Vents through the deck, topsides and hull. What would you use?

I have some ventilation to do for my fuel tank compartment.

A wonderful, unadvertised feature of fuel tanks is they permeate fuel stink.

I need to place 2 vents (as is specified by USCG construction guides), creating a natural air draft ventilation for the fuel tank compartment, which is below decks.

What would be the best way to do this on a catamaran?

Fuel tanks are down in a hull, not at bridge deck level.

What type of vents would you use to ensure a nice, steady flow of air?

My hull and deck are about 1 1/4” to 1 1/2” thick. (30 mm or so)

The wind comes from the bow 95+ percent of the time.

Thanks!
Chotu is offline   Reply With Quote
Old 31-12-2020, 05:45   #2
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Vents through the deck, topsides and hull. What would you use?

The deck is about 2/3 the width of this one.



And the fuel tanks are aft on the port side.

Tanks are located way down low, approximately below where the winch is above the number “42” in this pic.

Chotu is offline   Reply With Quote
Old 31-12-2020, 05:51   #3
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Vents through the deck, topsides and hull. What would you use?

I'd use some kind of louvered vents on the sides of the hull, just below the deck line (ducted down into the compartments). With a cat, that shouldn't be a downflooding concern. I'd face the louvers forward on one side of the hull, aft on the other. That way you'll get air forced through with the wind from the bow or from the side.


The fuel smell is an unfortunate feature of plastic gas tanks. Only way to avoid it is aluminum or stainless.
rslifkin is offline   Reply With Quote
Old 31-12-2020, 06:49   #4
Registered User

Join Date: Dec 2016
Location: MED
Boat: Hanse 430e
Posts: 438
Re: Vents through the deck, topsides and hull. What would you use?

https://www.westmarine.com/buy/perko...38?recordNum=3

As high up on the inside or outside (topsides) of the hull as possible.
Dogscout is offline   Reply With Quote
Old 31-12-2020, 07:00   #5
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Vents through the deck, topsides and hull. What would you use?

Quote:
Originally Posted by Dogscout View Post
https://www.westmarine.com/buy/perko...38?recordNum=3

As high up on the inside or outside (topsides) of the hull as possible.
Ah. They need to have a dryer hose size ventilation. These are way, way too small.

But were you just pointing out the vent type?

I have one of those vents already of the right size but it has almost no reach to get through the hull.


The fuel tank itself, which would use these vents you are showing, is ventilated already. The fuel tank compartment, however, is not. And it STINKS
Chotu is offline   Reply With Quote
Old 31-12-2020, 07:03   #6
Registered User

Join Date: Nov 2017
Posts: 137
Re: Vents through the deck, topsides and hull. What would you use?

Search variations on these: https://www.westmarine.com/buy/white...Y-_-PDP-Mobile

I know they're available with or w/o the 90° bend

Pat
Tusitala is offline   Reply With Quote
Old 31-12-2020, 07:04   #7
Registered User

Join Date: Jul 2018
Location: Watch Hill, RI
Boat: Crowther Custom Performance Cat
Posts: 105
Re: Vents through the deck, topsides and hull. What would you use?

Can you go smaller with small solar fans to assist air flow?
JimmyDarci is offline   Reply With Quote
Old 31-12-2020, 07:05   #8
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Vents through the deck, topsides and hull. What would you use?

To add to my earlier post, my boat uses a bunch of these (with collector boxes and 5 inch ducts) for bilge ventilation (can be found much cheaper elsewhere): https://www.westmarine.com/buy/attwo...0?recordNum=17
rslifkin is offline   Reply With Quote
Old 31-12-2020, 08:17   #9
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Vents through the deck, topsides and hull. What would you use?

Quote:
Originally Posted by Tusitala View Post
Search variations on these: https://www.westmarine.com/buy/white...Y-_-PDP-Mobile

I know they're available with or w/o the 90° bend

Pat
Nope. Think dryer vent. That’s the size hose.
Chotu is offline   Reply With Quote
Old 31-12-2020, 08:19   #10
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Vents through the deck, topsides and hull. What would you use?

Quote:
Originally Posted by rslifkin View Post
To add to my earlier post, my boat uses a bunch of these (with collector boxes and 5 inch ducts) for bilge ventilation (can be found much cheaper elsewhere): https://www.westmarine.com/buy/attwo...0?recordNum=17
I can’t shake the fear of these offshore for some reason. I feel like I’m the worse possible seas, they’ll start flooding my bilges with water splashing down.

Could be an unfounded fear but.... very uneasy about big holes like that at or below deck level on a sailboat.
Chotu is offline   Reply With Quote
Old 31-12-2020, 08:28   #11
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Vents through the deck, topsides and hull. What would you use?

