Old 22-10-2019, 01:57   #61
Registered User

Join Date: Aug 2017
Posts: 304
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Mystic38 View Post
Sorry..but there is no 80% rule at all.

If there was an 80% rule then a 50A cable and connector would be rated at 40A.

perhaps "Rule of thumb" is the phrase you are looking for... an approximate guess based upon some random set of subjective bias.. which as you see is a ridiculous concept..

with a well fitting, clean set of connectors there is zero need for any rule of thumb regarding utilization ratio.. a 50A cable/connector set can be run at 50A continuous.. and if it could not..it would not be a 50A cable/connector set

Conversely, to support the OP first post... with a badly fitting corroded set of connectors even a 10% rule of thumb would be dangerous.

The bottom line here should not be a discussion of whether a cable should be derated based upon a knee jerk subjective number with no validation based upon actual data, or whether the shore power should be wired direct to the boat or not, but that ALL shore power connectors and cables should be inspected and serviced regularly.



Then just call it life experience. Doesn't matter if it's "a rule". It's safe. And it works.
Dirk01 is offline   Reply With Quote
Old 22-10-2019, 07:46   #62
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Mystic38 View Post
Sorry..but there is no 80% rule at all.

There is history here.



Story (you can skip this): When I was in college we had an assignment to design a bolt pattern and select bolts for a blanking plate at the end of offload pipes on an oil tanker. We all got pretty much the same answer but it didn't make sense. My school was big on practical experience so we had a pretty good idea of what the numbers should be. As a group we went to the professor who was very pleased with himself. We all trooped off to the classroom and he walked through the method. He came up with the same number of bolt holes that we did. Then he challenged us. Did any of us look at what actual happened when we went to sea? The deck crew would put every other bolt in and there might be a stripped thread or a dropped nut so one would be missing. Working backwards on that basis and with a reasonable safety factor we got the bolt sizes we expected. The moral is users don't use stuff right.



There is also history, especially in electrical systems, on duty cycle. For example you'll often see cigarette lighter power points fused for 30A. This is a real pet peeve of mine. Sure they can carry 30A for a minute for a cigarette lighter. The continuous duty rating for the connector is only 6A! I've seen three triplex adapters ganged and seven devices plugged in to charge. Open up the panel and see the charred wire insulation. Not good.


There are a lot of intermittent loads on boats. Aircon start-up is a big one. Charging flat batteries at the beginning of bulk is a big one. A boat plugging in with Aircon and battery charger and water heater all flipped on is huge. So the engineers size for the big load (30 or 50A in the US, 16 or 32A in the EU) for a while and continuous load is smaller. Here is what I would do: size for the maximum intermittent load, check the continuous load and make a subjective assessment of whether the margin is big enough. 20% isn't big from the design perspective but probably big enough for the market. You have to look at boundary conditions. In this case it is the specs on the shore power circuit breaker.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 22-10-2019, 12:14   #63
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Shore Power Connections -- Again

Good post Auspicious.
One of the most contentious issues I dealt with on New Build Superyacht projects, were my contractual requirements for a detailed "load analysis"

Primarily for deciding on balanced Generator Sizing

The electrical contractors were comfortable performing one, but the Builders resisted, claiming every boat is different in how they use power.

I never bought that line and insisted....., ....design for the worst case scenario and provide adequate non-preferential switching to keep things safe in a shore power scenario.

Same applies to our smaller yachts, that are having more and more AC PowerPoint's .... The original AC distribution board is too small and you often need to add a 2nd sub panel for smaller more appropriately sized breakers.

On the Super yachts with unlimited budgets, the only way to insure proper compliance was to specify UMS Certification, (Unmanned Machinery Space) as part of the required documentation..... Smaller boats should study those requirements
Pelagic is offline   Reply With Quote
Old 22-10-2019, 12:49   #64
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Pelagic View Post
The electrical contractors were comfortable performing one, but the Builders resisted, claiming every boat is different in how they use power.
I agree with you. Boats the size you're talking about generally have multiple identical generators with frequency synchronization. This is great for sparing and for operational efficiency.

