Cruisers Forum
 

Go Back   Cruisers & Sailing Forums > Engineering & Systems > Electrical: Batteries, Generators & Solar
Cruiser Wiki Click Here to Login
Register Vendors FAQ Community Calendar Today's Posts Log in

Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 18-02-2018, 05:09   #1
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Refrigeration- 50-80% less daily power possible?

OK this is being done. It is a science project and is unlikely to ever be main stream but the attraction is obvious, particularly for sailboats that haven’t got the luxury of being plugged into the grid often.

There are good reasons this will never become mainstream. Up front cost is one. But the biggest one is that the big elec appliance boys are selling too many of their units.

The other thing is that while there is a wall socket that can be easily plugged into why would anyone want to bother with the trouble and expnce of doing a solar water heater install. The answer is they wouldn’t.

I like to think of boat systems holistically. Like in nature, who has had millions of years to learn and evolve from her mistakes. Everything in nature is connected and has multiple functions to survive as an complete eco system.

So when someone suggests a solar water heater to me I’m thinking how else can this benefit, and tie into other systems on our boat Radiant Solar Water Heating System - Â* Â* Â*Custom Marine Products - Marine Solar Systems . There are implications and impacts both positive and negative. So my mind drifts to thoughts like hot water- I know people are using it to reduce power consumption for refrigeration and store it in lieu of expensive batteries using clever, but simple, priority sequencing.

I know I’m guilty of thread drift and some people don’t want to hear LFP batts and Inverter powered UPSs when talking about DC Gens. But to me we sometimes also need to look at the big overall picture to see how something can best work in the boat as a whole system.

Seeing refrigeration on boats is generally such a large portion of our daily power budget wouldn’t it be good if we could reduce it. And perhaps have some added side benefit like some shower water. Sounds good to me.

Solakool | Solar hybrid air conditioning Australian company, quotes upto 80% power reduction

Microsolar System Water Heater Malaysian company. Claims 50% reduction in daily energy consumption. I have met and talked to the guy behind this. I am only a dumb helicopter engineer but I have seen his setups. I bought him a cup of coffee and picked his brain for hours. He is brilliant. As I said the commercial reality is that it will never be a raging success but, I think it definitely has some uses.

There are other makers I know of that have, and are doing this stuff. I saw one of these set up on a bank building in Panama. When I looked up the company, in the US it had gone. But I saw it working.

I’m thinking this could be a great concept if done for small sailboat refrigeration.

This also starts to make boat air conditioning closer to doable combined with LFP batts becoming another more popular option.

Solar panels are also becoming more affordable. Could our water heater stuck to the back of our PV panels also cool our PV seeing it sucking heat out of them? Sounds like another potential side benefit.

I’m sure you guys will come up with many reasons this sort of stuff wont work. I’m not trying to convince anyone here, I’m not convinced myself. Simply putting it out there for some thought and discussion. Maybe the collective wisdom has something to progress some of this maybe not.
Q Xopa is offline   Reply With Quote
Old 18-02-2018, 07:42   #2
Registered User

Join Date: Nov 2012
Location: La Honda, California
Boat: Beneteau Oceanis 50
Posts: 364
Re: Refrigeration- 50-80% less daily power possible?

The solakool system is nonsense. The idea of solar heating of the refrigerant to increase temp and pressure to enhance cooling demonstrates that these guys are clueless as to how refrigeration works.
Pitchondesign is offline   Reply With Quote
Old 18-02-2018, 08:29   #3
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Re: Refrigeration- 50-80% less daily power possible?

You may be correct, but you haven't given us much to go on. In the absence of facts or details you have provided it sounds more like an opinion.

Are you suggesting 'Thermal cooling' is all nonsense? That would mean the Ammonia chiller ice plants from a hundred years ago, now caravan kerosene fridges, shopping mall absorption chiller plants etc dont work.

I have heard many people say the, Earth is round, tobacco is good for you and Moon Landing was nonsense too.

I guess commonly accepted wisdom of the day are a bit of a moving target.

If you could offer something a little more technically specific.
Q Xopa is offline   Reply With Quote
Old 18-02-2018, 09:56   #4
Registered User

Join Date: Nov 2012
Location: La Honda, California
Boat: Beneteau Oceanis 50
Posts: 364
Re: Refrigeration- 50-80% less daily power possible?

