Cruisers Forum
 

Go Back   Cruisers & Sailing Forums > Engineering & Systems > Electrical: Batteries, Generators & Solar
Cruiser Wiki Click Here to Login
Register Vendors FAQ Community Calendar Today's Posts Log in

Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 26-07-2012, 06:36   #16
Registered User

Join Date: Mar 2006
Posts: 1,594
Re: Help! Why am I reading current on my water strainer.

Could be your neighbors are putting a current in the water that you are picking up through your ground.

Also make sure ALL DOCK recpt are wired correctly... No swap of HOT /NEUTRAL..
__________________
Randy

Cape Dory 25D Seraph
rtbates is offline   Reply With Quote
Old 26-07-2012, 06:51   #17
Registered User
 
bruce smith's Avatar

Join Date: Jul 2008
Location: puget sound/ caribbean
Boat: never wrecked a boat while awake or sober
Posts: 331
Re: Help! Why am I reading current on my water strainer.

The most learned and wisest cruisers do not have 'frigeration on a boat!
bruce smith is offline   Reply With Quote
Old 26-07-2012, 06:57   #18
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Help! Why am I reading current on my water strainer.

This is truly nothing to screw around with...as Maine Sail said...and you concurred...hire a pro and do it ASAP.

One piece of info strikes me as odd:

Quote:
There are just two main breakers one 40 amp one 30 amp, they both have to be on to get 220.
Do you have two 30A/120VAC shore power inlets or one 50A/250VAC shore power inlet?

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 26-07-2012, 06:57   #19
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
Haha, well when I got the boat and it had four...yes four, AC units I figured fixing the refer was only keeping the true sprit of the boat intact.
I am not picking up stay current from other boats as it only happens when I am connected to shore power with the main breakers closed.
DSDman is offline   Reply With Quote
Old 26-07-2012, 06:59   #20
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
just one 50 amp/220
DSDman is offline   Reply With Quote
Old 26-07-2012, 07:48   #21
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Help! Why am I reading current on my water strainer.

Having two CB to protect a 50/250 circuit is electrically incorrect, and not in accordance with the ABYC Standards. Doesn't really matter if "that's the way it has always been", it is not correct.

You should have a double pole 50A circuit breaker that breaks both L1 and L2 on overload. You could go a bit overboard and have a three pole circuit breaker that breaks L1, L2 and N on overload but that is not necessary.

I have not seen a panelboard wired this way and it leads me to believe that at one time this vessel was served by 2 x 30A/120VAC and was "converted" to 50A/250VAC without understanding all of the ramifications of said "conversion".

BTW, the quickest way to check for an improper neutral to safety ground bond on board is to unplug shore power and use your DMM to check for continuity at any 120VAC receptacle between N (the wide receptacle slot) and G. Anything < 25,000Ω is a failure and must be corrected.

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 26-07-2012, 07:53   #22
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
Thanks Charlie,
I think you may be right. The boat was originally a 110 boat and it does seem to make sense that may have happened in the past. Time to call in the pro's I guess.
DSDman is offline   Reply With Quote
Old 26-07-2012, 08:10   #23
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,469
Images: 5
Re: Help! Why am I reading current on my water strainer.

Quote:
Originally Posted by DSDman View Post
I am not picking up stay current from other boats as it only happens when I am connected to shore power with the main breakers closed.
Not necessarily...When you close your breaker not only do you power up but you tie into the rest of the electrical grid on the dock.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 26-07-2012, 08:17   #24
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
After I said that I went back and reread some of the post and that makes sense, basically I would be completing the circuit back to the dock from some other boat. I get it now.
DSDman is offline   Reply With Quote
Old 26-07-2012, 08:32   #25
Registered User

Join Date: Sep 2010
Posts: 793
Another danger that your breaker arrangement poses is the possibility of both 120v legs being energized even though you only have one breaker closed. If there is a 240v appliance turned on, say a hot water heater, it will bridge power between the two 120v legs. It could create quite the surprise.
twistedtree is offline   Reply With Quote
Old 26-07-2012, 08:34   #26
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Help! Why am I reading current on my water strainer.

Quote:
Not necessarily...When you close your breaker not only do you power up but you tie into the rest of the electrical grid on the dock.
There is a fine, but important point that has to be made about this statement. It is true as far as it goes. However, the safety ground wire, if the shore and the ship's systems are wired correctly, are always connected whenever the vessel is plugged in, regardless of the position of the shore power breakers (on board and ashore). Thus, the ship's DC system and the bonding system (such as it is on the subject boat) is always electrically tied to the safety ground system ashore, again, regardless of the position of the shore power breakers.

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 26-07-2012, 11:18   #27
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,469
Images: 5
Re: Help! Why am I reading current on my water strainer.

Personally, what I would do is (with the Harbor Masters permission) is unplug neighbor's dock cords around you to see if it effects the meter on your boat. Have someone on the meter in your boat reporting back to you. Don't just turn the breaker off, but unplug the cord completely.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 26-07-2012, 11:46   #28
Registered User

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40 (sold). Still have a Hobie 20
Posts: 2,945
Images: 7
Re: Help! Why am I reading current on my water strainer.

Quote:
Originally Posted by CharlieJ View Post
There is a fine, but important point that has to be made about this statement. It is true as far as it goes. However, the safety ground wire, if the shore and the ship's systems are wired correctly, are always connected whenever the vessel is plugged in, regardless of the position of the shore power breakers (on board and ashore). Thus, the ship's DC system and the bonding system (such as it is on the subject boat) is always electrically tied to the safety ground system ashore, again, regardless of the position of the shore power breakers.

Charlie
Not entirely true with a galvanic isolator as it isn't connected until a fault occurs, and never true if an isolation transformer is installed.

John
cal40john is offline   Reply With Quote
Old 26-07-2012, 12:40   #29
Registered User
 
DSDman's Avatar

Join Date: Nov 2010
Location: Chicopee, MA
Posts: 606
Images: 16
So would an easy test for stray current be to put a muti meter in the ground on the shore power plug and stick the other end in the water?
DSDman is offline   Reply With Quote
Old 26-07-2012, 12:47   #30
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,535
Re: Help! Why am I reading current on my water strainer.

Quote:
Not entirely true with a galvanic isolator as it isn't connected until a fault occurs, and never true if an isolation transformer is installed.
Of course!!

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
current, water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 21:33.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.