Old 24-04-2014, 02:31   #1
Registered User

Join Date: Jun 2011
Location: South Pacific
Boat: Outremer 55 Light
Posts: 153
Isotherm Freezer - Run, Stop, Run, Stop...

I have a small Isotherm freezer on my boat (normally draws about 3A @ 12V). I started it yesterday for the first time in about 9 months and it seemed to run ok until today. Now the compressor keeps stopping.

When I turn it on, the compressor starts, the pipe to the freezer box starts to cool but after about a minute the compressor stops. After a minute of 2, the compressor starts again and this cycle repeats again and again. The thermostat is constantly on so not causing this. I'm guessing that the compressor has some sort of overload protection that trips then resets and restarts the compressor, then trips again.

Could low gas cause this?
Cruisin Cat is offline   Reply With Quote
Old 24-04-2014, 03:30   #2
Registered User
 
Cavalier's Avatar

Join Date: Dec 2010
Location: Houston, TX
Boat: Beneteau 461 47'
Posts: 927
Images: 1
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
Originally Posted by Cruisin Cat View Post
I have a small Isotherm freezer on my boat (normally draws about 3A @ 12V). I started it yesterday for the first time in about 9 months and it seemed to run ok until today. Now the compressor keeps stopping.

When I turn it on, the compressor starts, the pipe to the freezer box starts to cool but after about a minute the compressor stops. After a minute of 2, the compressor starts again and this cycle repeats again and again. The thermostat is constantly on so not causing this. I'm guessing that the compressor has some sort of overload protection that trips then resets and restarts the compressor, then trips again.

Could low gas cause this?
Have you tried putting a multimeter across the power terminals of the compressor itself? That way you could determine whether the compressor is receiving power all the time (and it's a thermal cut-out issue) or whether the controller board is intermittently providing power to the compressor.

Going further, a leak in the system will cause the compressor to run harder than design. I typical sign of a compressor running with non-optimized differential pressure (or back-leak) is that the compressor will run at maximum rated current draw continually.
__________________
"By day the hot sun fermented us; and we were dizzied by the beating wind. At night we were stained by dew, and shamed into pettiness by the innumerable silences of stars."
Cavalier is offline   Reply With Quote
Old 24-04-2014, 04:00   #3
Registered User
 
wingless's Avatar

Join Date: Aug 2013
Location: Florida
Boat: 2000 Searay 380 Sundancer
Posts: 1,087
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
Originally Posted by Cavalier View Post
Have you tried putting a multimeter across the power terminals of the compressor itself? That way you could determine whether the compressor is receiving power all the time (and it's a thermal cut-out issue) or whether the controller board is intermittently providing power to the compressor.
+1

It might be the low-voltage cutoff causing the cycling.

If the voltage at the terminals is low before the compressor is running, from the house batteries being at a lower charge, with the compressor off, the voltage sense circuit could be happy, permitting the compressor to start. Then when the compressor is running, the normal voltage drop makes the sense circuit unhappy, causing the compressor to stop.

Another possible problem could be degraded wiring, causing good voltage w/ no current, but anacceptable voltage once current is flowing, making the sense circuit unhappy once the compressor starts. If the voltage at the terminal drops by more than a volt, then try a temporary direct run of 10 AWG, two-conductor, fused, to a solid supply or the fully-charged battery to check operation.
__________________
2000 SeaRay 380 Sundancer Mercruiser
454 MAG MPI Horizon 380hp / Westerbeke 7.0KW BCGB
many cool mods
wingless is offline   Reply With Quote
Old 24-04-2014, 04:45   #4
Registered User

Join Date: Jun 2011
Location: South Pacific
Boat: Outremer 55 Light
Posts: 153
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
Originally Posted by Cavalier View Post
Have you tried putting a multimeter across the power terminals of the compressor itself? That way you could determine whether the compressor is receiving power all the time (and it's a thermal cut-out issue) or whether the controller board is intermittently providing power to the compressor.

Going further, a leak in the system will cause the compressor to run harder than design. I typical sign of a compressor running with non-optimized differential pressure (or back-leak) is that the compressor will run at maximum rated current draw continually.
The electrical connection between the compressor control board and compressor is internal and not available to test. There is power connected to the compressor control board and terminals for the thermostat connection.

If the gas has leaked out of the system, will that cause the compressor to overload and trip?
Cruisin Cat is offline   Reply With Quote
Old 24-04-2014, 04:48   #5
Registered User

Join Date: Jun 2011
Location: South Pacific
Boat: Outremer 55 Light
Posts: 153
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
Originally Posted by wingless View Post
+1

It might be the low-voltage cutoff causing the cycling.