OK..... here is a detailed technical discussion.

Technical Review of Solakool Air Conditioning System
Summary
Put simply, the Solakool Air Conditioning system as put forward at*www.solakool.com.au*cannot possibly work in the manner described and the claims made for it such as “With Solakool’s patented technology, compressor run time is reduced by up to 80%” are preposterous. The product is either an outright scam, seeking to defraud those who wish to reduce their environmental impact and/or save energy (most likely), or it is the product of someone with gross misunderstandings of how the refrigeration cycle works (unlikely).*
It may be possible that the “solar panel” actually delivers a small increase in cycle efficiency by providing additional cooling capacity to the condenser, thereby reducing the energy used by the condenser fan. However, this is in total contradiction of how the system is claimed to work and the benefit delivered would be nothing like the 80% reduction in energy use claimed.

Why it cannot function as described
Let’s take a look at the explanation posted under “How it Works” on the Solakool website:

I’ll start by giving a brief explanation of the gas compression refrigeration cycle. Starting with the cooling element, , cooling takes place the evaporator (5) as heat from the air that is being cooled boils off the refrigerant liquid in the evaporator. The liquid is at a low pressure and at that pressure, it boils (changes to gas phase, or vaporises) at a very low temperature – typically -10⁰C to 0⁰C.*
As the liquid vaporises, it takes up a much larger volume and thereby pressurises the vessel containing it, which would stop further vaporisation if the gas was not removed to maintain a low pressure in the evaporator.*
The first function of the compressor is to remove the gas from the evaporator so that cooling can continue – Point 1.*
As the compressor runs, the compression of the gas generates heat, known as the heat of compression. After leaving the compressor, the gas is hot – typically 75⁰C to 100⁰C. In order for it to condense back to a liquid it must be cooled. The function of the condenser is to transfer the heat to the air being heated (outside air) causing the refrigerant to condense to liquid. Because the liquid has a much lower volume than the gas, this lowers the pressure in the condenser, allowing gas to continue to flow from the compressor.*
If the liquid was not cooled, the pressure in the condenser would quickly rise to the point that is was equal to the discharge pressure of the compressor and no further gas would flow – Point 2.
To complete the cycle, the cooled liquid (typically at 40⁰C to 50⁰C) passes through a restriction (4) into the much lower pressure evaporator vessel.*
Now note where the Solakool “Solar Panel” is located. At the part of the cycle where cooling is required to condense the refrigerant back to liquid, they claim to be adding heat from the sun. Furthermore, they claim that this heat raises the pressure of the gas, which it would – right at the part of the cycle where the primary goal is to reduce the pressure of the gas to allow more refrigerant to flow to facilitate cooling (Point 2).*
The explanation claims that by adding heat from the solar panel, the heating increases pressure to reduce the duty on the compressor "by up to 80%". This claim is ludicrous on 2 counts:
1.The increase in pressure would not do the work of the compressor – it would actually make the job of the compressor harder by increasing the discharge pressure and by adding more heat to the system that would have to then be rejected by the condenser.*
2.If the compressor is not running, the gas is not extracted from the evaporator and cooling quickly ceases (Point 1.) 80% reduction in compressor run time would also reduce effective cooling by around 80%.

So what is actually happening?
I’m not saying that this air conditioner doesn’t work – clearly it does actually produce cooling; it is just that the claims made regarding the “Solar Panel” are bogus.*
The first clue is here: “The result is that the condenser coil fills with refrigerant that has changed phase completely into liquid instead of aerated fluid as in regular air conditioners.” If the refrigerant had been heated by the “Solar Panel”, it would be driven further into the gaseous phase and would take longer to dissipate the heat and condense to liquid in the condenser. But this statement claims the opposite.*
This could only happen if the “Solar Panel” is dissipating heat, acting as an additional condenser.*
Now consider that, as anyone who owns a solar hot water heater knows, it takes several hours of full sunshine to raise the temperature of a tank of hot water to around 75⁰C. Yet this “Solar Panel” is receiving refrigerant above typically above 75⁰C; it seems highly unlikely that any significant additional heat would be added. Furthermore, in other than full sunshine, it would definitely act as a cooler to the hot gas.*
Confirmation of the hypothesis that the “Solar Panel” is acting as an extra cooling stage comes from the “Case Studies” section of the website:
“At least 4 hours of daylight per day (direct sunlight not required, only daylight)”
And this gem:
“The SolaKool system operates for up to 15 hours over night after only 4 hours exposure to daylight.”
How well does a solar hot water system operate on “daylight” – rather than “direct sunlight” ? Well as anybody that has ever used a solar hot water system knows, the answer is that it does not heat at all – your water goes cold as more heat is radiated off than absorbed in.*
Now, as final confirmation, examine the photos of recent installations. Note the size of the panels – they are tiny. Also note that they are located to avoid full exposure to the sun.