Owners keep adding stuff and it all plugs in. You have to size for growth and multiple generators helps, especially if you leave space to drop in one more some day.

In my view personal electronics have helped, especially if you put USB charging ports on the 12VDC bus instead of the 117VAC/240VAC bus. Opinion on my part.

Got to get the galley loads right. Boat systems other than thrusters (often mechanical/hydraulic on superyachts) are less.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 22-10-2019, 14:58   #65
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Shore Power Connections -- Again

Quote:
Originally Posted by sailcrazy View Post
followingI've never heard of "hard-wiring" the shore power cord in, and just pulling it out of the locker when you need it....eliminating the shore power plugin and receptacle all together. An interesting idea!

Very common on large power yachts and sport fishing boats but usually on a retractable reel. Glendinning makes a great shore power reel but you need some space for it. If hard-wiring just be sure the connections are in a j-box and you have plenty of strain relief. Not as uncommon as one would think but usually not found on production boats...
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-10-2019, 16:42   #66
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Maine Sail View Post
Very common on large power yachts and sport fishing boats but usually on a retractable reel. Glendinning makes a great shore power reel but you need some space for it. If hard-wiring just be sure the connections are in a j-box and you have plenty of strain relief. Not as uncommon as one would think but usually not found on production boats...
Hi Maine Sail
One question on those shore Power Cable Reels.

American Engineer I worked with for many years on Super yachts, insisted that the large cable be unwound completely and flaked on the dock as opposed to leaving unused portion on the Reel.

Claimed that leaving this wound would create a magnetic coil.

Never argued, but always wondered if this was true?

Seems there would be a warning in the documentation, which I never saw.
Pelagic is offline   Reply With Quote
Old 22-10-2019, 18:05   #67
Registered User

Join Date: Mar 2016
Location: New England. USA.
Boat: McCurdy & Rhodes Custom 46
Posts: 1,475
Shore Power Connections -- Again

I’m certainly not Maine sail but the coil would likely not be an issue assuming no unbalanced current, which would trip your RCD. The magnetic fields from the neutral and hot conductors will pretty much cancel each other out.
There is a valid argument that the tight coil of wire on the reel will run hotter than the loose wire on deck or dock. And that matters.
Coiled extension cords under a high continuous load ( space heater!) are a hazard. Don’t do that.
dfelsent is offline   Reply With Quote
Old 23-10-2019, 02:18   #68
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,448
Images: 241
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Pelagic View Post
... American Engineer I worked with for many years on Super yachts, insisted that the large cable be unwound completely and flaked on the dock as opposed to leaving unused portion on the Reel ...
Cable is not stored on a reel, but in a bin beneath it.
Glendinning operating instructions do NOT require fully extending the cable out of the storage bin.
Ie:
Extend the power cord: Pull out sufficient cord length that will allow you to route shore power cord to the electrical distribution box and plug the molded end into the receptacle.
However:
Experience has shown that when only a short section of power cable is regularly used, the cable may be subject to “kinking”. To relieve this condition, routinely extend the power cable completely and stretch it on any smooth surface. Allow the Cablemaster to retract the cable onto the reel.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 23-10-2019, 05:24   #69
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Shore Power Connections -- Again

Hi Gord,
On the ones we had onboard, the shore cable was definitely stored on a large reel about 5-6 ft in diameter.
Ships demands were 3 phase 380v 350amps, so a substantial cable about 50m long was on that reel that powered in and out via a roller system thru hull openings (either side)

I remember that power fed out via the Axel of that reel to the step up/down isolation transformer, then to the Frequency Controller.

All huge equipment in the 90's
Pelagic is offline   Reply With Quote
Old 23-10-2019, 06:54   #70
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Pelagic View Post
American Engineer I worked with for many years on Super yachts, insisted that the large cable be unwound completely and flaked on the dock as opposed to leaving unused portion on the Reel.

Claimed that leaving this wound would create a magnetic coil.
Quote:
Originally Posted by dfelsent View Post
I’m certainly not Maine sail but the coil would likely not be an issue assuming no unbalanced current, which would trip your RCD.
There will definitely be a magnetic field. It won't be sufficient given the balanced current to have any effect.

