Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
Cure is 48v dc genset .
A friend did that to his 38ft mono . Only a small Fla bank and a 5k military surplus 48v dc generator.
Like this would work

[url]https://polarpower.com/products/dc-generators/8080y-40205-diesel-dc-generator/[/url

You may need 2 on the cat.
Those are too small. I'm likely going with a 20kw and a 10kw, though there are some arguments to go with just one 20kw, but I like redundancy.
Jatar is offline   Reply With Quote
Old 19-05-2019, 09:34   #92
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,179
Re: Lithium battery C-rate question

Quote:
Originally Posted by Jatar View Post
Those are too small. I'm likely going with a 20kw and a 10kw, though there are some arguments to go with just one 20kw, but I like redundancy.
I posted a new link to a bigger genset but it didn't take so here is the new link

https://polarpower.com/products/dc-g.../8220y-3tnv88/
this link is for the 15k unit.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 19-05-2019, 10:07   #93
Registered User

Join Date: Feb 2016
Posts: 35
Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
I posted a new link to a bigger genset but it didn't take so here is the new link

https://polarpower.com/products/dc-g.../8220y-3tnv88/
this link is for the 15k unit.
I am already familiar with Polarpower, however, the two I'm interested in are these:

https://polarpower.com/products/dc-g...s/8340p-40415/
https://polarpower.com/products/dc-g...rs/8220i-3ca1/
Jatar is offline   Reply With Quote
Old 19-05-2019, 11:03   #94
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,179
Re: Lithium battery C-rate question

Quote:
Originally Posted by Jatar View Post
I am already familiar with Polarpower, however, the two I'm interested in are these:

https://polarpower.com/products/dc-g...s/8340p-40415/
https://polarpower.com/products/dc-g...rs/8220i-3ca1/
those look great I just posted the one that in individually would run st e system and in tandem would reduce the overall fuel consumption .
On lower rpm 15kw and about 3/4 gph at the higher rpm 18kw at 1 gph
Would make weight distribution easier as well
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 19-05-2019, 11:16   #95
Registered User

Join Date: Feb 2016
Posts: 35
Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
those look great I just posted the one that in individually would run st e system and in tandem would reduce the overall fuel consumption .
On lower rpm 15kw and about 3/4 gph at the higher rpm 18kw at 1 gph
Would make weight distribution easier as well
I originally considered that (and haven't ruled it out) but I like the idea of running only one generator and having it supply enough power to drive both motors at around 6 knots, with some power also left over to charge batteries.

The second 10 kw is there for times when I don't need to power the motors (like at anchor) but need to generate some power. I don't have to fire up a bigger generator.

In an emergency, together, the two supply enough power to run both motors at full power for as long as I have diesel fuel.

I'd love to hear counter arguments to this setup, as I have not fully decided on this yet. Right now, the three options I am considering are:

1) A 20kw plus a 10kw generator.
2) Two 15kw generators.
3) One 20kw generator (no redundancy, but reduced space needs and less initial cost, weight, and maintenance time and money).

I considered a single 30kw, but they are just too heavy.
Jatar is offline   Reply With Quote
Old 19-05-2019, 11:40   #96
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,179
Re: Lithium battery C-rate question

Quote:
Originally Posted by Jatar View Post
I originally considered that (and haven't ruled it out) but I like the idea of running only one generator and having it supply enough power to drive both motors at around 6 knots, with some power also left over to charge batteries.

The second 10 kw is there for times when I don't need to power the motors (like at anchor) but need to generate some power. I don't have to fire up a bigger generator.

In an emergency, together, the two supply enough power to run both motors at full power for as long as I have diesel fuel.

I'd love to hear counter arguments to this setup, as I have not fully decided on this yet. Right now, the three options I am considering are:

1) A 20kw plus a 10kw generator.
2) Two 15kw generators.
3) One 20kw generator (no redundancy, but reduced space needs and less initial cost, weight, and maintenance time and money).

I considered a single 30kw, but they are just too heavy.
well I'm a navy engineer so two 15kw units the o Crap redundancy aspect.
You just need a bit of extra at anchor that's what a Honda is for.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 19-05-2019, 13:24   #97
Registered User

Join Date: Feb 2016
Posts: 35
Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
well I'm a navy engineer so two 15kw units the o Crap redundancy aspect.
You just need a bit of extra at anchor that's what a Honda is for.
What does "the o Crap" mean?
Jatar is offline   Reply With Quote
Old 19-05-2019, 13:33   #98
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,179
Re: Lithium battery C-rate question

Quote:
Originally Posted by Jatar View Post
What does "the o Crap" mean?
one gen failure you would still be fully operational with the other one at max output.
That way a failure wouldn't prematurely end your cruise for repairs.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 19-05-2019, 13:45   #99
Registered User

Join Date: Feb 2016
Posts: 35
Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
one gen failure you would still be fully operational with the other one at max output.
That way a failure wouldn't prematurely end your cruise for repairs.
Well, not quite. Full max output on my cat means I need 30kw, not 15kw (2 SD15 servoprop motors, 15kw each).

However, yes, I can get along on 15kw, for a cruising speed of about 6 knots.

However, the issue is, if I run just one 15kw generator to motor at 6 knots, nothing is going back into my batteries. So, to motor and charge, I'd have to run two generators, both 15kw.

On the other hand, if I have one 20kw generator, I can motor and charge with only one generator running.

The second 10kw generator is to boost that power to 30kw for max. thrust, in an emergency. Or, if the 20kw breaks, I can still motor on the 10kw (yes, at a reduced speed of maybe 4 knots) but it will get me back to shore. However, most of the time, I would only have to run one generator.