So how well does it work?*
Here are the claims from the website:
“Depending on normal operating conditions savings of up to 80% may be achieved over a conventional system.”
“Based on standard operating conditions, the carbon footprint may be reduced by up to 80% compared to a conventional system.”*
These claims – if true would be verified by the Energy Star appraisal process and would dramatically exceed “conventional systems” in their performance. Astoundingly, they are foolish enough to publish the actual Energy Star ratings:


3.5 stars – that’s middle of the road performance and way below the 5 star efficiency systems that are readily available and deliver significantly higher energy efficiency!*
(See:*http://www.canstarblue.com.au/applia...conditioners/*)

In addition to all this there are multiple references to "Carbon Credits" as if they have some monetary value – which at present they do not – and certainly wouldn't be available for a bogus product like this anyway. It's just further evidence that this is a scam to defraud those that actually care about their carbon emissions.
Pitchondesign is offline   Reply With Quote
Old 19-02-2018, 08:41   #5
Registered User

Join Date: Mar 2011
Location: fl- various marinas
Boat: morgan O/I 33' sloop
Posts: 1,447
Re: Refrigeration- 50-80% less daily power possible?

You do not have to be an expert to go by the adage: if it sounds too be good to be true, it probably is not. With new tech claims it is always buyer beware
Dave22q is offline   Reply With Quote
Old 19-02-2018, 08:57   #6
Registered User

Join Date: Apr 2013
Posts: 30
Re: Refrigeration- 50-80% less daily power possible?

Quote:
Originally Posted by Pitchondesign View Post
The solakool system is nonsense. The idea of solar heating of the refrigerant to increase temp and pressure to enhance cooling demonstrates that these guys are clueless as to how refrigeration works.
How is that any different than my propane burner in my AC/DC/Propane unit in my motor home? Propane is burned to heat ammonia which then rises, condenses and mixes with hydrogen gas causing it to evaprorate and cool the condensing coil....voila cold temps.

EDIT: PS, Should have read the whole thread first! Claims seem to be a little optimistic to say the least.
CruiseEasy is offline   Reply With Quote
Old 19-02-2018, 09:08   #7
Registered User

Join Date: Dec 2013
Posts: 120
Re: Refrigeration- 50-80% less daily power possible?

The good news is YES it is technically possible to cool using solar.
The bad news is that it is not practical for two major reasons.
1) An extreme amount of insulation would be required to get the thermal load down to a few hundred watts for people and some low power appliances (LED lights and low power electronics).
2) The expense and size of the solar collector either direct electric conversion via solar panels for a compressor or ammonia cycle (look up propane refrigerators).
Great thinking but the devil is in the details. Many other methods can be used for small amounts of cooling but none are even as practical as these two.
lvictorlucas is offline   Reply With Quote
Old 19-02-2018, 09:28   #8
Registered User

Join Date: Oct 2012
Location: Seattle
Boat: Tayana Mariner 36
Posts: 122
Re: Refrigeration- 50-80% less daily power possible?

Yeah, believe what Pitchondesign wrote (or copy/pasted).

The give away is their own description simply trying to confuse people with words: "Refrigerant is circulated by the compressor (1), to the solar panel (2), where it is heated by solar thermal energy that has been collected and stored in the panel. The heated refrigerant is now hot and at high pressure due to expansion."

