At my AC panel I turn off the main AC breaker coming into the boat. I have a short power cord with a mail end on each end. I plug one onto my 1000W inverter and the other end into one of the boat's outlet. This energizes all the outlets etc on that particular circuit
In my case I only have one AC circuit so now all my outlets are hot. I have a cap that I put over the main breaker that reminds me to disconnect the cords on the inverter before I hook up to shore power.
searenity38 is offline   Reply With Quote
Old 25-01-2021, 11:37   #32
Registered User
 
LostDog88's Avatar

Join Date: Dec 2020
Location: Tacoma, WA
Boat: IN Process
Posts: 49
Talking Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by searenity38 View Post
At my AC panel I turn off the main AC breaker coming into the boat. I have a short power cord with a mail end on each end. I plug one onto my 1000W inverter and the other end into one of the boat's outlet. This energizes all the outlets etc on that particular circuit
In my case I only have one AC circuit so now all my outlets are hot. I have a cap that I put over the main breaker that reminds me to disconnect the cords on the inverter before I hook up to shore power.
While I did consider this as an option, as an electrician (on land) I can tell you it is never a good idea to create a "dead mans" plug.

But I have done it before and it works perfectly.

I'm looking for more of an auto situation.
https://www.cruisersforum.com/images/icons/icon10.gif
LostDog88 is offline   Reply With Quote
Old 25-01-2021, 11:41   #33
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Adding Inverter to Boat Electrical system

Wanting it to be automatic is why I built the sub-panel setup I did. The loads on the inverter sub-panel automatically transfer to inverter power (via the inverter's transfer switch) when power on the L1 bus drops offline. I still have to manually select between the shore inlets and the generator for power source, but the inverter operation is automatic.
rslifkin is offline   Reply With Quote
Old 25-01-2021, 15:21   #34
Registered User

Join Date: Nov 2015
Posts: 212
Re: Adding Inverter to Boat Electrical system

My first thought was that you need a power supply selector switch between the AC supply and your fuse board. This should be a three position switch with a off position between the supply choices.

On reflection I think what you really need is an electrician.

AC power from inverters or generators is dangerous. On boats it has the added complication of running without an earth line. Above earth power supplies need to be set up with bonding between all AC devices including the supply and modern safety standards would use an RCD as well.
john manning is offline   Reply With Quote
Old 25-01-2021, 15:34   #35
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by searenity38 View Post
At my AC panel I turn off the main AC breaker coming into the boat. I have a short power cord with a mail end on each end. I plug one onto my 1000W inverter and the other end into one of the boat's outlet. This energizes all the outlets etc on that particular circuit
In my case I only have one AC circuit so now all my outlets are hot. I have a cap that I put over the main breaker that reminds me to disconnect the cords on the inverter before I hook up to shore power.
That leaves none of the outlets protected by a breaker. Not a good idea.
mitiempo is offline   Reply With Quote
Old 25-01-2021, 15:41   #36
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by mitiempo View Post
That leaves none of the outlets protected by a breaker. Not a good idea.
With only a 1000w inverter, assuming it has overload protection, it's not a problem. The outlet circuit is likely good for 15 or 20 amps, so the inverter can't put out enough to overload the wiring.

Of course, the inverter plugged into outlet setup isn't a good idea for plenty of other reasons.
rslifkin is offline   Reply With Quote
Old 25-01-2021, 15:48   #37
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by rslifkin View Post
With only a 1000w inverter, assuming it has overload protection, it's not a problem. The outlet circuit is likely good for 15 or 20 amps, so the inverter can't put out enough to overload the wiring.

Of course, the inverter plugged into outlet setup isn't a good idea for plenty of other reasons.
Overload protection in an inverter will protect the inverter. Not whoever is using the outlet. If it has a GFCI there is protection to the user but if not it doesn't.
mitiempo is offline   Reply With Quote
Old 25-01-2021, 16:02   #38
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by mitiempo View Post
Overload protection in an inverter will protect the inverter. Not whoever is using the outlet. If it has a GFCI there is protection to the user but if not it doesn't.
Very true. But many boats have non GFCI outlets anyway.
rslifkin is offline   Reply With Quote
Old 25-01-2021, 16:14   #39
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by rslifkin View Post
Very true. But many boats have non GFCI outlets anyway.
Yes but the outlets are on a breaker. That is the safety.

If the inverter has a GFCI the outlets it is plugged in to will be protected. If not they will not be protected.

