Victron Multiplus Compact 2000 without voltage sensing?

Hello experts

I have been up until late last night troubleshooting a Victron Multiplus Compact 2000 that gives a "Low Batt" error. I need some help!

When I opened the units (2 in parallel) was surprised to find that these things do not have terminals to connect voltage sensing wires aka V-sense wires. The owner´s manual talks about them and the install manual shows them but the units do not have them.

(Just to make things absolutely weird, the manual you can see in your web browser by clicking here http://www.victronenergy.com/upload/...2%20-%20EN.pdf has the V-sensing wires but if you download it and open it with Acrobat you do not see them.)

I would expect that a voltage sensing wire would be used in this thing because even when running the things at 200A (measured at the battery; including other loads) the voltage drop between battery and the Multipluses is about 0.55V. (This is consistent with a 18ft cable run of 107 mm2 ) Therefore at 50% SOC the 12v at no load turn into say 11.5V loaded at battery the terminals and 11.0V at the Multipluses...


Now the questions:
- Has anyone been able to make these untis work reliably to their full rated capacity without voltage sensing?
- Is it true that some of these units have voltage sensing terminals and other don´t?

C
svlamorocha is offline   Reply With Quote
Old 23-11-2013, 14:17   #2
Registered User
 
careka's Avatar

Join Date: Apr 2009
Location: Lindesnes,Norway
Boat: Lagoon380 Comfort#637
Posts: 716
Images: 2
Send a message via Skype™ to careka
Re: Victron Multiplus Compact 2000 without voltage sensing?

Hmm, i am just about to by one...
careka is offline   Reply With Quote
Old 23-11-2013, 18:35   #3
Registered User

Join Date: Oct 2011
Location: Winter Bahamas - Summer BC
Boat: Lagoon 450, Bavaria Vision 40
Posts: 518
I always thought the voltage sensing is for the charger not for the inverter portion. My Multi Plus 3000 had the voltage sense connections.
roetter is offline   Reply With Quote
Old 24-11-2013, 02:58   #4
Registered User

Join Date: May 2006
Posts: 1,146
If you don't have enough battery capacity, then these units will drag the voltage down if they themselves are supplying near their full capacity. There are 2 combined so I assume that they are used hard sometimes.
I use my 3000 24v without voltage sensing.
For these 2 units, I would imagine that you would need 1000 ah + of 12v batteries with very fat cables with proper connections to avoid problems.
Fuss is offline   Reply With Quote
Old 24-11-2013, 03:57   #5
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Quote:
Originally Posted by Fuss View Post
If you don't have enough battery capacity, then these units will drag the voltage down if they themselves are supplying near their full capacity. There are 2 combined so I assume that they are used hard sometimes.
I use my 3000 24v without voltage sensing.
For these 2 units, I would imagine that you would need 1000 ah + of 12v batteries with very fat cables with proper connections to avoid problems.
Agreed. I have been on several boats with 2000's and 3000's and the only one that worked perfectly had a new 780Ah bank at 12V and fat wires as required by Victron. I am surprised over and over when I see folks trying to save money on the cables that Victron wants. I thought about voltage sensing as a way to avoid mitigating the effect of voltage drop. I was not happy when I saw that the V-sense dissapeared on the way from brochure to reality.
C
svlamorocha is offline   Reply With Quote
Old 24-11-2013, 04:00   #6
Registered User
 
careka's Avatar

Join Date: Apr 2009
Location: Lindesnes,Norway
Boat: Lagoon380 Comfort#637
Posts: 716
Images: 2
Send a message via Skype™ to careka
Re: Victron Multiplus Compact 2000 without voltage sensing?

So for a bank of 4 x 165 amp Gel , a inverter of 2000watt is to big or ?
careka is offline   Reply With Quote
Old 24-11-2013, 05:16   #7
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Victron Multiplus Compact 2000 without voltage sensing?

I've never seen an installation of a Multi Plus w/o sense wires; I'll check with Victron about the current models and post their reply. I was a dealer for them for years and installed quite a few units, mostly 2.5's and 3's… Remember that you can set the low voltage cut off in the software.
Scott Berg is offline   Reply With Quote
Old 24-11-2013, 12:34   #8
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by careka View Post
So for a bank of 4 x 165 amp Gel , a inverter of 2000watt is to big or ?
I do not know about gel batteries but I have no reason to believe that it makes a difference. Victron recommends that the 2000 should be used with battery capacities between 350 and 1000Ah.

This is particularly relevant for an owner that is not technically inclined and will get frustrated when they get low voltage alarms when drawing large inverter loads from a battery that is not fully charged.