First of all, a compressor doesn't circulate, it compresses.
But more importantly, the "at high pressure due to expansion". They need to go back to 4th grade science. Expansion would put the refrigerant at a lower pressure, not higher. There's no reason to expend the refrigerant, and then immediately condense it in the condenser. The truth is probably closer to the aforementioned use of the panel as another condenser. There's absolutely no reason to expand the refrigerant UNTIL it passes thru the Thermostatic Expansion Valve, which is the heart of the system and allows the refrigerate to absorb heat through the evaporator.

This company either has no concept of the refrigeration cycle, or they are trying to fool people not familiar with the refrigeration cycle. Probably both.
bauer965 is offline   Reply With Quote
Old 19-02-2018, 11:12   #9
Registered User

Join Date: Mar 2015
Location: Boston's North Shore
Boat: Pearson 10M
Posts: 839
Re: Refrigeration- 50-80% less daily power possible?

I think it important distinction here is the difference between an ammonia cycle and a Freon cycle: system
guyrj33 is offline   Reply With Quote
Old 19-02-2018, 11:27   #10
Registered User

Join Date: Oct 2012
Location: Seattle
Boat: Tayana Mariner 36
Posts: 122
Re: Refrigeration- 50-80% less daily power possible?

And to confuse people more, R290 (the refrigerant in the solakool product), is in fact simpy, propane.
bauer965 is offline   Reply With Quote
Old 19-02-2018, 11:57   #11
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Re: Refrigeration- 50-80% less daily power possible?

OK..... here is a detailed technical discussion.

Technical Review of Solakool Air Conditioning System
Summary
Put simply, the Solakool Air Conditioning system as put forward at*www.solakool.com.au*cannot possibly work in the manner described and the claims made for it such as “With Solakool’s patented technology, compressor run time is reduced by up to 80%” are preposterous.

The product is either an outright scam, seeking to defraud those who wish to reduce their environmental impact and/or save energy (most likely), or it is the product of someone with gross misunderstandings of how the refrigeration cycle works (unlikely).*
It may be possible that the “solar panel” actually delivers a small increase in cycle efficiency by providing additional cooling capacity to the condenser, thereby reducing the energy used by the condenser fan. However, this is in total contradiction of how the system is claimed to work and the benefit delivered would be nothing like the 80% reduction in energy use claimed.

OK firstly I am not an air conditioning expert. I do work on them regularly on aircraft and had training on air conditioning systems during my trade training to become a Licensed aircraft maintenance engineer. I am also open to learning and the fact that you may indeed be correct. I have no affiliation or interests in any of this stuff.

Some of your claims about Solarkool are, let’s say quite strong. No skin off my nose. I'm just trying to get closer to the truth.

In Australia, as in most developed countries, ps I am Australian, they have the ACCC to protect consumers from fraudulent business claims. If there are customer complaints about products this can be pursued quite vigorously. A quick search didn’t bring anything up that I could see. Do you know something I don’t? Australians in my experience aren’t shy to complain about something they feel misled about.


I agree that the explanation is somewhat vague. This could be them protecting their technology or it could be them preying on the markets desire to be green by exaggerating or flat out bullsh..g. It wouldn’t be the first time.

Why it cannot function as described
Let’s take a look at the explanation posted under “How it Works” on the Solakool website:

I’ll start by giving a brief explanation of the gas compression refrigeration cycle. Starting with the cooling element, , cooling takes place the evaporator (5) as heat from the air that is being cooled boils off the refrigerant liquid in the evaporator. The liquid is at a low pressure and at that pressure, it boils (changes to gas phase, or vaporises) at a very low temperature – typically -10⁰C to 0⁰C.*
As the liquid vaporises, it takes up a much larger volume and thereby pressurises the vessel containing it, which would stop further vaporisation if the gas was not removed to maintain a low pressure in the evaporator.*
The first function of the compressor is to remove the gas from the evaporator so that cooling can continue – Point 1.*
As the compressor runs, the compression of the gas generates heat, known as the heat of compression. After leaving the compressor, the gas is hot – typically 75⁰C to 100⁰C. In order for it to condense back to a liquid it must be cooled. The function of the condenser is to transfer the heat to the air being heated (outside air) causing the refrigerant to condense to liquid. Because the liquid has a much lower volume than the gas, this lowers the pressure in the condenser, allowing gas to continue to flow from the compressor.*
If the liquid was not cooled, the pressure in the condenser would quickly rise to the point that is was equal to the discharge pressure of the compressor and no further gas would flow – Point 2.
To complete the cycle, the cooled liquid (typically at 40⁰C to 50⁰C) passes through a restriction (4) into the much lower pressure evaporator vessel.*

Yes I agree with your explanation above. This is my understanding of the operation of a vapor cycle system.

