Cruisair Puzzler Problem

I've been working on 2 cruisair units which have various problems.

12000 btu unit-fair water flow, R-22 low side 75 and high side 325, and good air flow but only puts out 70 degree supply air with an 80 deg return. Rotary compressor runs hot. Flushed seawater system and Acid washed condensor heat exchanger but still no change.

16000 btu unit-Great water flow, good air flow, R-22 low side 75, high side 275 deg, 50 deg supply air with 75 deg return. Compressor runs hot and goes off on over temp after about 10 minutes of running, Acid washed condenser heat exchanger but still no change.

I'm looking for ideas on anything I might have missed. I don't know the history of these units but they're on a 1996 President MY. As a last resort I'm going to recover the refrigerant tomorrow, evacuate, and weigh in a new charge.
thanks in advance for your help...
Bill in JB
Quadrille in JB is offline   Reply With Quote
Old 10-08-2022, 11:48   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Cruisair Puzzler Problem

What are the vapor line and liquid line temperatures when you measure those pressures?
Sailmonkey is offline   Reply With Quote
Old 10-08-2022, 12:39   #3
Registered User

Join Date: Jun 2016
Location: Jensen Beach, Fl
Boat: O'Day 34
Posts: 392
Re: Cruisair Puzzler Problem

Quote:
Originally Posted by Sailmonkey View Post
What are the vapor line and liquid line temperatures when you measure those pressures?
I didn’t check the temperatures on the unit that is cooling well but goes off on over temp But the unit that is not cooling well Had a suction line temperature of 84° F.
Think was so far off that I didn’t continue to check superheat on this cap tube system.
Thanks for your reply
Quadrille in JB is offline   Reply With Quote
Old 10-08-2022, 13:50   #4
Registered User

Join Date: Jun 2016
Location: Jensen Beach, Fl
Boat: O'Day 34
Posts: 392
Re: Cruisair Puzzler Problem

I suspect with the correct suction pressure and high discharge pressure and 84 deg. suction temp that the system is contaminated with non-condensables.
Any thoughts on this?
thanks,
Bill in JB
Quadrille in JB is offline   Reply With Quote
Old 10-08-2022, 14:45   #5
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Cruisair Puzzler Problem

Both units sound like the charge is questionable, the water hot, and possibly the cap tubes slightly clogged.

Are these split systems?
Sailmonkey is offline   Reply With Quote
Old 10-08-2022, 14:54   #6
Registered User

Join Date: Jun 2016
Location: Jensen Beach, Fl
Boat: O'Day 34
Posts: 392
Re: Cruisair Puzzler Problem

No they are not split systems
I agree on the possibility of contaminated refrigerant
Quadrille in JB is offline   Reply With Quote
Old 10-08-2022, 15:04   #7
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Cruisair Puzzler Problem

I personally would check the charge with high and low side temperatures.

I use an iOS app called checkcharge to forgo the pressure temperature charts. I also enter the water temp as the condenser dry bulb temp and use a digital wet bulb thermometer inside to figure out how out of wack things really are. The high pressure isn’t too far out of the ballpark if the water is really hot as well.
Sailmonkey is offline   Reply With Quote
Old 10-08-2022, 16:19   #8
Registered User

Join Date: Jun 2016
Location: Jensen Beach, Fl
Boat: O'Day 34
Posts: 392
Re: Cruisair Puzzler Problem

Quote:
Originally Posted by Sailmonkey View Post
I personally would check the charge with high and low side temperatures.

I use an iOS app called checkcharge to forgo the pressure temperature charts. I also enter the water temp as the condenser dry bulb temp and use a digital wet bulb thermometer inside to figure out how out of wack things really are. The high pressure isn’t too far out of the ballpark if the water is really hot as well.
I’ll try it
Thanks
Quadrille in JB is offline   Reply With Quote
Reply

Tags
cruisair


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Yanmar SD20 Saildrive Puzzler...I'm stumped Zoid Engines and Propulsion Systems 15 02-05-2016 05:34
Fuel pipe puzzler Joben Construction, Maintenance & Refit 4 24-02-2015 11:02
Puzzler: Beta Marine 16 Fail to ignite swiftwaters Engines and Propulsion Systems 14 28-04-2014 09:11
Bulkhead Hole Waterproofing Puzzler windsaloft Construction, Maintenance & Refit 14 22-09-2009 21:07

Advertise Here


All times are GMT -7. The time now is 22:34.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.