Is there any reason to go with a breaker less than 15A on a DC panel branch cct assuming all wires are 18AWG or larger?

I'm currently debating if I want to have all 15A and 30A or also include some 5A and 10A for ccts with low loads (eg propane solanoid)
geoffr is offline   Reply With Quote
Old 24-04-2017, 18:28   #2
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Breaker sizing (Amps) in breaker panel

I believe you cannot have branch breakers in total more than 150% of the main breaker
All wire not in specifically excepted cases can be smaller than 16 awg
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 24-04-2017, 19:14   #3
Registered User

Join Date: Nov 2008
Location: Ottawa,Canada
Boat: Prout Snowgoose 37' Catamaran
Posts: 570
Re: Breaker sizing (Amps) in breaker panel

Scott - good point on the 150%. That may push me to the lower Amp breakers...need to check my math.
geoffr is offline   Reply With Quote
Old 24-04-2017, 19:45   #4
Registered User
 
deblen's Avatar

Join Date: Oct 2014
Location: Bay of Fundy,Grand Manan,N.B.,Canada N44.40 W66.50
Boat: Mascot 28 pilothouse motorsailer 28ft
Posts: 3,265
Images: 1
Re: Breaker sizing (Amps) in breaker panel

This chart may help you. / Len

https://www.bluesea.com/resources/1437
__________________
My personal experience & humble opinions-feel free to ignore both
.
deblen is online now   Reply With Quote
Old 24-04-2017, 20:27   #5
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Breaker sizing (Amps) in breaker panel

Keep in mind that sometimes the leads that come attached to an appliance (anything that uses electricity not just a refrigerator) can be quite small. Hella cabin fans are one of the most obvious examples. I have several 5 amp breakers for this situation although the feeding boat cable maybe say #14.
Frankly is offline   Reply With Quote
Old 25-04-2017, 08:18   #6
Registered User

Join Date: Nov 2011
Location: Georgian Bay
Boat: Ericson 35-2
Posts: 162
Re: Breaker sizing (Amps) in breaker panel

and the leads on most inline glass fuse holders are thin 16 gauge. What are they thinking..?
sailortype is offline   Reply With Quote
Old 25-04-2017, 08:25   #7
Registered User

Join Date: Jan 2017
Location: Sea of Cortez
Boat: Kelley-Peterson 46 cutter
Posts: 890
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by geoffr View Post
Is there any reason to go with a breaker less than 15A on a DC panel branch cct assuming all wires are 18AWG or larger?

I'm currently debating if I want to have all 15A and 30A or also include some 5A and 10A for ccts with low loads (eg propane solanoid)
Breakers protect the wire. Breakers do not regulate or limit current, as such. Breakers will protect your wire from being over-current and causing a fire.

A 12 ga wire is safe for 20 amps and should have a 20 amp or smaller breaker.

14 ga wire is safe with 15 amps.

16 ga wire probably needs a 10 amp breaker. I don't have the chart.

18 ga should probably be a 5 amp breaker.

This is what breakers are designed to do; prevent electrical fires. If you have 14 amps going through an 18 ga wire, the wire may get so hot it melts its insulation and/or ignites any flammable material the hot wire is near; wood, books, hull resins, other plastics.

Either re-size your wires to 14 ga (or larger) for the 15 amp breakers; or re-size your breakers to protect your smaller wires.
A short in an 18 gauge wire will quickly burn or melt the wire. A 5 amp breaker will trip before the wire can heat up enough to burn.

I hope this helps.
KP44 is offline   Reply With Quote
Old 25-04-2017, 08:38   #8
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by Frankly View Post
Keep in mind that sometimes the leads that come attached to an appliance (anything that uses electricity not just a refrigerator) can be quite small. Hella cabin fans are one of the most obvious examples. I have several 5 amp breakers for this situation although the feeding boat cable maybe say #14.
That's an excellent comment. You don't want the smallest wire to be the fuse.
Cadence is offline   Reply With Quote
Old 25-04-2017, 08:48   #9
Registered User

Join Date: Dec 2016
Location: PNW
Boat: J/42
Posts: 938
Re: Breaker sizing (Amps) in breaker panel

Um... maybe obvious but some equipment requires 5 amp protection or less. E.g. Seatalk instruments. Although one could use a branch circuit with in-line fuse in those cases, I kind of have an aversion to hidden fuses scattered around the system.
toddster8 is offline   Reply With Quote
Old 25-04-2017, 08:58   #10
Marine Service Provider

Join Date: Sep 2011
Location: California
Boat: Alerion Express 38 Yawl (former)
Posts: 468
Re: Breaker sizing (Amps) in breaker panel

Blue Sea Systems has a really good app on selecting wire sizes and circuit protection. It's based on ABYC standards, and while it's uber-comprehensive, you can be confident in the answers. It's call the Circuit Wizard.

I think that some of the previous information offered in this forum may have been extra conservative and not actually based on the standards. Unfortunately, there are many variables including the quality of the wire you're using, whether you're measuring the gauge in SAE or AWG, whether the wire is in the engine room, and so forth. That's a pretty good reason for using the Circuit Wizard.

