Re: Have 240 vac shore power, but only 120 vac used

Wow, all this input is wonderful. Thanks.

I'm back on the boat Monday and I'll confirm exactly how I'm wired. It's been a while since I focused on this, because it ain't broke, but I know it's flawed. It was an article about a boat fire started by a shore power inlet corrosion problem that woke me up and made me start asking these questions (I know that issue is mostly a maintenance issue - but if I split the load on my 240v legs I'd have less chance of heat).

An isolation transformer is a whole new education for me. Been reading all morning so far. It might be overkill for my needs, but giving it careful thought. In the few cases when I can't get the right/enough shore power the genset and a mooring is a fine alternative. My only issue with my genset is that it's not well insulated and it's in the center of the boat so it puts heat into the cabin. Running it so I can run aircon is almost counter productive, especially once I'm cool and I can turn it all off, but then the genset just bleeds out it's heat for hours.

A lot to think about. Thanks again for all the input. More from me with the facts when I can confirm them.
jr_spyder is offline   Reply With Quote
Old 22-10-2016, 07:02   #17
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Have 240 vac shore power, but only 120 vac used

Great tool for the price... Not a Fluke, but damn close... I have 2...
Clamp to your heart's content...

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 22-10-2016, 17:12   #18
Registered User

Join Date: Sep 2013
Location: San Francisco Bay
Boat: Chung Hwa Boat Builders, Magellan 36
Posts: 447
Re: Have 240 vac shore power, but only 120 vac used

It might be a good idea to follow the wires. By that I mean look at the incoming (power off if you don't like living dangerously) wiring. If it is in fact 240v 4 wire then usually in the US it is white (neutral), green (ground), black (120V), red (120V). Between red and black =240. Between either red or black and neutral is 120. A house panel may use either "hot " leg to power a 120V circuit. In your boat you have to determine if both hot legs are utilized. Follow the wires. If they are not both used then there should be a wire that goes nowhere behind your incoming power plug. Good luck
foufou is offline   Reply With Quote
Old 23-10-2016, 15:07   #19
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 362
Re: Have 240 vac shore power, but only 120 vac used

Could be a PO found most marinas had 50 amp services. So they made a modified shore cable but only wired 1 leg with 120 volt. If that is so, you would be well served to have a new panel using both legs.
Zil is offline   Reply With Quote
Old 24-10-2016, 12:21   #20
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Have 240 vac shore power, but only 120 vac used

I agree with Zil. I think the previous owner changed something. Probably because their dock only had 110v. It might be as simple as switching a wire back. Look for a stacked connection and an empty post over by those big fuses or behind your panel.
Thumbs Up is offline   Reply With Quote
Old 24-10-2016, 16:26   #21
Registered User
 
jr_spyder's Avatar

Join Date: Aug 2011
Location: Boston area
Boat: Little Harbor 46 (1988)
Posts: 327
Re: Have 240 vac shore power, but only 120 vac used

Hi all,

I got on the boat today and dove into the facts.

The 50 amp inlet only has three wires coming out of the back and into the boat. Black, white and green; so 1 hot leg, neutral and ground. There is a forth lug for another hot leg wire but nothing is connected to it. All the wires are 6 awg.

The AC breaker in my main panel is only wired for 120v. Also the safety switch that selects power from either shore or genset is wired for 120v. Its quite clear this panel has never seen 240v.

I agree with the notion that a previous owner changed the inlet to a standard 50 amp setup for ease of plugging in at marinas, but kept the rest of the boat at 120v.

I understand the idea but have no plans to change the system to a properly wired and balanced 240v. I've never had a single problem with any of this so don't see the need for what would be a very extensive change. Also, I've been reducing power usage on board, not increasing it, which is a better overall course and investment I think.

I'll add the correct ELCI breaker at the inlet and a galvanic isolator and sleep better for having these safety features that I don't have now.

Thanks again for all the help here. I've learned a few things and now have a good plan.

JR
jr_spyder is offline   Reply With Quote
Old 24-10-2016, 16:29   #22
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Have 240 vac shore power, but only 120 vac used

Quote:
Originally Posted by jr_spyder View Post
Hi all,

I got on the boat today and dove into the facts.

