Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by SFH View Post
d4Raffy,
The shore charger (80A) is charging the truster batteries (OPTIMA RED TOP batteries) but I often get low voltage alarm.

I want to get rid of the Cristec MOSFET 100A 3-splitter since it cant handle the load from the Balmar AT-165 and replace it with a setup that improves charging of my truster battery pack in the bov: Faster and with an optimal charge profile matching the three different batpacks instead of "one fits all"

Steen
just checking - but where is the alarm coming from ? Normally Alarms are on the Service Bank - if this is the case .... something else maybe amiss ... like your Thruster bank is dead and/or the alternator is not supplying enough supplement.

Understand your thoughts for your 100A splitter - I have a Sterling zero volt drop 120A splitter - but the amperage seems to detail the input feed - not sure how many amps will actually go through these things to the connected Banks. This is obviously where a relay is best - for straight amp pass thru and no volt drop.

But ..then .. it sounds like.

We need some form of 'intelligent' 12/24v charging for when the alternator is feeding, there is no load on the Banks and the battery type is different than that configured in our alternator regulation profile (typically the Service Bank).

I am coming round to thinking :
A 240v 'intelligent' charger for the Service Bank - on Generator or ShorePower
2 x 'intelligent' 12v chargers to Engine and Thruster/Windlass from the Service Bank - for top up and ongoing maintenance
Alternator (optimally regulated to the Service Bank battery type ) charging the Service Bank.
2 x Relay combiners to combine the Thruster/Windlass to the Service and the Engine to the Service - as required. I might wire the Thruster/Windlass activation relay to my Windlass activator switch.
Also my Solar charging the Service Bank ..... have both MPPT and PWM.

Mind you - if you read the Smart Gauge stuff on their website - they say that all this profiling is a waste of time .... just use intelligent combiner relays.
And ... if every other Bank is hanging off the Service Bank - what happens if that has a problem - everything stops. ... hmmm

Are we over complicating things ....
d4raffy is offline   Reply With Quote
Old 19-05-2015, 09:15   #32
SFH
Registered User
 
SFH's Avatar

Join Date: Jun 2013
Location: Danish
Boat: Jeanneau Yacht 53
Posts: 99
Send a message via Skype™ to SFH
Re: Need to charge three banks but wants to get rid of the battery isolator

The bov truster is actually operating at 24V.

2 x 2 12V OPTIMA RED TOP are coupled to a battery coupler and the coupler is charged/supplied directly from the Cristec MOSFET isolator next to the housebank

Hence my concerns regarding the potential voltage drop: From shore charger/alternator through Christec MOSFET isolator through 2x30FT cable through the truster battery coupler before it finally reaches the truster batteries

Steen
SFH is offline   Reply With Quote
Old 19-05-2015, 09:33   #33
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by SFH View Post
The bov truster is actually operating at 24V.

2 x 2 12V OPTIMA RED TOP are coupled to a battery coupler and the coupler is charged/supplied directly from the Cristec MOSFET isolator next to the housebank

Hence my concerns regarding the potential voltage drop: From shore charger/alternator through Christec MOSFET isolator through 2x30FT cable through the truster battery coupler before it finally reaches the truster batteries

Steen
Is your house bank also 24V? If it is 12V then a typical combining relay won't work and you would need a Tollbridge or a Sterling 12V to 24V battery to battery charger....
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 19-05-2015, 09:42   #34
SFH
Registered User
 
SFH's Avatar

Join Date: Jun 2013
Location: Danish
Boat: Jeanneau Yacht 53
Posts: 99
Send a message via Skype™ to SFH
Re: Need to charge three banks but wants to get rid of the battery isolator

Maine

No. The house bank is 12V.

The bov thruster is a CT 125 24V from Max Power and batteries are connected 2xP / 2xS.

It IS working but

1. the bov thruster low voltage alarm sounds everytime I use the thruster 5-6 secs

2. the batteries are only four years old

3. I want to ensure that take everything into account before upgrading the alternator on the engine to an AT-165

Steen
SFH is offline   Reply With Quote
Old 19-05-2015, 10:32   #35
Registered User
 
d4raffy's Avatar

Join Date: Oct 2009
Location: Med
Boat: Sunbeam 44
Posts: 112
Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by SFH View Post
The bov truster is actually operating at 24V.