And remember that you're dealing with both the ampacity of the wire (it's ability to get rid of heat due to current flow) and the voltage drop (which is generally what gets you on a 12V boat circuit).

Here's one example:

Voltage: 12V
Max current: 45A
Length of conductor: 10'
Allowed voltage drop: 10%
Insulation temp rating: 105 deg C
Not in engine room.
2-3 wires in the bundle
Duration: 30 minutes

Answer: 8 AWG

14 gauge would work from a voltage drop standpoint, but 8 gauge was needed due to ampacity.

I don't know that I would take the time to calculate every circuit on the boat, but I find it very handy to at least verify that you're doing the right thing.

Chuck Hawley
Chuck Hawley is offline   Reply With Quote
Old 25-04-2017, 09:03   #11
Registered User

Join Date: Jan 2017
Location: Sea of Cortez
Boat: Kelley-Peterson 46 cutter
Posts: 890
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by geoffr View Post
Is there any reason to go with a breaker less than 15A on a DC panel branch cct assuming all wires are 18AWG or larger?

I'm currently debating if I want to have all 15A and 30A or also include some 5A and 10A for ccts with low loads (eg propane solanoid)
I think there is confusion between conductor ratings and overcurrent protection. You need to be concerned about overcurrent protection.


Small Conductors, the overcurrent protection shall not exceed ...
18 AWG Copper. 7 amperes, provided all the following conditions are met:
(1) Continuous loads do not exceed 5.6 amperes.
(2) Overcurrent protection is provided by Branch-circuit-rated circuit breakers listed and marked for use with 18 AWG copper wire.

16 AWG Copper. 10 amperes, provided all the following conditions are met:
(1) Continuous loads do not exceed 8 amperes.
(2) Overcurrent protection is provided by Branch-circuit-rated circuit breakers listed and marked for use with 16 AWG copper wire.

14 AWG Copper. 15 amperes

12 AWG Copper. 20 amperes

10 AWG Copper. 30 amperes

So the 18 ga wire may have up to a 7 amp breaker.
KP44 is offline   Reply With Quote
Old 25-04-2017, 10:01   #12
Registered User

Join Date: Nov 2008
Location: Ottawa,Canada
Boat: Prout Snowgoose 37' Catamaran
Posts: 570
Re: Breaker sizing (Amps) in breaker panel

It seems we are looking at different data... for a single 18AWG wire with 105C insulation I read the chart below as 20A. The wire is not in the engine compartment.

https://www.bluesea.com/support/refe...e_Sizing_Chart

Although it's true it's not free air...so perhaps the right side is safer - 3conductors - so 12A.

Having said that I think 5A breaker makes sense for other reasons. (150% as noted by Scott)
geoffr is offline   Reply With Quote
Old 25-04-2017, 10:10   #13
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: Breaker sizing (Amps) in breaker panel

Your insulation may be treasured at 105C but your termination may only be rated for 75C.
masonc is offline   Reply With Quote
Old 25-04-2017, 10:48   #14
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by masonc View Post
Your insulation may be treasured at 105C but your termination may only be rated for 75C.
I have found some as low as 65C, not an easy spec to find thou.

In very general terms you want the breaker sizes large enough to not nuisance trip under the load but smaller then the ampacity of the wire. On a personal level I like to use a smaller size to better match equipment ratings as an additional failsafe. The last panel I built for a family member was mostly 5 and 10 amp breakers for instance (lights etc).

Also you can use breakers for equipment protection, some things you still want fuses thou. When we do some of the military projects they require all circuit protection be via breaker on a central panel unless a special fuse is required by the equipment. There are a number of high end boat builders that do the same with things like 2.5 amp and 3 amp breakers for electronics.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 25-04-2017, 10:48   #15
Registered User
 
S/V Alchemy's Avatar

Join Date: May 2008
Location: Nova Scotia until Spring 2021
Boat: Custom 41' Steel Pilothouse Cutter
Posts: 4,976
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by sailortype View Post
and the leads on most inline glass fuse holders are thin 16 gauge. What are they thinking..?
They are thinking you will have 1 amp fuses. I have a 5 amp breaker to a number of low-draw electronics called "electronics". It feeds a four fuse sub-panel with 1 amp fuses. The wires from the breaker are 14 ga. and 16 ga. outbound.
__________________
Can't sail? Read about our travels at https://alchemyonpassage.blogspot.com/. Can't sleep? Read www.alchemy2009.blogspot.com for fast relief. Can't read? Avoid www.volumesofsalt.blogspot.com, because it's just personal reviews of sea books.
S/V Alchemy is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
kyocera Solar Panel Volts no Amps deepthought Electrical: Batteries, Generators & Solar 28 04-06-2019 07:08
Solar amps in, consumption amps out, check my math please? Jarel Design Electrical: Batteries, Generators & Solar 24 26-04-2017 16:13
Amps v Amp hours v Amps/Hr StuM Electrical: Batteries, Generators & Solar 255 25-01-2016 14:21
Solar Panel Max Amps zboss Marine Electronics 17 16-08-2015 11:48
Sailboat Solar Panel Sizing silviris Electrical: Batteries, Generators & Solar 47 08-05-2013 15:51

Advertise Here


All times are GMT -7. The time now is 18:24.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.