Old 11-12-2023, 01:22   #16
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,520
Images: 241
Re: What AWG for 120 V inlet?

See DIAGRAM 1*, [and E-11.17.1], excerpted from the Out of Date 2008 version of ABYC ‘E-11' AC and DC ELECTRICAL SYSTEMS ON BOATS

* Single Phase 120-Volt Systems with Shore-Grounded (White) Neutral Conductor and Grounding (Green) Conductor.
Page 33 ➥ http://www.blackfinforums.com/sites/.../abyc-e-11.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 11-12-2023, 04:36   #17
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,503
Re: What AWG for 120 V inlet?

I believe those white toggles are all breakers.
team karst is offline   Reply With Quote
Old 11-12-2023, 04:55   #18
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,520
Images: 241
Re: What AWG for 120 V inlet?

Indeed.
Note: The 2P Main 120VAC Breaker - bur NO 12VDC Main Brkr.

__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 11-12-2023, 05:15   #19
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,039
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by GordMay View Post
Indeed.
Note: The 2P Main 120VAC Breaker - bur NO 12VDC Main Brkr.

Yes, that is the required elci breaker. Because it is more than 10’ away from the shore power inlet, an additional breaker is installed closer to the inlet so as to comply with ABYC.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 11-12-2023, 09:44   #20
Registered User

Join Date: Sep 2020
Posts: 482
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by GordMay View Post
See DIAGRAM 1*, [and E-11.17.1], excerpted from the Out of Date 2008 version of ABYC ‘E-11' AC and DC ELECTRICAL SYSTEMS ON BOATS

* Single Phase 120-Volt Systems with Shore-Grounded (White) Neutral Conductor and Grounding (Green) Conductor.
Page 33 ➥ http://www.blackfinforums.com/sites/.../abyc-e-11.pdf
It appears from the second diagram i have to reverse my breakers putting the ELCI first after shore power, then the second double pole at the distribution panel.
BAD ORCA is offline   Reply With Quote
Old 11-12-2023, 09:55   #21
Registered User

Join Date: Sep 2020
Posts: 482
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by GordMay View Post
Indeed.
Note: The 2P Main 120VAC Breaker - bur NO 12VDC Main Brkr.
Thanks GordMay. I think i need to re-read E-11 again. Its been a while since I did. The 12 volt side currently has no main breaker. The DC side of the panel will be fused before it connects to the DC and there is the 1,2,Off switch on the DC side at the distribution panel as well as an ON/OFF switch between the battery and the main busbar.

E 11.10.1.4.3 makes an exception for a breaker if there is a fuse of 100% rating at the source of power which i would assume is the positive DC busbar thats connected to my lithium house bank. I would interpret that to mean that i need a fuse between the positive busbar and my DC distribution panel that is rated to accept 100% of the DC load current as well as a fuse between the battery and the busbar which i will have (class T 400 amp).

I think im interpreting this correctly.
BAD ORCA is offline   Reply With Quote
Old 11-12-2023, 10:37   #22
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,039
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by BAD ORCA View Post
It appears from the second diagram i have to reverse my breakers putting the ELCI first after shore power, then the second double pole at the distribution panel.
If youbring the elci to within 10’ of the inlet, you don’t need the other breaker at all.

But because the elci is more than 10’ from the inlet, you have an additional breaker within 10’ of the inlet. This is specifically mentioned in E11 as a workaround.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 15-12-2023, 08:06   #23
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 533
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by BAD ORCA View Post
Thanks God. I think im good and wont have to trim anything. I can get 8 gauge ring terminals or even power lugs to fit everything except possibly the shore power inlet plug as you mentioned. I will have to double check my power cord inlet and see if i can make it work without trimming any wires.
I used 10 ga. - Ancor marine wire (triplex blk-wht-grn)

30 amp service

Run is about 08-10 feet from shore connector on boat to main panel

Also installed new shore power connector and galvanic isolation diode on green wire at same time

cheers.
sinnerman is offline   Reply With Quote
Old 15-12-2023, 17:47   #24
Registered User

Join Date: Aug 2012
Posts: 66
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by s/v Jedi View Post
I use 8 AWG for 30A circuits and 6 AWG for 50A circuits.