2 x 2 12V OPTIMA RED TOP are coupled to a battery coupler and the coupler is charged/supplied directly from the Cristec MOSFET isolator next to the housebank



Not sure what a 'battery coupler' is - doesn't this mean you have being trying to charge a 24v bank from a 12v-14v source via your Cristec splitter?
I'm unclear on this area - perhaps Maine can advise ? But I would have thought you would need a 24v charging profile for that bank .... ..?? Maybe you killed the bank somehow ....


Sent from my iPad using Cruisers Sailing Forum
d4raffy is offline   Reply With Quote
Old 19-05-2015, 10:38   #36
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Need to charge three banks but wants to get rid of the battery isolator

Sounds really fishy, Steen!

A diagram would help immensly.

From what info you've provided, it seems you have a 12VDC house battery bank from which you are attempting to charge 24V bow thruster batteries.

And, the run is 30'....a long way....

What do you mean by the "battery coupler" for the thruster batteries?

And, how exactly, are those batteries wired?

What do you mean by "2X30' cable"??? Are you perhaps running two positive and two negative cables forward, one set to each 12VDC thruster battery?

Are you sure you're getting 24VDC to the thruster?

And, if so, how are you charging the batteries with only 12VDC source (the house batteries)?

Some more detailed information would help us to help answer your questions.

Bill
btrayfors is offline   Reply With Quote
Old 19-05-2015, 11:02   #37
SFH
Registered User
 
SFH's Avatar

Join Date: Jun 2013
Location: Danish
Boat: Jeanneau Yacht 53
Posts: 99
Send a message via Skype™ to SFH
Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by d4raffy View Post
just checking - but where is the alarm coming from ? Normally Alarms are on the Service Bank - if this is the case .... something else maybe amiss ... like your Thruster bank is dead and/or the alternator is not supplying enough supplement.

Understand your thoughts for your 100A splitter - I have a Sterling zero volt drop 120A splitter - but the amperage seems to detail the input feed - not sure how many amps will actually go through these things to the connected Banks. This is obviously where a relay is best - for straight amp pass thru and no volt drop.

But ..then .. it sounds like.

We need some form of 'intelligent' 12/24v charging for when the alternator is feeding, there is no load on the Banks and the battery type is different than that configured in our alternator regulation profile (typically the Service Bank).

I am coming round to thinking :
A 240v 'intelligent' charger for the Service Bank - on Generator or ShorePower
2 x 'intelligent' 12v chargers to Engine and Thruster/Windlass from the Service Bank - for top up and ongoing maintenance
Alternator (optimally regulated to the Service Bank battery type ) charging the Service Bank.
2 x Relay combiners to combine the Thruster/Windlass to the Service and the Engine to the Service - as required. I might wire the Thruster/Windlass activation relay to my Windlass activator switch.
Also my Solar charging the Service Bank ..... have both MPPT and PWM.

Mind you - if you read the Smart Gauge stuff on their website - they say that all this profiling is a waste of time .... just use intelligent combiner relays.
And ... if every other Bank is hanging off the Service Bank - what happens if that has a problem - everything stops. ... hmmm

Are we over complicating things ....
d4Raffy,

All lot of things to think about and very good points. I also like the redundancy in the system

btrayfors,

I have attached schematic diagram showing the wiring.

"15" is the Cristec MOSFET isolator next to the house bank.
"269" is the coupler

There is a wire from "270" to my DC panel. I guess that is the low voltage alarm wire

Steen
Attached Thumbnails
Click image for larger version

Name:	Bov Thruster.PNG
Views:	173
Size:	89.5 KB
ID:	102358  
SFH is offline   Reply With Quote
Old 19-05-2015, 11:46   #38
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Need to charge three banks but wants to get rid of the battery isolator

Steen,

Sorry, I'm just not getting it.

1. Are all 4 batteries 12VDC?

2. Which are the thruster batteries?

3. Do you have a make/model number for the "controller" (item 269)?

Perhaps someone more familiar with European wiring circuits and equipment could chime in?

Bill
btrayfors is offline   Reply With Quote
Old 19-05-2015, 12:03   #39
SFH
Registered User
 
SFH's Avatar

Join Date: Jun 2013
Location: Danish
Boat: Jeanneau Yacht 53
Posts: 99
Send a message via Skype™ to SFH
Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by d4raffy View Post
just checking - but where is the alarm coming from ? Normally Alarms are on the Service Bank - if this is the case .... something else maybe amiss ... like your Thruster bank is dead and/or the alternator is not supplying enough supplement.