If the voltage at the terminals is low before the compressor is running, from the house batteries being at a lower charge, with the compressor off, the voltage sense circuit could be happy, permitting the compressor to start. Then when the compressor is running, the normal voltage drop makes the sense circuit unhappy, causing the compressor to stop.

Another possible problem could be degraded wiring, causing good voltage w/ no current, but anacceptable voltage once current is flowing, making the sense circuit unhappy once the compressor starts. If the voltage at the terminal drops by more than a volt, then try a temporary direct run of 10 AWG, two-conductor, fused, to a solid supply or the fully-charged battery to check operation.
The voltage supply at the compressor control board terminal with the compressor running is 12.35V so I don't think that's causing the problem
Cruisin Cat is offline   Reply With Quote
Old 24-04-2014, 14:20   #6
Registered User
 
katsumi's Avatar

Join Date: Feb 2011
Location: Sydney,NSW, Australia
Boat: Lagoon 400
Posts: 151
Re: Isotherm Freezer - Run, Stop, Run, Stop...

We also have an Isotherm fridge which is doing the same thing, it has no problem with cooling, the small freezer section need defrosting every couple of weeks (been like that since new) We would be interested if you find a cause to the compressor cycling on and off.
__________________
Dream as if you'll live forever. Live as if you'll die today.
- James Dean -
katsumi is offline   Reply With Quote
Old 24-04-2014, 16:53   #7
Registered User
 
capt-couillon's Avatar

Join Date: Mar 2013
Location: Onboard (Boot Key Harbor)
Boat: Cornado 25
Posts: 493
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
If the gas has leaked out of the system, will that cause the compressor to overload and trip?
Inadequate refrigerant along with several other conditions can cause an improper differential between the high and low sides of the compressor. This causes the compressor to have to work harder than designed, and it overheats causing the thermal overload switch to kick out until it cools down.

This sounds like why your system is short cycling. Best bet at this point is to get a refrigeration tech onboard to determine what is causing the improper differential pressure. Not always easy to do in the south pacific... but without a set of gauges and the knowledge to use them, you are pretty well stuck.

Wish I could be more encouraging. One of the reasons I don't have refrigeration.
capt-couillon is offline   Reply With Quote
Old 24-04-2014, 17:08   #8
Registered User

Join Date: Jun 2011
Location: South Pacific
Boat: Outremer 55 Light
Posts: 153
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Quote:
Originally Posted by capt-couillon View Post
Inadequate refrigerant along with several other conditions can cause an improper differential between the high and low sides of the compressor. This causes the compressor to have to work harder than designed, and it overheats causing the thermal overload switch to kick out until it cools down.

This sounds like why your system is short cycling. Best bet at this point is to get a refrigeration tech onboard to determine what is causing the improper differential pressure. Not always easy to do in the south pacific... but without a set of gauges and the knowledge to use them, you are pretty well stuck.

Wish I could be more encouraging. One of the reasons I don't have refrigeration.
Thanks, that's what I guessed even though I don't know much about refrigeration.
Cruisin Cat is offline   Reply With Quote
Old 24-04-2014, 18:06   #9
Registered User
 
capt-couillon's Avatar

Join Date: Mar 2013
Location: Onboard (Boot Key Harbor)
Boat: Cornado 25
Posts: 493
Re: Isotherm Freezer - Run, Stop, Run, Stop...

Hate it when a good guess is an unfortunate situation...

Soldier on..
capt-couillon is offline   Reply With Quote
Reply

Tags
freezer, isotherm


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Isotherm 5801 Cycling?? Anyone have an Isotherm? ssullivan Plumbing Systems and Fixtures 8 16-02-2013 07:10
For Sale: Indel Isotherm Freezer Box/Strainer $900 Conchfritterz Classifieds Archive 0 20-06-2012 13:43
What islands to stop at and what islands not to stop at that is the question?Carib- Ram Atlantic & the Caribbean 11 21-05-2012 17:57
For Sale: Indel Isotherm Freezer Box - Compressor / Groco Strainer 1.87cf Water Cooled $900 Conchfritterz Classifieds Archive 1 12-05-2012 23:24
For Sale: Indel Isotherm Freezer Box - Compressor / Strainer 1.87cf Air Cooled $700 Conchfritterz Classifieds Archive 3 13-01-2012 21:02

Advertise Here


All times are GMT -7. The time now is 09:39.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.