Powering outlets with a double male cord from the inverter the current does not go through the breaker on the panel.
mitiempo is offline   Reply With Quote
Old 28-01-2021, 03:36   #40
Registered User

Join Date: Mar 2012
Location: On board in Leros, Greece
Boat: Hunter Legend 420 Passage
Posts: 863
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by LostDog88 View Post
...How the heck do ya'll wire in an inverter so that the outlets you use when plugged into shore power work when you are not on shore power?
Quote:
Originally Posted by rslifkin View Post
In that case, choose an inverter with a built in transfer switch. Personally, I'm putting in a Victron Multiplus 12/2000/80.
The advantages of the Multiplus system needs to be further explained because it can solve all of the OPs problems without any external switches or major wiring changes to the AC sockets.

Charger/inverters like the Victron MultiPlus, and also the Mastervolt Combi, can supplement the shore power AC by producing AC from the batteries, via the inverter, when extra load is needed. They do this by always staying in sync with the shorepower phase.

This is called "Power Assist", so the unit is installed in “series” or "in line" with the shorepower circuit. This way all AC outlet sockets get either shore power or inverter power automatically. For example, where pontoons have 10 amp breakers and 12 amps is demanded by the boat loads it can supply the extra 2 amps AC load from the batteries. This happens in milliseconds without blowing the horepower breakers. When the load falls below 10 amps it goes back to charging the batteries.
sailinglegend is offline   Reply With Quote
Old 28-01-2021, 05:03   #41
Registered User

Join Date: Oct 2011
Location: Moss, Norway
Boat: 35' Jeanneau Espace 1000 DL
Posts: 354
Re: Adding Inverter to Boat Electrical system

You need an electrician! There are lots of ways to kill yourself , or others , if you get this wrong.

You need to pay special attention to the earth to neutral connections. Earth connected to neutral is called TN (terra neutral). Both most inverters and most gensets have neutral connected to earth, BUT you need to be absolutely shure of this. my paguro generator was wired to earth at the center of generator coil . I had disconnect this , and connect earth to neutral outside the genset. You should only have neutral connected to earth at one single spot, at any given time. You must have a GFCI breaker between the earth-neutral connection and the panel/outlets.

Even a "working" system can be dangerous if you connect to a shorepower connection with inverted polarity, generator with IT (isolated terra) output, or a floating earth.

Get an electrician to: Install a isolation transformer, and wire it in TN fashion, to match the earth wiring in your inverter.
Wire your generator in TN (terra neutral) fashion, same as your inverter.

Now, all of your A/C sources has the same earth system , earth connected to neutral. The isolation transformer isolates the boat from earth-faults on land, and takes care of the dreaded inverted polarity.

.manitu
__________________
Is it possible that my sole purpose in life is to act as a warning to others?
manitu is offline   Reply With Quote
Old 28-01-2021, 05:33   #42
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,314
Re: Adding Inverter to Boat Electrical system

Quote:
Originally Posted by sailinglegend View Post
The advantages of the Multiplus system needs to be further explained because it can solve all of the OPs problems without any external switches or major wiring changes to the AC sockets.

Charger/inverters like the Victron MultiPlus, and also the Mastervolt Combi, can supplement the shore power AC by producing AC from the batteries, via the inverter, when extra load is needed. They do this by always staying in sync with the shorepower phase.

This is called "Power Assist", so the unit is installed in “series” or "in line" with the shorepower circuit. This way all AC outlet sockets get either shore power or inverter power automatically. For example, where pontoons have 10 amp breakers and 12 amps is demanded by the boat loads it can supply the extra 2 amps AC load from the batteries. This happens in milliseconds without blowing the horepower breakers. When the load falls below 10 amps it goes back to charging the batteries.

In my case I explicitly disabled that feature. I'm only powering outlets and a couple of lights through the inverter, so it won't cover my big draws like the water heater, A/C, electric stove, etc. So the assist isn't very useful to me.

I've got twin 50A / 125V shore power and the inverter only part of 1 of those legs. If I'm at a dock with twin 30A, managing power to stay within that is no big deal. If I'm stuck with a single 30A, then I'm pretty limited, but the inverter assist wouldn't be all that helpful. I just end up firing up the generator if I need more power for a little while (6.5kw, so 54 amps total to distribute however I want across the 2 legs).
rslifkin is offline   Reply With Quote
Reply

Tags
boat, cal, electric, electrical, electrical system, inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Adding inverter/charger pequod Electrical: Batteries, Generators & Solar 5 20-01-2017 23:28
Adding Solar Panels and Inverter Buchido Electrical: Batteries, Generators & Solar 1 02-12-2016 23:07
Adding water system to my commercial fishing boat. polyurea Liveaboard's Forum 15 08-01-2015 17:45
Complicated Electrical Question - Good Puzzle for You Electrical Geniuses Dockhead Electrical: Batteries, Generators & Solar 36 07-09-2010 06:14
Marine Electrical Gear For sale Trace Inverter, switches Sea Stewards Classifieds Archive 0 07-04-2008 12:06

Advertise Here


All times are GMT -7. The time now is 21:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.