Understand your thoughts for your 100A splitter - I have a Sterling zero volt drop 120A splitter - but the amperage seems to detail the input feed - not sure how many amps will actually go through these things to the connected Banks. This is obviously where a relay is best - for straight amp pass thru and no volt drop.

But ..then .. it sounds like.

We need some form of 'intelligent' 12/24v charging for when the alternator is feeding, there is no load on the Banks and the battery type is different than that configured in our alternator regulation profile (typically the Service Bank).

I am coming round to thinking :
A 240v 'intelligent' charger for the Service Bank - on Generator or ShorePower
2 x 'intelligent' 12v chargers to Engine and Thruster/Windlass from the Service Bank - for top up and ongoing maintenance
Alternator (optimally regulated to the Service Bank battery type ) charging the Service Bank.
2 x Relay combiners to combine the Thruster/Windlass to the Service and the Engine to the Service - as required. I might wire the Thruster/Windlass activation relay to my Windlass activator switch.
Also my Solar charging the Service Bank ..... have both MPPT and PWM.

Mind you - if you read the Smart Gauge stuff on their website - they say that all this profiling is a waste of time .... just use intelligent combiner relays.
And ... if every other Bank is hanging off the Service Bank - what happens if that has a problem - everything stops. ... hmmm

Are we over complicating things ....
Quote:
Originally Posted by btrayfors View Post
Steen,

Sorry, I'm just not getting it.

1. Are all 4 batteries 12VDC?

2. Which are the thruster batteries?

3. Do you have a make/model number for the "controller" (item 269)?

Perhaps someone more familiar with European wiring circuits and equipment could chime in?

Bill
Bill,

Thanks for your patience (it's French wiring - why keep it simple if you can make it complicated ).

The schematic in my previous ONLY shows the bovthruster setup. All the shown batteries are located in the bov in a bank. The Cristec isolator (15) is connected to the housebank (12V/660Ah) and the chargers (not shown)

I checked the MAX POWER CT125 thruster manual. It has a number but only refers to it as a relay

Just for reference I have added the spec pages for the boat - a JEANNEAU YACHT 53. 12V house bank and 24V thruster...

Steen
Attached Thumbnails
Click image for larger version

Name:	Spec.PNG
Views:	145
Size:	199.5 KB
ID:	102376  
SFH is offline   Reply With Quote
Old 19-05-2015, 12:21   #40
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Need to charge three banks but wants to get rid of the battery isolator

Quote:
Originally Posted by SFH View Post
Bill,

Thanks for your patience (it's French wiring - why keep it simple if you can make it complicated ).

The schematic in my previous ONLY shows the bovthruster setup. All the shown batteries are located in the bov in a bank. The Cristec isolator (15) is connected to the housebank (12V/660Ah) and the chargers (not shown)

I checked the MAX POWER CT125 thruster manual. It has a number but only refers to it as a relay

Just for reference I have added the spec pages for the boat - a JEANNEAU YACHT 53. 12V house bank and 24V thruster...

Steen
Merci, mon ami. Maintenant je comprends. C'est bien francais, donc c'est un peu compliqué. At least for we lesser mortals :-)

The "isolator" is just an automatic battery switch, supposed to pass current to the weaker batteries first and to maintain all those connected. Good.

God only knows what the controller is for. It looks like it might somehow take inputs from the four 12V thruster batteries, and from the house battery bank via the isolator, and magically come up with the 24VDC needed for the thruster.

As you say, why keep it simple when you can come up with such a plan?

Maybe someone else can decipher this one. Sorry, I can't.

Bill
btrayfors is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 Battery banks and 1 MPPT charge controller? MBLittle Electrical: Batteries, Generators & Solar 32 17-09-2017 09:04
Battery Isolator with Battery Drain Bensigler Electrical: Batteries, Generators & Solar 83 28-11-2011 12:50
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47
What Is the Best Way to Charge Two Battery Banks? bobfnbw Electrical: Batteries, Generators & Solar 11 20-11-2009 03:40

Advertise Here


All times are GMT -7. The time now is 00:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.