Main breaker popping at 10A

Good day all,

Over the past few months, I've noticed that the 30A main shore power (125V) breaker on my Nauticat 40 will pop when I am running about 10A worth of appliances. For example, if I run one space heater at 1500W it will pop, but if I run 500W and 650W heaters it will make it through the night.

I initially suspected a faulty breaker, but I noted that it gets warm to the touch when it pops. This makes me think that, as a thermal breaker should, it is behaving itself. Of note, my voltmeter that is built into the system shows 125V.

I'm reasonably familiar with 125V systems as I installed the 125V systems on my previous 2 boats. But I guess since they were newly installed systems (by me) I never had to troubleshoot any problems such as I'm having now.

Any ideas or suggestions on how I can pin down this issue would be appreciated.

Thanks!
Korvessa
Korvessa is offline   Reply With Quote
Old 19-02-2018, 08:52   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Main breaker popping at 10A

Either bad wiring at breaker (lose connections getting hot) Or bad breaker. Look at the back.

Measure actual current to confirm draw.
smac999 is offline   Reply With Quote
Old 19-02-2018, 09:15   #3
Registered User
 
pesarsten's Avatar

Join Date: Jan 2012
Location: St Pete
Boat: Sabre 34 , Island Packet 38
Posts: 738
Re: Main breaker popping at 10A

If the breaker is getting warm , replace it. Breakers fail with age and corrosion. If you want a cheap way to confirm that it's the breaker, back feed your panel through one of the other breakers preferably a 20 amp one. But as cheap as they are, just replace it.
__________________
All that is necessary for the triumph of evil is that good men do nothing. Edmund Burke
pesarsten is offline   Reply With Quote
Old 19-02-2018, 09:16   #4
Registered User
 
Korvessa's Avatar

Join Date: Apr 2016
Location: Anacortes WA, USA
Boat: Nauticat 40 (1985)
Posts: 38
Re: Main breaker popping at 10A

Quote:
Originally Posted by smac999 View Post

Measure actual current to confirm draw.
Thanks for the suggestions. Your suggestion of measuring actual current makes me realize that my voltmeter isn't up to the job. Lucky for me I like buying tools...

Do you have a suggestion for a good meter that measures amps?

Korvessa
Korvessa is offline   Reply With Quote
Old 19-02-2018, 09:37   #5
Registered User

Join Date: May 2008
Posts: 3,536
Re: Main breaker popping at 10A

If you have an ammeter up-stream from the breaker just watch that while you cycle the breaker.

But I agree with the others. I've had four breakers die on my boat over the years. Each time it worked OK but popped at a lower amperage than it used to. It's easier to diagnose the problem by first replacing the breaker. If that doesn't fix it, then get out the multimeter.
CarlF is offline   Reply With Quote
Old 19-02-2018, 09:48   #6
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Main breaker popping at 10A

The Fluke
Clamp On Ammeters are great. I have a model 337
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 19-02-2018, 09:55   #7
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,524
Re: Main breaker popping at 10A

Running heaters, even within spec, often fries things gradually. When I lived aboard in the PNW, I had to replace the 30 amp shore power cord every year due to the receptacle just burning up slowly. I didnt have a 1500 watt heater, but more like 1100/1200 max. Often run on the lower setting. The inside of your breaker may be pretty brown too!
... and yes to breakers failing now and then even on the 12V side...
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 19-02-2018, 23:35   #8
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Main breaker popping at 10A

Quote:
Originally Posted by Korvessa View Post
Thanks for the suggestions. Your suggestion of measuring actual current makes me realize that my voltmeter isn't up to the job. Lucky for me I like buying tools...

Do you have a suggestion for a good meter that measures amps?

Korvessa
get a clamp meter that can measure both AC and DC current.

Fluke is really good. cheaper stuff likely work just fine too.
smac999 is offline   Reply With Quote
Old 20-02-2018, 00:17   #9
Senior Cruiser

Cruisers Forum Supporter

Join Date: May 2013
Location: Oregon to Alaska
Boat: Wheeler Shipyard 83' ex USCG
Posts: 3,514
Re: Main breaker popping at 10A

Breakers trip when an internal metal piece distorts because too much amperage is passing thru. Over time the distorting metal becomes fatigued and trips at a reduced amperage.
Lepke is offline   Reply With Quote
Old 20-02-2018, 08:09   #10
Registered User

Join Date: Jun 2017
Location: Clearwater, FL
Boat: S2 11.0a
Posts: 80
Re: Main breaker popping at 10A

I had an electrician explain that a circuit breaker should be replaced if it ever trips to protect a circuit - it's a "controlled explosion" and is really meant for only a single use? Turning it on and off as a switch is also not desirable for a typical breaker. Maybe another electrician can clarify this for us all?
RobinScurr is offline   Reply With Quote
Old 20-02-2018, 08:15   #11
Registered User
 
Korvessa's Avatar

Join Date: Apr 2016
Location: Anacortes WA, USA
Boat: Nauticat 40 (1985)
Posts: 38
Re: Main breaker popping at 10A

Quote:
Originally Posted by RobinScurr View Post
I had an electrician explain that a circuit breaker should be replaced if it ever trips to protect a circuit - it's a "controlled explosion" and is really meant for only a single use? Turning it on and off as a switch is also not desirable for a typical breaker. Maybe another electrician can clarify this for us all?
I'm suspicious of that advice. If a breaker is a single use item, then it is inferior in every way to a fuse.

