Old 09-05-2023, 16:35   #16
Registered User

Join Date: May 2023
Location: Hampton, VA
Boat: Leopard 40, 40ft
Posts: 9
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by NorthCoastJoe View Post
Have you looked at the back of your shore power connector?
Yes, no burns or melted plastic. All insulation looks good visually. Put SmartConnectors on a few years ago just after new set of cables.
2Cents is offline   Reply With Quote
Old 09-05-2023, 16:40   #17
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Tayana 37
Posts: 996
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by 2Cents View Post
Yes, no burns or melted plastic. All insulation looks good visually. Put SmartConnectors on a few years ago just after new set of cables.
Any chance you could have cross wired neutral and ground either on the cable on on the smartplug inlet?

As someone else suggested I would start from the pedestal inward.
Statistical is offline   Reply With Quote
Old 15-05-2023, 07:58   #18
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 529
Re: Weird Nuisance Breaker Trips

It could also be a defective breaker.

I had an issue with an ECLI (leakage breaker at the box) in a new office I was building out. The breaker would trip randomly for no reason.

The electrician explained that the breakers get flaky with age, especially if the capacitors which are part of the leakage measuring circuitry inside start to get weak, it makes them overly sensitive.

Changing the ECLI breaker cured the issue.

Maybe the marina could check this out for you...

Cheers
sinnerman is online now   Reply With Quote
Old 15-05-2023, 09:50   #19
Registered User

Join Date: Oct 2020
Posts: 21
Re: Weird Nuisance Breaker Trips

Some euro and other boats that are made in 220V markets continue to ship to 120V markets with breakers rated for 1/2 the amperage needed in the 120V versus 220V environment. On our boat, things worked pretty well, even for years. But eventually after a pattern of mysterious tripping of breakers, we ultimately replaced all of the mis-rated breakers (on the boat) and have never had a problem since, at any marina, home or away.
justinfinity is offline   Reply With Quote
Old 15-05-2023, 12:22   #20
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 529
Re: Weird Nuisance Breaker Trips

I am not sure if anyone else posted this, but it is a good explanation of AC leakage on a boat.

https://panbo.com/gfci-and-elci-brea...their-warning/

Interesting notes on Inverters:

""..The presence of the inverter immediately attracted my suspicion that it was causing the issues. Inverters and reverse Y-adapters are the most frequent causes of ELCI nuisance tripping. A look around the boat revealed there were no breakers to isolate the inverter, so to test this theory I disconnected the inverter from the back of the AC panel. With inverter removed the boat was able to draw power from the marina without issue. Reconnecting the inverter immediately tripped the ELCI..."

".. 31.6.7.1.3 – The inverter/charger output neutral shall be grounded at the inverter/charger only when the device is the AC power source..."

"...So this means the inverter has to create a tie between neutral and ground when power is coming out of the inverter and break that tie when it’s coming from shore power. That’s because your boat isn’t a sub-panel any longer as the inverter or generator is the primary source of power.

Many inverters do this using relays, including the one onboard this boat. When there’s shore power coming into the inverter the relays are energized and that causes them to break the tie between neutral and ground. But, before those relays could receive power and break the tie the shore power ELCI breaker in the pedestal was seeing a fault condition (because of the tie between neutral and ground on the boat) and tripping the breaker..."


Cheers...
sinnerman is online now   Reply With Quote
Old 15-05-2023, 14:03   #21
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 529
Re: Weird Nuisance Breaker Trips

Adding some verbiage to my previous post above, per the ref. article, there is a 110 vac "normally closed" relay located inside the inverter. The relay receives its power from Shore Power .

The relay's function is to physically connect the boat's 110 volt AC neutral and AC ground (green wire) together when the inverter is supplying 120vac to the boat.

Being a "normally closed" relay, this means when everything is OFF, the contacts are closed (fail safe position), and the two wires are connected together.

The contacts only "open" and break this connection when the relay is energized when Shore Power is connected. (the actual purpose of the relay...)

Unfortunately, since the Shore Power pedestal-mounted ELCI is electronic, and the relay in the inverter is mechanical, before the mechanical relay has a chance to actuate, the faster-responding pedestal mounted ELCI has already sensed an improper neutral-to-ground connection and "tripped".