Now note where the Solakool “Solar Panel” is located. At the part of the cycle where cooling is required to condense the refrigerant back to liquid, they claim to be adding heat from the sun. Furthermore, they claim that this heat raises the pressure of the gas, which it would – right at the part of the cycle where the primary goal is to reduce the pressure of the gas to allow more refrigerant to flow to facilitate cooling (Point 2).*
The explanation claims that by adding heat from the solar panel, the heating increases pressure to reduce the duty on the compressor "by up to 80%".

Yes agree that this number is unlikely. Sales pitches are never conservative when they are talking about their products attributes. Remember in the thread title it ends in a ?

I didn’t take this as a research paper from a highly respected scientist. These are usually discredited at some stage later too. Cant believe everything we read eh.

This claim is ludicrous on 2 counts:
1.The increase in pressure would not do the work of the compressor – it would actually make the job of the compressor harder by increasing the discharge pressure and by adding more heat to the system that would have to then be rejected by the condenser.*

You may be correct but my understanding is that the compressor discharge has a reed valve. Or maybe they have added one it there wasn’t one initially. Again they are not too big or specific on details. Least the ones I work on do.

My understanding is that the compressor wouldn’t be operating, ie cycled off, when these temps and pressures were high. Ie the sun is heating the panels.

2.If the compressor is not running, the gas is not extracted from the evaporator and cooling quickly ceases (Point 1.)

Yes agreed, if there is no gas flowing through the system to create a pressure drop across the capillary tube at the start of the evaporator there will be no expansion, and as you correctly say no cooling. But I think there would be a flow through the system with heat being applied to the refrigerant before the condenser. The old caravan propane or kerosene small absorption chillers worked like this.

Your explanation is not so convincing as you have put your understanding or interpretation there of, of the operation of this stuff but no facts or credible corroborating evidence. I for example have many opinions and no doubt most them are wrong.

80% reduction in compressor run time would also reduce effective cooling by around 80%.

OK again you may be correct. My perhaps misguided thinking is that there should be a flow without the compressor turning past the compressor valves. It can only go in one direction due the valves. The motive force for the flow I would think would be the expansion of the refrigerant being heated before the condenser. So I think it should be forced into the condenser,

Then as you say the gas cools and condenses into liquid. Being cooled through the condenser will reduce the pressure. So should there not be a flow from the high pressure before the condenser to the low pressure decreasing as it goes through the condenser? Basically a thermosyphon.


So what is actually happening?
I’m not saying that this air conditioner doesn’t work – clearly it does actually produce cooling;

OK, I was starting to wrongly get the impression you thought it didn’t work using words like scam, ludicrous etc. it sounds like you’re passionate about all this.

it is just that the claims made regarding the “Solar Panel” are bogus.*

‘Bogus’, subtle choice of words, seeing your telling me you think it works. Claims exaggerated, I have very little doubts. It is marketing hype let’s face it.


The first clue is here: “The result is that the condenser coil fills with refrigerant that has changed phase completely into liquid instead of aerated fluid as in regular air conditioners.”

Yes, again I’m not sure exactly how it is done. Maybe that is a deliberate tactic or oversimplified or just not articulated well. I don’t think this is evidence of it conclusively working or not working.

If the refrigerant had been heated by the “Solar Panel”, it would be driven further into the gaseous phase and would take longer to dissipate the heat and condense to liquid in the condenser. But this statement claims the opposite.*

Again I don’t know but I would have thought that a hotter ambient air would I agree take longer to dissipate the heat because of a smaller temp difference (delta T) between ambient and the refrigerant. But a hotter refrigerant is the opposite. Yes I agree that a hotter charge will be ‘more gaseous’. But if the compressor is cycled off it is not adding to the heat it is simply replacing the heat the compressor would have generated.

This could only happen if the “Solar Panel” is dissipating heat, acting as an additional condenser.*

Maybe it is, a bigger (effective) condenser capacity doesn’t sound like a ‘smoking gun’ to me.