Korvessa
Korvessa is offline   Reply With Quote
Old 20-02-2018, 08:27   #12
Registered User
 
Boatyarddog's Avatar

Join Date: Nov 2014
Location: Olympia, Washington
Boat: 1979 Mariner Ketch 32-Hull 202
Posts: 2,124
Images: 2
Re: Main breaker popping at 10A

Quote:
Originally Posted by pesarsten View Post
If the breaker is getting warm , replace it. Breakers fail with age and corrosion. If you want a cheap way to confirm that it's the breaker, back feed your panel through one of the other breakers preferably a 20 amp one. But as cheap as they are, just replace it.
Not sure if you are plugging into the same outlet each time.
Corrosion internally at the outlet, will cause resistance, or in the breaker it self.
At the screw attachments on the plug outlet.
A lot of outlets are push in the bare end wires for connections, not correct.
AC wiring needs a solid connection in marine application, hook connectors or ring to the screw ends.
Solid crimps on the wires, heat shrink to the connector ends. Older vessels, and most mass produced, boat manufacturers do not spend the time to do this step.
There are plug in amperage draw measuring devices available a Home Depot, Lowes, electrical stores.
Check each plug, for excessive amp draw.
Cheers
SV Cloud Duster
Boatyarddog is offline   Reply With Quote
Old 20-02-2018, 08:51   #13
Registered User
 
uncle stinkybob's Avatar

Join Date: Mar 2016
Posts: 697
Re: Main breaker popping at 10A

Quote:
Originally Posted by Korvessa View Post
Good day all,

Over the past few months, I've noticed that the 30A main shore power (125V) breaker on my Nauticat 40 will pop when I am running about 10A worth of appliances. For example, if I run one space heater at 1500W it will pop, but if I run 500W and 650W heaters it will make it through the night.

I initially suspected a faulty breaker, but I noted that it gets warm to the touch when it pops. This makes me think that, as a thermal breaker should, it is behaving itself. Of note, my voltmeter that is built into the system shows 125V.

I'm reasonably familiar with 125V systems as I installed the 125V systems on my previous 2 boats. But I guess since they were newly installed systems (by me) I never had to troubleshoot any problems such as I'm having now.

Any ideas or suggestions on how I can pin down this issue would be appreciated.

Thanks!
Korvessa
I had a similar issue. I found a corroded splice in the main triplex wiring from shore power plug to a/c breaker panel. Not sure why they spliced but it was done terribly with crappy butt connectors and electrical tape. Check all connections for corrosion and loose screws, anything that will induce resistance. When diagnosing electrics I start with in this order, Source-Path-Load. Good luck!
uncle stinkybob is offline   Reply With Quote
Old 20-02-2018, 09:20   #14
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Main breaker popping at 10A

I doubt you meter isn't up to the task. Replace the breaker. If you had a bad connection to make a 30A break trip at around 10A you would have already burnt to the waterline.
Cadence is offline   Reply With Quote
Old 20-02-2018, 09:42   #15
Registered User

Join Date: Oct 2007
Location: Charleston, SC
Boat: Stevens 47
Posts: 199
Re: Main breaker popping at 10A

I agree with previous posters that the likely problem is a bad breaker. They don't last forever.

As to potential bad connections, an easy test is to load your system whilst monitoring the voltage. Monitoring the voltage at the panel will tell you if you have a bad connection between the pedestal and the panel, say at the shore power inlet. Measuring at the load will tell you if you have a bad connection between the panel and the load.

Don't be surprised or worried if you have some voltage drop, say 5 or even 10 volts, but if you voltage is dropping into the double digits, you've got a problem. If you're seeing anything less than 100 volts, look for something hot.
sainted is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Volvo Penta 10A Cooling Problem Richard-R Engines and Propulsion Systems 4 07-07-2016 12:30
10a Dual Battery Solar Controller? EagleBay Electrical: Batteries, Generators & Solar 2 19-02-2014 01:07
Starter exciter input drawing >10A, normal? jbrownson Electrical: Batteries, Generators & Solar 32 20-05-2013 13:49
My 20 Amp Breaker Keeps Popping and Shutting Down Genset Turtlep Electrical: Batteries, Generators & Solar 4 26-07-2012 13:23

Advertise Here


All times are GMT -7. The time now is 18:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.