As for a third Honda generator... then I would have to care for three generators, and, that Honda is gas powered. I am a diesel/electric boat, I don't want to carry more gas. The dingy gas is bad enough. On top of that, the Honda can't possibly put out enough power to run my A/C, etc. A 10kw would do all that easily.
Jatar is offline   Reply With Quote
Old 19-05-2019, 14:41   #100
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,179
Re: Lithium battery C-rate question

Quote:
Originally Posted by Jatar View Post
Well, not quite. Full max output on my cat means I need 30kw, not 15kw (2 SD15 servoprop motors, 15kw each).

However, yes, I can get along on 15kw, for a cruising speed of about 6 knots.

However, the issue is, if I run just one 15kw generator to motor at 6 knots, nothing is going back into my batteries. So, to motor and charge, I'd have to run two generators, both 15kw.

On the other hand, if I have one 20kw generator, I can motor and charge with only one generator running.

The second 10kw generator is to boost that power to 30kw for max. thrust, in an emergency. Or, if the 20kw breaks, I can still motor on the 10kw (yes, at a reduced speed of maybe 4 knots) but it will get me back to shore. However, most of the time, I would only have to run one generator.

As for a third Honda generator... then I would have to care for three generators, and, that Honda is gas powered. I am a diesel/electric boat, I don't want to carry more gas. The dingy gas is bad enough. On top of that, the Honda can't possibly put out enough power to run my A/C, etc. A 10kw would do all that easily.
sounds well planned out then looking forward to the build thread and associated pictures .
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 19-05-2019, 15:47   #101
Registered User

Join Date: Feb 2016
Posts: 35
Re: Lithium battery C-rate question

Quote:
Originally Posted by newhaul View Post
sounds well planned out then looking forward to the build thread and associated pictures .
I'll document the whole thing on video and post it when the time comes. Thank you for offering your suggestions, nothing is yet written in stone, I'm just weighing possibilities up until I buy. Fortunately (or unfortunately, depending on how you look at it) I have about three years to get my ducks in a row before I start my build. I'm waiting to retire from my job, so that sets my timetable. Hopefully, some better batteries come along in that time, but we'll see.
Jatar is offline   Reply With Quote
Old 19-05-2019, 16:53   #102
Registered User

Join Date: Aug 2011
Posts: 142
Re: Lithium battery C-rate question

Here's an Oceanvolt Cat walk through with owners comments:
Part 1
https://youtu.be/o6kOvjS1ytE

Part 2
https://youtu.be/nchKhM_TxYk
Go Wildcats is offline   Reply With Quote
Old 19-05-2019, 19:08   #103
Registered User

Join Date: Sep 2015
Posts: 445
Re: Lithium battery C-rate question

One nice advantage of a 48VDC setup is that you can use it for your house energy bank as well. I didn’t notice if you already factored that into your demand calcs... but your bank could be a good bit bigger, and I know I would prefer it.

I like the 20kw+10kw gen sets, assuming they work together like you describe (no idea). It’s better to run one generator at nearly full bore then to have one loafing along at half power.
nebster is offline   Reply With Quote
Old 19-05-2019, 20:54   #104
Registered User

Join Date: Jan 2014
Location: Coffs Harbour, NSW
Boat: FreeFlow 50 cat
Posts: 1,337
Re: Lithium battery C-rate question

If you look at your OV speed/resistance curves on your proposal, you may notice that there is not much difference between running the SD15 at 75% ie 10 kW, compared to full power. Diminishing returns. So your 20kW DC genset feeding 10 to each motor is quite reasonable.

As for redundancy on the DC genset, I assume you're in the US, so local PolarPower is the go to option. Suggest to Research their field performance wrt reliability and MTBF if you can. Are they used in any applications by military or telecommunications for remote location, continuous unattended operation?

We were lucky in Australia having a local engineering company making the most reliable DC gensets we could find worldwide, so went with their 16kW Eniquest which puts out 15kW continuous. I believe they have never had a failure of any of their gensets in over 15 years!

If you pick the right DC Genset, and you are absolutely diligent with feeding it clean air and fuel ( 2 micron filtering) and change oil religiously, and you can monitor oil temp, water temp etc., you might reconsider the redundancy aspect on this item vs weight/cost/maintenance penalty.

With regen and enough solar, your daily house loads should be well and truly covered except for more than say 4 days in a row of heavy cloud cover, if at anchor.


Sent from my iPad using Cruisers Sailing Forum
BigBeakie is offline   Reply With Quote
Old 23-05-2019, 01:01   #105
Registered User

Join Date: Nov 2016
Posts: 97
Re: Lithium battery C-rate question

Did you look into the Torqeedo batteries ?
https://www.torqeedo.com/us/en-us/pr...-/2104-00.html

Not LFP (BMW EV technology), must also more energy density, and already used on quite a few sailboats.
yvest is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tesla Lithium battery question. DeepFrz Lithium Power Systems 132 14-09-2018 15:15
AC battery charger for AGM start battery and Lithium bank exMaggieDrum Electrical: Batteries, Generators & Solar 75 19-06-2018 14:35
Lithium Ion Breakthrough - forgetful-scientists-accidentally-quadruple-lithium-ion-ba zboss Electrical: Batteries, Generators & Solar 8 22-08-2015 23:35
A Quick Question Re: Fast Battery Discharge Rate With Solar. monte Electrical: Batteries, Generators & Solar 29 28-06-2014 08:08
Charge Acceptance Rate as Proxy for Battery Health? SVNeko Electrical: Batteries, Generators & Solar 1 16-06-2014 13:00

Advertise Here


All times are GMT -7. The time now is 14:11.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.