To solve this, the electrician installed a double-pole breaker on the AC output of the inverter. This (double pole) breaker makes/breaks both the 120 vac "hot" and 120vac "neutral" connections from the inverter to the 120vac bus.

Therefore, with the breaker "open" , the closed relay is "isolated" from the 120 vac system and no ELCI trip will occur.

The breaker would normally remain open at all times. It would only be closed when Shore Power is disconnected and the inverter is actually supplying the boat's 120vac power.

Actually, IMHO this is a much better way to wire the system. There needs to be a physical isolation of the inverter from the 120 vac bus unless the inverter is actually supplying power. If the inverter had an internal short, it could take down the entire 120vac system without having a way to isolate it...


Long winded, I apologize.

If I said anything incorrect, here please feel free to comment.

Cheers.
sinnerman is online now   Reply With Quote
Old 15-05-2023, 14:22   #22
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,003
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by sinnerman View Post
Adding some verbiage to my previous post above, per the ref. article, there is a 110 vac "normally closed" relay located inside the inverter. The relay receives its power from Shore Power .

The relay's function is to physically connect the boat's 110 volt AC neutral and AC ground (green wire) together when the inverter is supplying 120vac to the boat.

Being a "normally closed" relay, this means when everything is OFF, the contacts are closed (fail safe position), and the two wires are connected together.

The contacts only "open" and break this connection when the relay is energized when Shore Power is connected. (the actual purpose of the relay...)

Unfortunately, since the Shore Power pedestal-mounted ELCI is electronic, and the relay in the inverter is mechanical, before the mechanical relay has a chance to actuate, the faster-responding pedestal mounted ELCI has already sensed an improper neutral-to-ground connection and "tripped".

To solve this, the electrician installed a double-pole breaker on the AC output of the inverter. This (double pole) breaker makes/breaks both the 120 vac "hot" and 120vac "neutral" connections from the inverter to the 120vac bus.

Therefore, with the breaker "open" , the closed relay is "isolated" from the 120 vac system and no ELCI trip will occur.

The breaker would normally remain open at all times. It would only be closed when Shore Power is disconnected and the inverter is actually supplying the boat's 120vac power.

Actually, IMHO this is a much better way to wire the system. There needs to be a physical isolation of the inverter from the 120 vac bus unless the inverter is actually supplying power. If the inverter had an internal short, it could take down the entire 120vac system without having a way to isolate it...


Long winded, I apologize.

If I said anything incorrect, here please feel free to comment.

Cheers.
None of that trouble exists with an isolation transformer (hint…)
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 15-05-2023, 15:01   #23
Registered User
 
sailingharry's Avatar

Join Date: Jun 2009
Location: Annapolis, MD
Boat: Sabre 34-1 (sold) and Saga 43
Posts: 2,320
Re: Weird Nuisance Breaker Trips

I skimmed through the responses, didn't see the one I was looking for. Sorry if this is a duplicate.

I suffered with this when I replaced my inverter and modified the wiring to the typical system where shore power goes through the inverter. (Under the original installation, the inverter was either connected as a charger, or as an inverter, but never both, with two interlocked breakers on the main panel. As a result, it was never connected to shore power while also feeding ships)

It turns out that on many boats, including mine, there is a single neutral bus . This causes problems with an inverter. I split my bus in two and solved the problem. The first neutral bus consists of nothing but the shore power wire and the lead to the inverter (but would also include any loads not served by the inverter). The second neutral bus is everything downstream of the inverter.
sailingharry is offline   Reply With Quote
Old 15-05-2023, 15:58   #24
Registered User

Join Date: Nov 2011
Location: Southern California
Boat: HYLAS Sloop 46
Posts: 7
Re: Weird Nuisance Breaker Trips

I had a problem similar to this on my Hylas 46 a few years ago. After replacing my charger/inverter at considerable cost and effort, I discovered that the problem was in a GFCI socket in the stern head. Replaced that receptical and the grounding problem was resolved.
seasilk is offline   Reply With Quote
Old 16-05-2023, 08:06   #25
Registered User

Join Date: May 2010
Location: Florida
Boat: Leopard 4200 Catamaran
Posts: 13
Re: Weird Nuisance Breaker Trips