It is true that 10 AWG can do a 30A circuit but after the shore cables, which are long and 10 AWG as well as questionable outlets/inlets/plugs, creating a low resistance path inside the boat is simple.
Plus 1
drdoyle is offline   Reply With Quote
Old 16-12-2023, 11:16   #25
Registered User

Join Date: Oct 2007
Location: North Carolina
Boat: Hunter 54
Posts: 127
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by GordMay View Post
See DIAGRAM 1*, [and E-11.17.1], excerpted from the Out of Date 2008 version of ABYC ‘E-11' AC and DC ELECTRICAL SYSTEMS ON BOATS

* Single Phase 120-Volt Systems with Shore-Grounded (White) Neutral Conductor and Grounding (Green) Conductor.
Page 33 ➥ http://www.blackfinforums.com/sites/.../abyc-e-11.pdf



Hello Gord,
If you have access to the latest revision of ABYC-E11 would you please check to see if ABYC corrected the ELCI application error?
The 2008 version of ABYC-E11 that you sent a link to, shows five diagrams for wiring an isolation transformer along with an ELCI device (on pages 36 through 41) in these diagrams the transformer makes the ELCI device unable to detect a current unbalance and the ELCI will just sit there doing nothing during a ground fault event at the transformer secondary. I explained all this to the ABYC engineer in a written change request in 2018. In the mean time people using out of date ABYC-E11 as a guide to install isolation transformers should question Diagrams 5 through 9 in the link you sent. An ELCI device at the primary of a transformer as shown in diagrams 5 through 9 cannot sense a ground fault at the secondary.
Ahmet Erkan is offline   Reply With Quote
Old 17-12-2023, 02:21   #26
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,520
Images: 241
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by Ahmet Erkan View Post
Hello Gord,
If you have access to the latest revision of ABYC-E11 would you please check to see if ABYC corrected the ELCI application error? ...
Sorry, I do not have access.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 17-12-2023, 13:01   #27
Registered User

Join Date: Oct 2007
Location: North Carolina
Boat: Hunter 54
Posts: 127
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by GordMay View Post
Sorry, I do not have access.

Thank you anyway Captain.
How does a boater get (buy) a copy of a ABYC standard?
The ABYC requires you to be a business owner, ABYC trained technician, manufacturer, student etc. Just about anybody but an ordinary sailor.
Ahmet Erkan is offline   Reply With Quote
Old 17-12-2023, 13:19   #28
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,135
Re: What AWG for 120 V inlet?

Quote:
Originally Posted by Ahmet Erkan View Post
Thank you anyway Captain.
How does a boater get (buy) a copy of a ABYC standard?
The ABYC requires you to be a business owner, ABYC trained technician, manufacturer, student etc. Just about anybody but an ordinary sailor.
Join under the business category as "Ahmet's Boats"

or take the on-line course as a non-member and get access to all electrical standards. https://abycinc.org/events/EventDeta...1793487&group=
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sailing Charleston inlet to St. Johns Rivers inlet toddmurray Atlantic & the Caribbean 34 28-07-2021 05:44
Crimping issue with FTZ 1-2 AWG Power Lugs & 2 AWG Cable ayates Electrical: Batteries, Generators & Solar 48 28-06-2019 06:32
Pls Help Aussie and Crimp terminals, metric and AWG mischief Electrical: Batteries, Generators & Solar 3 13-05-2012 04:35
Sailing from Fire Island Inlet to Shinnecock Inlet Dswerdloff Navigation 5 10-11-2011 06:25
AWG 6 Gauge for 30 Amp Iota Charger ? unbusted67 Electrical: Batteries, Generators & Solar 31 27-03-2010 18:06

Advertise Here


All times are GMT -7. The time now is 04:40.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.