C
svlamorocha is offline   Reply With Quote
Old 24-11-2013, 12:36   #9
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by Scott Berg View Post
I've never seen an installation of a Multi Plus w/o sense wires; I'll check with Victron about the current models and post their reply. I was a dealer for them for years and installed quite a few units, mostly 2.5's and 3's… Remember that you can set the low voltage cut off in the software.
Scott
Thanks for the tip re: software. I am tired of dealing with supposed inverter technicians that do not even have the Victron software and cable. Now that you raise this I will just but the thing and do it myself.

C
svlamorocha is offline   Reply With Quote
Old 24-11-2013, 13:03   #10
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Ok
Where are you?
I could loan them to you if you can easily find them

S
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 24-11-2013, 16:19   #11
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by svlamorocha View Post

I do not know about gel batteries but I have no reason to believe that it makes a difference. Victron recommends that the 2000 should be used with battery capacities between 350 and 1000Ah.

This is particularly relevant for an owner that is not technically inclined and will get frustrated when they get low voltage alarms when drawing large inverter loads from a battery that is not fully charged.

C
Firstly voltage sense is irrelevant for the invertor side of the unit. It can play no part. The invertor has to operate on the delivered voltage. Sense wires have nothing to do with invertor operation

Secondly you have upwards of 4000kw which is upto nearly 400 A on a < 700aH battery bank that could be undercharged. and your wondering why you're getting low voltage alarms. !!!!


If they are gels , these have no place on a boat , they tend to be undercharged unless subject to long periods of trickle charge final charging. Gels will spend their life on a boat undercharged. Given the wire runs there could be quite a drop during charging , that's making the issue worse

Way too big inverters on far too small a bank. ( that's more then likely undercharged )

What AC loads are being pulled off when the low bat kicks in.

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 24-11-2013, 18:02   #12
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by careka View Post
So for a bank of 4 x 165 amp Gel , a inverter of 2000watt is to big or ?
Before losses to the inverter that's about twice the Pukert factor of a 12 volt bank setting at 12.5 volts. 4 times Pukert if running 2 X 2Kw inverters in parallel.

Now factor in voltage drop in the cable, and inverter losses, lower resting voltages, and other 12 volt nominal loads running from the bats.

and

anything running for longer than a minute or 2, and yes,

your bank is to small.


Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 24-11-2013, 19:56   #13
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by goboatingnow View Post
Firstly voltage sense is irrelevant for the invertor side of the unit. It can play no part. The invertor has to operate on the delivered voltage. Sense wires have nothing to do with invertor operation
Thanks. The physics of that is 100% clear. Unfortunately the owners are led to believe that the unit has voltage sensing at the battery and the alarms and panel readings are based on battery voltage, which they are not.

How can it be OK to say that the thing has voltage sensing and then you open the cover and the terminals are not there?

Quote:
Originally Posted by goboatingnow View Post
Secondly you have upwards of 4000kw which is upto nearly 400 A on a < 700aH battery bank that could be undercharged. and your wondering why you're getting low voltage alarms. !!!!

Way too big inverters on far too small a bank. ( that's more then likely undercharged )

What AC loads are being pulled off when the low bat kicks in.

Dave
No one has ever dared to draw 4000 VA. I tested at 200A at 50% SOC (per panel) and got 11.5V at the battery and 11V at the inverter when the alarm kicked in less than a couple of minutes. The bank´s capacity is 780Ah (4 new Trojans in 2x2 configuration) . I am yet to get good data on battery condition (new but who knows how were they maintained before delivery) to cover the battery angle.

The alarm in the VE panel is set at 10.5V and I am still wondering whether this "low batt" alarm is a different alarm or Multiplus measures voltage differently than my Fluke tester (applied at the inverter input). I am still awaiting word from Victron on that.
svlamorocha is offline   Reply With Quote
Old 24-11-2013, 20:00   #14
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by Scott Berg View Post
Ok
Where are you?
I could loan them to you if you can easily find them

S
Thanks; I am in Argentina. I go back to the states I will buy one set...
Thanks again. C
svlamorocha is offline   Reply With Quote
Old 24-11-2013, 21:06   #15
Registered User

Join Date: Jul 2013
Location: Usually South Florida these days
Posts: 952
Re: Victron Multiplus Compact 2000 without voltage sensing?

Quote:
Originally Posted by svlamorocha View Post
(Just to make things absolutely weird, the manual you can see in your web browser by clicking here http://www.victronenergy.com/upload/...2%20-%20EN.pdf has the V-sensing wires but if you download it and open it with Acrobat you do not see them.)
Might you have an older version of Acrobat reader on your computer that that could be incorrectly interpreting the graphics in the document when it is opened as a local file? Perhaps your browser is newer & shows all the graphics when the document is viewed there?
pbiJim is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 23:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.