Now consider that, as anyone who owns a solar hot water heater knows, it takes several hours of full sunshine to raise the temperature of a tank of hot water to around 75⁰C.

Yes, sure 75C will take some time. So will the required cooling load. I guess in the pre 75C times is what a compressor is for.

You seem very sure of your interpretation of this. You could be correct.


One of my nagging doubts is that it must work to at least some degree, being they haven’t been run out of town yet. I’m definitely not sure that’s why I’m putting this out there. The more I learn the more questions I have. I am here to learn. I certainly don’t believe all of these guys claims.


Yet this “Solar Panel” is receiving refrigerant above typically above 75⁰C; it seems highly unlikely (so you don’t know. You seem confident enough to comment strongly) that any significant additional heat would be added.

I assume the cooling loads are less too during these periods.

Furthermore, in other than full sunshine, it would definitely act as a cooler to the hot gas.*
Confirmation of the hypothesis that the “Solar Panel” is acting as an extra cooling stage comes from the “Case Studies” section of the website:

I’m not sure if you’re saying this is proof it doesn’t work. It sounds like how you described how condensers work and I agree with. Maybe it can/ does work either ways depending on the ambient temperature. I don’t know. You sound quite sure it cant. How do you explain that it does?

“At least 4 hours of daylight per day (direct sunlight not required, only daylight)”

And this gem:
“The SolaKool system operates for up to 15 hours over night after only 4 hours exposure to daylight.”

I guess this comes down to storage volume and collector area and efficiency. I don’t know so cant comment.

How well does a solar hot water system operate on “daylight” – rather than “direct sunlight” ?

Yes agreed, not particularly good choice of words.

Well as anybody that has ever used a solar hot water system knows, the answer is that it does not heat at all – your water goes cold as more heat is radiated off than absorbed in.*

True, but it is not as if the heat from the system will be radiated away as the controller has stopped the flow through the panels at this point. So obviously we don’t get solar heating at night or cloudy days. That’s when the booster system kicks in. Heating some of the time is better than none of the time like non solar systems.

Now, as final confirmation, examine the photos of recent installations. Note the size of the panels – they are tiny. Also note that they are located to avoid full exposure to the sun.


So how well does it work?*
Here are the claims from the website:
“Depending on normal operating conditions savings of up to 80% may be achieved over a conventional system.”

“Based on standard operating conditions, the carbon footprint may be reduced by up to 80% compared to a conventional system.”*

These claims – if true would be verified by the Energy Star appraisal process and would dramatically exceed “conventional systems” in their performance. Astoundingly, they are foolish enough to publish the actual Energy Star ratings: Yes I never said their marketing guys are technically conversant.


3.5 stars – that’s middle of the road performance and way below the 5 star efficiency systems that are readily available and deliver significantly higher energy efficiency!*
(See:*http://www.canstarblue.com.au/applia...conditioners/*)

Yes not good. But I also know there are many holes in the Energy star ratings/ SEERs etc.

I am not sure of the facts about this, which is why I am answering the question. I have very little doubts there’s a lot of marketing hype in here.


In addition to all this there are multiple references to "Carbon Credits" Yes agreed this is playing on Joe publics desire to feel environmentally responsible. Advertising drivel. as if they have some monetary value – which at present they do not – and certainly wouldn't be available for a bogus product like this anyway. It's just further evidence that this is a scam to defraud those that actually care about their carbon emissions.

I have to say I appreciate your effort in spending time on this but you haven’t really added much more than some supposition and some emotive words. To me your arguments, like Solarkool, are a little light on conclusive facts. Neither you or Solarkool have convinced me either way.

My thinking on this stuff is that there is something to it, the big question is how much to determine if it is to some extent practically usable?

In answer to the comment re propane ammonia fridges. Yes they are another example of ‘Thermal’ driven chillers. Very old and established technology. However not quite the same as this is a vapor cycle system. Similar in a number of ways but the actual cooling is derived by absorbing and evaporating water in and out of ammonia. Vapor cycles work on expansion and vaporizing of a refrigerant.