On two different boats, I have experienced these gremlins . In both cases, a competent electrician came aboard and assured me the problem was NOT the hot water heater element. In both cases, in desperation, I finally removed the hot water heater connections, and everything magically started working as expected! Of course, replacing the element fixed the problem. One boat was bonded, one was not. Since, on two more boats, I have simply replaced the heater element at the first sign of gremlins! I know, it’s wired, but so are gremlins!
larrymac is offline   Reply With Quote
Old 16-05-2023, 08:31   #26
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,334
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by larrymac View Post
I finally removed the hot water heater connections, and everything magically started working as expected! Of course, replacing the element fixed the problem. One boat was bonded, one was not.
Not unusual, water heater elements are high on the list of devices that seemingly have a high propensity to leak electrons.
When chasing down electrical issues disconnecting all the wiring to the heater, (not just turning it off,) is a good first step.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 16-05-2023, 12:19   #27
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,003
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by Bowdrie View Post
Not unusual, water heater elements are high on the list of devices that seemingly have a high propensity to leak electrons.
When chasing down electrical issues disconnecting all the wiring to the heater, (not just turning it off,) is a good first step.
I use an outlet to plug the water heater into
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 16-05-2023, 12:23   #28
Registered User

Join Date: May 2023
Location: Hampton, VA
Boat: Leopard 40, 40ft
Posts: 9
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by sinnerman View Post
It could also be a defective breaker.

I had an issue with an ECLI (leakage breaker at the box) in a new office I was building out. The breaker would trip randomly for no reason.

The electrician explained that the breakers get flaky with age, especially if the capacitors which are part of the leakage measuring circuitry inside start to get weak, it makes them overly sensitive.

Changing the ECLI breaker cured the issue.

Maybe the marina could check this out for you...

Cheers
Being they are all pretty new to us around here anyway, I would say it's not the ECLI. I had a bad one in my house as well once. Thanks though, appreciate any help and ideas
2Cents is offline   Reply With Quote
Old 16-05-2023, 12:42   #29
Registered User

Join Date: May 2023
Location: Hampton, VA
Boat: Leopard 40, 40ft
Posts: 9
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by larrymac View Post
On two different boats, I have experienced these gremlins . In both cases, a competent electrician came aboard and assured me the problem was NOT the hot water heater element. In both cases, in desperation, I finally removed the hot water heater connections, and everything magically started working as expected! Of course, replacing the element fixed the problem. One boat was bonded, one was not. Since, on two more boats, I have simply replaced the heater element at the first sign of gremlins! I know, it’s wired, but so are gremlins!
I have thought about this as well, but I have two, two pole shore power breakers, and separate breakers for each water heater. We are tripping the pedestal right when the shore power breakers on boat are closed, no power to any other load. Was this the case with your water heaters as well, breakers to them open, but tripping the GFI?
2Cents is offline   Reply With Quote
Old 16-05-2023, 12:48   #30
Registered User

Join Date: May 2023
Location: Hampton, VA
Boat: Leopard 40, 40ft
Posts: 9
Re: Weird Nuisance Breaker Trips

Quote:
Originally Posted by s/v Jedi View Post
None of that trouble exists with an isolation transformer (hint…)
I don't disagree, but I am a right way all the time kinda guy, so part of me says it's been this way for 15 years, so the new shore equipment is just too sensitive lets put in two shiny new isolation transformers, problems solved.

The other part tells me there are numerous boats of similar age around us, that don't have this issue, so somewhere there is a problem that needs diagnosing, not hiding.

The idea of completely isolating boat from shore power using a transformer sounds like a phenomenally smart thing to do in general though.
2Cents is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microsoft Streets & Trips w/GPS marlborosounds General Sailing Forum 15 10-08-2009 05:46
Experienced Crew for Daysails/short trips? SW FL Sailingdiver Crew Archives 4 26-02-2009 06:04
Battery Charger Trips GFIC with Gen power The Mons Electrical: Batteries, Generators & Solar 2 04-01-2008 12:10
Freedom 25 Trips Earth leakage breaker toewsrus Electrical: Batteries, Generators & Solar 9 12-08-2007 05:35
Multiple Trips to the Bahamas within Twelve Months freedbill Rules of the Road, Regulations & Red Tape 15 28-07-2006 09:01

Advertise Here


All times are GMT -7. The time now is 08:32.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.