Old 09-04-2022, 14:42   #31
TBo
Registered User

Join Date: Apr 2022
Posts: 1
Re: 3 flashes on Danfoss control

Hi all,
I’m bouncing that thread again as it seems a good repository on the subject.

I currently have the 3 flashes code on my danfoss BD50F compressor (part of a 24V watercooled frigoboat fridge /freezer from 2009 with a 101N0210 controller, installed by the boatyard).

I’ve read the previous entries and they are very educational but my situation seems a bit different:

From a base case where the fridge has been off for days, when I start it, it runs, cools down and stops when it reaches the desired temp. It then slowly warms up and when the thermostat triggers, the compressor starts for 2s, stops and displays 3 flashes. The same restart/fail/flash cycle repeats every 30s or so.

But, if i switch off the power and wait long enough (a few hours), then the [start, cool down, stop, warm up, {restart, run 2s, fail, wait 30s, repeat}] cycle works. I’ve been able to do that many times.

To me, and without further testing, that tells me the compressor is ok, the controller is ok, the electrical parts are ok.

The system refrigerant load has apparently never been changed (not during my 6year ownership, and probably never judging by the cover on the service valve).

What exactly could cause that failure to subsequently cool again after the initial cool down?

Thanks for your insights

Tom
TBo is offline   Reply With Quote
Old 09-04-2022, 15:32   #32
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: 3 flashes on Danfoss control

It happens all the time....
A unit running creating heat and load uses more amps...the amps either cause the failing controller to fail OR most likely result in a voltage drop that is knocking out the controller.

Do the Electrical tests this smart guy talks about in his electrical troubleshooting videos:



The electrical tests are the same for all danfoss compressors.

Cheers
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 10-04-2022, 02:22   #33
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,482
Images: 241
Re: 3 flashes on Danfoss control

Greetings and welcome aboard the CF, Tom.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 05-08-2023, 04:54   #34
Registered User

Join Date: Aug 2023
Posts: 1
Re: 3 flashes on Danfoss control

Good morning,

After many years, my refrigerator has stopped working.
I then replaced the danfoss 101n210 control unit with the 212 version, as the 210 is now out of production.
I also replaced the thermostat.

The fridge started correctly and ran for a whole day. At some point, however, it shut down and did not start again. I called a technician who charged the fridge and then checked that all the parts were OK and told me that the problem could only be the controller. I tried changing the controller and also a new thermostat, but nothing, the problem still exists.

What could it be? Why did it work for a day when the controller was replaced and then never started again?

In my case the controller also flashes three times.

Thank you for all the support
dav31195 is offline   Reply With Quote
Old 10-08-2023, 20:02   #35
Registered User

Join Date: Oct 2018
Posts: 52
Re: 3 flashes on Danfoss control

Had a compressor that would not start, & the winding resistance was not right on one of them. Cut the compressor apart & found the shorting link on the center of the star winding was a poor conection. On removing the link & refitting the compressor would now run. It did satisfy my curiosity. as to why??
Attached Thumbnails
Click image for larger version

Name:	DANFOSS  BD35F WINDING CIRC Faulty readings.jpg
Views:	56
Size:	340.0 KB
ID:	279488   Click image for larger version

Name:	DANFOSS BD35F SHORT LINK.jpg
Views:	53
Size:	406.6 KB
ID:	279489  

DeBe is offline   Reply With Quote
Old 10-08-2023, 22:22   #36
Registered User

Join Date: Aug 2009
Location: Onboard, currently cruising in SE Asia
Boat: St. Francis 44 Mk II (Catamaran)
Posts: 181
Send a message via Skype™ to SoggyPaws
Re: 3 flashes on Danfoss control

One of the best sources of Danfoss compressor troubleshooting this page on Coastal Climate Control's website. They have a really good 1-page PDF flow chart that helps you figure out where in the system your issue might lie. (Videos too, if you are into Youtube).

https://coastalclimatecontrol.com/re...roubleshooting

It's specifically for Frigoboat units, but that's just a standard Danfoss system with a little passive cooling built in.
SoggyPaws is offline   Reply With Quote
Old 22-03-2024, 21:08   #37
Registered User
 
OldGreyB's Avatar

Join Date: Jan 2016
Location: East Coast, Australia
Boat: Lagoon 400
Posts: 214
Images: 1
Re: 3 flashes on Danfoss control

Oze Pete,
THANKS!

The post #9 on this thread in 19-09-2017 worked a treat today for me. It required #5. Replace Electronic unit.

But I had a spare unit from a fortuitous gifting a year ago from another cruiser doing a fridge upgrade. Now the Admiral is very happy again.

Best Regards
OldGreyB
OldGreyB is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
m700pro flashes tune????? pesarsten Marine Electronics 0 28-01-2014 16:30
240vac Danfoss Compressor to 12vdc Danfoss cat man do Plumbing Systems and Fixtures 15 30-05-2013 13:13
Five flashes Eddien Plumbing Systems and Fixtures 2 04-10-2012 03:06
Handy Information on Danfoss Refrigeration Control Modules Captain Bill Plumbing Systems and Fixtures 6 11-11-2010 12:33
NEEDED---Danfoss electronic control unit james taylor Classifieds Archive 2 26-10-2007 23:57

Advertise Here


All times are GMT -7. The time now is 06:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.