I’m also not understanding the comment about “An extreme amount of insulation would be required to get the thermal load down to a few hundred watts for people and some low power appliances (LED lights and low powerelectronics).” Insulation? I’m not sure where this comes into the discussion. Or ” size of the solar collector either direct electric conversion via solar panels for a compressor or ammonia cycle”. I’m not sure how we got to panel size or ammonia cycle (I’m aware of absorption chillers)? Did I miss something?

Also, I’m not very smart but I cant understand what is meant by
“There's no reason to expend the refrigerant”.

“a Compressor doesn’t circulate, it compresses” I’m not sure what you’re trying to say here. I would say it does both. But term it’s function however you like. It is just a mechanical displacement device, usually with valves. The valves are going to ensure that the flow will only ‘circulate’ in one direction. And yes if there is a restriction, (which there will be in any system) then I guess it will ‘compress’. As I understand it a restriction to flow causes an increase in pressure, ie compression. But I am willing to hear and learn from your explanation.

Yes agreed the main cooling function of the a vapor cycle system happens at the ‘Thermal expansion valve’. However there is also a pressure drop across the condenser when it cools the charge (which is supposedly a condensers function). Heating increases pressure, and cooling decreases pressure when I went to school, might have been 4th grade.

I think the truth is that this obviously works to some extent. I have heard a lot of ‘hypothesizing’ but very few of us have a chance to find out the facts on it.

I’m not trying to convince anyone.

All good stuff.
Q Xopa is offline   Reply With Quote
Old 19-02-2018, 12:24   #12
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Re: Refrigeration- 50-80% less daily power possible?

Yes R290 probably is confusing to most people. Most things in life are confusing to me.

I'm not sure if people not understanding how it works means it doesnt work.

And yes it is propane, dont quote me but I think with some butane as well.

I'm not an expert but, I do believe it does work quite well as a refrigerant. By many sources (there always seem to be some opposing opinions), it works better than R134 and R410.
Q Xopa is offline   Reply With Quote
Old 19-02-2018, 12:48   #13
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Refrigeration- 50-80% less daily power possible?

Solakool proudly shows their INNOVATION PATENT APPROVAL on their home page. Except, an Australian Innovation Patent is basically a preliminary half patent. It can't be enforced and has no effect until AFTER a second lengthy procedure and examination. It is not the same as a full patent, and does not actually indicate the patented "thing" actually works.

So, that's one deception.

Then there's the repeated claim of savings"up to 80%". That means, the savings may be zero, there are no assured savings, but if there are any saving they will never exceed 80%. Well, that's totally meaningless. There simply are no assured savings. None? Guaranteed NOTHING will be saved?

Yeah. And while ammonia cooling is still used in large commercial systems precisely because it works so well (even the International Space Station uses it) there's a downside, in that highly toxic ammonia leaks can kill everyone near the unit. Which is also why the ISS had to button down all quarters while they did a little EVA to fix exactly such a leak last year. It may be a necessary evil for log cabins and RV's, but in the contained spaces of a boat cabin in corrosive salt air...a very bad idea.

There's just no there there. Which is not to discourage the OP, please DO SPEND MONEY FOR US ALL to prove that Solakool aren't hoaxsters and that we can all sheepishly apologize for doubting you, as we convert our systems a year or two from now to match the one you're cobbling together. See, the really great part of being a pessimist and card-carrying cynic, is that it is always such a PLEASANT SURPRISE when you are wrong about these things. And I won't just apologize for doubting it, I'll throw in a bottle of wine in a pretty gift bag. Anyone else wanna go in on a full gift case of wine if he's right?
hellosailor is offline   Reply With Quote
Old 19-02-2018, 13:27   #14
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Re: Refrigeration- 50-80% less daily power possible?

Quote:
Originally Posted by hellosailor View Post
Solakool proudly shows their INNOVATION PATENT APPROVAL on their home page. Except, an Australian Innovation Patent is basically a preliminary half patent. It can't be enforced and has no effect until AFTER a second lengthy procedure and examination. It is not the same as a full patent, and does not actually indicate the patented "thing" actually works.

So, that's one deception.

Then there's the repeated claim of savings"up to 80%". That means, the savings may be zero, there are no assured savings, but if there are any saving they will never exceed 80%. Well, that's totally meaningless. There simply are no assured savings. None? Guaranteed NOTHING will be saved?