Quote:
Originally Posted by GordMay View Post
Cable is not stored on a reel, but in a bin beneath it.
Glendinning operating instructions do NOT require fully extending the cable out of the storage bin.
Some reels store the cord on the reel and use slip rings. I'm not a fan of that sort but they are out there.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 23-10-2019, 07:40   #71
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,448
Images: 241
Re: Shore Power Connections -- Again

My apologies, for my mistake. The Glendinning “CR” series are reel style, not bin storage.
https://www.glendinningprods.com/pro...master-marine/
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 23-10-2019, 08:11   #72
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Shore Power Connections -- Again

Quote:
Originally Posted by GordMay View Post
My apologies, for my mistake. The Glendinning “CR” series are reel style, not bin storage.

Correct. The CM series run from a bin, the CR series store on the reel. Bin storage takes a bit more room and alignment during installation is important to avoid the shore power cord equivalent of castling. The reel storage approach is easier to install but slip rings lead to the same sort of heat, corrosion, and resistance issues as a connector. In addition they are electrically noisy during operation. I'm not a fan.


I should point out that I'm not a fan of slip rings. Reel storage is fine. I've seen reels with pig tails--no slip rings--that are fine and pretty convenient. Big. Probably beyond the CF constituency.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 25-10-2019, 07:11   #73
Marine Service Provider

Join Date: Feb 2012
Location: Vienna, Austria
Boat: Vagabond 47
Posts: 928
Re: Shore Power Connections -- Again

not only check them. One has to renew them every year by cutting the wire shorter.
moseriw is offline   Reply With Quote
Old 25-10-2019, 07:30   #74
Registered User

Join Date: Sep 2012
Posts: 38
Re: Shore Power Connections -- Again

A ground fault interrupter is not an over current device and must be paired with on on s circuit - ground fault breakers have both functions, ground fault receptacles do not.

A ground fault protector will usually trip when bad connections cause arcing

Current National Electrical Code (NEC) requires all shore power feeds to be ground fault protected - many old marinas are not.

The NEC mandates that over current protection and wiring systems be sized for 125% of the connected load. However receptacle loads are not subject to that and several 15 amp receptacles (the most common one in the US) can be connected to a single 15 amp circuit. While it is probably a good idea to limit loads to 80%, there is no requirement to do so and your wife's 1500 Watt hair drier draws about 13 amps (86%).

A circuit breaker will trip if subjected to rated amp loads over a long period of time, especially if its a thermal (vs magnetic) type breaker.

Finally, according to UL-489 the maximum temperature on electrical panels, switches, etc is 50 deg C (about 140 deg F) and the NEC defines the maximum temperature for wiring systems as 50 deg C above ambient. Both of those are pretty warm
Bbolino is offline   Reply With Quote
Old 25-10-2019, 07:49   #75
Registered User

Join Date: Aug 2011
Location: New York, New York
Boat: Dufour Safari 27'
Posts: 1,911
Re: Shore Power Connections -- Again

Quote:
Originally Posted by Bbolino View Post
Current National Electrical Code (NEC) requires all shore power feeds to be ground fault protected - many old marinas are not.

While it is probably a good idea to limit loads to 80%, there is no requirement to do so and your wife's 1500 Watt hair drier draws about 13 amps (86%).
It is scary how bad some of the marina pedestals are. Thankfully I don't have to use shore power very often.

While her hair dryer draws 86%, I am guessing (hoping?) she doesn't need it more than three hours!!
ArmyDaveNY is offline   Reply With Quote
Reply

Tags
grass, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
Portable Honda Gen to Shore Power- Can this power hot water electrics? simonpickard Electrical: Batteries, Generators & Solar 25 03-06-2019 07:30
Power Panel - Shore power light dmksails Electrical: Batteries, Generators & Solar 5 10-08-2017 10:02
Improving on Shore Power Connections Pelagic Electrical: Batteries, Generators & Solar 28 18-02-2015 11:03
Leopard 38: Shore Power Connections hikersailor Leopard Catamarans, Robertson & Caine 0 16-08-2014 16:48

Advertise Here


All times are GMT -7. The time now is 19:50.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.