas A series goes to 50a and the C series goes to 100a. above that they sell them as 2 or 3 pole ganged breakers.

that seems way too high for a DC panel. windlass and other high loads should have own feeds / fuses. and a panel really should not have that kind of draw on it.
smac999 is offline   Reply With Quote
Old 16-09-2018, 20:05   #3
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 4,960
Re: Replacing ganged DC breakers

Quote:
Originally Posted by Corvidae View Post
In the midst of a fairly aggressive electrical refit and I've been kind of stumped by the breaker set up. The original panel has 3 60amp breakers connected, in parallel, to a bus bar for the house DC circuit. And for the life of me, I'm not really sure what amperage breaker to replace them with to match the original sizing with a single breaker. The simple answer is a 60amp breaker, but a parallel circuit like that should be able to handle 180 amps, except there's no way the power would be distributed evenly so the actual rating would be far lower, but I'm not sure how much lower.

Any suggestions?

The parallel breakers for high loads are sold as a set of two or three breakers, with a rated trip current at 2x or 3x the rating of individual breakers. You can take a look at the Blue Sea Systems catalog to see for yourself. The idea is that the very small internal resistance of each breaker, combined with a low-resistance busbar connecting them, is enough to ensure that the current flow is even amongst them. Since they will all trip if one trips, any uneven distribution of current would serve to cause them to trip earlier.


So, in your situation, a 180 amp breaker would be a suitable replacement. DC breakers in that size are uncommon, at least in a configuration that will fit a standard panel along with other breakers, but are available for freeform mounting. Depending on the nature of the load, you may also be able to use a fuse, which would be cheaper and less likely to fail closed.
Jammer is offline   Reply With Quote
Old 17-09-2018, 04:44   #4
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Re: Replacing ganged DC breakers

Dealing with bad breakers on a customers cat. At first glance it looked like 3x30 amp breakers with single switch, in actuality it was 2 30 amp breakers and one 65 Volt breaker all tied together as one, the 65 Volt breaker to protect against incorrect / faulty shore power wiring, also there is a special motor start delay built into the breakers.
Dulcesuenos is offline   Reply With Quote
Old 17-09-2018, 04:51   #5
Registered User

Join Date: Mar 2017
Location: Indian Harbour Beach
Boat: Gallart 13.50 MS
Posts: 132
Re: Replacing ganged DC breakers

My plan is to remove the entire panel. So a surface mount breaker would work just fine. Thank you all for the info.
Corvidae is offline   Reply With Quote
Old 17-09-2018, 05:47   #6
Registered User

Join Date: Oct 2015
Posts: 2,007
Re: Replacing ganged DC breakers

Quote:
Originally Posted by Corvidae View Post
My plan is to remove the entire panel. So a surface mount breaker would work just fine. Thank you all for the info.
Don't forget, when changing the size of the breaker to be sure that you match it to the wire that it is protecting.

If sized properly, the 60AMP breakers could have been connected with wire as small as AWG 10. If you bump to a 180 Amp breaker or fuse you'll need to go to at least an AWG 2--or larger depending on the physical setup.
billknny is offline   Reply With Quote
Old 17-09-2018, 07:14   #7
Registered User

Join Date: Mar 2017
Location: Indian Harbour Beach
Boat: Gallart 13.50 MS
Posts: 132
Re: Replacing ganged DC breakers

The wire on both sides is 4/0, it's the main feeder wire to the DC panel. The panel it's in is going to go away. Because it's the housing for the ac transfer switch, that's been replaced elsewhere, the battery charger transfer switch that's been replaced elsewhere, the generator control circuits for a generator that is no longer there, and the electrical harnesses for the two diesel engines that are no longer there.

