Kohler 6EKOD shutdown help

Hello all,

I have a Kohler 6ekod generator with 650ish hours. I recently had it serviced and after running the generator for about 4 hours after service I am now getting a RunRelCoil shutdown. I have not tried to restart it yet as I can not find any information in the manual relating to this fault.

Has anyone seen this before??

Thanks
fjohnston is offline   Reply With Quote
Old 27-01-2018, 05:07   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,530
Images: 241
Re: Kohler 6EKOD shutdown help

FWIW:
RunRelCoil Shutdwn - Run Relay Coil Overload - Excessive current on the run (70) line. Check for shorted relays or shorted wires.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 29-03-2018, 12:03   #3
Registered User

Join Date: Oct 2011
Location: Canada
Boat: CT 56
Posts: 545
Images: 3
Send a message via Skype™ to undercutter
Re: Kohler 6EKOD shutdown help

Quote:
Originally Posted by GordMay View Post
FWIW:
RunRelCoil Shutdwn - Run Relay Coil Overload - Excessive current on the run (70) line. Check for shorted relays or shorted wires.
Good thing we have you around Gord.

I recently experienced the same fault code (runrelcoil) on my genset and the Kohler Service group had no clue and had never seen this fault code before. Google provided the link to this thread which got me thinking in the right direction.

There are no relays in this system as they have been replaced by a solid state board (relay interface board) but your premise was exactly correct in that there was too much current draw on the line. This narrowed it down to either the fuel solenoid or the fuel pump. As it turned out it was the fuel pump drawing too much power to run and I replaced it with a spare which I had on board.

Thanks again Gord as if you hadn't replied to this thread I would probably still be looking for the problem. Hopefully this additional information will help the next guy and I made sure to let the support group at Kohler Brisbane know as well.
undercutter is offline   Reply With Quote
Old 31-07-2023, 02:50   #4
Registered User

Join Date: Jul 2010
Location: Sausalito/ Med
Boat: 1998 Nauticat 515
Posts: 14
Send a message via Skype™ to lelievre12
Re: Kohler 6EKOD shutdown help

Yup, I had the same error with my Kohler 7EKZoF. RUNRELCOIL.
I think the fuel filter blocks, then the fuel lift pump overheats and shorts. In my case the terminal on the 20 amp fuse also melted. This in turn cuts power on F2/F2A wire. Main ADC controller then dies.

So change your fuel filters often and carry a spare lift pump. Or if your fuel tanks are above the genset you can disconnect the lift pump, you don’t need it.

If your controller goes dead then check for 12V on the F2A wire on the controller plug. If no volts then check the terminals of the 20amp fuse.

Hope this helps. my genset was only 400 hours old.
lelievre12 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Perkins 4-108 Power Loss and Shutdown RJ86 Engines and Propulsion Systems 25 19-10-2021 09:04
Air-X Wind Generator in Shutdown Mode seandepagnier Electrical: Batteries, Generators & Solar 6 17-03-2021 12:27
Unexplained Ford-Lehman Shutdown jan bogart Powered Boats 2 21-06-2010 06:13
Adler Barbour recharge after long shutdown? svnakia Plumbing Systems and Fixtures 11 23-07-2008 13:48

Advertise Here


All times are GMT -7. The time now is 18:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.