Quote:
Originally Posted by Chotu View Post
I can’t shake the fear of these offshore for some reason. I feel like I’m the worse possible seas, they’ll start flooding my bilges with water splashing down.

Could be an unfounded fear but.... very uneasy about big holes like that at or below deck level on a sailboat.

On my boat I did end up turning the forward facing pair (which are about 2/3 of the way forward on the hull) around to face aft. The boat had an issue with blowing spray down the vents in rough seas up on plane. Never took solid water down them or enough to be an issue. Since turning the vents around, I haven't taken a drop of water down them (they're about 3.5 feet above the waterline). And the 2 pairs further aft on the hull (around the mid-point and just forward of the transom) that face aft have never taken water. On a cat where there's no heeling, I'd expect it to be less of an issue. On a monohull sailboat, I wouldn't do it.

Well designed collector boxes would also mitigate the issue, either a spray deflector between the vent and the tube, or the vent tube entering the top of the collector, or at one end with a baffle. Mine are open collector boxes with the ducts coming out the bottom (poor factory design), so they're very easy to dump water down.

If turning the vents around didn't fix the issue, my plan was to build water separator boxes, basically a dorade with a vent tube going in and one going out and a water drain to a thru hull above the water line. Then unless the vent were completely submerged, any water that splashed in would just drain back out without ending up in the bilge.


You could also go for scoops above the gunwale like typical sailboat dorades would use. One forward and one aft facing for each compartment.
rslifkin is offline   Reply With Quote
Old 31-12-2020, 08:34   #12
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Vents through the deck, topsides and hull. What would you use?

To add on to my last post, here are a couple of pictures showing the vent placement I was describing on my boat.
Attached Thumbnails
Click image for larger version

Name:	IMG_20191014_081926.jpg
Views:	115
Size:	426.8 KB
ID:	229688   Click image for larger version

Name:	IMG_20191014_114345.jpg
Views:	96
Size:	423.8 KB
ID:	229689  

rslifkin is offline   Reply With Quote
Old 31-12-2020, 09:03   #13
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,526
Re: Vents through the deck, topsides and hull. What would you use?

I would vent out the back up high, or (preferably to me) into the cockpit. Use a 3" vent with plastic hose (like used in bilge vents, kinda like dryer hose) from bottom up to the vent. That way the chimney effect will draw it out better. it's amazing how much chimney effect you get in 4-6 ft of head!
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 31-12-2020, 09:48   #14
Registered User

Join Date: Oct 2011
Boat: KH 49x, Custom
Posts: 1,760
Images: 2
Re: Vents through the deck, topsides and hull. What would you use?

I would use louvred vents and build dorade Boxes on the inside.

I would have the louvred vent mounted inside the Box rather than have a hose leading to the Box. Now you can attach any size hose, from the box to the tank, you want.

Build a baffle and drain, and you're good to go.


This isn't structural, so polyester should work fine.

This way, hull thickness isn't a consideration. Either silicone the vents to the hull, or through bolt, depending on the design.

Ps, make one side of your box removable with screws for cleaning, and wasp nest removal.

Cheers.
Paul.
GRIT is offline   Reply With Quote
Old 31-12-2020, 10:03   #15
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,509
Re: Vents through the deck, topsides and hull. What would you use?

I have a hidden fuel vent for my diesel tank. An idea I saw on (I think) a Hinckley.

It is a 1/4 inch stainless diameter standpipe that goes up a few inches inside a vertical stern rail tube and three tiny holes drilled near the base of that stern rail far below the inside standpipe. That makes the vent invisible and water proof. I've had it this way for about 20 years with zero problems.

I don't know about tank odors needing venting. The purpose of the vent is to prevent a partial vacuum or pressurization of the tank when drawing fuel and allowing air pressure to equalize as the fuel expands or contracts by ambient temperature or from the warming from the excess fuel return from the injection pump.
stormalong is offline   Reply With Quote
Reply

Tags
deck, hull


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Two Deck Vents Tartan57 General Classifieds (no boats) 3 18-02-2018 18:35
Measure speed through water without making hole through hull. Lars_L Construction, Maintenance & Refit 29 26-03-2015 11:58
Orana 44: Orana hull window seals are "leaking" black on the topsides Sail IC Fountaine Pajot 6 28-01-2015 10:11
Mahe 36: Topsides, Deck, Cap vayacondios Fountaine Pajot 0 03-07-2011 20:02
Cowl Vents or Solar Vents Wanted clausont Classifieds Archive 2 23-10-2008 10:46

Advertise Here


All times are GMT -7. The time now is 16:49.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.