Re: Using old Volvo Engine loom 14 pairs for 230V possible

@Statistical #30
From ISO 13297-2020:
Quote:
11.5 A separate DC equipotential conductor shall be connected from the metallic case or chassis of the inverter or inverter/charger to the main grounding/earthing point or its bus, and be of an amperage rating equal to the DC positive conductor. This conductor shall not be connected to the DC negative at the inverter or inverter/charger.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 30-05-2023, 08:50   #32
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: Using old Volvo Engine loom 14 pairs for 230V possible

Quote:
Originally Posted by CharlieJ View Post
@Statistical #30
From ISO 13297-2020:
I meant specifically involving two or more conductors.

"be of an amperage rating equal to the DC positive conductor."

The wording implies there will be both only a single ground conductor and the DC positive connection will be made with only a single conductor. What if there isn't a DC positive conductor but DC positive conductors? What if there is no sufficiently large single grounding conductor available. Now someone can say well it doesn't explicitly prohibit multiple conductors but it also does specifically use the singular. That leave is vague and open eneded which is problematic.

Personally I would probably just use two conductors of sufficient combined ampacity but I am not sure the regs specifically allow that.

In an ideal world it would be clearly stated like as an example:
Quote:
A separate DC equipotential conductor(s) shall be connected from the metallic case or chassis of the inverter or inverter/charger to the main grounding/earthing point or its bus, and be of an amperage rating equal to the DC positive conductor(s). This conductor shall not be connected to the DC negative at the inverter or inverter/charger. If the DC positive connection is made using two or more conductors the ampacity of the grounding conductor must equal the combined ampacity. If necessary two or more grounding conductors of at least 50mm2 can be used in parallel to satisfy this requirement.
Statistical is offline   Reply With Quote
Old 30-05-2023, 09:02   #33
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Using old Volvo Engine loom 14 pairs for 230V possible

@Statistical #32
Not bad.

Horse officially dead.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
engine, volvo


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How Many Pairs of Shoes do you Carry Aboard? Target9000 Families, Kids and Pets Afloat 144 02-03-2014 10:41
Wiring Loom for Jeanneau 43 DS Alenka Construction, Maintenance & Refit 2 02-01-2014 01:33
Tips and Tricks for Sailing in Pairs sneuman Seamanship & Boat Handling 20 14-01-2012 17:44
Can I separate two pairs of batteries? Stevebellevue Electrical: Batteries, Generators & Solar 4 03-04-2011 07:24

Advertise Here


All times are GMT -7. The time now is 20:37.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.