At the moment, the only thing still active in the 2' by 2' panel is the main breaker for the AC and DC circuits. Which I plan on putting in a much, much smaller enclosure.
Corvidae is offline   Reply With Quote
Old 17-09-2018, 09:24   #8
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,539
Re: Replacing ganged DC breakers

Quote:
Originally Posted by Dulcesuenos View Post
Dealing with bad breakers on a customers cat. At first glance it looked like 3x30 amp breakers with single switch, in actuality it was 2 30 amp breakers and one 65 Volt breaker all tied together as one, the 65 Volt breaker to protect against incorrect / faulty shore power wiring, also there is a special motor start delay built into the breakers.

Your OP says DC and this post says it is for the AC circuit. The C/B you describe in your second post is typical for an A/C mains circuit.

If you cannot tell the difference you need to bring in a professional.
stormalong is offline   Reply With Quote
Old 17-09-2018, 09:33   #9
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Re: Replacing ganged DC breakers

Quote:
Originally Posted by stormalong View Post
Your OP says DC and this post says it is for the AC circuit. The C/B you describe in your second post is typical for an A/C mains circuit.

If you cannot tell the difference you need to bring in a professional.
Thanks for catching that, for some reason I thought the post said AC I hadn't had my coffee yet[emoji12]
Clearly I knew I, was speaking about AC breakers, unless for some reason you've seen shore power in DC
Dulcesuenos is offline   Reply With Quote
Old 17-09-2018, 10:42   #10
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Replacing ganged DC breakers

The hole post is confusing, AC or DC The OP sounded like DC then one came in that was a post of AC.
Cadence is offline   Reply With Quote
Old 20-09-2018, 20:21   #11
Registered User

Join Date: Aug 2017
Posts: 216
Re: Replacing ganged DC breakers

Quote:
Originally Posted by smac999 View Post
the problem is you won't find a 180a breaker that fits in a standard DC panel. that is why they put 3 in parallel.

IE the blueseas A series goes to 50a and the C series goes to 100a. above that they sell them as 2 or 3 pole ganged breakers.

that seems way too high for a DC panel. windlass and other high loads should have own feeds / fuses. and a panel really should not have that kind of draw on it.


I agree can't see why you could possibly need 3 times 60 you can weld with that amperage - and that's undesirable
james247 is offline   Reply With Quote
Old 20-09-2018, 20:44   #12
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,539
Re: Replacing ganged DC breakers

Quote:
Originally Posted by james247 View Post
I agree can't see why you could possibly need 3 times 60 you can weld with that amperage - and that's undesirable

Read responses eight and nine.
stormalong is offline   Reply With Quote
Old 24-09-2018, 14:19   #13
Registered User

Join Date: Mar 2017
Location: Indian Harbour Beach
Boat: Gallart 13.50 MS
Posts: 132
Re: Replacing ganged DC breakers

Just to clarify, it's a DC circuit. As to why it's so large of a circuit, my guess is that you could conceivably be starting both motors, and the generator, while the radar and refrigerator was on, the davit winch was lifting the outboard, and the windlass is raising the anchor. It's very unlikely, but if you're going to plan a circuit, you plan for full use. It's also a 40 year old boat, so adding up every incandescent light comes out to a decent load as well.

Honestly I may down size the circuit a bit. The windlass is the only big thing on it any more, and it draws less than 60. The starters are gone with the engines, and the generator is off on it's own now. The fridge is also running on 110 now, instead of the ancient 12v system that was in there.
Corvidae is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing old/stock circuit breakers ValiantV Electrical: Batteries, Generators & Solar 26 31-05-2017 18:56
Suitability Of Ganged 6v Batteries as a Large House Bank S/V Alchemy Electrical: Batteries, Generators & Solar 13 03-09-2012 11:29
Electrical Panels/ Circuit Breakers CaptainK Marine Electronics 12 14-05-2006 20:29
DC Overcurrent Protection (Fuses or Breakers) GordMay Electrical: Batteries, Generators & Solar 1 10-02-2006 06:02
breakers vs. fuses Steve Rust Construction, Maintenance & Refit 1 02-12-2003 03:51

Advertise Here


All times are GMT -7. The time now is 07:33.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.