The 50 amp inlet only has three wires coming out of the back and into the boat. Black, white and green; so 1 hot leg, neutral and ground. There is a forth lug for another hot leg wire but nothing is connected to it. All the wires are 6 awg.

The AC breaker in my main panel is only wired for 120v. Also the safety switch that selects power from either shore or genset is wired for 120v. Its quite clear this panel has never seen 240v.

I agree with the notion that a previous owner changed the inlet to a standard 50 amp setup for ease of plugging in at marinas, but kept the rest of the boat at 120v.

I understand the idea but have no plans to change the system to a properly wired and balanced 240v. I've never had a single problem with any of this so don't see the need for what would be a very extensive change. Also, I've been reducing power usage on board, not increasing it, which is a better overall course and investment I think.

I'll add the correct ELCI breaker at the inlet and a galvanic isolator and sleep better for having these safety features that I don't have now.

Thanks again for all the help here. I've learned a few things and now have a good plan.

JR
Sounds like a good plan!
DotDun is offline   Reply With Quote
Old 25-10-2016, 04:08   #23
Registered User

Join Date: Sep 2015
Location: Toledo, OH
Boat: 1939 Richardson Cruisabout 33
Posts: 50
Re: Have 240 vac shore power, but only 120 vac used

In typical homes, there are two legs coming into a breaker box. Most circuits are 120V, but a few high-load circuits are double-width breakers that combine the two legs to power items such as Air conditioning, heat, hot water, electric range, dryer, etc.
On your boat, it is apparent that there are no devices that demand a 240V input.
So what you will probably want to do is have all of your Air Conditioning on one leg, and Battery Charger, and all other necessities on another. This way the load is not all on one hot wire in your shore power cord. If you only have a 30 amp outlet to plug into, you may have to continue to regulate when you turn on air conditioning or your charger.
As all others say, of course consult a professional. There are always some things that should be verified, like polarity, bonding, etc... And you need somebody good at using a meter and troubleshooting and who knows what to look for.
Kentb is offline   Reply With Quote
Old 25-10-2016, 04:55   #24
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,463
Re: Have 240 vac shore power, but only 120 vac used

Quote:
Originally Posted by jr_spyder View Post
Hi all,

I got on the boat today and dove into the facts.

The 50 amp inlet only has three wires coming out of the back and into the boat. Black, white and green; so 1 hot leg, neutral and ground. There is a forth lug for another hot leg wire but nothing is connected to it. All the wires are 6 awg.

The AC breaker in my main panel is only wired for 120v. Also the safety switch that selects power from either shore or genset is wired for 120v. Its quite clear this panel has never seen 240v.

I agree with the notion that a previous owner changed the inlet to a standard 50 amp setup for ease of plugging in at marinas, but kept the rest of the boat at 120v.

Good feedback; always useful to close the info loop on issues like this...

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 26-10-2016, 03:49   #25
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Have 240 vac shore power, but only 120 vac used

Quote:
Originally Posted by jr_spyder View Post
Hi all,

I got on the boat today and dove into the facts.

The 50 amp inlet only has three wires coming out of the back and into the boat. Black, white and green; so 1 hot leg, neutral and ground. There is a forth lug for another hot leg wire but nothing is connected to it. All the wires are 6 awg.
Quote:
Originally Posted by HappyMdRSailor View Post
Jr-

Sounds like you have an empty terminal on the backside of your 250V/50A inlet...


And if you have 6 AWG all the way to your main panel, you're probably good... Still suggest you get a clamp on ammeter... The info gleaned can be invaluable...
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
120 & 220V Shore Power Bill Balme Electrical: Batteries, Generators & Solar 6 07-01-2013 16:53
Newby requesting advice about 120/ 240 volt wiring Menby Electrical: Batteries, Generators & Solar 15 01-07-2012 10:44
For Sale: Refrigeration Components 120 VAC Achernome Classifieds Archive 0 30-05-2012 05:23
For Sale: Victron 7 KW 230/240 vAC Isolation Transformer - $500 rkupsaw Classifieds Archive 0 23-03-2011 10:06
120 VAC GFCI Outlet velero Electrical: Batteries, Generators & Solar 1 11-01-2010 12:39

Advertise Here


All times are GMT -7. The time now is 15:15.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.