Calculating House Bank DC Fuse size.

Have not been able to find any guidance on sizing the Main Fuse for my new 24 volt house bank

So I took the conservative approach of assuming every DC consumer was turned on at the same time and both invertors were putting out maximum DC to AC conversion.

This is how I plan on wiring the 8 new 12 volt 260AH AM’s for 24Volt service with Main Fuse then new Master switch going to main Distribution Studs.

From the calculations of consumers below should the ratings of equipment be sized as such?
  • Distribution stud 400A
  • Battery Switch 400A
  • Fuse Rating 350A
  • Wiring sized for 400A
Is this how you do it?..... Thanks!

Consumer ..................................DC 24v Amps
Inverter 1800 Watt ............................... 75.00
Inverter 3000 Watt ...............................125.00
Auto pilot ................................................12 .00
4 x Isotherm Fridges ...............................12.00
Nav Lights .................................................6 .00
Nav Electronics .........................................2.00
E.R. Lights .................................................. 5.00
Lights/Fans ................................................8. 00
Bow Thruster ...........................................50.00
Anchor Windlass .....................................45.00
Other............................................. ....5.00
Total DC 24V Amps............................345


Attached Thumbnails
Click image for larger version

Name:	Draft 1 Scaled New Batt layout.jpg
Views:	387
Size:	44.8 KB
ID:	4458  
Pelagic is offline   Reply With Quote
Old 28-07-2008, 02:05   #2
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,444
Working on the principle of the fuse protecting the wiring you rating sounds reasonable, you have rated the main fuse to be higher than the max. load and less than the wiring / hardware rating.
As soon as the downstream wiring and / or bus is rated lower than 350 amps, additional protection is required "downstream".
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Reply

Tags
fuses


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Charging for 780AH @ 24V House Bank Pelagic Electrical: Batteries, Generators & Solar 24 05-11-2014 08:46
36vdc Motor Bank and 12vdc House Bank bobola Electrical: Batteries, Generators & Solar 24 22-12-2009 20:30
House battery bank size bottleinamessage Electrical: Batteries, Generators & Solar 16 05-04-2007 20:00
Calculating Block Load Charlie Construction, Maintenance & Refit 12 27-03-2007 13:57
Fuse Protection Ted Beyer Electrical: Batteries, Generators & Solar 5 17-05-2005 10:07

Advertise Here


All times are GMT -7. The time now is 14:28.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.