Yeah. And while ammonia cooling is still used in large commercial systems precisely because it works so well (even the International Space Station uses it) there's a downside, in that highly toxic ammonia leaks can kill everyone near the unit. Which is also why the ISS had to button down all quarters while they did a little EVA to fix exactly such a leak last year. It may be a necessary evil for log cabins and RV's, but in the contained spaces of a boat cabin in corrosive salt air...a very bad idea.

There's just no there there. Which is not to discourage the OP, please DO SPEND MONEY FOR US ALL to prove that Solakool aren't hoaxsters and that we can all sheepishly apologize for doubting you, as we convert our systems a year or two from now to match the one you're cobbling together. See, the really great part of being a pessimist and card-carrying cynic, is that it is always such a PLEASANT SURPRISE when you are wrong about these things. And I won't just apologize for doubting it, I'll throw in a bottle of wine in a pretty gift bag. Anyone else wanna go in on a full gift case of wine if he's right?
Yes agreed, I cant argue with your logic about no guarantee of performance. I guess by your round about reasoning on guarantee of performance, or lack there of, it could also be argued that there is no guarantee it doesn't perform. I'm not too sure what your actually arguing here.

Again I'm not arguing for these guys trying to convince you guys. I'm not convinced either. Just asking.

Patents or not, or whatever. Ok I'm sure you're correct about this, however I'm still not sure if that verifies if it works or not.

Ammonia, yes all good to know thanks. I didnt realize Solarkool or me was suggesting to use it.

No need for anyone to feel sheepish. It's good to see people of conviction.

I wouldn't buy that bottle of wine yet as I'm not planning on doing any of this in the foreseeable future.

Cynicism is great, I'm a fan myself. But fewer opinions and more relevant facts would be better.
Q Xopa is offline   Reply With Quote
Old 19-02-2018, 13:51   #15
Registered User

Join Date: Nov 2012
Location: La Honda, California
Boat: Beneteau Oceanis 50
Posts: 364
Re: Refrigeration- 50-80% less daily power possible?

Quote:
Originally Posted by hellosailor View Post
Solakool proudly shows their INNOVATION PATENT APPROVAL on their home page. Except, an Australian Innovation Patent is basically a preliminary half patent. It can't be enforced and has no effect until AFTER a second lengthy procedure and examination. It is not the same as a full patent, and does not actually indicate the patented "thing" actually works.

So, that's one deception.

Then there's the repeated claim of savings"up to 80%". That means, the savings may be zero, there are no assured savings, but if there are any saving they will never exceed 80%. Well, that's totally meaningless. There simply are no assured savings. None? Guaranteed NOTHING will be saved?

Yeah. And while ammonia cooling is still used in large commercial systems precisely because it works so well (even the International Space Station uses it) there's a downside, in that highly toxic ammonia leaks can kill everyone near the unit. Which is also why the ISS had to button down all quarters while they did a little EVA to fix exactly such a leak last year. It may be a necessary evil for log cabins and RV's, but in the contained spaces of a boat cabin in corrosive salt air...a very bad idea.

There's just no there there. Which is not to discourage the OP, please DO SPEND MONEY FOR US ALL to prove that Solakool aren't hoaxsters and that we can all sheepishly apologize for doubting you, as we convert our systems a year or two from now to match the one you're cobbling together. See, the really great part of being a pessimist and card-carrying cynic, is that it is always such a PLEASANT SURPRISE when you are wrong about these things. And I won't just apologize for doubting it, I'll throw in a bottle of wine in a pretty gift bag. Anyone else wanna go in on a full gift case of wine if he's right?
I'll go in on a second case if wine. Chilled of course, with a solakool system.
Pitchondesign is offline   Reply With Quote
Reply

Tags
refrigeration


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
boom less, track less staysail advice Abrain Deck hardware: Rigging, Sails & Hoisting 17 19-12-2013 08:57
LEDs for Less Power Consumption dennisail Marine Electronics 107 27-04-2011 16:07
Average Refrigeration Daily Amp-Hours sailorboy1 Electrical: Batteries, Generators & Solar 11 11-03-2011 19:59
Daily Machinery Checks - What Do You Do ? Dockhead Engines and Propulsion Systems 8 25-11-2010 11:35

Advertise Here


All times are GMT -7. The time now is 20:33.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.